If he thinks a HSW will never activate, what makes him think a VSW will
activate?
I totally agree with you that the HSW is appropriate and your
installation is in compliance with NFPA 13.
Travis Mack, SET
MFP Design, LLC
2508 E Lodgepole Drive
Gilbert, AZ 85298
480-505-9271
fax: 866-430-6107
email:[email protected]
http://www.mfpdesign.com
https://www.facebook.com/pages/MFP-Design-LLC/92218417692
Send large files to us via: https://www.hightail.com/u/MFPDesign
On 7/6/2015 12:01 PM, Rocci Cetani 3 wrote:
I know there is no such thing as a listed heat collector......his claim is
the head will never activate sitting at 15' AFF
Rocci Cetani III, CET
Lead Designer
Water-Based Fire Protections Systems Layout, Nicet Level III
Northern California Fire Protection Services Inc.
16840 Joleen Way Bldg. A
Morgan Hill, CA 93037
P-(408) 776-1580 EXT.111
F-(408) 776-1590
C- (408) 595-3906
[email protected]
www.norcalfire.com
CONFIDENTIALITY NOTICE: This message and any document accompanying it may
contain confidential information
belonging to the sender. The information is intended only for the use of
individual or entity named above. If you are not the intended recipient, or
the employee or agent responsible to deliver this message to the intended
recipient, you are hereby notified that any disclosure, copying or taking of
any action in reliance on the contents of this information is strictly
prohibited. If you have received this transmission in error, please
immediately notify us by telephone to arrange for return of the documents.
-----Original Message-----
From: Sprinklerforum [mailto:[email protected]]
On Behalf Of Travis Mack, SET
Sent: Monday, July 06, 2015 11:37 AM
To: [email protected]
Subject: Re: Column Protection
No such thing as a listed heat collector.
NFPA 13 simply calls out the use of a sidewall, it does not state horizontal
or vertical for type to be used.
You may need to ask him where the requirement for a VERTICAL sidewall is
indicated.
Travis Mack, SET
MFP Design, LLC
2508 E Lodgepole Drive
Gilbert, AZ 85298
480-505-9271
fax: 866-430-6107
email:[email protected]
http://www.mfpdesign.com
https://www.facebook.com/pages/MFP-Design-LLC/92218417692
Send large files to us via: https://www.hightail.com/u/MFPDesign
On 7/6/2015 11:20 AM, Rocci Cetani 3 wrote:
I have a FM questioning the use of horizontal sidewall sprinklers (he
thinks it should be a vertical sidewall) with no heat collectors @ 15'
AFF...NFPA
13 2013 17.1.4.1 only states a sidewall sprinkler pointed in the
direction of the column @ 15' AFF. Any suggestions?
Rocci Cetani III, CET
Lead Designer
Water-Based Fire Protections Systems Layout, Nicet Level III
Northern California Fire Protection Services Inc.
16840 Joleen Way Bldg. A
Morgan Hill, CA 93037
P-(408) 776-1580 EXT.111
F-(408) 776-1590
C- (408) 595-3906
[email protected]
www.norcalfire.com <http://www.norcalfire.com/>
CONFIDENTIALITY NOTICE: This message and any document accompanying it
may contain confidential information
belonging to the sender. The information is intended only for the use
of individual or entity named above. If you are not the intended
recipient, or the employee or agent responsible to deliver this
message to the intended recipient, you are hereby notified that any
disclosure, copying or taking of any action in reliance on the
contents of this information is strictly prohibited. If you have
received this transmission in error, please immediately notify us by
telephone to arrange for return of the documents.
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl
er.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org