I don't know Ron, you're going too fast. I like plain old water ready to go 
more than built-in contingencies. I'm still wondering how you know I get home 
from work, eat cold chicken, forget to watch The State of the Union, cool the 
beer on the back porch, etc ...

> On Jan 29, 2014, at 8:53 PM, "rongreenman ." <[email protected]> wrote:
> 
> What does a couple of minutes mean if that contingency is built into the
> design. Isn't the design area essentially the area we have agreed to lose
> relative to the cost of a system. If zero is the goal you've already failed
> because there can't be a fire without something (the fuel) being damaged.
> So we are always sacrificing something, and that is a design parameter. If
> I per code have to increase the design area by 30% for a dry system I'm
> agreeing that the conditions of risk, considering costs, is acceptable. If
> I have cold and can't afford loss I can use a high speed deluge system with
> spark detection, and all the high costs associated with it and have the
> absolute minimal FIRE damage. Now we can talk water damage. Oops. And one
> last question. Why  is the time from ignition to a wet head going off
> acceptable, but two more minutes (stated time) means fully engulfed and
> total loss? Is there magic involved?
> 
> 
> On Wed, Jan 29, 2014 at 6:41 PM, rongreenman . <[email protected]>wrote:
> 
>> Brad,
>> 
>> If you think a compressor is too much of a waste of energy then I'd
>> suggest getting rid of your car, going to bed at sundown, eating cold food,
>> turning the thermostat down to never go on, etc. Waste is using unnecessary
>> resources. That's a value judgement. Perhaps the cost of running a
>> compressor is less a cost than the potential of killing or maiming someone,
>> rolling multiple trucks to fight a post explosion fire, lots of land-fill
>> debris to process, lots of water expended and then needing processing, and
>> the materials to rebuild. Then there's the lawyers, and the lawyers, and
>> the lawyers, and the lawyers to pay for. Did I mention the costly lawyers?
>> 
>> 
>> On Wed, Jan 29, 2014 at 5:49 PM, Brad Casterline 
>> <[email protected]>wrote:
>> 
>>> I'm sure future head makers could come up with an RTI so good that 20
>>> seconds after Van Dame stuck a lit cigarette to it with chewing gum every
>>> head in the place would be ready to flow, but what good is that if the
>>> water takes 2 minutes to get there or the stuff that is right there is
>>> mixed with fuel?
>>> 
>>>> On Jan 29, 2014, at 7:27 PM, Brad Casterline <[email protected]>
>>> wrote:
>>>> 
>>>> Andy, I imagine a Dry System air compressor kicking on and off when
>>> it's 90F and I think waste of energy and an expansion chamber on an AF
>>> system only needed when it's hot as a waste of money. Freeze protection is
>>> only needed a few months a year I most places. We need a 3rd option!
>>>> 
>>>>> On Jan 29, 2014, at 6:55 PM, Andy <[email protected]> wrote:
>>>>> 
>>>>> Mixing was from years past. I believe the reports. I just passed on a
>>> job because I would only do a dry system.
>>>>> Andy
>>>>> 
>>>>> 
>>>>> 
>>>>>> On Jan 29, 2014, at 7:37 PM, Brad Casterline <[email protected]>
>>> wrote:
>>>>>> 
>>>>>> No Scott please don't tell me how it ends, I have not seen it yet ;)
>>> seriously, I saw your name on that final report- are you totally Anti Anti
>>> freeze now, no if ands or buts?
>>>>>> 
>>>>>>> On Jan 29, 2014, at 6:26 PM, Scott A Futrell <[email protected]>
>>> wrote:
>>>>>>> 
>>>>>>> A child lit a couch on fire with matches and the sprinkler operated
>>> with the resulting fireball injuring her and her mother.  Official damage
>>> report: limited to point of origin, except for signs and damage from
>>> explosion - windows blown out remote from the ignition.
>>>>>>> 
>>>>>>> Do we need to say more Brad?
>>>>>>> 
>>>>>>> Scott Futrell
>>>>>>> 
>>>>>>> (763) 425-1001 x12 Office
>>>>>>> (612) 759-5556 Cell
>>>>>>> 
>>>>>>> 
>>>>>>> 
>>>>>>> -----Original Message-----
>>>>>>> From: [email protected] [mailto:
>>> [email protected]] On Behalf Of Brad
>>> Casterline
>>>>>>> Sent: Wednesday, January 29, 2014 5:43 PM
>>>>>>> To: [email protected]
>>>>>>> Subject: Re: NFPA 25 & Antifreeze Comment(s) RETORT
>>>>>>> 
>>>>>>> I doubt it offends anyone. I think the biggest factor is the size of
>>> the fire-- I think I could could set a wadded up pile of shop drawings on
>>> fire ( appropriate for many jobs I drew) and put the fire out with 100% AF.
>>> But I would not want to pour it out on 30,000, 100 watt light bulbs :)
>>>>>>> 
>>>>>>>> On Jan 29, 2014, at 5:34 PM, Andy-Johnston <
>>> [email protected]> wrote:
>>>>>>>> 
>>>>>>>> After reading my last post. It was not ment to be continuous. Only
>>> express my fears of the short cuts the installers may take in the field.
>>>>>>>> Not ment to offend.
>>>>>>>> Andy
>>>>>>>> 
>>>>>>>> -------- Original message --------
>>>>>>>> From: Brad Casterline <[email protected]>
>>>>>>>> Date: 01/29/2014  12:51 PM  (GMT-05:00)
>>>>>>>> To: [email protected]
>>>>>>>> Subject: RE: NFPA 25 & Antifreeze Comment(s) RETORT
>>>>>>>> 
>>>>>>>> Good point, I guess for pre-mixed we would not, we would just keep
>>>>>>>> pumping it in until it was full, never mind, thanks Roland...
>>>>>>>> 
>>>>>>>> -----Original Message-----
>>>>>>>> From: Roland Huggins [mailto:[email protected]]
>>>>>>>> Sent: Wednesday, January 29, 2014 11:41 AM
>>>>>>>> To: [email protected]
>>>>>>>> Subject: Re: NFPA 25 & Antifreeze Comment(s) RETORT
>>>>>>>> 
>>>>>>>> HUH????  What does the system volume have to do with it?
>>>>>>>> 
>>>>>>>> 
>>>>>>>> Roland Huggins, PE - VP Engineering
>>>>>>>> American Fire Sprinkler Assn.       ---      Fire Sprinklers Saves
>>> Lives
>>>>>>>> Dallas, TX
>>>>>>>> http://www.firesprinkler.org
>>>>>>>> 
>>>>>>>> 
>>>>>>>> 
>>>>>>>> 
>>>>>>>> 
>>>>>>>> On Jan 28, 2014, at 6:52 PM, Brad Casterline <
>>> [email protected]>
>>>>>>>> wrote:
>>>>>>>> 
>>>>>>>>> And this focus on 'percent by volume' has got to be the silliest
>>>>>>>>> aspect of
>>>>>>>> this whole mess, as if we know the exact cubic feet of the inside of
>>>>>>>> all the pipe and fittings ;)
>>>>>>>> 
>>>>>>>> _______________________________________________
>>>>>>>> Sprinklerforum mailing list
>>>>>>>> [email protected]
>>>>>>>> 
>>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl
>>>>>>>> er.org
>>>>>>>> 
>>>>>>>> _______________________________________________
>>>>>>>> Sprinklerforum mailing list
>>>>>>>> [email protected]
>>>>>>>> 
>>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl
>>>>>>>> er.org _______________________________________________
>>>>>>>> Sprinklerforum mailing list
>>>>>>>> [email protected]
>>>>>>>> 
>>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl
>>>>>>>> er.org
>>>>>>> _______________________________________________
>>>>>>> Sprinklerforum mailing list
>>>>>>> [email protected]
>>>>>>> 
>>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>>>>>>> _______________________________________________
>>>>>>> Sprinklerforum mailing list
>>>>>>> [email protected]
>>>>>>> 
>>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>>>>>> _______________________________________________
>>>>>> Sprinklerforum mailing list
>>>>>> [email protected]
>>>>>> 
>>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>>>>> _______________________________________________
>>>>> Sprinklerforum mailing list
>>>>> [email protected]
>>>>> 
>>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>>>> _______________________________________________
>>>> Sprinklerforum mailing list
>>>> [email protected]
>>>> 
>>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>>> _______________________________________________
>>> Sprinklerforum mailing list
>>> [email protected]
>>> 
>>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>>> 
>> 
>> 
>> 
>> --
>> Ron Greenman
>> Instructor
>> Fire Protection Engineering Technology
>> Bates Technical College
>> 1101 So. Yakima Ave.
>> Tacoma, WA 98405
>> 
>> [email protected]
>> 
>> http://www.bates.ctc.edu/fireprotection/
>> 
>> 253.680.7346
>> 253.576.9700 (cell)
>> 
>> Member:
>> ASEE, SFPE, ASCET, NFPA, AFSA, NFSA, AFAA, NIBS, WSAFM, WFC, WFSC
>> 
>> They are happy men whose natures sort with their vocations. -Francis
>> Bacon, essayist, philosopher, and statesman (1561-1626)
>> 
>> A problem well stated is a problem half solved. -Charles F. Kettering,
>> inventor and engineer (1876-1958)
>> 
> 
> 
> 
> -- 
> Ron Greenman
> Instructor
> Fire Protection Engineering Technology
> Bates Technical College
> 1101 So. Yakima Ave.
> Tacoma, WA 98405
> 
> [email protected]
> 
> http://www.bates.ctc.edu/fireprotection/
> 
> 253.680.7346
> 253.576.9700 (cell)
> 
> Member:
> ASEE, SFPE, ASCET, NFPA, AFSA, NFSA, AFAA, NIBS, WSAFM, WFC, WFSC
> 
> They are happy men whose natures sort with their vocations. -Francis Bacon,
> essayist, philosopher, and statesman (1561-1626)
> 
> A problem well stated is a problem half solved. -Charles F. Kettering,
> inventor and engineer (1876-1958)
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to