My Bad, Mike!

jgamble do you have anything definitive you could mail me off Forum? I found
a bit of info-- might be old; what I saw was still in the questionable
phase.

Has anyone designed a Circulating Closed-Loop System per NFPA 13?. We cannot
use them where the temp is less than 40F, but maintaining 40F in some spaces
a few months a year combined with clean wet sprinklers might be a 3rd option
(for residential) to AF and DRY.

Brad     

-----Original Message-----
From: Mike Cabral [mailto:[email protected]] 
Sent: Monday, February 03, 2014 11:10 AM
To: [email protected]
Cc: [email protected]
Subject: Re: Calcium Chloride Loops?

I was referring to the mfg. of the CPVC. Sorry for the confusion.  

Mike C

Sent from my iPhone

> On Feb 2, 2014, at 9:47 PM, Brad Casterline <[email protected]>
wrote:
> 
> Reality! I don't think there is a specific manufacturer because if there
were they would have been Sponsoring a lot of tests the last few years. This
is the stuff used on roads in Winter- it seems to dislike evergreen trees
though. There is a bit more info I think if we search the archives for
"Calcium Chloride antifreeze protection". We have just GOT to find a 3rd
alternative to AF and DRY for residential, in my view.
> 
>> On Feb 2, 2014, at 9:19 PM, Mike Cabral <[email protected]>
wrote:
>> 
>> Don't know about compatibility with CPVC that would need to be checked
out with the manufacture. However, you still need to screw the head into a
fitting and then there is the seal on the sprinkler head. In my view this is
a non starter. 
>> 
>> Mike
>> 
>> Sent from my iPhone
>> 
>>> On Feb 2, 2014, at 7:20 PM, Brad Casterline <[email protected]>
wrote:
>>> 
>>> Thanks again by the way Mike . And from experience in New Zealand it was
pointed out that it can wreak havoc (corrosion) on steel/iron. And Ron G
questioned the MSDS (but the Navy eats it up, and 22 to zip Seahawks at the
half?)
>>> The point is good luck and fortune getting 'regular' antifreeze U.L.
Listed now...
>>> 
>>>> On Feb 2, 2014, at 6:15 PM, Brad Casterline <[email protected]>
wrote:
>>>> 
>>>> Ya Mike this is one of the good responses I mentioned and the main
drawback I have brooded over-  we can put rovers on Mars but we can't keep
NaCl2 in pipe? How about CPVC?
>>>> 
>>>>> On Feb 2, 2014, at 5:56 PM, Mike Cabral <[email protected]>
wrote:
>>>>> 
>>>>> As I recall Calcium Chloride is very hard to contain. It will weep out
of perfect threaded connection, packing glands etc. Very slippery stuff. 
>>>>> 
>>>>> Mike C 
>>>>> 
>>>>> Sent from my iPhone
>>>>> 
>>>>>> On Feb 2, 2014, at 12:19 PM, Brad Casterline
<[email protected]> wrote:
>>>>>> 
>>>>>> In Sep 2010 I posted 'Calcium Chloride Loops'?
>>>>>> Somewhere along the line the thread got renamed, but there was some
good responses exposing the drawbacks to it replacing combustible antifreeze
first.
>>>>>> My (lack of) money is on overcoming these drawbacks beating any U.L.
Listed alcohol based fluid to market-- for residential anyway.
>>>>>> I imagine 1) no city tap hence no tapping fee or BFP, 2) freeze
protection to -40F, 3) small Gallon high PSI pressure tanks hence K=2.8, 4)
limit the heat release rate of the most challenging residential fire to 1.6
MW , meaning the wet stuff is on the red stuff at about 10 seconds for a
small room and maybe twice that for a big room.
>>>>>> If I were a maker of auto sprinkler system things (Residential
Department) this is the direction I would be looking.
>>>>>> 
>>>>>> Brad
>>>>>> _______________________________________________
>>>>>> Sprinklerforum mailing list
>>>>>> [email protected]
>>>>>>
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>>>>> _______________________________________________
>>>>> Sprinklerforum mailing list
>>>>> [email protected]
>>>>>
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>>>> _______________________________________________
>>>> Sprinklerforum mailing list
>>>> [email protected]
>>>>
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>>> _______________________________________________
>>> Sprinklerforum mailing list
>>> [email protected]
>>>
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>> _______________________________________________
>> Sprinklerforum mailing list
>> [email protected]
>>
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
>
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to