No such thing as a listed heat collector.

NFPA 13 simply calls out the use of a sidewall, it does not state horizontal or vertical for type to be used.

You may need to ask him where the requirement for a VERTICAL sidewall is indicated.

Travis Mack, SET
MFP Design, LLC
2508 E Lodgepole Drive
Gilbert, AZ 85298
480-505-9271
fax: 866-430-6107
email:[email protected]

http://www.mfpdesign.com
https://www.facebook.com/pages/MFP-Design-LLC/92218417692
Send large files to us via: https://www.hightail.com/u/MFPDesign

On 7/6/2015 11:20 AM, Rocci Cetani 3 wrote:
I have a FM questioning the use of horizontal sidewall sprinklers (he thinks
it should be a vertical sidewall) with no heat collectors @ 15' AFF...NFPA
13 2013   17.1.4.1  only states a sidewall sprinkler pointed in the
direction of the column @ 15' AFF.  Any suggestions?

Rocci Cetani III, CET

Lead Designer

Water-Based Fire Protections Systems Layout, Nicet Level III

Northern California Fire Protection Services Inc.

16840 Joleen Way Bldg. A

Morgan Hill, CA 93037

P-(408) 776-1580 EXT.111

F-(408) 776-1590

C- (408) 595-3906

[email protected]

www.norcalfire.com <http://www.norcalfire.com/>

CONFIDENTIALITY NOTICE: This message and any document accompanying it may
contain confidential information

belonging to the sender. The information is intended only for the use of
individual or entity named above. If you are not the intended recipient, or
the employee or agent responsible to deliver this message to the intended
recipient, you are hereby notified that any disclosure, copying or taking of
any action in reliance on the contents of this information is strictly
prohibited. If you have received this transmission in error, please
immediately notify us by telephone to arrange for return of the documents.

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to