I was taught that sidewall sprinklers cannot be used in an extra hazard
application.  At least that is what I recall.  Additionally, the protection
areas and maximum spacing table for sidewall heads do not have any
information for extra hazard occupancies. I am reviewing a set of plans for
a paint spray booth and sprinklers must be spaced in ducts at 12 foot
intervals.  The designers called out sidewall sprinklers on plans.  How is
this best accomplished if you can't use sidewall sprinklers?

Zach