Got it...Here is some info for Draft Curtains:
NFPA 13 Section A.3.3.8
A.3.3.8 Draft Curtain. Additional information about the sizeand
installation of draft curtains can be found in NFPA 204.
From CBC:
*910.3.5.1 Construction. *Draft curtains shall be constructed of sheet
metal, lath and plaster, gypsum board or other *approved *materials which
provide equivalent performance to resist the passage of smoke. Joints and
connections shall be smoke tight. [F]

On Thu, Feb 11, 2016 at 9:56 PM, Travis Mack <[email protected]> wrote:

> These are not draft stops. They are draft curtains required by the listing
> of the sprinkler.
>
> The listing only states it has to be constructed of a material that does
> not let heat pass over or through.
>
> Travis Mack, SET
> MFP Design, LLC
> "Follow" us on Facebook:
> https://www.facebook.com/pages/MFP-Design-LLC/92218417692
> Send large files to MFP Design via:
> https://www.hightail.com/u/MFPDesign
>
> Sent from my iPhone
>
> > On Feb 11, 2016, at 10:28 PM, [email protected] wrote:
> >
> > Here is some food for though...
> >
> > Check out NFPA 13 Section 8.14.5.2 (3)
> >
> > ...The draft stop has to stay in place before and during sprinkler
> operation.
> >
> > This is from the CBC:
> > 718.3.1 Draftstopping materials.
> > Draftstopping materials shall not be less than 1/2-inch (12.7 mm) gypsum
> board, 3/8-inch (9.5 mm) wood structural panel, 3/8-inch (9.5 mm)
> particleboard, 1-inch (25-mm) nominal lumber, cement fiberboard, batts or
> blankets of mineral wool or glass fiber, or other approved materials
> adequately supported. The integrity of draftstops shall be maintained.
> >
> > Sent from my iPhone
> >
> >> On Feb 11, 2016, at 7:20 PM, rongreenman . <[email protected]>
> wrote:
> >>
> >> Ed has a good point. I was thinking the opposite, is it heavy enough to
> not
> >> blow around?
> >>
> >>> On Thu, Feb 11, 2016 at 6:45 PM, Travis Mack <[email protected]>
> wrote:
> >>>
> >>> Yeah. They just want to staple in place at top.
> >>>
> >>> Travis Mack, SET
> >>> MFP Design, LLC
> >>> "Follow" us on Facebook:
> >>> https://www.facebook.com/pages/MFP-Design-LLC/92218417692
> >>> Send large files to MFP Design via:
> >>> https://www.hightail.com/u/MFPDesign
> >>>
> >>> Sent from my iPhone
> >>>
> >>>>> On Feb 11, 2016, at 6:45 PM, rongreenman . <[email protected]>
> >>>> wrote:
> >>>>
> >>>> just let it hang vertically along a long edge?
> >>>>
> >>>>
> >>>> On Thu, Feb 11, 2016 at 3:49 PM, Travis Mack, SET <
> [email protected]>
> >>>> wrote:
> >>>>
> >>>>> I have a customer that is asking if batt insulation can be secured to
> >>> the
> >>>>> roof decking and used as a draft curtain for the Tyco CC
> sprinklers.  I
> >>>>> have never seen an application such as this, but it doesn't seem to
> be
> >>>>> prohibited in the datasheet.  The only requirement is that it must be
> >>>>> constructed of a material so that heat can not pass through or over.
> >>>>>
> >>>>> What do you think?  Could insulation secured to the roof/floor deck
> >>> serve
> >>>>> as a draft curtain for these sprinklers?  My gut feeling is that it
> >>> would
> >>>>> not be suitable, but I can't find something in the data sheet to
> support
> >>>>> that.  My only thought is that activation of a sprinkler could
> possibly
> >>>>> knock the insulation down.
> >>>>>
> >>>>> --
> >>>>> Travis Mack, SET
> >>>>> MFP Design, LLC
> >>>>> 2508 E Lodgepole Drive
> >>>>> Gilbert, AZ 85298
> >>>>> 480-505-9271
> >>>>> fax: 866-430-6107
> >>>>> email:[email protected]
> >>>>>
> >>>>> http://www.mfpdesign.com
> >>>>> https://www.facebook.com/pages/MFP-Design-LLC/92218417692
> >>>>> Send large files to us via: https://www.hightail.com/u/MFPDesign
> >>>>>
> >>>>> _______________________________________________
> >>>>> Sprinklerforum mailing list
> >>>>> [email protected]
> >>>
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
> >>>>
> >>>>
> >>>>
> >>>> --
> >>>> Ron Greenman
> >>>> Instructor
> >>>> Fire Protection Engineering Technology
> >>>> Bates Technical College
> >>>> 1101 So. Yakima Ave.
> >>>> Tacoma, WA 98405
> >>>>
> >>>> [email protected]
> >>>>
> >>>> http://www.bates.ctc.edu/fireprotection/
> >>>>
> >>>> 253.680.7346
> >>>> 253.576.9700 (cell)
> >>>>
> >>>> Member:
> >>>> ASEE, SFPE, ASCET, NFPA, AFSA, NFSA, AFAA, NIBS, WSAFM, WFC, WFSC
> >>>>
> >>>> They are happy men whose natures sort with their vocations. -Francis
> >>> Bacon,
> >>>> essayist, philosopher, and statesman (1561-1626)
> >>>>
> >>>> A problem well stated is a problem half solved. -Charles F. Kettering,
> >>>> inventor and engineer (1876-1958)
> >>>> _______________________________________________
> >>>> Sprinklerforum mailing list
> >>>> [email protected]
> >>>
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
> >>> _______________________________________________
> >>> Sprinklerforum mailing list
> >>> [email protected]
> >>>
> >>>
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
> >>
> >>
> >>
> >> --
> >> Ron Greenman
> >> Instructor
> >> Fire Protection Engineering Technology
> >> Bates Technical College
> >> 1101 So. Yakima Ave.
> >> Tacoma, WA 98405
> >>
> >> [email protected]
> >>
> >> http://www.bates.ctc.edu/fireprotection/
> >>
> >> 253.680.7346
> >> 253.576.9700 (cell)
> >>
> >> Member:
> >> ASEE, SFPE, ASCET, NFPA, AFSA, NFSA, AFAA, NIBS, WSAFM, WFC, WFSC
> >>
> >> They are happy men whose natures sort with their vocations. -Francis
> Bacon,
> >> essayist, philosopher, and statesman (1561-1626)
> >>
> >> A problem well stated is a problem half solved. -Charles F. Kettering,
> >> inventor and engineer (1876-1958)
> >> _______________________________________________
> >> Sprinklerforum mailing list
> >> [email protected]
> >>
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
> > _______________________________________________
> > Sprinklerforum mailing list
> > [email protected]
> >
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
>
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>



-- 
Juan Munguia

[image: Thorpe Design Inc – Fire Sprinkler Systems]

C 209-380-0599
O 925.634.5758
F 925.634.5975
E [email protected]
W www.thorpedesign.com
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to