Yes, I see that now... looks like I have another PI to add to the NFPA 13
list. Look for that line of sprinklers to be removed in the 2025 edition
haha.

The above is my opinion and has not been processed as a formal
interpretation in accordance with the NFPA Regulations Governing Committee
Projects. This is provided with the understanding that the AFSA assumes no
liability for this opinion or actions taken on it and they are not to be
considered the official position of the NFPA or its technical committees.
AFSA cannot provide design or consulting engineering services, and this
opinion should therefore not be considered, nor relied upon, as such.


Kevin Hall, M.Eng., P.E., ET, CWBSP, PMSFPE

Coordinator, Engineering and Technical Services

American Fire Sprinkler Association

[email protected]

214-349-5971


On Wed, Oct 27, 2021 at 12:19 PM J H via Sprinklerforum <
[email protected]> wrote:

> Kevin,
> That's true for most of the sprinklers in the diagram but look at figure
> A.3.3.206.6 (2019) - the farthest loop from the supply has sprinklers on it
> and it's connecting both loops - those sprinklers are receiving water from
> two mains. Likewise, per the definition of a main the only main in Ed's
> example is the center line. Everything else are looped branchlines per the
> definitions.
>
> JH
>
>
> On Wed, Oct 27, 2021 at 9:09 AM Kevin Hall via Sprinklerforum <
> [email protected]> wrote:
>
> > The annex shows the branch lines fed by the cross main from two
> directions,
> > the sprinkler can still only receive water from one direction from the
> > branch line... that is the distinction in the definition.
> >
> > The above is my opinion and has not been processed as a formal
> > interpretation in accordance with the NFPA Regulations Governing
> Committee
> > Projects. This is provided with the understanding that the AFSA assumes
> no
> > liability for this opinion or actions taken on it and they are not to be
> > considered the official position of the NFPA or its technical committees.
> > AFSA cannot provide design or consulting engineering services, and this
> > opinion should therefore not be considered, nor relied upon, as such.
> >
> >
> > Kevin Hall, M.Eng., P.E., ET, CWBSP, PMSFPE
> >
> > Coordinator, Engineering and Technical Services
> >
> > American Fire Sprinkler Association
> >
> > [email protected]
> >
> > 214-349-5971
> >
> >
> > On Wed, Oct 27, 2021 at 12:05 PM J H via Sprinklerforum <
> > [email protected]> wrote:
> >
> > > I have a problem with the simplified definition floated out here that a
> > > grid system is one that feeds a sprinkler from two directions because
> of
> > > the illustration of a looped system in the annex of '13 which shows
> > > sprinklers attached to the end portion of the loop resulting in those
> > > sprinklers receiving water from two directions. Technically the only
> > cross
> > > main is the center piping - everything else are looped branchlines. I
> > would
> > > be prepared for kickback from a knowledgeable AHJ. I would personally
> > avoid
> > > a design like this if at all possible to avoid the headache of hashing
> it
> > > out w/ an AHJ. But if it's the difference between a system like this
> and
> > a
> > > fire pump it might be worth the fight.
> > >
> > > JH
> > >
> > > On Wed, Oct 27, 2021 at 6:04 AM Sean Conlin via Sprinklerforum <
> > > [email protected]> wrote:
> > >
> > > > If you were to put caps on the left and right lines going north and
> > > south,
> > > > it resembles a compound gridded system and a sprinkler can receive
> > water
> > > > from both sides.
> > > >
> > > > The east and west lines are essentially the mains and so is the 4" in
> > the
> > > > middle.
> > > >
> > > > Yes is has a looped piping  arrangement and is symmetrical but it is
> a
> > > > gridded system by NFPA-13 definition.  If you were to not tie the
> lines
> > > > together, it would be a loop.
> > > >
> > > > Regards,
> > > >
> > > > Sean W. Conlin
> > > > E:[email protected]
> > > >
> > > > This message, including any attachments is considered confidential
> and
> > > for
> > > > use only by the intended recipient(s).
> > > > Any other distribution, copying or disclosure is strictly prohibited.
> > > > Please delete this communication and notify
> > > > Demand Sprinkler Design Inc. if you are not the intended recipient or
> > > have
> > > > received this message in error. Demand
> > > > Sprinkler Design Inc. accepts no responsibility or liability for any
> > loss
> > > > or damage from use, including damage from viruses.
> > > >
> > > > -----Original Message-----
> > > > From: Ed Kramer <[email protected]>
> > > > Sent: October 26, 2021 1:31 PM
> > > > To: [email protected]
> > > > Subject: Gridded dry system
> > > >
> > > > Is this sprinkler system a gridded system?   I've avoided this type
> of
> > > > design in the past for dry systems because it 'kinda' a grid, but not
> > > > really.  Now I'm questioning my questioning.  What are your thoughts?
> > > >
> > > >
> > > >
> > > > Reference NFPA 13 (2019) sections 8.2.3.10 and 3.3.206.5.
> > > >
> > > >
> > > >
> > > >
> > https://www.dropbox.com/s/u2hw3cbvlga4fcq/Dry%20Attic%20System.pdf?dl=0
> > > >
> > > >
> > > >
> > > >
> > > >
> > > > Ed Kramer
> > > >
> > > >
> > > >
> > > >
> > > > _______________________________________________
> > > > Sprinklerforum mailing list
> > > > [email protected]
> > > >
> > > >
> > >
> >
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
> > > >
> > > _______________________________________________
> > > Sprinklerforum mailing list
> > > [email protected]
> > >
> > >
> >
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
> > >
> > _______________________________________________
> > Sprinklerforum mailing list
> > [email protected]
> >
> >
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
> >
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
>
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to