These are not draft stops. They are draft curtains required by the listing of 
the sprinkler. 

The listing only states it has to be constructed of a material that does not 
let heat pass over or through. 

Travis Mack, SET
MFP Design, LLC
"Follow" us on Facebook: 
https://www.facebook.com/pages/MFP-Design-LLC/92218417692
Send large files to MFP Design via:
https://www.hightail.com/u/MFPDesign

Sent from my iPhone

> On Feb 11, 2016, at 10:28 PM, [email protected] wrote:
> 
> Here is some food for though...
> 
> Check out NFPA 13 Section 8.14.5.2 (3)
> 
> ...The draft stop has to stay in place before and during sprinkler operation.
> 
> This is from the CBC:
> 718.3.1 Draftstopping materials. 
> Draftstopping materials shall not be less than 1/2-inch (12.7 mm) gypsum 
> board, 3/8-inch (9.5 mm) wood structural panel, 3/8-inch (9.5 mm) 
> particleboard, 1-inch (25-mm) nominal lumber, cement fiberboard, batts or 
> blankets of mineral wool or glass fiber, or other approved materials 
> adequately supported. The integrity of draftstops shall be maintained.
> 
> Sent from my iPhone
> 
>> On Feb 11, 2016, at 7:20 PM, rongreenman . <[email protected]> wrote:
>> 
>> Ed has a good point. I was thinking the opposite, is it heavy enough to not
>> blow around?
>> 
>>> On Thu, Feb 11, 2016 at 6:45 PM, Travis Mack <[email protected]> wrote:
>>> 
>>> Yeah. They just want to staple in place at top.
>>> 
>>> Travis Mack, SET
>>> MFP Design, LLC
>>> "Follow" us on Facebook:
>>> https://www.facebook.com/pages/MFP-Design-LLC/92218417692
>>> Send large files to MFP Design via:
>>> https://www.hightail.com/u/MFPDesign
>>> 
>>> Sent from my iPhone
>>> 
>>>>> On Feb 11, 2016, at 6:45 PM, rongreenman . <[email protected]>
>>>> wrote:
>>>> 
>>>> just let it hang vertically along a long edge?
>>>> 
>>>> 
>>>> On Thu, Feb 11, 2016 at 3:49 PM, Travis Mack, SET <[email protected]>
>>>> wrote:
>>>> 
>>>>> I have a customer that is asking if batt insulation can be secured to
>>> the
>>>>> roof decking and used as a draft curtain for the Tyco CC sprinklers.  I
>>>>> have never seen an application such as this, but it doesn't seem to be
>>>>> prohibited in the datasheet.  The only requirement is that it must be
>>>>> constructed of a material so that heat can not pass through or over.
>>>>> 
>>>>> What do you think?  Could insulation secured to the roof/floor deck
>>> serve
>>>>> as a draft curtain for these sprinklers?  My gut feeling is that it
>>> would
>>>>> not be suitable, but I can't find something in the data sheet to support
>>>>> that.  My only thought is that activation of a sprinkler could possibly
>>>>> knock the insulation down.
>>>>> 
>>>>> --
>>>>> Travis Mack, SET
>>>>> MFP Design, LLC
>>>>> 2508 E Lodgepole Drive
>>>>> Gilbert, AZ 85298
>>>>> 480-505-9271
>>>>> fax: 866-430-6107
>>>>> email:[email protected]
>>>>> 
>>>>> http://www.mfpdesign.com
>>>>> https://www.facebook.com/pages/MFP-Design-LLC/92218417692
>>>>> Send large files to us via: https://www.hightail.com/u/MFPDesign
>>>>> 
>>>>> _______________________________________________
>>>>> Sprinklerforum mailing list
>>>>> [email protected]
>>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>>>> 
>>>> 
>>>> 
>>>> --
>>>> Ron Greenman
>>>> Instructor
>>>> Fire Protection Engineering Technology
>>>> Bates Technical College
>>>> 1101 So. Yakima Ave.
>>>> Tacoma, WA 98405
>>>> 
>>>> [email protected]
>>>> 
>>>> http://www.bates.ctc.edu/fireprotection/
>>>> 
>>>> 253.680.7346
>>>> 253.576.9700 (cell)
>>>> 
>>>> Member:
>>>> ASEE, SFPE, ASCET, NFPA, AFSA, NFSA, AFAA, NIBS, WSAFM, WFC, WFSC
>>>> 
>>>> They are happy men whose natures sort with their vocations. -Francis
>>> Bacon,
>>>> essayist, philosopher, and statesman (1561-1626)
>>>> 
>>>> A problem well stated is a problem half solved. -Charles F. Kettering,
>>>> inventor and engineer (1876-1958)
>>>> _______________________________________________
>>>> Sprinklerforum mailing list
>>>> [email protected]
>>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>>> _______________________________________________
>>> Sprinklerforum mailing list
>>> [email protected]
>>> 
>>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>> 
>> 
>> 
>> -- 
>> Ron Greenman
>> Instructor
>> Fire Protection Engineering Technology
>> Bates Technical College
>> 1101 So. Yakima Ave.
>> Tacoma, WA 98405
>> 
>> [email protected]
>> 
>> http://www.bates.ctc.edu/fireprotection/
>> 
>> 253.680.7346
>> 253.576.9700 (cell)
>> 
>> Member:
>> ASEE, SFPE, ASCET, NFPA, AFSA, NFSA, AFAA, NIBS, WSAFM, WFC, WFSC
>> 
>> They are happy men whose natures sort with their vocations. -Francis Bacon,
>> essayist, philosopher, and statesman (1561-1626)
>> 
>> A problem well stated is a problem half solved. -Charles F. Kettering,
>> inventor and engineer (1876-1958)
>> _______________________________________________
>> Sprinklerforum mailing list
>> [email protected]
>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to