Thanks Ron, after rereading my own question, I meant to ask - You put a wet 
system inside the cooler with ESFR's? 
But you answered it anyway - I see you installed the the system above the 
cooler and installed 2" drops through the cooler supplying the ESFRs. 
Interesting - still a lot cheaper than ESFR dry pendents. And a lot better 
since they are not needed. I appreciate this thread, it has definitely changed 
my way of thinking about coolers situations. 

Thanks,

Bobby Gillett

Sent from my iPhone

> On Jun 28, 2014, at 5:54 PM, <[email protected]> wrote:
> 
> 38F. Yes an ESFR wet with 2" drops through the deck.
> 
> Ron fletcher Sent from my iPhone
> 
>> On Jun 28, 2014, at 3:21 PM, "Bobby Gillett" <[email protected]> wrote:
>> 
>> What temp was your beer cooler?
>> You put a wet system in with ESFR's?
>> 
>> Thank you,
>> 
>> Bobby Gillett
>> Living Water Fire Protection
>> Cantonment, FL
>> 
>> Sent from my iPhone
>> 
>>> On Jun 28, 2014, at 2:52 PM, <[email protected]> wrote:
>>> 
>>> We did a 45' high 40k sq ft beer cooler with ESFR's. After it was up and 
>>> running we put temp recorders in front of reefer units. 30' up, 15' up and 
>>> on floor. Recorded every 30 minutes for 5 days. Nothing varied more than 
>>> one degree. Some one told me that the reefer units could not produce the 
>>> BTU's needed to lower the temp to 30F. We have done many coolers with wet 
>>> systems. The only incident I remember is a head went off when a unit went 
>>> into defrost.
>>> 
>>> Ron fletcher Sent from my iPhone
>>> 
>>>> On Jun 28, 2014, at 10:14 AM, "Scott A Futrell" <[email protected]> wrote:
>>>> 
>>>> How cold is the air conditioning the space?  Are pipes and sprinklers in 
>>>> front of, or near colder air used to maintain 38 degrees?
>>>> 
>>>> Scott
>>>> 
>>>> Office: (763) 425-1001 x 12
>>>> Cell: (612) 759-5556
>>>> 
>>>> -----Original Message-----
>>>> From: Sprinklerforum 
>>>> [mailto:[email protected]] On Behalf Of Brad 
>>>> Casterline
>>>> Sent: Saturday, June 28, 2014 11:06 AM
>>>> To: [email protected]
>>>> Subject: Re: Cooler Calc
>>>> 
>>>> Maybe that's where John D's AND READILY MAINTAINED thinking comes in-- 
>>>> even after a failure like that you would have several hours before the 
>>>> pipe froze solid.
>>>> 
>>>>> On Jun 28, 2014, at 10:47 AM, Richard Mote <[email protected]> 
>>>>> wrote:
>>>>> 
>>>>> I was told about 20 years ago by someone that installs walk in coolers 
>>>>> and freezers, that the only difference between was the setting on the 
>>>>> thermostat. If the thermostat malfunctions a 38°F cooler can very quickly 
>>>>> become a freezer.   
>>>> 
>>>> _______________________________________________
>>>> Sprinklerforum mailing list
>>>> [email protected]
>>>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>>> _______________________________________________
>>> Sprinklerforum mailing list
>>> [email protected]
>>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>> _______________________________________________
>> Sprinklerforum mailing list
>> [email protected]
>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to