A point that has been made indirectly but worth repeating is that these are TWO 
SEPARATE and UNRELATED CALCULATIONS.

One  - fire flow - it normally made by the Civil engineer, or maybe on rare 
occasions a fire protection engineer. The procedure typically follows that 
outlined in Appendix B of the IFC, or a similar method depending on 
jurisdiction.  If the engineer is on the ball, they will verify sprinkler 
calculation flows (inside sprinklers and hose allowances) to confirm their pipe 
sizes work for both calculations. Usually on a commercial job, the fire flows 
are greater than the sprinkler demands and will drive the sizing of the 
underground at the site. Not always the case on an industrial or warehouse site.

The other calc - the sprinkler system calc - is just that.  The demand of the 
sprinkler system inside the building plus hose allowances.  If the site 
engineer is doing their job well, they'd ask the professional in charge of fire 
protection, be it the design build contractor or the design team P.E. getting 
paid to spec the fire protection, for recommended pipe sizing for the 
underground supply into the building. THIS pipe sizing depends entirely on the 
sprinkler calcs.

The problem of course is that too often the engineer specifying the fire 
protection couldn't explain what a hose allowance is, let alone the difference 
between it and the site fire flow. So they throw an note on the plans to get 
the sizing from the low-bid sprinkler contractor; or worse, they just guess at 
lead-in sizes (6 inch seems to work most of the time - except for when it 
doesn't).

On a side note, if you want to have fun, ask a Civil engineer about the special 
testing requirements for underground fire mains. Many have no clue they need to 
do any more than pressure test to 50 psi over static and flush just enough to 
get the chlorine out.

Mark A. Sornsin, P.E. | Karges-Faulconbridge, Inc. | Fire Protection Engineer | 
Fargo, ND | direct: 701.552.9905 | mobile: 701.371.5759 | 
http://www.kfiengineers.com

-----Original Message-----
From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Brian Harris
Sent: Tuesday, December 22, 2015 2:13 PM
To: [email protected]
Subject: RE: Fire Flow vs Hydraulic calc's

Peter-
Much appreciated.

Brian Harris, CET
BVS Systems Inc.
bvssytemsinc.com


______________________________________________________________________
This email has been scanned by the Symantec Email Security.cloud service.
For more information please visit http://www.symanteccloud.com
______________________________________________________________________
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to