It isn't but you can use pendents in any position in a duct. Use a dry pendant near the top if you have freezing conditions.
On Mon, Aug 8, 2016 at 3:02 PM, Zachary Siegrist <[email protected] > wrote: > I was taught that sidewall sprinklers cannot be used in an extra hazard > application. At least that is what I recall. Additionally, the protection > areas and maximum spacing table for sidewall heads do not have any > information for extra hazard occupancies. I am reviewing a set of plans for > a paint spray booth and sprinklers must be spaced in ducts at 12 foot > intervals. The designers called out sidewall sprinklers on plans. How is > this best accomplished if you can't use sidewall sprinklers? > > Zach > > > _______________________________________________ > Sprinklerforum mailing list > [email protected] > http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler. > org > > -- Ron Greenman 4110 Olson Dr., NW Gig Harbor, WA 98335 [email protected] 253.576.9700 The Universe is monstrously indifferent to the presence of man. -Werner Herzog, screenwriter, film director, author, actor and opera director (1942-)