I didn't get it, had it all along. :)  My oscillating cannons were an attempt 
at sarcastic humor.  

In the mean time I've got to get back to detailing protection for those OH III 
Slurpee Machines at those gas stations since they're gonna let the canopies go 
up in flames, got to protect at least one sure fire revenue source............. 
 


Craig L. Prahl 
Fire Protection Group Lead/SME
CH2MHILL
Lockwood Greene
1500 International Drive
Spartanburg, SC  29303
Direct - 864.599.4102
Fax - 864.599.8439
CH2MHILL Extension  74102
[email protected]


-----Original Message-----
From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Steve Leyton
Sent: Wednesday, December 09, 2015 4:08 PM
To: [email protected]
Subject: RE: Canopies Over gas Pumps

Finally, he gets it.   And BTW, oscillating cannons are total overkill - we've 
used fixed monitors successfully on several projects.

You raise an interesting point on the question of non-metallic cars, but let's 
also keep an eye out for a wave of fire incident reports on vehicle fires that 
aren't controlled by OH1 sprinklers.  When there's a pandemic rate of 
occurrence, we should revisit that.   

SL



-----Original Message-----
From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of [email protected]
Sent: Wednesday, December 09, 2015 1:01 PM
To: [email protected]
Subject: RE: Canopies Over gas Pumps

Foam-water deluge with autonomous, GPS interfaced, thermal seeking, oscillating 
high pressure foam cannons, go large or go home.  ;)

Seriously, if a client specifies a certain system and chooses not to heed your 
alternative recommendations, you provide it as requested since they're paying 
for it and they are paying you to design it.

I wonder how long ago that 0.15 criteria was developed?  Probably when cars 
were mostly steel?  For today's plastic cars I doubt that would have much 
affect then add Hybrids with batteries.  

Craig L. Prahl 
Fire Protection Group Lead/SME
CH2MHILL
Lockwood Greene
1500 International Drive
Spartanburg, SC  29303
Direct - 864.599.4102
Fax - 864.599.8439
CH2MHILL Extension  74102
[email protected]


-----Original Message-----
From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Steve Leyton
Sent: Wednesday, December 09, 2015 3:06 PM
To: [email protected]
Subject: RE: Canopies Over gas Pumps

Those are nice pictures.   Many of them don't actually show fires at filling 
stations (at least one shows a collision with a tanker truck).  Those that do 
include a lot of vehicle fires and many of those are outside of the area of the 
canopy.  If you go to NFPA's website, you'll find at least a couple pages that 
underscore that this is a low rate-of-occurrence event and that 61% of these 
fires are classified as vehicle fires (back to OH1 are we?).    Look, I don't 
want anyone to think I've lost my passionate concern for public safety, but 
there is a cost-benefit equation to just about everything, including the 
standards we use every day.   I think that the information I've seen on The 
Internets (including what's to be inferred from the Google images of gas 
station fires) underscores what I said yesterday.  It's not a compelling risk 
from the perspective that it's not a high percentage risk of occurrence, and 
it's definitely not a flammable liquids storage issue.

If anyone out there wants to pay for a foam suppression system, I will NOT 
discourage them, but if I were their consultant I would not be programming one 
on their behalf.

http://www.nfpa.org/safety-information/for-consumers/vehicles/service-station-safety

http://www.nfpa.org/research/reports-and-statistics/fires-by-property-type/business-and-mercantile/fires-at-us-service-stations


SL






-----Original Message-----
From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of David Blackwell
Sent: Wednesday, December 09, 2015 11:54 AM
To: [email protected]
Subject: RE: Canopies Over gas Pumps

Google "gas station fire" and select the images tab to see some big gas station 
fires.  [If you don't select "images" the top story is about "Man trying to 
kill spider ignites gas pump fire - CNN Video"]

Respectfully,


David W. S. Blackwell, II, PE, CFPE, CFI I Chief Engineer Office of State Fire 
Marshal SC Department of Labor, Licensing, & Regulation, 141 Monticello Trail, 
Columbia, SC 29203
Telephone: 803.896.9800 [Office] 803.896.9833 [Direct]
Fax: 803.896.9806 [Office]
Email:   [email protected]
Website:  http://www.scfiremarshal.llronline.com/


Please note that you can find a lot of information on our website at  
http://www.scfiremarshal.llronline.com/ including contact information, current 
events, laws, regulations, policies, forms, procedures, and links to other 
website resources for further information.


-----Original Message-----
From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Steve Leyton
Sent: Tuesday, December 08, 2015 5:19 PM
To: [email protected]
Subject: RE: Canopies Over gas Pumps

*** SCDLLR NOTICE *** This email is from an external email address. Please use 
caution when deciding whether to open any attachments or when clicking links 
inside the email.

EXACTLY.   None of us has ever seen a gas station fire in all likelihood 
because the equipment is equipped with so many fail-safety devices and so long 
as idiots aren't smoking or lighting incense as they refuel, it's very low 
risk, empirically speaking.  If there's a fire on the ground, how well does a 
canopy trap heat?  With no walls, the horizontal movement of byproducts is 
going to be fairly high-velocity, no?  Unless you have some fire modeling or 
test data in hand, your and my guesses are the best we're going to have with 
regard to the chances of sprinklers skipping or even operating at all.  The AHJ 
is probably requiring sprinklers for the reason you state - so he/she can sleep 
at night, so give them sprinklers.

As to the use of foam by responders, I think everyone would agree that there's 
a significant difference in the metrics of programming operations in a muni 
fire department than in the cost-benefit analysis of a fixed foam extinguishing 
system and the impact it would have on the design of the protected premises.  
Water has been successfully fire tested in flammable liquids fires, from mist 
to ESFR.  So if the AHJ wants sprinklers, give them "sprinklers".

SL



-----Original Message-----
From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of [email protected]
Sent: Tuesday, December 08, 2015 2:04 PM
To: [email protected]
Subject: RE: Canopies Over gas Pumps

Wow, really?  What is that stuff the guys in the red trucks spray on liquid 
fuel spills and over car fires?

Hate to disagree but OH I is even questionable for a parking garage regardless 
of what NPFA says and for a gas station well it's just silly.   I've never seen 
a little gas station fire.

But at the end of the day you do what allows you to sleep at night.

Craig L. Prahl
Fire Protection Group Lead/SME
CH2MHILL
Lockwood Greene
1500 International Drive
Spartanburg, SC  29303
Direct - 864.599.4102
Fax - 864.599.8439
CH2MHILL Extension  74102
[email protected]


-----Original Message-----
From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Steve Leyton
Sent: Tuesday, December 08, 2015 4:51 PM
To: [email protected]
Subject: RE: Canopies Over gas Pumps

Please, stop.  This is NOT flammable liquids storage.   Foam and wind effect 
and all this other stuff is Henny-Penny-the-sky-is-falling distraction (IMHO). 
7.3.5.2 of 30A states, " Where required, an automatic fire suppression system 
shall be installed in accordance with the appropriate NFPA standard, 
manufacturer's instructions, and the listing requirements of the systems.   
Obviously, NFPA 13 doesn't have a prescriptive for fuel island canopies, so 
let's use some common sense.   The fuel is stored in UG tanks away from the 
islands and retail store or cashiers hut.   NFPA 30 doesn't apply as this isn't 
storage, but Chapter 18 states that when a hose is used in the transfer of F/C 
liquids as part of an "incidental operation", it shall be equipped with a 
self-closing valve.   That's what a automotive fuel hose does - it's a dead man 
that kicks off from several triggers including back pressure and impact.  So 
the movie scene of a guy having a heart attack and squirting a steady stream of 
fuel into the air as a crow drops a burning cigarette butt into the pool is ... 
far-fetched.  At most, we can reasonable expect that there could be a quart of 
gasoline on the ground if there's an accident, so we would be protecting for 
that and the cars at the island that are ostensibly full or nearly full of 
fuel.  Just like in an OH 1 parking garage.

OH 2 if it's a month ending in Y ... my 3¢.

SL





-----Original Message-----
From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of [email protected]
Sent: Tuesday, December 08, 2015 10:25 AM
To: [email protected]
Subject: RE: Canopies Over gas Pumps

This is outside the purview of NFPA 13.

You're dealing with flammable and combustible liquids, hydrocarbons on which 
water alone will have limited affect.

For fuel loading/unloading stations it is common to employ foam-water deluge 
for the area below the canopy.

Also an option is dry chemical.  Pyrochem has a system called ATTENDANT II 
(distributed by Tyco)

The HAJ would have to approve either one but more tend to lean towards a 
sprinklered solution than a one-shot gaseous system.  A very windy day could 
totally render a gaseous extinguishing system useless.

For design you do need to consider wind effect on your system discharge.  Don't 
get swayed into the minimum .16 gpm/sf permitted on foam-water systems.  You 
can have coverage issues again due to wind influences.

NFPA 30, NFPA 30A, NFPA 16 and NFPA 2001 are good places to start.

Good luck and have fun!

Craig L. Prahl
Fire Protection Group Lead/SME
CH2MHILL
Lockwood Greene
1500 International Drive
Spartanburg, SC  29303
Direct - 864.599.4102
Fax - 864.599.8439
CH2MHILL Extension  74102
[email protected]


-----Original Message-----
From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of James Crawford
Sent: Tuesday, December 08, 2015 1:04 PM
To: [email protected]
Subject: Canopies Over gads Pumps

Looking for some direction on the protection of a Gas Service station canopy 
over the gas pumps.



We have an AHJ that want the canopy protected, but I can't find anything that 
outlines the protection requirements for this area. My first thought is Extra 
Hazard group 1.



Can someone point me in the right direction





Thank you





James Crawford

Phaser Fire Protection Ltd.

Phone  604-888-0318

Fax 604-888-4732

Cel 604-790-0938

Email  [email protected]



_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to