Gentlemen,

You should be solving this puzzle using 15ft squares to comply with the
usual rules with no uncovered floor areas.

Alternatively use a circle of 21’-2 1/2” diameter and have no uncovered
floor areas. The 15ft circle is not showing the correct solution.

The circle is based on the diagonal of the 15ft square. Check that area of
coverage and distance between sprinklers does not exceed the rules maximum
spacing.

Regards,

Russell Gregory

Christchurch

New Zealand

 

From: Sprinklerforum [mailto:[email protected]]
On Behalf Of Brad Casterline
Sent: Tuesday, 14 June 2016 12:57 AM
To: [email protected]
Subject: RE: Angled Wall Spacing

 

https://www.dropbox.com/s/5ut5v9vbbk3y5ii/JAMES%20ANGLED%20WALL%20SPACING.pd
f?dl=0

 

Here is what I was thinking. I agree if using standard coverage sprks
Examples 2 and 3 would need a sprk added, but it is not due to the distance
between B and C. Due to the round pattern and square spacing I believe
Example 4 is (at least) equivalent to Example 1.

 

Anyone with me on this?

 

thanks,

Brad  

 

  _____  

From: Sprinklerforum [mailto:[email protected]]
On Behalf Of Kenneth Berman
Sent: Sunday, June 12, 2016 2:03 PM
To: [email protected]
Subject: Re: Angled Wall Spacing

 

using extended coverage allows further distance from walls, which brings
heads closer than 21-2 1/2.

 

On Fri, Jun 10, 2016 at 2:58 PM, Parsley Consulting
<[email protected]> wrote:

I'll chime in as well.

Example 3 is closer to being correct, as the sprinklers at B and C aren't
more than 7'-6" from a wall, measured perpendicular to the wall.

The error, to me, is the distance of 21'-2½" between B and C.  I don't see
how that would be allowable, even if you were using extended coverage
sprinklers.  Table 8.8.2.1.2 limits the distance between such sprinklers,
with the maximum being 20'-0" in OH and LH occupancies.

I don't see how that would be allowed.

Ken Wagoner, SET
Parsley Consulting
350 West 9th Avenue, Suite 206
Escondido, California 92025
Phone 760-745-6181
Visit our website <http://www.parsleyconsulting.com/>  

On 06/10/2016 12:51 PM, Ben Young wrote:

Agreed Tony.



On Friday, June 10, 2016, Tony Eggster <[email protected]> wrote:

#2 & #3 are both wrong.

#2 is spaced too far, measured perpendicularly, from the angled wall.

#3 will require an additional sprinkler between B and C. If you draw a 15X15
square template on your drawings you will see an obvious void of sprinkler
coverage requiring protection.

 

On Fri, Jun 10, 2016 at 12:20 PM, James Litvak <[email protected]>
wrote:

The problem with A.8.6.3.2.3 is that it only shows the one sprinkler. What
I'm concerned about is the distance between sprinklers B and C. In example 3
all the sprinklers are spaced correctly from the walls but B and C are 21'-2
1/2" apart. The way I understand it, they still need to be 15'-0" along that
wall, even though they're spaced correctly from every wall. Is that correct?


 

 

James



On Friday, June 10, 2016, Brian Harris <[email protected]> wrote:

Check out A.8.6.3.2.3 it should shed some light on it.

 

Brian Harris, CET

BVS Systems Inc.

bvssytemsinc.com <http://bvssystemsinc.com/> 

 

From: Sprinklerforum [mailto:[email protected]]
On Behalf Of James Litvak
Sent: Friday, June 10, 2016 1:45 PM
To: [email protected]
Subject: Angled Wall Spacing

 

I am wondering if I've been thinking about sprinkler spacing along angled
walls properly. What I mean is walls not at a right angle. The PDF I made in
the link below really helps explain it. In example 1, four heads are spaced
correctly at 225 sq. ft. In examples 2 and 3 one of the walls is angled. My
question is, are either example 2 or 3 correct, or are they both wrong? My
thought is that example 2 is incorrect, and for example 3 to be correct
there would need to be an additional sprinkler along the angled wall between
sprinklers B and C. 

https://www.dropbox.com/s/7fg0l79rtwbawne/Angled%20Wall%20Spacing.pdf?dl=0

 

James


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

 

 

-- 

Benjamin Young




_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

 


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

 

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to