Where does it say the sidewall is pointed up? I have only seen these
installed in the horizontal position for this application.
Any steel columns shall be protected by 1-hour fireproofing or a
sidewall sprinkler directed to one side of the column at the top or at
the 15 ft (4.6 m) level, whichever is lower. Flow from these sprinklers
shall be permitted to be omitted from the sprinkler system demand for
hydraulic calculations.
Travis Mack, SET
MFP Design, LLC
2508 E Lodgepole Drive
Gilbert, AZ 85298
480-505-9271
fax: 866-430-6107
email:[email protected]
http://www.mfpdesign.com
https://www.facebook.com/pages/MFP-Design-LLC/92218417692
Send large files to us via: https://www.hightail.com/u/MFPDesign
On 7/6/2015 1:57 PM, Kenneth Berman wrote:
You're all missing an important point, the horizontal sidewall is pointed
upwards. A vertical sidewall, upwards, is incorrect. The horizontal
sidewall cools the column from fifteen feet upwards, and the water returned
by gravity cools the column below fifteen feet.
On Mon, Jul 6, 2015 at 2:50 PM, Parsley Consulting <
[email protected]> wrote:
Rocci,
I'd echo Travis and Mark's comments. When all else fails, point to
12.12.2.2.4.1, 16.1.4.1, 17.1.4.1, or 18.2.1 (whichever is appropriate) and
ask him, politely of course, how he's reaching the conclusion that the
sidewall sprinkler must be vertical.
In short, ask him to "prove it."
*Ken Wagoner, SET
*Parsley Consulting***
*350 West 9th Avenue, Suite 206
*Escondido, California 92025
*****Phone 760-745-6181*
Visit our website <http://www.parsleyconsulting.com/> ***
On 07/06/2015 11:20 AM, Rocci Cetani 3 wrote:
I have a FM questioning the use of horizontal sidewall sprinklers (he
thinks
it should be a vertical sidewall) with no heat collectors @ 15' AFF...NFPA
13 2013 17.1.4.1 only states a sidewall sprinkler pointed in the
direction of the column @ 15' AFF. Any suggestions?
Rocci Cetani III, CET
Lead Designer
Water-Based Fire Protections Systems Layout, Nicet Level III
Northern California Fire Protection Services Inc.
16840 Joleen Way Bldg. A
Morgan Hill, CA 93037
P-(408) 776-1580 EXT.111
F-(408) 776-1590
C- (408) 595-3906
[email protected]
www.norcalfire.com <http://www.norcalfire.com/>
CONFIDENTIALITY NOTICE: This message and any document accompanying it may
contain confidential information
belonging to the sender. The information is intended only for the use of
individual or entity named above. If you are not the intended recipient,
or
the employee or agent responsible to deliver this message to the intended
recipient, you are hereby notified that any disclosure, copying or taking
of
any action in reliance on the contents of this information is strictly
prohibited. If you have received this transmission in error, please
immediately notify us by telephone to arrange for return of the documents.
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org