Your AHJ is interpreting incorrectly.  38F is not subject to freezing.

I had this same argument the other day.  I wrote a simple equation, stamped and 
sealed it and submitted it.  I finally received my approval.

Using dry sprinklers when they are not necessary is not good fire protection in 
my opinion. Installing dry sprinklers is doing the owner a disservice.

John

Fire sprinklers save lives

Sent from my iPad

On Jun 27, 2014, at 12:33 PM, "Bob" <[email protected]> wrote:

> Sure, 8.4.9 Dry Sprinklers.
> 8.4.9.1 Where dry sprinklers are connected to wet pipe sprinkler systems
> protecting areas subject to freezing temperatures, the minimum exposed
> length of the barrel of the dry sprinkler shall be in accordance with Table
> 8.4.9.1.
>
> This section explicitly state where subject to freezing, and 38F isn't
> subject to freezing.  However, in my case the AHJ has interpreted in the
> past that if it's not maintained at or above 40F it's subject to freezing.
>
> Thank You,
>
> Bob Knight, CET III
> 208-318-3057
> www.Firebyknight.com
>
>
>
> -----Original Message-----
> From: Sprinklerforum [mailto:[email protected]]
> On Behalf Of IPA
> Sent: Friday, June 27, 2014 1:28 PM
> To: [email protected]
> Subject: Re: Cooler Calc
>
> care to share?
>
>
> On Fri, Jun 27, 2014 at 12:16 PM, Bob <[email protected]> wrote:
>
>> Nix the last question, I just found the answer.
>>
>> Thank You,
>>
>> Bob Knight, CET III
>> 208-318-3057
>> www.Firebyknight.com
>>
>>
>>
>> -----Original Message-----
>> From: Sprinklerforum [mailto:
>> [email protected]]
>> On Behalf Of Bob
>> Sent: Friday, June 27, 2014 1:09 PM
>> To: [email protected]
>> Subject: RE: Cooler Calc
>>
>> 13 words it, in the section on dry pipe systems, at or above 40F.
>> Where do I find it that on a wet system that I don't need to apply the
>> temperature in the same way?
>>
>> Thank You,
>>
>> Bob Knight, CET III
>> 208-318-3057
>> www.Firebyknight.com
>>
>>
>>
>> -----Original Message-----
>> From: Sprinklerforum [mailto:
>> [email protected]]
>> On Behalf Of John Denhardt
>> Sent: Friday, June 27, 2014 1:01 PM
>> To: <[email protected]>
>> Subject: Re: Cooler Calc
>>
>> Agree - we had done numerous cooler boxes and never have had an issue.
>> Usually the stored products will be damaged if they freeze.  In many
>> case, the refrigeration unit shuts down if the temperature drops below
>> a certain set temperature; 35 degree F is typical.
>>
>> Installing dry sprinklers where they are not required or necessarily
>> is not good fire protection in my opinion.
>>
>> John
>>
>> Fire sprinklers save lives
>>
>> Sent from my iPad
>>
>> On Jun 27, 2014, at 11:54 AM, "[email protected]"
>> <[email protected]> wrote:
>>
>>> Exactly, we do 38F coolers with ESFR's. Never had a ..., I better
>>> not say
>> that might jinx it.
>>> Ron F
>>>
>>> -----Original Message-----
>>> From: Sprinklerforum
>>> [mailto:[email protected]] On Behalf Of
>>> John Denhardt
>>> Sent: Friday, June 27, 2014 11:49 AM
>>> To: <[email protected]>
>>> Subject: Re: Cooler Calc
>>>
>>> If the area is not subject to freezing, no need for dry sprinklers.
>>> NFPA
>> 13 only requires dry sprinklers or other method when the area is
>> subject to freezing AND can not be readily maintained above 40 degrees F.
>>>
>>> The above is my personal opinion .....
>>>
>>>
>>> John
>>>
>>> Fire sprinklers save lives
>>>
>>> Sent from my iPad
>>>
>>> On Jun 27, 2014, at 11:42 AM, "Bob" <[email protected]> wrote:
>>>
>>>> Ron,
>>>> The temperature is maintained at 38F.  The sprinklers used were EC
>>>> OH SR dry sprinklers.
>>>>
>>>> Thank You,
>>>>
>>>> Bob Knight, CET III
>>>> 208-318-3057
>>>> www.Firebyknight.com
>>>>
>>>>
>>>>
>>>> -----Original Message-----
>>>> From: Sprinklerforum
>>>> [mailto:[email protected]]
>>>> On Behalf Of [email protected]
>>>> Sent: Friday, June 27, 2014 12:37 PM
>>>> To: [email protected]
>>>> Subject: RE: Cooler Calc
>>>>
>>>> A couple questions. If it is a cooler why do you need dry pendent
>>>> heads? And if it has to be dry heads and they are on a wet system
>>>> the RA could still be reduced couldn't it?
>>>>
>>>> Ron F
>>>>
>>>> -----Original Message-----
>>>> From: Sprinklerforum
>>>> [mailto:[email protected]]
>>>> On Behalf Of Bob
>>>> Sent: Friday, June 27, 2014 11:29 AM
>>>> To: [email protected]
>>>> Subject: RE: Cooler Calc
>>>>
>>>> Ron,
>>>> Yes this is a remodel adding only the cooler.  The existing ceiling
>>>> demand was well above the .2 need in the cooler.
>>>>
>>>> Thank You,
>>>>
>>>> Bob Knight, CET III
>>>> 208-318-3057
>>>> www.Firebyknight.com
>>>>
>>>>
>>>>
>>>> -----Original Message-----
>>>> From: Sprinklerforum
>>>> [mailto:[email protected]]
>>>> On Behalf Of rongreenman .
>>>> Sent: Friday, June 27, 2014 12:11 PM
>>>> To: [email protected]
>>>> Subject: Re: Cooler Calc
>>>>
>>>> If the job is just the cooler then I think all the heads is
>>>> sufficient within the perimeter of the cooler. If it's a part of
>>>> the larger job you need to calc all the possible design areas. Not
>>>> knowing the layout I can't say but maybe the ceiling somewhere is a
>>>> design area, the cooler is potentially a design area, etc. But he's
>>>> nuts if he thinks you need to add other sprinklers not in the fire
>>>> area
>> to make the fire area be 1500 sqft.
>>>> Real is real. Math is math. Often the twin don't meet.
>>>>
>>>>
>>>> On Fri, Jun 27, 2014 at 11:03 AM, Mike Hill <[email protected]>
>> wrote:
>>>>
>>>>> I don't suppose that you are lucky enough to have a fire rated cooler.
>>>>>
>>>>> Common sense would say that you calculate the cooler.
>>>>>
>>>>> Common practice would say calculate the cooler and/or a 1500 sq. ft.
>>>>> area outside of the cooler.
>>>>>
>>>>> Mike Hill
>>>>>
>>>>> -----Original Message-----
>>>>> From: Sprinklerforum [mailto:
>>>>> [email protected]]
>>>>> On Behalf Of Bob
>>>>> Sent: Friday, June 27, 2014 1:47 PM
>>>>> To: [email protected]
>>>>> Subject: RE: Cooler Calc
>>>>>
>>>>> His stand is that I have one of three options that I have not used:
>>>>> (1) Density/area curves of Figure 11.2.3.1.1 in accordance with
>>>>> the density/area method of 11.2.3.2
>>>>> (2) The room that creates the greatest demand in accordance with
>>>>> the room design method of 11.2.3.3
>>>>> (3) Special design areas in accordance with 11.2.3.4
>>>>>
>>>>> Keep in mind that this is a jurisdiction that has told me in the
>>>>> past that you can't use the exceptions in 13 (this was before they
>>>>> became part of the body), and that they can't use common sense.
>>>>>
>>>>>
>>>>>
>>>>> Thank You,
>>>>>
>>>>> Bob Knight, CET III
>>>>> 208-318-3057
>>>>> www.Firebyknight.com
>>>>>
>>>>>
>>>>>
>>>>> -----Original Message-----
>>>>> From: Sprinklerforum [mailto:
>>>>> [email protected]]
>>>>> On Behalf Of Tim Stone
>>>>> Sent: Friday, June 27, 2014 11:41 AM
>>>>> To: [email protected]
>>>>> Subject: RE: Cooler Calc
>>>>>
>>>>> The Cooler is a closed in room with a space above. You calculate
>>>>> all the heads inside the cooler if less than 1500 SF. If the area
>>>>> outside the cooler is fully sprinklered then you probably have
>>>>> performed calcs already. I'd ask the AHJ to review NFPA 13.
>>>>>
>>>>> Regards,
>>>>> G. Tim Stone
>>>>>
>>>>> G. Tim Stone Consulting, LLC
>>>>> NICET Level III Engineering Technician Fire Protection Sprinkler
>>>>> Design and Consulting Services
>>>>>
>>>>>              117 Old Stage Rd. - Essex Jct., VT. 05452
>>>>> CELL: (802) 373-0638   TEL: (802) 434-2968   Fax: (802) 434-4343
>>>>>                         [email protected]
>>>>>
>>>>> -----Original Message-----
>>>>> From: Sprinklerforum [mailto:
>>>>> [email protected]]
>>>>> On Behalf Of Bob
>>>>> Sent: Friday, June 27, 2014 1:12 PM
>>>>> To: [email protected]
>>>>> Subject: Cooler Calc
>>>>>
>>>>> I have a 1,392 sf cooler.  I calc'ed the entire area of the cooler
>>>>> and submitted.  The AHJ is telling me that I need to calc
>>>>> additional sprinklers at the ceiling to have a 1500 sf design
>>>>> area.  I don't think I need to do this, I was looking at this as a
>>>>> separate fire area, and I don't see it being much different than
>>>>> not adding heads below ducts or other large obstructions.  Do I
>>>>> need to calc additional sprinklers at the ceiling for this
> application?
>>>>>
>>>>> Thank You,
>>>>>
>>>>> Bob Knight, CET III
>>>>> 208-318-3057
>>>>> www.Firebyknight.com
>>>>>
>>>>>
>>>>>
>>>>>
>>>>>
>>>>> _______________________________________________
>>>>> Sprinklerforum mailing list
>>>>> [email protected]
>>>>>
>>>>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firespr
>>>>> in
>>>>> k
>>>>> l
>>>>> er.org
>>>>>
>>>>> _______________________________________________
>>>>> Sprinklerforum mailing list
>>>>> [email protected]
>>>>>
>>>>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firespr
>>>>> in
>>>>> k
>>>>> l
>>>>> er.org
>>>>>
>>>>> _______________________________________________
>>>>> Sprinklerforum mailing list
>>>>> [email protected]
>>>>>
>>>>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firespr
>>>>> in
>>>>> k
>>>>> l
>>>>> er.org
>>>>>
>>>>> _______________________________________________
>>>>> Sprinklerforum mailing list
>>>>> [email protected]
>>>>>
>>>>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firespr
>>>>> in
>>>>> k
>>>>> l
>>>>> er.org
>>>>>
>>>>
>>>>
>>>>
>>>> --
>>>> Ron Greenman
>>>> Instructor
>>>> Fire Protection Engineering Technology Bates Technical College
>>>> 1101 So. Yakima Ave.
>>>> Tacoma, WA 98405
>>>>
>>>> [email protected]
>>>>
>>>> http://www.bates.ctc.edu/fireprotection/
>>>>
>>>> 253.680.7346
>>>> 253.576.9700 (cell)
>>>>
>>>> Member:
>>>> ASEE, SFPE, ASCET, NFPA, AFSA, NFSA, AFAA, NIBS, WSAFM, WFC, WFSC
>>>>
>>>> They are happy men whose natures sort with their vocations.
>>>> -Francis Bacon, essayist, philosopher, and statesman (1561-1626)
>>>>
>>>> A problem well stated is a problem half solved. -Charles F.
>>>> Kettering, inventor and engineer (1876-1958)
>>>> _______________________________________________
>>>> Sprinklerforum mailing list
>>>> [email protected]
>>>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firespri
>>>> nk
>>>> l
>>>> er.org
>>>>
>>>> _______________________________________________
>>>> Sprinklerforum mailing list
>>>> [email protected]
>>>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firespri
>>>> nk l er.org _______________________________________________
>>>> Sprinklerforum mailing list
>>>> [email protected]
>>>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firespri
>>>> nk
>>>> l
>>>> er.org
>>>>
>>>> _______________________________________________
>>>> Sprinklerforum mailing list
>>>> [email protected]
>>>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firespri
>>>> nk
>>>> l
>>>> er.org
>>> _______________________________________________
>>> Sprinklerforum mailing list
>>> [email protected]
>>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprin
>>> kl er.org _______________________________________________
>>> Sprinklerforum mailing list
>>> [email protected]
>>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprin
>>> kl
>>> er.org
>> _______________________________________________
>> Sprinklerforum mailing list
>> [email protected]
>>
>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl
>> er.org
>>
>> _______________________________________________
>> Sprinklerforum mailing list
>> [email protected]
>>
>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl
>> er.org
>>
>> _______________________________________________
>> Sprinklerforum mailing list
>> [email protected]
>>
>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl
>> er.org
>>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to