These are not draft stops. They are draft curtains required by the listing of the sprinkler.
The listing only states it has to be constructed of a material that does not let heat pass over or through. Travis Mack, SET MFP Design, LLC "Follow" us on Facebook: https://www.facebook.com/pages/MFP-Design-LLC/92218417692 Send large files to MFP Design via: https://www.hightail.com/u/MFPDesign Sent from my iPhone > On Feb 11, 2016, at 10:28 PM, [email protected] wrote: > > Here is some food for though... > > Check out NFPA 13 Section 8.14.5.2 (3) > > ...The draft stop has to stay in place before and during sprinkler operation. > > This is from the CBC: > 718.3.1 Draftstopping materials. > Draftstopping materials shall not be less than 1/2-inch (12.7 mm) gypsum > board, 3/8-inch (9.5 mm) wood structural panel, 3/8-inch (9.5 mm) > particleboard, 1-inch (25-mm) nominal lumber, cement fiberboard, batts or > blankets of mineral wool or glass fiber, or other approved materials > adequately supported. The integrity of draftstops shall be maintained. > > Sent from my iPhone > >> On Feb 11, 2016, at 7:20 PM, rongreenman . <[email protected]> wrote: >> >> Ed has a good point. I was thinking the opposite, is it heavy enough to not >> blow around? >> >>> On Thu, Feb 11, 2016 at 6:45 PM, Travis Mack <[email protected]> wrote: >>> >>> Yeah. They just want to staple in place at top. >>> >>> Travis Mack, SET >>> MFP Design, LLC >>> "Follow" us on Facebook: >>> https://www.facebook.com/pages/MFP-Design-LLC/92218417692 >>> Send large files to MFP Design via: >>> https://www.hightail.com/u/MFPDesign >>> >>> Sent from my iPhone >>> >>>>> On Feb 11, 2016, at 6:45 PM, rongreenman . <[email protected]> >>>> wrote: >>>> >>>> just let it hang vertically along a long edge? >>>> >>>> >>>> On Thu, Feb 11, 2016 at 3:49 PM, Travis Mack, SET <[email protected]> >>>> wrote: >>>> >>>>> I have a customer that is asking if batt insulation can be secured to >>> the >>>>> roof decking and used as a draft curtain for the Tyco CC sprinklers. I >>>>> have never seen an application such as this, but it doesn't seem to be >>>>> prohibited in the datasheet. The only requirement is that it must be >>>>> constructed of a material so that heat can not pass through or over. >>>>> >>>>> What do you think? Could insulation secured to the roof/floor deck >>> serve >>>>> as a draft curtain for these sprinklers? My gut feeling is that it >>> would >>>>> not be suitable, but I can't find something in the data sheet to support >>>>> that. My only thought is that activation of a sprinkler could possibly >>>>> knock the insulation down. >>>>> >>>>> -- >>>>> Travis Mack, SET >>>>> MFP Design, LLC >>>>> 2508 E Lodgepole Drive >>>>> Gilbert, AZ 85298 >>>>> 480-505-9271 >>>>> fax: 866-430-6107 >>>>> email:[email protected] >>>>> >>>>> http://www.mfpdesign.com >>>>> https://www.facebook.com/pages/MFP-Design-LLC/92218417692 >>>>> Send large files to us via: https://www.hightail.com/u/MFPDesign >>>>> >>>>> _______________________________________________ >>>>> Sprinklerforum mailing list >>>>> [email protected] >>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org >>>> >>>> >>>> >>>> -- >>>> Ron Greenman >>>> Instructor >>>> Fire Protection Engineering Technology >>>> Bates Technical College >>>> 1101 So. Yakima Ave. >>>> Tacoma, WA 98405 >>>> >>>> [email protected] >>>> >>>> http://www.bates.ctc.edu/fireprotection/ >>>> >>>> 253.680.7346 >>>> 253.576.9700 (cell) >>>> >>>> Member: >>>> ASEE, SFPE, ASCET, NFPA, AFSA, NFSA, AFAA, NIBS, WSAFM, WFC, WFSC >>>> >>>> They are happy men whose natures sort with their vocations. -Francis >>> Bacon, >>>> essayist, philosopher, and statesman (1561-1626) >>>> >>>> A problem well stated is a problem half solved. -Charles F. Kettering, >>>> inventor and engineer (1876-1958) >>>> _______________________________________________ >>>> Sprinklerforum mailing list >>>> [email protected] >>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org >>> _______________________________________________ >>> Sprinklerforum mailing list >>> [email protected] >>> >>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org >> >> >> >> -- >> Ron Greenman >> Instructor >> Fire Protection Engineering Technology >> Bates Technical College >> 1101 So. Yakima Ave. >> Tacoma, WA 98405 >> >> [email protected] >> >> http://www.bates.ctc.edu/fireprotection/ >> >> 253.680.7346 >> 253.576.9700 (cell) >> >> Member: >> ASEE, SFPE, ASCET, NFPA, AFSA, NFSA, AFAA, NIBS, WSAFM, WFC, WFSC >> >> They are happy men whose natures sort with their vocations. -Francis Bacon, >> essayist, philosopher, and statesman (1561-1626) >> >> A problem well stated is a problem half solved. -Charles F. Kettering, >> inventor and engineer (1876-1958) >> _______________________________________________ >> Sprinklerforum mailing list >> [email protected] >> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org > _______________________________________________ > Sprinklerforum mailing list > [email protected] > http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org