The Brits are playing around with mist for houses, and there's a whacko on
the SFPE LinkedIn site that has a product that' supposed to everything you
need, like live through the vent, by ventilating the fire.


On Mon, Feb 3, 2014 at 10:54 AM, Brad Casterline <[email protected]>wrote:

> My Bad, Mike!
>
> jgamble do you have anything definitive you could mail me off Forum? I
> found
> a bit of info-- might be old; what I saw was still in the questionable
> phase.
>
> Has anyone designed a Circulating Closed-Loop System per NFPA 13?. We
> cannot
> use them where the temp is less than 40F, but maintaining 40F in some
> spaces
> a few months a year combined with clean wet sprinklers might be a 3rd
> option
> (for residential) to AF and DRY.
>
> Brad
>
> -----Original Message-----
> From: Mike Cabral [mailto:[email protected]]
> Sent: Monday, February 03, 2014 11:10 AM
> To: [email protected]
> Cc: [email protected]
> Subject: Re: Calcium Chloride Loops?
>
> I was referring to the mfg. of the CPVC. Sorry for the confusion.
>
> Mike C
>
> Sent from my iPhone
>
> > On Feb 2, 2014, at 9:47 PM, Brad Casterline <[email protected]>
> wrote:
> >
> > Reality! I don't think there is a specific manufacturer because if there
> were they would have been Sponsoring a lot of tests the last few years.
> This
> is the stuff used on roads in Winter- it seems to dislike evergreen trees
> though. There is a bit more info I think if we search the archives for
> "Calcium Chloride antifreeze protection". We have just GOT to find a 3rd
> alternative to AF and DRY for residential, in my view.
> >
> >> On Feb 2, 2014, at 9:19 PM, Mike Cabral <[email protected]>
> wrote:
> >>
> >> Don't know about compatibility with CPVC that would need to be checked
> out with the manufacture. However, you still need to screw the head into a
> fitting and then there is the seal on the sprinkler head. In my view this
> is
> a non starter.
> >>
> >> Mike
> >>
> >> Sent from my iPhone
> >>
> >>> On Feb 2, 2014, at 7:20 PM, Brad Casterline <[email protected]>
> wrote:
> >>>
> >>> Thanks again by the way Mike . And from experience in New Zealand it
> was
> pointed out that it can wreak havoc (corrosion) on steel/iron. And Ron G
> questioned the MSDS (but the Navy eats it up, and 22 to zip Seahawks at the
> half?)
> >>> The point is good luck and fortune getting 'regular' antifreeze U.L.
> Listed now...
> >>>
> >>>> On Feb 2, 2014, at 6:15 PM, Brad Casterline <[email protected]>
> wrote:
> >>>>
> >>>> Ya Mike this is one of the good responses I mentioned and the main
> drawback I have brooded over-  we can put rovers on Mars but we can't keep
> NaCl2 in pipe? How about CPVC?
> >>>>
> >>>>> On Feb 2, 2014, at 5:56 PM, Mike Cabral <[email protected]>
> wrote:
> >>>>>
> >>>>> As I recall Calcium Chloride is very hard to contain. It will weep
> out
> of perfect threaded connection, packing glands etc. Very slippery stuff.
> >>>>>
> >>>>> Mike C
> >>>>>
> >>>>> Sent from my iPhone
> >>>>>
> >>>>>> On Feb 2, 2014, at 12:19 PM, Brad Casterline
> <[email protected]> wrote:
> >>>>>>
> >>>>>> In Sep 2010 I posted 'Calcium Chloride Loops'?
> >>>>>> Somewhere along the line the thread got renamed, but there was some
> good responses exposing the drawbacks to it replacing combustible
> antifreeze
> first.
> >>>>>> My (lack of) money is on overcoming these drawbacks beating any U.L.
> Listed alcohol based fluid to market-- for residential anyway.
> >>>>>> I imagine 1) no city tap hence no tapping fee or BFP, 2) freeze
> protection to -40F, 3) small Gallon high PSI pressure tanks hence K=2.8, 4)
> limit the heat release rate of the most challenging residential fire to 1.6
> MW , meaning the wet stuff is on the red stuff at about 10 seconds for a
> small room and maybe twice that for a big room.
> >>>>>> If I were a maker of auto sprinkler system things (Residential
> Department) this is the direction I would be looking.
> >>>>>>
> >>>>>> Brad
> >>>>>> _______________________________________________
> >>>>>> Sprinklerforum mailing list
> >>>>>> [email protected]
> >>>>>>
>
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
> >>>>> _______________________________________________
> >>>>> Sprinklerforum mailing list
> >>>>> [email protected]
> >>>>>
>
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
> >>>> _______________________________________________
> >>>> Sprinklerforum mailing list
> >>>> [email protected]
> >>>>
>
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
> >>> _______________________________________________
> >>> Sprinklerforum mailing list
> >>> [email protected]
> >>>
>
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
> >> _______________________________________________
> >> Sprinklerforum mailing list
> >> [email protected]
> >>
>
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
> > _______________________________________________
> > Sprinklerforum mailing list
> > [email protected]
> >
>
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
>
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
>
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>



-- 
Ron Greenman
Instructor
Fire Protection Engineering Technology
Bates Technical College
1101 So. Yakima Ave.
Tacoma, WA 98405

[email protected]

http://www.bates.ctc.edu/fireprotection/

253.680.7346
253.576.9700 (cell)

Member:
ASEE, SFPE, ASCET, NFPA, AFSA, NFSA, AFAA, NIBS, WSAFM, WFC, WFSC

They are happy men whose natures sort with their vocations. -Francis Bacon,
essayist, philosopher, and statesman (1561-1626)

A problem well stated is a problem half solved. -Charles F. Kettering,
inventor and engineer (1876-1958)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org