Rocci,
I'd echo Travis and Mark's comments. When all else fails, point to
12.12.2.2.4.1, 16.1.4.1, 17.1.4.1, or 18.2.1 (whichever is appropriate)
and ask him, politely of course, how he's reaching the conclusion that
the sidewall sprinkler must be vertical.
In short, ask him to "prove it."
*Ken Wagoner, SET
*Parsley Consulting***
*350 West 9th Avenue, Suite 206
*Escondido, California 92025
*****Phone 760-745-6181*
Visit our website <http://www.parsleyconsulting.com/> ***
On 07/06/2015 11:20 AM, Rocci Cetani 3 wrote:
I have a FM questioning the use of horizontal sidewall sprinklers (he thinks
it should be a vertical sidewall) with no heat collectors @ 15' AFF...NFPA
13 2013 17.1.4.1 only states a sidewall sprinkler pointed in the
direction of the column @ 15' AFF. Any suggestions?
Rocci Cetani III, CET
Lead Designer
Water-Based Fire Protections Systems Layout, Nicet Level III
Northern California Fire Protection Services Inc.
16840 Joleen Way Bldg. A
Morgan Hill, CA 93037
P-(408) 776-1580 EXT.111
F-(408) 776-1590
C- (408) 595-3906
[email protected]
www.norcalfire.com <http://www.norcalfire.com/>
CONFIDENTIALITY NOTICE: This message and any document accompanying it may
contain confidential information
belonging to the sender. The information is intended only for the use of
individual or entity named above. If you are not the intended recipient, or
the employee or agent responsible to deliver this message to the intended
recipient, you are hereby notified that any disclosure, copying or taking of
any action in reliance on the contents of this information is strictly
prohibited. If you have received this transmission in error, please
immediately notify us by telephone to arrange for return of the documents.
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org