I appreciate your patience with me Travis.
Now please place your foot on this device and I'll see if we have your size
in stock :)
On Mar 29, 2016 5:55 PM, "Travis Mack, SET" <[email protected]> wrote:

> I'll try one time then give up.
>
> This was never really about activation times and obstruction issue. You
> have a fair bit of flexibility with the attic sprinklers...16-22" down.
>
> The problem is when you have a varying roof deck, from a design side - for
> guys that try to be as correct as possible, it is darn near impossible to
> get this correct.  Again the only way I can see to fix it from the
> descriptions here is hang the main much lower than you would normally for a
> system like this and then field cut every sprig so that you are 16-22"
> below the insulation at the point the sprinkler is located.  That amount of
> labor was likely not included in the bid as it is pretty easy for a decent
> design guy to hit those sprigs or even not use sprigs if you have a
> consistent roof deck.
>
> The idea of getting the builder to create a fairly smooth deck was a good
> idea as it seems that it was just done haphazardly by the insulator.
>
> Our job is not just about activation times and stuff like that (which is
> vitally important).  It is also about getting the correct material
> fabricated so the fitter can install the system in a timely manner.
>
> Travis Mack, SET
> MFP Design, LLC
> 2508 E Lodgepole Drive
> Gilbert, AZ 85298
> 480-505-9271
> fax: 866-430-6107
> email:[email protected]
>
> http://www.mfpdesign.com
> https://www.facebook.com/pages/MFP-Design-LLC/92218417692
> Send large files to us via: https://www.hightail.com/u/MFPDesign
> LinkedIn: https://www.linkedin.com/in/travismack
>
> On 3/29/2016 3:48 PM, Brad Casterline wrote:
>
>> Well, if you guys say so then fine, I appologize.
>> I just woke up from a nap and, the set-up is still clear-- I just don't
>> think the problem is as dramatic as you guys do.
>> We have not had to wet the underside of the deck since the 'old style'
>> days. So to me it is an obstrution issue, all along the path of the throw.
>> The deflectors are angled and the same angle is good for up to 30 feet of
>> throw.
>> Technically you could chip out enough insulation directly above the heads,
>> say one square foot by whatever depth to get min 16" deflector
>> distance...,
>> could you not?
>>
>> Or maybey I should go back to bed and wake up as a shoe salesman.
>>
>> Brad
>> On Mar 29, 2016 3:37 PM, "Brian Harris" <[email protected]>
>> wrote:
>>
>> Travis-
>>> Yup that about sums it up, I thought I was losing my mind there for a
>>> minute.....
>>>
>>> Brian Harris, CET
>>> BVS Systems Inc.
>>> bvssytemsinc.com
>>>
>>>
>>> -----Original Message-----
>>> From: Sprinklerforum [mailto:
>>> [email protected]] On Behalf Of Travis Mack
>>> Sent: Tuesday, March 29, 2016 4:05 PM
>>> To: [email protected]
>>> Subject: Re: Tyco Attic Heads
>>>
>>> Brian:
>>>
>>> Your problem has been very clear from the beginning.
>>>
>>> My guess is you would have to drop the main to about 2' below the lowest
>>> point of insulation. Then field cut every sprig. Couple that with a
>>> sloping
>>> dry system and you have an installation nightmare.
>>>
>>> Travis Mack, SET
>>> MFP Design, LLC
>>> "Follow" us on Facebook:
>>> https://www.facebook.com/pages/MFP-Design-LLC/92218417692
>>> Send large files to MFP Design via:
>>> https://www.hightail.com/u/MFPDesign
>>>
>>> Sent from my iPhone
>>>
>>> On Mar 29, 2016, at 12:58 PM, Brian Harris <[email protected]>
>>>>
>>> wrote:
>>>
>>>> Brad-
>>>> You're missing the point or maybe I haven't explained it clearly which
>>>>
>>> is entirely probable. The deflector distance is no longer taken from the
>>> roof deck, it has to be taken from the bottom of the insulation. With the
>>> insulation varying greatly in thickness it is damn near impossible to
>>> install the system with some reasonable sense of order. Hence the reason
>>> for "some kind of iso-surface".
>>>
>>>> Brian Harris, CET
>>>> BVS Systems Inc.
>>>> bvssytemsinc.com
>>>>
>>>>
>>>> -----Original Message-----
>>>> From: Sprinklerforum
>>>> [mailto:[email protected]] On Behalf Of
>>>> Brad Casterline
>>>> Sent: Tuesday, March 29, 2016 1:50 PM
>>>> To: [email protected]
>>>> Subject: RE: Tyco Attic Heads
>>>>
>>>> In other words, only where the intermediate members exceed 10" depth,
>>>>
>>> will it Maybe need a shave - a few inches deep by six feet long.
>>>
>>>> It is ludicrous to insist on some kind of insulation iso-surface for
>>>>
>>> things to work right!
>>>
>>>> On Mar 29, 2016 12:28 PM, "Brad Casterline" <[email protected]>
>>>>>
>>>> wrote:
>>>
>>>>
>>>>> It would only be a problem if the rafter depth plus gob depth
>>>>> exceeded deflector depth, so you're looking at 16" to 22" (6"
>>>>> variation, like you said).
>>>>>
>>>>> But in that regard, it is not an activation issue, it is only an
>>>>> obstruction issue.
>>>>> Shave it where necessary to not be an obstruction?
>>>>> On Mar 29, 2016 12:07 PM, "Brian Harris" <[email protected]>
>>>>> wrote:
>>>>>
>>>>> Brad-
>>>>>> The real issue we're having is the haphazard way the sprayed on
>>>>>> insulation was installed, there's no way to establish minimum &
>>>>>> maximum deflector distances.
>>>>>>
>>>>>> Brian Harris, CET
>>>>>> BVS Systems Inc.
>>>>>> bvssytemsinc.com
>>>>>>
>>>>>>
>>>>>> -----Original Message-----
>>>>>> From: Sprinklerforum [mailto:
>>>>>> [email protected]] On Behalf Of Brad
>>>>>> Casterline
>>>>>> Sent: Tuesday, March 29, 2016 11:23 AM
>>>>>> To: [email protected]
>>>>>> Subject: RE: Tyco Attic Heads
>>>>>>
>>>>>> Nope. Smoothness above the sprinkler only affects activation times,
>>>>>> and the differences are only a few seconds.
>>>>>> Do you worry if the intermediate framing members are 2x4, 2x6, 2x8,
>>>>>> or
>>>>>> 2x10 (a 6" variation)? Do you worry if they are perpendicular or
>>>>>> parallel to the throw? No, because min deflector distance for
>>>>>> back-to-back at the peak is 16". This is to get the throw beneath
>>>>>> the 'unsmoothness' of the bottom of the deck.
>>>>>> The U.L. tests of Tyco BB heads 'started' with previously listed QR,
>>>>>> EC
>>>>>> heads- only the Deflectors were changed, and the throw patterns at
>>>>>> different pressures were measured. They did that by not changing the
>>>>>> bottom of the deck or changing deflector distance, but by raising
>>>>>> and lowering the Floor :).
>>>>>>
>>>>>> And actually I think a little roughness at the bottom of the deck
>>>>>> might even enhance activation a bit-- but I am certainly no
>>>>>> Sprinkler
>>>>>> Scientist- and the Modeling of BB heads activation and patterns I
>>>>>> have done has been rather coarse, i.e., quick and dirty ;)
>>>>>>
>>>>>> b
>>>>>> On Mar 29, 2016 9:46 AM, "Brian Harris" <[email protected]>
>>>>>> wrote:
>>>>>>
>>>>>> I talked with tech support and while he wasn't too concerned about
>>>>>>> the roughness off the insulation he did agree the insulation needs
>>>>>>> to be "shaved" to a uniform depth to assure proper deflector
>>>>>>>
>>>>>> distances.
>>>
>>>> Brian Harris, CET
>>>>>>> BVS Systems Inc.
>>>>>>> bvssytemsinc.com
>>>>>>>
>>>>>>>
>>>>>>> -----Original Message-----
>>>>>>> From: Sprinklerforum [mailto:
>>>>>>> [email protected]] On Behalf Of Bruce
>>>>>>> Verhei
>>>>>>> Sent: Tuesday, March 29, 2016 10:44 AM
>>>>>>> To: [email protected]
>>>>>>> Subject: Re: Tyco Attic Heads
>>>>>>>
>>>>>>> I like Matt's advice. Tyco may have information from original test
>>>>>>>
>>>>>> series.
>>>>>>
>>>>>>> Sometimes some of conditions are to meet extreme distance or a
>>>>>>> minimum available pressure.
>>>>>>>
>>>>>>> While I'd repeat that Tyco's comments would apply to this
>>>>>>> particular project only, could you post?
>>>>>>>
>>>>>>> Best
>>>>>>>
>>>>>>> Bruce
>>>>>>>
>>>>>>> On Mar 29, 2016, at 06:41, Matt Grise <[email protected]> wrote:
>>>>>>>>
>>>>>>>> I would call tyco's technical hotline.
>>>>>>>>
>>>>>>>> Matt Grisé PE*, LEED AP, NICET II Sales Engineer Alliance Fire
>>>>>>>> Protection
>>>>>>>> 130 w 9th Ave.
>>>>>>>> North Kansas City, MO 64116
>>>>>>>>
>>>>>>>> *Licensed in KS & MO
>>>>>>>>
>>>>>>>> 913.888.0647 ph
>>>>>>>> 913.888.0618 f
>>>>>>>> 913.526.7443 cell
>>>>>>>> www. AFPsprink.com
>>>>>>>>
>>>>>>>>
>>>>>>>>
>>>>>>>> -----Original Message-----
>>>>>>>> From: Sprinklerforum
>>>>>>>> [mailto:[email protected]] On Behalf
>>>>>>>> Of Brian Harris
>>>>>>>> Sent: Tuesday, March 29, 2016 8:40 AM
>>>>>>>> To: [email protected]
>>>>>>>> Subject: RE: Tyco Attic Heads
>>>>>>>>
>>>>>>>> "bounce..."
>>>>>>>>
>>>>>>>> Brian Harris, CET
>>>>>>>> BVS Systems Inc.
>>>>>>>> bvssytemsinc.com
>>>>>>>>
>>>>>>>> -----Original Message-----
>>>>>>>> From: Sprinklerforum
>>>>>>>> [mailto:[email protected]] On Behalf
>>>>>>>> Of Brian Harris
>>>>>>>> Sent: Tuesday, March 29, 2016 8:23 AM
>>>>>>>> To: [email protected]
>>>>>>>> Subject: Tyco Attic Heads
>>>>>>>>
>>>>>>>> Working on a project that we've installed Tyco attic heads and the
>>>>>>>> GC
>>>>>>>>
>>>>>>> has now gone in and added roughly several inches of spray on
>>>>>>>
>>>>>> insulation.
>>>
>>>> When I say roughly I mean roughly, the depth varies from 6" to 12"
>>>>>>> with no consistency what so ever. I've told them that most of the
>>>>>>> piping will have to be lowered to stay within the required
>>>>>>> clearances but I also think the insulation needs to be "shaved" to
>>>>>>> a smooth consistent finish, obviously that didn't go over so well.
>>>>>>> Since attic heads are considered extended coverage I think it's
>>>>>>> safe to assume they need to be installed per the requirements of
>>>>>>> NFPA as well, under a smooth flat surface. Am I missing something?
>>>>>>>
>>>>>>>> Brian Harris, CET
>>>>>>>> BVS Systems Inc.
>>>>>>>> Sprinkler Division
>>>>>>>> bvssystemsinc.com<http://bvssystemsinc.com/>
>>>>>>>> Phone: 704.896.9989
>>>>>>>> Fax: 704.896.1935
>>>>>>>>
>>>>>>>> _______________________________________________
>>>>>>>> Sprinklerforum mailing list
>>>>>>>> [email protected]
>>>>>>>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesp
>>>>>>>> rin kl er.org _______________________________________________
>>>>>>>> Sprinklerforum mailing list
>>>>>>>> [email protected]
>>>>>>>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesp
>>>>>>>> rin kl er.org _______________________________________________
>>>>>>>> Sprinklerforum mailing list
>>>>>>>> [email protected]
>>>>>>>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesp
>>>>>>>> rin
>>>>>>>> kl
>>>>>>>> er.org
>>>>>>>>
>>>>>>> _______________________________________________
>>>>>>> Sprinklerforum mailing list
>>>>>>> [email protected]
>>>>>>>
>>>>>>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firespri
>>>>>>> nkl er.org _______________________________________________
>>>>>>> Sprinklerforum mailing list
>>>>>>> [email protected]
>>>>>>>
>>>>>>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firespri
>>>>>>> nkl
>>>>>>> er.org
>>>>>>>
>>>>>> _______________________________________________
>>>>>> Sprinklerforum mailing list
>>>>>> [email protected]
>>>>>>
>>>>>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprin
>>>>>> k ler.org _______________________________________________
>>>>>> Sprinklerforum mailing list
>>>>>> [email protected]
>>>>>>
>>>>>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprin
>>>>>> k
>>>>>> ler.org
>>>>>>
>>>>> _______________________________________________
>>>> Sprinklerforum mailing list
>>>> [email protected]
>>>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl
>>>> er.org _______________________________________________
>>>> Sprinklerforum mailing list
>>>> [email protected]
>>>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl
>>>> er.org
>>>>
>>> _______________________________________________
>>> Sprinklerforum mailing list
>>> [email protected]
>>>
>>>
>>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>>> _______________________________________________
>>> Sprinklerforum mailing list
>>> [email protected]
>>>
>>>
>>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>>>
>>> _______________________________________________
>> Sprinklerforum mailing list
>> [email protected]
>>
>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>>
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
>
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to