Here is some food for though...

Check out NFPA 13 Section 8.14.5.2 (3)

...The draft stop has to stay in place before and during sprinkler operation.

This is from the CBC:
718.3.1 Draftstopping materials. 
Draftstopping materials shall not be less than 1/2-inch (12.7 mm) gypsum board, 
3/8-inch (9.5 mm) wood structural panel, 3/8-inch (9.5 mm) particleboard, 
1-inch (25-mm) nominal lumber, cement fiberboard, batts or blankets of mineral 
wool or glass fiber, or other approved materials adequately supported. The 
integrity of draftstops shall be maintained.

Sent from my iPhone

> On Feb 11, 2016, at 7:20 PM, rongreenman . <[email protected]> wrote:
> 
> Ed has a good point. I was thinking the opposite, is it heavy enough to not
> blow around?
> 
>> On Thu, Feb 11, 2016 at 6:45 PM, Travis Mack <[email protected]> wrote:
>> 
>> Yeah. They just want to staple in place at top.
>> 
>> Travis Mack, SET
>> MFP Design, LLC
>> "Follow" us on Facebook:
>> https://www.facebook.com/pages/MFP-Design-LLC/92218417692
>> Send large files to MFP Design via:
>> https://www.hightail.com/u/MFPDesign
>> 
>> Sent from my iPhone
>> 
>>>> On Feb 11, 2016, at 6:45 PM, rongreenman . <[email protected]>
>>> wrote:
>>> 
>>> just let it hang vertically along a long edge?
>>> 
>>> 
>>> On Thu, Feb 11, 2016 at 3:49 PM, Travis Mack, SET <[email protected]>
>>> wrote:
>>> 
>>>> I have a customer that is asking if batt insulation can be secured to
>> the
>>>> roof decking and used as a draft curtain for the Tyco CC sprinklers.  I
>>>> have never seen an application such as this, but it doesn't seem to be
>>>> prohibited in the datasheet.  The only requirement is that it must be
>>>> constructed of a material so that heat can not pass through or over.
>>>> 
>>>> What do you think?  Could insulation secured to the roof/floor deck
>> serve
>>>> as a draft curtain for these sprinklers?  My gut feeling is that it
>> would
>>>> not be suitable, but I can't find something in the data sheet to support
>>>> that.  My only thought is that activation of a sprinkler could possibly
>>>> knock the insulation down.
>>>> 
>>>> --
>>>> Travis Mack, SET
>>>> MFP Design, LLC
>>>> 2508 E Lodgepole Drive
>>>> Gilbert, AZ 85298
>>>> 480-505-9271
>>>> fax: 866-430-6107
>>>> email:[email protected]
>>>> 
>>>> http://www.mfpdesign.com
>>>> https://www.facebook.com/pages/MFP-Design-LLC/92218417692
>>>> Send large files to us via: https://www.hightail.com/u/MFPDesign
>>>> 
>>>> _______________________________________________
>>>> Sprinklerforum mailing list
>>>> [email protected]
>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>>> 
>>> 
>>> 
>>> --
>>> Ron Greenman
>>> Instructor
>>> Fire Protection Engineering Technology
>>> Bates Technical College
>>> 1101 So. Yakima Ave.
>>> Tacoma, WA 98405
>>> 
>>> [email protected]
>>> 
>>> http://www.bates.ctc.edu/fireprotection/
>>> 
>>> 253.680.7346
>>> 253.576.9700 (cell)
>>> 
>>> Member:
>>> ASEE, SFPE, ASCET, NFPA, AFSA, NFSA, AFAA, NIBS, WSAFM, WFC, WFSC
>>> 
>>> They are happy men whose natures sort with their vocations. -Francis
>> Bacon,
>>> essayist, philosopher, and statesman (1561-1626)
>>> 
>>> A problem well stated is a problem half solved. -Charles F. Kettering,
>>> inventor and engineer (1876-1958)
>>> _______________________________________________
>>> Sprinklerforum mailing list
>>> [email protected]
>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>> _______________________________________________
>> Sprinklerforum mailing list
>> [email protected]
>> 
>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
> 
> 
> 
> -- 
> Ron Greenman
> Instructor
> Fire Protection Engineering Technology
> Bates Technical College
> 1101 So. Yakima Ave.
> Tacoma, WA 98405
> 
> [email protected]
> 
> http://www.bates.ctc.edu/fireprotection/
> 
> 253.680.7346
> 253.576.9700 (cell)
> 
> Member:
> ASEE, SFPE, ASCET, NFPA, AFSA, NFSA, AFAA, NIBS, WSAFM, WFC, WFSC
> 
> They are happy men whose natures sort with their vocations. -Francis Bacon,
> essayist, philosopher, and statesman (1561-1626)
> 
> A problem well stated is a problem half solved. -Charles F. Kettering,
> inventor and engineer (1876-1958)
> _______________________________________________