Peter-
Much appreciated.

Brian Harris, CET
BVS Systems Inc.
bvssytemsinc.com


-----Original Message-----
From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Pete Schwab
Sent: Tuesday, December 22, 2015 3:03 PM
To: [email protected]
Subject: RE: Fire Flow vs Hydraulic calc's

Brian


A.11.1.4.2 Appropriate area/density, other design criteria, and water supply 
requirements should be based on scientifically based engineering analyses that 
can include submitted fire testing, calculations, or results from appropriate 
computational models.
Recommended water supplies anticipate successful sprinkler operation. Because 
of the small but still significant number of uncontrolled fires in sprinklered 
properties, which have various causes, there should be an adequate water supply 
available for fire department use.
The hose stream demand required by this standard is intended to provide the 
fire department with the extra flow they need to conduct mop-up operations and 
final extinguishment of a fire at a sprinklered property. This is not the fire 
department manual fire flow, which is determined by other codes or standards. 
However, it is not the intent of this standard to require that the sprinkler 
demand be added to the manual fire flow demand required by other codes and 
standards.
While the other codes and standards can factor in the presence of a sprinkler 
system in the determination of the manual fire flow requirement, the sprinkler 
system water demand and manual fire flow demand are intended to be separate 
standalone calculations. NFPA 1 emphasizes this fact by the statement in 
A.18.4.1 that "It is not the intent to add the minimum fire protection water 
supplies, such as for a sprinkler system, to the minimum fire flow for manual 
fire suppression purposes required by this section."

Peter Schwab
VP of Purchasing and Engineering technologies

Wayne Automatic Fire Sprinklers Inc.
222 Capitol Court
Ocoee, Fl 34761

Mobile: (407) 468-8248
Direct: (407) 877-5570
Fax: (407) 656-8026

www.waynefire.com






-----Original Message-----
From: Pete Schwab
Sent: Tuesday, December 22, 2015 1:59 PM
To: [email protected]
Subject: RE: Fire Flow vs Hydraulic calc's

See NFPA 13 2016 Edition A.11.1.4.2

Peter Schwab
VP of Purchasing and Engineering technologies

Wayne Automatic Fire Sprinklers Inc.
222 Capitol Court
Ocoee, Fl 34761

Mobile: (407) 468-8248
Direct: (407) 877-5570
Fax: (407) 656-8026

www.waynefire.com






-----Original Message-----
From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Duane Johnson
Sent: Tuesday, December 22, 2015 1:48 PM
To: [email protected]
Subject: RE: Fire Flow vs Hydraulic calc's

To add, the fire flow is based on construction type, building height/area, and 
occupancy...items definitely not found in NFPA 13. The IFC has one method. ISO 
has another method.


Duane Johnson, PE
Design Manager
Strickland Fire Protection
5113 Berwyn Road
College Park, MD 20740
301-474-1136 Office
301-455-0010 Cell


-----Original Message-----
From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Matt Grise
Sent: Tuesday, December 22, 2015 1:50 PM
To: [email protected]
Subject: RE: Fire Flow vs Hydraulic calc's

Check the IBC/IFC (index... not sure what section). Fire Flow is the amount of 
water required to be delivered by the fire hydrants for the FD to spray on  a 
burning building. The amount required is dictated by the code, but the actual 
water available is determined entirely by the underground piping. Unless you 
are providing or designing the underground loops around the building, it is 
probably out of  your control.

Matt Grisé PE*, LEED AP, NICET II
Sales Engineer
Alliance Fire Protection
130 w 9th Ave.
North Kansas City, MO 64116

*Licensed in KS & MO 
 
913.888.0647 ph
913.888.0618 f
913.526.7443 cell
www. AFPsprink.com 
 


-----Original Message-----
From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Brian Harris
Sent: Tuesday, December 22, 2015 12:47 PM
To: [email protected]
Subject: Fire Flow vs Hydraulic calc's

Can someone please put into laymen's terms the difference between doing a fire 
flow demand calc for the underground and the hydraulic calc's for the sprinkler 
system? We have been running into some projects lately where the civil engineer 
tries to pawn sizing the underground off onto the sprinkler contractor. I try 
telling them that's their responsibility not ours but I'd like something more 
definitive to have on hand.

Brian Harris, CET
BVS Systems Inc.
Sprinkler Division
bvssystemsinc.com<http://bvssystemsinc.com/>
Phone: 704.896.9989
Fax: 704.896.1935

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to