That is what the contractor is arguing. The NFPA 13 definitions of draft curtains are in reference to separation of ESFR and SR, water spray systems and hazard separation.

It is an outside the box thinking for sure. As you say, if it is stapled to the deck, that would prevent heat from passing through and over. That is the only criteria in the datasheet.


Travis Mack, SET
MFP Design, LLC
2508 E Lodgepole Drive
Gilbert, AZ 85298
480-505-9271
fax: 866-430-6107
email:[email protected]

http://www.mfpdesign.com
https://www.facebook.com/pages/MFP-Design-LLC/92218417692
Send large files to us via: https://www.hightail.com/u/MFPDesign

On 2/12/2016 8:19 AM, Matthew J Willis wrote:
LOL.

I say it does meet it.
Insulation by default blocks heat..

R/
Matt


Matthew J. Willis
Project Manager
Rapid Fire Protection Inc.
*NEW ADDRESS*
1530 Samco Road
Rapid City, SD 57702
Office-605.348.2342
Direct Line-605.593.5063
Cell-605.391.2733
Fax:-605.348.0108






-----Original Message-----
From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Travis Mack
Sent: Friday, February 12, 2016 8:16 AM
To: [email protected]
Subject: Re: Tyco CC sprinklers / draft curtain

Well, the customer called Tyco and they could not say definitively if the 
insulation would meet the requirements or not.



Travis Mack, SET
MFP Design, LLC
"Follow" us on Facebook: 
https://www.facebook.com/pages/MFP-Design-LLC/92218417692
Send large files to MFP Design via:
https://www.hightail.com/u/MFPDesign

Sent from my iPhone

On Feb 11, 2016, at 4:49 PM, Travis Mack, SET <[email protected]> wrote:

I have a customer that is asking if batt insulation can be secured to the roof 
decking and used as a draft curtain for the Tyco CC sprinklers.  I have never 
seen an application such as this, but it doesn't seem to be prohibited in the 
datasheet.  The only requirement is that it must be constructed of a material 
so that heat can not pass through or over.

What do you think?  Could insulation secured to the roof/floor deck serve as a 
draft curtain for these sprinklers?  My gut feeling is that it would not be 
suitable, but I can't find something in the data sheet to support that.  My 
only thought is that activation of a sprinkler could possibly knock the 
insulation down.

--
Travis Mack, SET
MFP Design, LLC
2508 E Lodgepole Drive
Gilbert, AZ 85298
480-505-9271
fax: 866-430-6107
email:[email protected]

http://www.mfpdesign.com
https://www.facebook.com/pages/MFP-Design-LLC/92218417692
Send large files to us via: https://www.hightail.com/u/MFPDesign

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to