You and I are on the same page. We were just hoping to get a definitive answer from the manufacturer.

Travis Mack, SET
MFP Design, LLC
2508 E Lodgepole Drive
Gilbert, AZ 85298
480-505-9271
fax: 866-430-6107
email:[email protected]

http://www.mfpdesign.com
https://www.facebook.com/pages/MFP-Design-LLC/92218417692
Send large files to us via: https://www.hightail.com/u/MFPDesign

On 2/12/2016 8:53 AM, Ed Kramer wrote:
The AHJ is going to have to make the final call.  My pay scale isn't high
enough to make those types decisions, but if it were,  I'd say no.  If water
spray from the 1st sprinkler or 2 damages the insulation to allow heat to
flow past it, you've lost your heat barrier and the 1000 sf design area is
out-the-window.

Back to my regularly scheduled program.

Ed Kramer
Bamford Fire Sprinkler

-----Original Message-----
From: Sprinklerforum [mailto:[email protected]]
On Behalf Of Travis Mack, SET
Sent: Friday, February 12, 2016 9:28 AM
To: [email protected]
Subject: Re: Tyco CC sprinklers / draft curtain

That is what the contractor is arguing.  The NFPA 13 definitions of draft
curtains are in reference to separation of ESFR and SR, water spray systems
and hazard separation.

It is an outside the box thinking for sure.  As you say, if it is stapled to
the deck, that would prevent heat from passing through and over.  That is
the only criteria in the datasheet.


Travis Mack, SET
MFP Design, LLC
2508 E Lodgepole Drive
Gilbert, AZ 85298
480-505-9271
fax: 866-430-6107
email:[email protected]

http://www.mfpdesign.com
https://www.facebook.com/pages/MFP-Design-LLC/92218417692
Send large files to us via: https://www.hightail.com/u/MFPDesign

On 2/12/2016 8:19 AM, Matthew J Willis wrote:
LOL.

I say it does meet it.
Insulation by default blocks heat..

R/
Matt


Matthew J. Willis
Project Manager
Rapid Fire Protection Inc.
*NEW ADDRESS*
1530 Samco Road
Rapid City, SD 57702
Office-605.348.2342
Direct Line-605.593.5063
Cell-605.391.2733
Fax:-605.348.0108






-----Original Message-----
From: Sprinklerforum
[mailto:[email protected]] On Behalf Of
Travis Mack
Sent: Friday, February 12, 2016 8:16 AM
To: [email protected]
Subject: Re: Tyco CC sprinklers / draft curtain

Well, the customer called Tyco and they could not say definitively if the
insulation would meet the requirements or not.


Travis Mack, SET
MFP Design, LLC
"Follow" us on Facebook:
https://www.facebook.com/pages/MFP-Design-LLC/92218417692
Send large files to MFP Design via:
https://www.hightail.com/u/MFPDesign

Sent from my iPhone

On Feb 11, 2016, at 4:49 PM, Travis Mack, SET <[email protected]>
wrote:
I have a customer that is asking if batt insulation can be secured to the
roof decking and used as a draft curtain for the Tyco CC sprinklers.  I have
never seen an application such as this, but it doesn't seem to be prohibited
in the datasheet.  The only requirement is that it must be constructed of a
material so that heat can not pass through or over.
What do you think?  Could insulation secured to the roof/floor deck serve
as a draft curtain for these sprinklers?  My gut feeling is that it would
not be suitable, but I can't find something in the data sheet to support
that.  My only thought is that activation of a sprinkler could possibly
knock the insulation down.
--
Travis Mack, SET
MFP Design, LLC
2508 E Lodgepole Drive
Gilbert, AZ 85298
480-505-9271
fax: 866-430-6107
email:[email protected]

http://www.mfpdesign.com
https://www.facebook.com/pages/MFP-Design-LLC/92218417692
Send large files to us via: https://www.hightail.com/u/MFPDesign

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprink
ler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl
er.org

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl
er.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to