We're not suppose to use QR in EH either but I say balderdash.
That is for big open spaces beacase you could have a bunch of heads going
off way over there when the emergency is way over here. Small spaces with
fast fires are better off if you use low temp qr and calc every head
possible going off
On Aug 8, 2016 5:02 PM, "Zachary Siegrist" <[email protected]>
wrote:

> I was taught that sidewall sprinklers cannot be used in an extra hazard
> application.  At least that is what I recall.  Additionally, the protection
> areas and maximum spacing table for sidewall heads do not have any
> information for extra hazard occupancies. I am reviewing a set of plans for
> a paint spray booth and sprinklers must be spaced in ducts at 12 foot
> intervals.  The designers called out sidewall sprinklers on plans.  How is
> this best accomplished if you can't use sidewall sprinklers?
>
> Zach
>
>