How about the spray booth for a 747 Brad? Or a B-52?

On Mon, Aug 8, 2016 at 5:38 PM, Brad Casterline <[email protected]>
wrote:

> Show me a spray booth with forty sprinklers Steve
> On Aug 8, 2016 7:36 PM, "Steve Leyton" <[email protected]> wrote:
>
>> Sure.  And fires that can be spread by running fuel such as plastics and
>> FCL’s (not to mention BLEVE’s) can set off 40 standard response sprinklers
>> in a minute.   I can only imagine the sheer volume of responding sprinklers
>> and skipping that could occur based on how smooth or bumpy the roof/ceiling
>> assembly is if you started wantonly plugging QR control-mode sprinklers
>> into EH fires.   (On paper) MDD = .80    ADD = .275
>>
>>
>>
>> My opinion only,
>>
>> Steve L.
>>
>>
>>
>>
>>
>>
>>
>> *From:* Sprinklerforum [mailto:sprinklerforum-bounces
>> @lists.firesprinkler.org] *On Behalf Of *Brad Casterline
>> *Sent:* Monday, August 08, 2016 5:17 PM
>> *To:* [email protected]
>> *Subject:* Re: Paint spray application
>>
>>
>>
>> Shakey ground is all i have ever known Ken.
>> I am no more a professional than you are.
>> THINK MAN!
>> small spaces with fast fires need the fastest acting sprinklers we can
>> muster.
>> I've been in court myself a couple times- neither one over sprinklers
>> though--
>> please stop being so stodgy!
>>
>> On Aug 8, 2016 7:05 PM, "Parsley Consulting" <[email protected]>
>> wrote:
>>
>> I don't know, Brad.  You're standing on pretty shaky ground there.
>>
>> The decision to use QR sprinklers in an extra hazard occpuancy is a
>> direct contradiction to 8.4.1.1.2 of NFPA 13, including the 2016 edition,
>> or a similar section number, at least as far back as the 1999 edition.  If
>> you install QR sprinklers in a space that is legitimately classed as an
>> extra hazard occupancy, aren't you directly contradicting this particular
>> section of NFPA 13?  The handbook provides the following explanatory text
>> on the topic:
>>
>> Extra hazard occupancies are characterized by the probability of
>> fast-developing fires with high heat release rates that have the potential
>> to open a large number of quick-response sprinklers before the sprinklers
>> have time to control the fire. The operation of a large number of
>> sprinklers in a relatively short time period has the potential to overtax
>> the system. For this reason, quick-response sprinklers using the area
>> design method of Chapter 11 are not permitted for the protection of extra
>> hazard occupancies. Additional perspective on this can be found in the
>> discussion of safety margin found in B.2.1.
>>
>> Further, I'm not aware of any QR sprinkler which has been tested and
>> listed by an NRTL for use in protecting extra hazard occupancies.  Barring
>> that, to follow the guidance you're suggesting the
>> contractor/designer/installer has to violate both NFPA 13 AND the listing
>> of the sprinkler.  I'm not suggesting the gloom and doom drama of "people
>> could die", however it does concern me greatly when I read suggestions to
>> ignore both texts.
>>
>> My thought about that is to make sure your insurance is paid up, and have
>> a good lawyer on retainer.  I don't know of a good defense while sitting in
>> the witness chair to a question similar to, "Are you telling me you ignored
>> the applicable law and the manufacturer's recommendations for the
>> installation of that sprinkler?"
>>
>> When I have nightmares I think about having to answer questions similar
>> to that.
>>
>>
>>
>>
>>
>>
>> *Ken Wagoner, SET Parsley Consulting 350 West 9th Avenue, Suite 206
>> Escondido, California 92025 Phone 760-745-6181 <760-745-6181> Visit our
>> website <http://www.parsleyconsulting.com/> *
>>
>>
>> On 08/08/2016 4:17 PM, Brad Casterline wrote:
>>
>> We're not suppose to use QR in EH either but I say balderdash.
>> That is for big open spaces beacase you could have a bunch of heads going
>> off way over there when the emergency is way over here. Small spaces with
>> fast fires are better off if you use low temp qr and calc every head
>> possible going off
>>
>>
>>
>>
>>
>>
>> _______________________________________________
>> Sprinklerforum mailing list
>> [email protected]
>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-
>> firesprinkler.org
>>
>> _______________________________________________
>> Sprinklerforum mailing list
>> [email protected]
>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-
>> firesprinkler.org
>>
>>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.
> org
>
>


-- 
Ron Greenman

4110 Olson Dr., NW
Gig Harbor, WA 98335

[email protected]

253.576.9700

The Universe is monstrously indifferent to the presence of man. -Werner
Herzog, screenwriter, film director, author, actor and opera
director (1942-)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to