So, on any looped system, if you add sprinklers to the looped main (adding
flow from more than two directions) does that now constitute a grid? I see
both viewpoints but am posing as devil's advocate. As I said I would steer
clear from the original scenario unless necessity dictated otherwise.

JH

On Wed, Oct 27, 2021 at 9:58 AM J H <[email protected]> wrote:

> I would call it a Tree/Loop hybrid. :-P
>
> The branchlines are not connecting two parallel cross mains per the
> definition of a grid.
> JH
>
>
> On Wed, Oct 27, 2021 at 9:50 AM Kevin Hall <[email protected]>
> wrote:
>
>> If the pipe marked in red is removed and capped off, it eliminates any
>> split flows/transfer lines on the branch lines. So with the red pipe
>> removed I would define it as a tree. With the red pipe installed, I would
>> define it as a grid.
>>
>> The above is my opinion and has not been processed as a formal
>> interpretation in accordance with the NFPA Regulations Governing Committee
>> Projects. This is provided with the understanding that the AFSA assumes no
>> liability for this opinion or actions taken on it and they are not to be
>> considered the official position of the NFPA or its technical committees.
>> AFSA cannot provide design or consulting engineering services, and this
>> opinion should therefore not be considered, nor relied upon, as such.
>>
>>
>> Kevin Hall, M.Eng., P.E., ET, CWBSP, PMSFPE
>>
>> Coordinator, Engineering and Technical Services
>>
>> American Fire Sprinkler Association
>>
>> [email protected]
>>
>> 214-349-5971
>>
>>
>> On Wed, Oct 27, 2021 at 12:47 PM J H via Sprinklerforum <
>> [email protected]> wrote:
>>
>>> So, for discussions sake take a look at the image link - what would you
>>> all
>>> call this system? I have my opinion but I don't see how it's much
>>> different
>>> than Ed's original drawing:
>>> https://ibb.co/xSW04dj
>>>
>>> On Wed, Oct 27, 2021 at 9:46 AM J H <[email protected]> wrote:
>>>
>>> > So, for discussions sake take a look at the image link - what would you
>>> > all call this system? I have my opinion but I don't see how it's much
>>> > different than Ed's original drawing:
>>> > https://ibb.co/xSW04dj
>>> >
>>> > On Wed, Oct 27, 2021 at 9:40 AM Kevin Hall <[email protected]>
>>> > wrote:
>>> >
>>> >> Yes, I see that now... looks like I have another PI to add to the
>>> NFPA 13
>>> >> list. Look for that line of sprinklers to be removed in the 2025
>>> edition
>>> >> haha.
>>> >>
>>> >> The above is my opinion and has not been processed as a formal
>>> >> interpretation in accordance with the NFPA Regulations Governing
>>> Committee
>>> >> Projects. This is provided with the understanding that the AFSA
>>> assumes no
>>> >> liability for this opinion or actions taken on it and they are not to
>>> be
>>> >> considered the official position of the NFPA or its technical
>>> committees.
>>> >> AFSA cannot provide design or consulting engineering services, and
>>> this
>>> >> opinion should therefore not be considered, nor relied upon, as such.
>>> >>
>>> >>
>>> >> Kevin Hall, M.Eng., P.E., ET, CWBSP, PMSFPE
>>> >>
>>> >> Coordinator, Engineering and Technical Services
>>> >>
>>> >> American Fire Sprinkler Association
>>> >>
>>> >> [email protected]
>>> >>
>>> >> 214-349-5971
>>> >>
>>> >>
>>> >> On Wed, Oct 27, 2021 at 12:19 PM J H via Sprinklerforum <
>>> >> [email protected]> wrote:
>>> >>
>>> >>> Kevin,
>>> >>> That's true for most of the sprinklers in the diagram but look at
>>> figure
>>> >>> A.3.3.206.6 (2019) - the farthest loop from the supply has
>>> sprinklers on
>>> >>> it
>>> >>> and it's connecting both loops - those sprinklers are receiving water
>>> >>> from
>>> >>> two mains. Likewise, per the definition of a main the only main in
>>> Ed's
>>> >>> example is the center line. Everything else are looped branchlines
>>> per
>>> >>> the
>>> >>> definitions.
>>> >>>
>>> >>> JH
>>> >>>
>>> >>>
>>> >>> On Wed, Oct 27, 2021 at 9:09 AM Kevin Hall via Sprinklerforum <
>>> >>> [email protected]> wrote:
>>> >>>
>>> >>> > The annex shows the branch lines fed by the cross main from two
>>> >>> directions,
>>> >>> > the sprinkler can still only receive water from one direction from
>>> the
>>> >>> > branch line... that is the distinction in the definition.
>>> >>> >
>>> >>> > The above is my opinion and has not been processed as a formal
>>> >>> > interpretation in accordance with the NFPA Regulations Governing
>>> >>> Committee
>>> >>> > Projects. This is provided with the understanding that the AFSA
>>> >>> assumes no
>>> >>> > liability for this opinion or actions taken on it and they are not
>>> to
>>> >>> be
>>> >>> > considered the official position of the NFPA or its technical
>>> >>> committees.
>>> >>> > AFSA cannot provide design or consulting engineering services, and
>>> this
>>> >>> > opinion should therefore not be considered, nor relied upon, as
>>> such.
>>> >>> >
>>> >>> >
>>> >>> > Kevin Hall, M.Eng., P.E., ET, CWBSP, PMSFPE
>>> >>> >
>>> >>> > Coordinator, Engineering and Technical Services
>>> >>> >
>>> >>> > American Fire Sprinkler Association
>>> >>> >
>>> >>> > [email protected]
>>> >>> >
>>> >>> > 214-349-5971
>>> >>> >
>>> >>> >
>>> >>> > On Wed, Oct 27, 2021 at 12:05 PM J H via Sprinklerforum <
>>> >>> > [email protected]> wrote:
>>> >>> >
>>> >>> > > I have a problem with the simplified definition floated out here
>>> >>> that a
>>> >>> > > grid system is one that feeds a sprinkler from two directions
>>> >>> because of
>>> >>> > > the illustration of a looped system in the annex of '13 which
>>> shows
>>> >>> > > sprinklers attached to the end portion of the loop resulting in
>>> those
>>> >>> > > sprinklers receiving water from two directions. Technically the
>>> only
>>> >>> > cross
>>> >>> > > main is the center piping - everything else are looped
>>> branchlines. I
>>> >>> > would
>>> >>> > > be prepared for kickback from a knowledgeable AHJ. I would
>>> personally
>>> >>> > avoid
>>> >>> > > a design like this if at all possible to avoid the headache of
>>> >>> hashing it
>>> >>> > > out w/ an AHJ. But if it's the difference between a system like
>>> this
>>> >>> and
>>> >>> > a
>>> >>> > > fire pump it might be worth the fight.
>>> >>> > >
>>> >>> > > JH
>>> >>> > >
>>> >>> > > On Wed, Oct 27, 2021 at 6:04 AM Sean Conlin via Sprinklerforum <
>>> >>> > > [email protected]> wrote:
>>> >>> > >
>>> >>> > > > If you were to put caps on the left and right lines going
>>> north and
>>> >>> > > south,
>>> >>> > > > it resembles a compound gridded system and a sprinkler can
>>> receive
>>> >>> > water
>>> >>> > > > from both sides.
>>> >>> > > >
>>> >>> > > > The east and west lines are essentially the mains and so is
>>> the 4"
>>> >>> in
>>> >>> > the
>>> >>> > > > middle.
>>> >>> > > >
>>> >>> > > > Yes is has a looped piping  arrangement and is symmetrical but
>>> it
>>> >>> is a
>>> >>> > > > gridded system by NFPA-13 definition.  If you were to not tie
>>> the
>>> >>> lines
>>> >>> > > > together, it would be a loop.
>>> >>> > > >
>>> >>> > > > Regards,
>>> >>> > > >
>>> >>> > > > Sean W. Conlin
>>> >>> > > > E:[email protected]
>>> >>> > > >
>>> >>> > > > This message, including any attachments is considered
>>> confidential
>>> >>> and
>>> >>> > > for
>>> >>> > > > use only by the intended recipient(s).
>>> >>> > > > Any other distribution, copying or disclosure is strictly
>>> >>> prohibited.
>>> >>> > > > Please delete this communication and notify
>>> >>> > > > Demand Sprinkler Design Inc. if you are not the intended
>>> recipient
>>> >>> or
>>> >>> > > have
>>> >>> > > > received this message in error. Demand
>>> >>> > > > Sprinkler Design Inc. accepts no responsibility or liability
>>> for
>>> >>> any
>>> >>> > loss
>>> >>> > > > or damage from use, including damage from viruses.
>>> >>> > > >
>>> >>> > > > -----Original Message-----
>>> >>> > > > From: Ed Kramer <[email protected]>
>>> >>> > > > Sent: October 26, 2021 1:31 PM
>>> >>> > > > To: [email protected]
>>> >>> > > > Subject: Gridded dry system
>>> >>> > > >
>>> >>> > > > Is this sprinkler system a gridded system?   I've avoided this
>>> >>> type of
>>> >>> > > > design in the past for dry systems because it 'kinda' a grid,
>>> but
>>> >>> not
>>> >>> > > > really.  Now I'm questioning my questioning.  What are your
>>> >>> thoughts?
>>> >>> > > >
>>> >>> > > >
>>> >>> > > >
>>> >>> > > > Reference NFPA 13 (2019) sections 8.2.3.10 and 3.3.206.5.
>>> >>> > > >
>>> >>> > > >
>>> >>> > > >
>>> >>> > > >
>>> >>> >
>>> >>>
>>> https://www.dropbox.com/s/u2hw3cbvlga4fcq/Dry%20Attic%20System.pdf?dl=0
>>> >>> > > >
>>> >>> > > >
>>> >>> > > >
>>> >>> > > >
>>> >>> > > >
>>> >>> > > > Ed Kramer
>>> >>> > > >
>>> >>> > > >
>>> >>> > > >
>>> >>> > > >
>>> >>> > > > _______________________________________________
>>> >>> > > > Sprinklerforum mailing list
>>> >>> > > > [email protected]
>>> >>> > > >
>>> >>> > > >
>>> >>> > >
>>> >>> >
>>> >>>
>>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>>> >>> > > >
>>> >>> > > _______________________________________________
>>> >>> > > Sprinklerforum mailing list
>>> >>> > > [email protected]
>>> >>> > >
>>> >>> > >
>>> >>> >
>>> >>>
>>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>>> >>> > >
>>> >>> > _______________________________________________
>>> >>> > Sprinklerforum mailing list
>>> >>> > [email protected]
>>> >>> >
>>> >>> >
>>> >>>
>>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>>> >>> >
>>> >>> _______________________________________________
>>> >>> Sprinklerforum mailing list
>>> >>> [email protected]
>>> >>>
>>> >>>
>>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>>> >>>
>>> >>
>>> _______________________________________________
>>> Sprinklerforum mailing list
>>> [email protected]
>>>
>>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>>>
>>
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to