IMHO, defining a grid as any system that can supply a sprinkler from more
than one direction is a poor threshold. Just because you install sprinklers
on a looped main or line, does not magically turn it into a gridded system.
The location of the sprinklers should have nothing to do with it.

May I suggest the following definition of gridded piping: "piping installed
such that any loop in the system has more than one connection capable of
providing water to the loop from the same supply; a loopty loop." Maybe
leave the last part out. Up to you.


-Skyler

On Wed, Oct 27, 2021, 12:17 PM Chad Mitchell via Sprinklerforum <
[email protected]> wrote:

> Here is an Informal Interpretation of a similar layout from November 13,
> 2009.
>
> https://www.dropbox.com/sh/8e4v0xvfri07c5i/AADbhtdz25iS_1Qkdbnh1lWqa?dl=0
>
> Regards,
>
> Chad Mitchell
> Mid Atlantic Fire Protection, Inc.
>
> -----Original Message-----
> From: Sprinklerforum <[email protected]> On
> Behalf Of J H via Sprinklerforum
> Sent: Wednesday, October 27, 2021 1:03 PM
> Cc: J H <[email protected]>;
> [email protected]
> Subject: Re: Gridded dry system
>
> So, on any looped system, if you add sprinklers to the looped main (adding
> flow from more than two directions) does that now constitute a grid? I see
> both viewpoints but am posing as devil's advocate. As I said I would steer
> clear from the original scenario unless necessity dictated otherwise.
>
> JH
>
> On Wed, Oct 27, 2021 at 9:58 AM J H <[email protected]> wrote:
>
> > I would call it a Tree/Loop hybrid. :-P
> >
> > The branchlines are not connecting two parallel cross mains per the
> > definition of a grid.
> > JH
> >
> >
> > On Wed, Oct 27, 2021 at 9:50 AM Kevin Hall <[email protected]>
> > wrote:
> >
> >> If the pipe marked in red is removed and capped off, it eliminates
> >> any split flows/transfer lines on the branch lines. So with the red
> >> pipe removed I would define it as a tree. With the red pipe
> >> installed, I would define it as a grid.
> >>
> >> The above is my opinion and has not been processed as a formal
> >> interpretation in accordance with the NFPA Regulations Governing
> >> Committee Projects. This is provided with the understanding that the
> >> AFSA assumes no liability for this opinion or actions taken on it and
> >> they are not to be considered the official position of the NFPA or its
> technical committees.
> >> AFSA cannot provide design or consulting engineering services, and
> >> this opinion should therefore not be considered, nor relied upon, as
> such.
> >>
> >>
> >> Kevin Hall, M.Eng., P.E., ET, CWBSP, PMSFPE
> >>
> >> Coordinator, Engineering and Technical Services
> >>
> >> American Fire Sprinkler Association
> >>
> >> [email protected]
> >>
> >> 214-349-5971
> >>
> >>
> >> On Wed, Oct 27, 2021 at 12:47 PM J H via Sprinklerforum <
> >> [email protected]> wrote:
> >>
> >>> So, for discussions sake take a look at the image link - what would
> >>> you all call this system? I have my opinion but I don't see how it's
> >>> much different than Ed's original drawing:
> >>> https://ibb.co/xSW04dj
> >>>
> >>> On Wed, Oct 27, 2021 at 9:46 AM J H <[email protected]>
> wrote:
> >>>
> >>> > So, for discussions sake take a look at the image link - what
> >>> > would you all call this system? I have my opinion but I don't see
> >>> > how it's much different than Ed's original drawing:
> >>> > https://ibb.co/xSW04dj
> >>> >
> >>> > On Wed, Oct 27, 2021 at 9:40 AM Kevin Hall
> >>> > <[email protected]>
> >>> > wrote:
> >>> >
> >>> >> Yes, I see that now... looks like I have another PI to add to the
> >>> NFPA 13
> >>> >> list. Look for that line of sprinklers to be removed in the 2025
> >>> edition
> >>> >> haha.
> >>> >>
> >>> >> The above is my opinion and has not been processed as a formal
> >>> >> interpretation in accordance with the NFPA Regulations Governing
> >>> Committee
> >>> >> Projects. This is provided with the understanding that the AFSA
> >>> assumes no
> >>> >> liability for this opinion or actions taken on it and they are
> >>> >> not to
> >>> be
> >>> >> considered the official position of the NFPA or its technical
> >>> committees.
> >>> >> AFSA cannot provide design or consulting engineering services,
> >>> >> and
> >>> this
> >>> >> opinion should therefore not be considered, nor relied upon, as
> such.
> >>> >>
> >>> >>
> >>> >> Kevin Hall, M.Eng., P.E., ET, CWBSP, PMSFPE
> >>> >>
> >>> >> Coordinator, Engineering and Technical Services
> >>> >>
> >>> >> American Fire Sprinkler Association
> >>> >>
> >>> >> [email protected]
> >>> >>
> >>> >> 214-349-5971
> >>> >>
> >>> >>
> >>> >> On Wed, Oct 27, 2021 at 12:19 PM J H via Sprinklerforum <
> >>> >> [email protected]> wrote:
> >>> >>
> >>> >>> Kevin,
> >>> >>> That's true for most of the sprinklers in the diagram but look
> >>> >>> at
> >>> figure
> >>> >>> A.3.3.206.6 (2019) - the farthest loop from the supply has
> >>> sprinklers on
> >>> >>> it
> >>> >>> and it's connecting both loops - those sprinklers are receiving
> >>> >>> water from two mains. Likewise, per the definition of a main the
> >>> >>> only main in
> >>> Ed's
> >>> >>> example is the center line. Everything else are looped
> >>> >>> branchlines
> >>> per
> >>> >>> the
> >>> >>> definitions.
> >>> >>>
> >>> >>> JH
> >>> >>>
> >>> >>>
> >>> >>> On Wed, Oct 27, 2021 at 9:09 AM Kevin Hall via Sprinklerforum <
> >>> >>> [email protected]> wrote:
> >>> >>>
> >>> >>> > The annex shows the branch lines fed by the cross main from
> >>> >>> > two
> >>> >>> directions,
> >>> >>> > the sprinkler can still only receive water from one direction
> >>> >>> > from
> >>> the
> >>> >>> > branch line... that is the distinction in the definition.
> >>> >>> >
> >>> >>> > The above is my opinion and has not been processed as a formal
> >>> >>> > interpretation in accordance with the NFPA Regulations
> >>> >>> > Governing
> >>> >>> Committee
> >>> >>> > Projects. This is provided with the understanding that the
> >>> >>> > AFSA
> >>> >>> assumes no
> >>> >>> > liability for this opinion or actions taken on it and they are
> >>> >>> > not
> >>> to
> >>> >>> be
> >>> >>> > considered the official position of the NFPA or its technical
> >>> >>> committees.
> >>> >>> > AFSA cannot provide design or consulting engineering services,
> >>> >>> > and
> >>> this
> >>> >>> > opinion should therefore not be considered, nor relied upon,
> >>> >>> > as
> >>> such.
> >>> >>> >
> >>> >>> >
> >>> >>> > Kevin Hall, M.Eng., P.E., ET, CWBSP, PMSFPE
> >>> >>> >
> >>> >>> > Coordinator, Engineering and Technical Services
> >>> >>> >
> >>> >>> > American Fire Sprinkler Association
> >>> >>> >
> >>> >>> > [email protected]
> >>> >>> >
> >>> >>> > 214-349-5971
> >>> >>> >
> >>> >>> >
> >>> >>> > On Wed, Oct 27, 2021 at 12:05 PM J H via Sprinklerforum <
> >>> >>> > [email protected]> wrote:
> >>> >>> >
> >>> >>> > > I have a problem with the simplified definition floated out
> >>> >>> > > here
> >>> >>> that a
> >>> >>> > > grid system is one that feeds a sprinkler from two
> >>> >>> > > directions
> >>> >>> because of
> >>> >>> > > the illustration of a looped system in the annex of '13
> >>> >>> > > which
> >>> shows
> >>> >>> > > sprinklers attached to the end portion of the loop resulting
> >>> >>> > > in
> >>> those
> >>> >>> > > sprinklers receiving water from two directions. Technically
> >>> >>> > > the
> >>> only
> >>> >>> > cross
> >>> >>> > > main is the center piping - everything else are looped
> >>> branchlines. I
> >>> >>> > would
> >>> >>> > > be prepared for kickback from a knowledgeable AHJ. I would
> >>> personally
> >>> >>> > avoid
> >>> >>> > > a design like this if at all possible to avoid the headache
> >>> >>> > > of
> >>> >>> hashing it
> >>> >>> > > out w/ an AHJ. But if it's the difference between a system
> >>> >>> > > like
> >>> this
> >>> >>> and
> >>> >>> > a
> >>> >>> > > fire pump it might be worth the fight.
> >>> >>> > >
> >>> >>> > > JH
> >>> >>> > >
> >>> >>> > > On Wed, Oct 27, 2021 at 6:04 AM Sean Conlin via
> >>> >>> > > Sprinklerforum < [email protected]>
> wrote:
> >>> >>> > >
> >>> >>> > > > If you were to put caps on the left and right lines going
> >>> north and
> >>> >>> > > south,
> >>> >>> > > > it resembles a compound gridded system and a sprinkler can
> >>> receive
> >>> >>> > water
> >>> >>> > > > from both sides.
> >>> >>> > > >
> >>> >>> > > > The east and west lines are essentially the mains and so
> >>> >>> > > > is
> >>> the 4"
> >>> >>> in
> >>> >>> > the
> >>> >>> > > > middle.
> >>> >>> > > >
> >>> >>> > > > Yes is has a looped piping  arrangement and is symmetrical
> >>> >>> > > > but
> >>> it
> >>> >>> is a
> >>> >>> > > > gridded system by NFPA-13 definition.  If you were to not
> >>> >>> > > > tie
> >>> the
> >>> >>> lines
> >>> >>> > > > together, it would be a loop.
> >>> >>> > > >
> >>> >>> > > > Regards,
> >>> >>> > > >
> >>> >>> > > > Sean W. Conlin
> >>> >>> > > > E:[email protected]
> >>> >>> > > >
> >>> >>> > > > This message, including any attachments is considered
> >>> confidential
> >>> >>> and
> >>> >>> > > for
> >>> >>> > > > use only by the intended recipient(s).
> >>> >>> > > > Any other distribution, copying or disclosure is strictly
> >>> >>> prohibited.
> >>> >>> > > > Please delete this communication and notify Demand
> >>> >>> > > > Sprinkler Design Inc. if you are not the intended
> >>> recipient
> >>> >>> or
> >>> >>> > > have
> >>> >>> > > > received this message in error. Demand Sprinkler Design
> >>> >>> > > > Inc. accepts no responsibility or liability
> >>> for
> >>> >>> any
> >>> >>> > loss
> >>> >>> > > > or damage from use, including damage from viruses.
> >>> >>> > > >
> >>> >>> > > > -----Original Message-----
> >>> >>> > > > From: Ed Kramer <[email protected]>
> >>> >>> > > > Sent: October 26, 2021 1:31 PM
> >>> >>> > > > To: [email protected]
> >>> >>> > > > Subject: Gridded dry system
> >>> >>> > > >
> >>> >>> > > > Is this sprinkler system a gridded system?   I've avoided
> this
> >>> >>> type of
> >>> >>> > > > design in the past for dry systems because it 'kinda' a
> >>> >>> > > > grid,
> >>> but
> >>> >>> not
> >>> >>> > > > really.  Now I'm questioning my questioning.  What are
> >>> >>> > > > your
> >>> >>> thoughts?
> >>> >>> > > >
> >>> >>> > > >
> >>> >>> > > >
> >>> >>> > > > Reference NFPA 13 (2019) sections 8.2.3.10 and 3.3.206.5.
> >>> >>> > > >
> >>> >>> > > >
> >>> >>> > > >
> >>> >>> > > >
> >>> >>> >
> >>> >>>
> >>> https://www.dropbox.com/s/u2hw3cbvlga4fcq/Dry%20Attic%20System.pdf?d
> >>> l=0
> >>> >>> > > >
> >>> >>> > > >
> >>> >>> > > >
> >>> >>> > > >
> >>> >>> > > >
> >>> >>> > > > Ed Kramer
> >>> >>> > > >
> >>> >>> > > >
> >>> >>> > > >
> >>> >>> > > >
> >>> >>> > > > _______________________________________________
> >>> >>> > > > Sprinklerforum mailing list
> >>> >>> > > > [email protected]
> >>> >>> > > >
> >>> >>> > > >
> >>> >>> > >
> >>> >>> >
> >>> >>>
> >>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprin
> >>> kler.org
> >>> >>> > > >
> >>> >>> > > _______________________________________________
> >>> >>> > > Sprinklerforum mailing list
> >>> >>> > > [email protected]
> >>> >>> > >
> >>> >>> > >
> >>> >>> >
> >>> >>>
> >>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprin
> >>> kler.org
> >>> >>> > >
> >>> >>> > _______________________________________________
> >>> >>> > Sprinklerforum mailing list
> >>> >>> > [email protected]
> >>> >>> >
> >>> >>> >
> >>> >>>
> >>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprin
> >>> kler.org
> >>> >>> >
> >>> >>> _______________________________________________
> >>> >>> Sprinklerforum mailing list
> >>> >>> [email protected]
> >>> >>>
> >>> >>>
> >>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprin
> >>> kler.org
> >>> >>>
> >>> >>
> >>> _______________________________________________
> >>> Sprinklerforum mailing list
> >>> [email protected]
> >>>
> >>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprin
> >>> kler.org
> >>>
> >>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
>
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
> This email and any files transmitted with it are confidential and intended
> solely for the use of the individual or entity to whom they are addressed.
> If you have received this email in error please notify the system manager.
> This message contains confidential information and is intended only for the
> individual named. If you are not the named addressee you should not
> disseminate, distribute or copy this e-mail. Please notify the sender
> immediately by e-mail if you have received this e-mail by mistake and
> delete this e-mail from your system. If you are not the intended recipient
> you are notified that disclosing, copying, distributing or taking any
> action in reliance on the contents of this information is strictly
> prohibited.
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
>
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to