Not true. The head will activate if it sees flame impingement or otherwise reaches activation temperature - which is the only time the column will need to have water spraying directly onto it.
Mark A. Sornsin, P.E. | Karges-Faulconbridge, Inc. | Fire Protection Engineer | Fargo, ND | direct: 701.552.9905 | mobile: 701.371.5759 | http://www.kfiengineers.com -----Original Message----- From: Sprinklerforum [mailto:[email protected]] On Behalf Of Rocci Cetani 3 Sent: Monday, July 06, 2015 2:02 PM To: [email protected] Subject: RE: Column Protection I know there is no such thing as a listed heat collector......his claim is the head will never activate sitting at 15' AFF Rocci Cetani III, CET Lead Designer Water-Based Fire Protections Systems Layout, Nicet Level III Northern California Fire Protection Services Inc. 16840 Joleen Way Bldg. A Morgan Hill, CA 93037 P-(408) 776-1580 EXT.111 F-(408) 776-1590 C- (408) 595-3906 [email protected] www.norcalfire.com CONFIDENTIALITY NOTICE: This message and any document accompanying it may contain confidential information belonging to the sender. The information is intended only for the use of individual or entity named above. If you are not the intended recipient, or the employee or agent responsible to deliver this message to the intended recipient, you are hereby notified that any disclosure, copying or taking of any action in reliance on the contents of this information is strictly prohibited. If you have received this transmission in error, please immediately notify us by telephone to arrange for return of the documents. -----Original Message----- From: Sprinklerforum [mailto:[email protected]] On Behalf Of Travis Mack, SET Sent: Monday, July 06, 2015 11:37 AM To: [email protected] Subject: Re: Column Protection No such thing as a listed heat collector. NFPA 13 simply calls out the use of a sidewall, it does not state horizontal or vertical for type to be used. You may need to ask him where the requirement for a VERTICAL sidewall is indicated. Travis Mack, SET MFP Design, LLC 2508 E Lodgepole Drive Gilbert, AZ 85298 480-505-9271 fax: 866-430-6107 email:[email protected] http://www.mfpdesign.com https://www.facebook.com/pages/MFP-Design-LLC/92218417692 Send large files to us via: https://www.hightail.com/u/MFPDesign On 7/6/2015 11:20 AM, Rocci Cetani 3 wrote: > I have a FM questioning the use of horizontal sidewall sprinklers (he > thinks it should be a vertical sidewall) with no heat collectors @ 15' AFF...NFPA > 13 2013 17.1.4.1 only states a sidewall sprinkler pointed in the > direction of the column @ 15' AFF. Any suggestions? > > > > > > Rocci Cetani III, CET > > Lead Designer > > Water-Based Fire Protections Systems Layout, Nicet Level III > > > > Northern California Fire Protection Services Inc. > > 16840 Joleen Way Bldg. A > > Morgan Hill, CA 93037 > > P-(408) 776-1580 EXT.111 > > F-(408) 776-1590 > > C- (408) 595-3906 > > > > [email protected] > > www.norcalfire.com <http://www.norcalfire.com/> > > > > CONFIDENTIALITY NOTICE: This message and any document accompanying it > may contain confidential information > > belonging to the sender. The information is intended only for the use > of individual or entity named above. If you are not the intended > recipient, or the employee or agent responsible to deliver this > message to the intended recipient, you are hereby notified that any > disclosure, copying or taking of any action in reliance on the > contents of this information is strictly prohibited. If you have > received this transmission in error, please immediately notify us by telephone to arrange for return of the documents. > > > > _______________________________________________ > Sprinklerforum mailing list > [email protected] > http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl > er.org _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org ______________________________________________________________________ This email has been scanned by the Symantec Email Security.cloud service. For more information please visit http://www.symanteccloud.com ______________________________________________________________________ ______________________________________________________________________ This email has been scanned by the Symantec Email Security.cloud service. For more information please visit http://www.symanteccloud.com ______________________________________________________________________ _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
