Well, thanks anyway.
I guess all the heavy lifters must be too busy hobnobbing with the upper
echelon to consider what i thought was a compelling case.

I am nothing if not tenacious though so I'll try again some other day on
something else.

rbc
On Jun 13, 2016 7:57 AM, "Brad Casterline" <[email protected]> wrote:

https://www.dropbox.com/s/5ut5v9vbbk3y5ii/JAMES%20ANGLED%20WALL%20SPACING.pdf?dl=0



Here is what I was thinking. I agree if using standard coverage sprks
Examples 2 and 3 would need a sprk added, but it is not due to the distance
between B and C. Due to the round pattern and square spacing I believe
Example 4 is (at least) equivalent to Example 1.



Anyone with me on this?



thanks,

Brad


------------------------------

*From:* Sprinklerforum [mailto:
[email protected]] *On Behalf Of *Kenneth
Berman
*Sent:* Sunday, June 12, 2016 2:03 PM
*To:* [email protected]
*Subject:* Re: Angled Wall Spacing



using extended coverage allows further distance from walls, which brings
heads closer than 21-2 1/2.



On Fri, Jun 10, 2016 at 2:58 PM, Parsley Consulting <
[email protected]> wrote:

I'll chime in as well.

Example 3 is closer to being correct, as the sprinklers at B and C aren't
more than 7'-6" from a wall, measured perpendicular to the wall.

The error, to me, is the distance of 21'-2½" between B and C.  I don't see
how that would be allowable, even if you were using extended coverage
sprinklers.  Table 8.8.2.1.2 limits the distance between such sprinklers,
with the maximum being 20'-0" in OH and LH occupancies.

I don't see how that would be allowed.






*Ken Wagoner, SET Parsley Consulting 350 West 9th Avenue, Suite 206
Escondido, California 92025 Phone 760-745-6181 <760-745-6181> Visit our
website <http://www.parsleyconsulting.com/> *

On 06/10/2016 12:51 PM, Ben Young wrote:

Agreed Tony.



On Friday, June 10, 2016, Tony Eggster < <[email protected]>
[email protected]> wrote:

#2 & #3 are both wrong.

#2 is spaced too far, measured perpendicularly, from the angled wall.

#3 will require an additional sprinkler between B and C. If you draw a
15X15 square template on your drawings you will see an obvious void of
sprinkler coverage requiring protection.



On Fri, Jun 10, 2016 at 12:20 PM, James Litvak <[email protected]>
wrote:

The problem with A.8.6.3.2.3 is that it only shows the one sprinkler. What
I'm concerned about is the distance between sprinklers B and C. In example
3 all the sprinklers are spaced correctly from the walls but B and C are
21'-2 1/2" apart. The way I understand it, they still need to be 15'-0"
along that wall, even though they're spaced correctly from every wall. Is
that correct?





James



On Friday, June 10, 2016, Brian Harris <[email protected]> wrote:

Check out A.8.6.3.2.3 it should shed some light on it.



*Brian Harris, CET*

BVS Systems Inc.

bvssytemsinc.com <http://bvssystemsinc.com/>



*From:* Sprinklerforum [mailto:
[email protected]] *On Behalf Of *James Litvak
*Sent:* Friday, June 10, 2016 1:45 PM
*To:* [email protected]
*Subject:* Angled Wall Spacing



I am wondering if I've been thinking about sprinkler spacing along angled
walls properly. What I mean is walls not at a right angle. The PDF I made
in the link below really helps explain it. In example 1, four heads are
spaced correctly at 225 sq. ft. In examples 2 and 3 one of the walls is
angled. My question is, are either example 2 or 3 correct, or are they both
wrong? My thought is that example 2 is incorrect, and for example 3 to be
correct there would need to be an additional sprinkler along the angled
wall between sprinklers B and C.

<https://www.dropbox.com/s/7fg0l79rtwbawne/Angled%20Wall%20Spacing.pdf?dl=0>
https://www.dropbox.com/s/7fg0l79rtwbawne/Angled%20Wall%20Spacing.pdf?dl=0



James


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org





-- 

Benjamin Young



_______________________________________________

Sprinklerforum mailing list

[email protected]

http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org




_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org



_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to