Have had some sites/AHJs look for a HSW rotated so that the deflector is
perpedicular to the floor. Idea being that more water hits the column.
Seemed like a good idea to me as it does seem that a only a small bit of
the discharged water is hitting the column when installed parallel with the
floor.

Damien Shannon.

On 6 July 2015 at 22:10, Travis Mack, SET <[email protected]> wrote:

> The sprinklers at the roof will help to cool the structure.  My
> understanding the 15' sprinkler is to help prevent buckling of the column.
>
> Travis Mack, SET
> MFP Design, LLC
> 2508 E Lodgepole Drive
> Gilbert, AZ 85298
> 480-505-9271
> fax: 866-430-6107
> email:[email protected]
>
> http://www.mfpdesign.com
> https://www.facebook.com/pages/MFP-Design-LLC/92218417692
> Send large files to us via: https://www.hightail.com/u/MFPDesign
>
> On 7/6/2015 2:09 PM, Kenneth Berman wrote:
>
>> What cools a fifty foot column above fifteen feet? Codes don't say install
>> horizontal, vertical, up, down. In Tennessee gravity pulls the water down.
>> I'm cooling twenty nine feet of column to prevent collapse.
>>
>> On Mon, Jul 6, 2015 at 3:55 PM, John Denhardt <
>> [email protected]>
>> wrote:
>>
>>  Agree - I never seen one pointed up.
>>>
>>> John
>>>
>>> -----Original Message-----
>>> From: Sprinklerforum [mailto:
>>> [email protected]] On Behalf Of Travis
>>> Mack,
>>> SET
>>> Sent: Monday, July 06, 2015 5:00 PM
>>> To: [email protected]
>>> Subject: Re: Column Protection
>>>
>>> Where does it say the sidewall is pointed up?  I have only seen these
>>> installed in the horizontal position for this application.
>>>
>>> Any steel columns shall be protected by 1-hour fireproofing or a
>>> sidewall sprinkler directed to one side of the column at the top or at
>>> the 15 ft (4.6 m) level, whichever is lower. Flow from these sprinklers
>>> shall be permitted to be omitted from the sprinkler system demand for
>>> hydraulic calculations.
>>>
>>>
>>> Travis Mack, SET
>>> MFP Design, LLC
>>> 2508 E Lodgepole Drive
>>> Gilbert, AZ 85298
>>> 480-505-9271
>>> fax: 866-430-6107
>>> email:[email protected]
>>>
>>> http://www.mfpdesign.com
>>> https://www.facebook.com/pages/MFP-Design-LLC/92218417692
>>> Send large files to us via: https://www.hightail.com/u/MFPDesign
>>>
>>> On 7/6/2015 1:57 PM, Kenneth Berman wrote:
>>>
>>>> You're all missing an important point, the horizontal sidewall is
>>>> pointed
>>>> upwards. A vertical sidewall, upwards, is incorrect. The horizontal
>>>> sidewall cools the column from fifteen feet upwards, and the water
>>>>
>>> returned
>>>
>>>> by gravity cools the column below fifteen feet.
>>>>
>>>> On Mon, Jul 6, 2015 at 2:50 PM, Parsley Consulting <
>>>> [email protected]> wrote:
>>>>
>>>>  Rocci,
>>>>>       I'd echo Travis and Mark's comments. When all else fails, point
>>>>> to
>>>>> 12.12.2.2.4.1, 16.1.4.1, 17.1.4.1, or 18.2.1 (whichever is appropriate)
>>>>>
>>>> and
>>>
>>>> ask him, politely of course, how he's reaching the conclusion that the
>>>>> sidewall sprinkler must be vertical.
>>>>>       In short, ask him to "prove it."
>>>>> *Ken Wagoner, SET
>>>>> *Parsley Consulting***
>>>>> *350 West 9th Avenue, Suite 206
>>>>> *Escondido, California 92025
>>>>> *****Phone 760-745-6181*
>>>>> Visit our website <http://www.parsleyconsulting.com/> ***
>>>>>
>>>>>
>>>>> On 07/06/2015 11:20 AM, Rocci Cetani 3 wrote:
>>>>>
>>>>>  I have a FM questioning the use of horizontal sidewall sprinklers (he
>>>>>> thinks
>>>>>> it should be a vertical sidewall) with no heat collectors @ 15'
>>>>>>
>>>>> AFF...NFPA
>>>
>>>> 13 2013   17.1.4.1  only states a sidewall sprinkler pointed in the
>>>>>> direction of the column @ 15' AFF.  Any suggestions?
>>>>>>
>>>>>>
>>>>>>
>>>>>> Rocci Cetani III, CET
>>>>>>
>>>>>> Lead Designer
>>>>>>
>>>>>> Water-Based Fire Protections Systems Layout, Nicet Level III
>>>>>>
>>>>>>
>>>>>> Northern California Fire Protection Services Inc.
>>>>>>
>>>>>> 16840 Joleen Way Bldg. A
>>>>>>
>>>>>> Morgan Hill, CA 93037
>>>>>>
>>>>>> P-(408) 776-1580 EXT.111
>>>>>>
>>>>>> F-(408) 776-1590
>>>>>>
>>>>>> C- (408) 595-3906
>>>>>>
>>>>>>
>>>>>> [email protected]
>>>>>>
>>>>>> www.norcalfire.com <http://www.norcalfire.com/>
>>>>>>
>>>>>>
>>>>>> CONFIDENTIALITY NOTICE: This message and any document accompanying it
>>>>>>
>>>>> may
>>>
>>>> contain confidential information
>>>>>>
>>>>>> belonging to the sender. The information is intended only for the use
>>>>>>
>>>>> of
>>>
>>>> individual or entity named above. If you are not the intended
>>>>>>
>>>>> recipient,
>>>
>>>> or
>>>>>> the employee or agent responsible to deliver this message to the
>>>>>>
>>>>> intended
>>>
>>>> recipient, you are hereby notified that any disclosure, copying or
>>>>>>
>>>>> taking
>>>
>>>> of
>>>>>> any action in reliance on the contents of this information is strictly
>>>>>> prohibited. If you have received this transmission in error, please
>>>>>> immediately notify us by telephone to arrange for return of the
>>>>>>
>>>>> documents.
>>>
>>>>
>>>>>> _______________________________________________
>>>>>> Sprinklerforum mailing list
>>>>>> [email protected]
>>>>>>
>>>>>>
>>>>>>
>>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>>>
>>>>
>>>>>>  _______________________________________________
>>>>> Sprinklerforum mailing list
>>>>> [email protected]
>>>>>
>>>>>
>>>>>
>>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>>>
>>>> _______________________________________________
>>>> Sprinklerforum mailing list
>>>> [email protected]
>>>>
>>>>
>>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>>>
>>> _______________________________________________
>>> Sprinklerforum mailing list
>>> [email protected]
>>>
>>>
>>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>>> _______________________________________________
>>> Sprinklerforum mailing list
>>> [email protected]
>>>
>>>
>>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>>>
>>>  _______________________________________________
>> Sprinklerforum mailing list
>> [email protected]
>>
>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>>
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
>
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>



-- 

*Damien Shannon*
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to