Kevin,
That's true for most of the sprinklers in the diagram but look at figure
A.3.3.206.6 (2019) - the farthest loop from the supply has sprinklers on it
and it's connecting both loops - those sprinklers are receiving water from
two mains. Likewise, per the definition of a main the only main in Ed's
example is the center line. Everything else are looped branchlines per the
definitions.

JH


On Wed, Oct 27, 2021 at 9:09 AM Kevin Hall via Sprinklerforum <
[email protected]> wrote:

> The annex shows the branch lines fed by the cross main from two directions,
> the sprinkler can still only receive water from one direction from the
> branch line... that is the distinction in the definition.
>
> The above is my opinion and has not been processed as a formal
> interpretation in accordance with the NFPA Regulations Governing Committee
> Projects. This is provided with the understanding that the AFSA assumes no
> liability for this opinion or actions taken on it and they are not to be
> considered the official position of the NFPA or its technical committees.
> AFSA cannot provide design or consulting engineering services, and this
> opinion should therefore not be considered, nor relied upon, as such.
>
>
> Kevin Hall, M.Eng., P.E., ET, CWBSP, PMSFPE
>
> Coordinator, Engineering and Technical Services
>
> American Fire Sprinkler Association
>
> [email protected]
>
> 214-349-5971
>
>
> On Wed, Oct 27, 2021 at 12:05 PM J H via Sprinklerforum <
> [email protected]> wrote:
>
> > I have a problem with the simplified definition floated out here that a
> > grid system is one that feeds a sprinkler from two directions because of
> > the illustration of a looped system in the annex of '13 which shows
> > sprinklers attached to the end portion of the loop resulting in those
> > sprinklers receiving water from two directions. Technically the only
> cross
> > main is the center piping - everything else are looped branchlines. I
> would
> > be prepared for kickback from a knowledgeable AHJ. I would personally
> avoid
> > a design like this if at all possible to avoid the headache of hashing it
> > out w/ an AHJ. But if it's the difference between a system like this and
> a
> > fire pump it might be worth the fight.
> >
> > JH
> >
> > On Wed, Oct 27, 2021 at 6:04 AM Sean Conlin via Sprinklerforum <
> > [email protected]> wrote:
> >
> > > If you were to put caps on the left and right lines going north and
> > south,
> > > it resembles a compound gridded system and a sprinkler can receive
> water
> > > from both sides.
> > >
> > > The east and west lines are essentially the mains and so is the 4" in
> the
> > > middle.
> > >
> > > Yes is has a looped piping  arrangement and is symmetrical but it is a
> > > gridded system by NFPA-13 definition.  If you were to not tie the lines
> > > together, it would be a loop.
> > >
> > > Regards,
> > >
> > > Sean W. Conlin
> > > E:[email protected]
> > >
> > > This message, including any attachments is considered confidential and
> > for
> > > use only by the intended recipient(s).
> > > Any other distribution, copying or disclosure is strictly prohibited.
> > > Please delete this communication and notify
> > > Demand Sprinkler Design Inc. if you are not the intended recipient or
> > have
> > > received this message in error. Demand
> > > Sprinkler Design Inc. accepts no responsibility or liability for any
> loss
> > > or damage from use, including damage from viruses.
> > >
> > > -----Original Message-----
> > > From: Ed Kramer <[email protected]>
> > > Sent: October 26, 2021 1:31 PM
> > > To: [email protected]
> > > Subject: Gridded dry system
> > >
> > > Is this sprinkler system a gridded system?   I've avoided this type of
> > > design in the past for dry systems because it 'kinda' a grid, but not
> > > really.  Now I'm questioning my questioning.  What are your thoughts?
> > >
> > >
> > >
> > > Reference NFPA 13 (2019) sections 8.2.3.10 and 3.3.206.5.
> > >
> > >
> > >
> > >
> https://www.dropbox.com/s/u2hw3cbvlga4fcq/Dry%20Attic%20System.pdf?dl=0
> > >
> > >
> > >
> > >
> > >
> > > Ed Kramer
> > >
> > >
> > >
> > >
> > > _______________________________________________
> > > Sprinklerforum mailing list
> > > [email protected]
> > >
> > >
> >
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
> > >
> > _______________________________________________
> > Sprinklerforum mailing list
> > [email protected]
> >
> >
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
> >
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
>
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to