Sorry but unless you can convince the EOR, AHJ and Insurance people of your 
concept, it just ain’t gonna fly.

Designing something completely contrary to the manufacturers listing based on a 
feeling or opinion alone is a recipe for litigation.

And if you look at some of the FM Global recommendations for storage there are 
times when the recommendation seems to be contradictory to logic as far as 
using higher temperature and different design criteria but they have actual 
testing as their backup.


Craig L. Prahl
Fire Protection Group Lead/SME
CH2M
200 Verdae Blvd.
Greenville, SC  29607
Direct - 864.920.7540
Fax - 864.920.7129
CH2MHILL Extension  77540
[email protected]


From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Brad Casterline
Sent: Monday, August 08, 2016 7:18 PM
To: [email protected]
Subject: Re: Paint spray application [EXTERNAL]


We're not suppose to use QR in EH either but I say balderdash.
That is for big open spaces beacase you could have a bunch of heads going off 
way over there when the emergency is way over here. Small spaces with fast 
fires are better off if you use low temp qr and calc every head possible going 
off
On Aug 8, 2016 5:02 PM, "Zachary Siegrist" 
<[email protected]<mailto:[email protected]>> wrote:
I was taught that sidewall sprinklers cannot be used in an extra hazard 
application.  At least that is what I recall.  Additionally, the protection 
areas and maximum spacing table for sidewall heads do not have any information 
for extra hazard occupancies. I am reviewing a set of plans for a paint spray 
booth and sprinklers must be spaced in ducts at 12 foot intervals.  The 
designers called out sidewall sprinklers on plans.  How is this best 
accomplished if you can't use sidewall sprinklers?

Zach

_______________________________________________
Sprinklerforum mailing list
[email protected]<mailto:[email protected]>
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to