Here is an Informal Interpretation of a similar layout from November 13, 2009.

https://www.dropbox.com/sh/8e4v0xvfri07c5i/AADbhtdz25iS_1Qkdbnh1lWqa?dl=0

Regards,

Chad Mitchell
Mid Atlantic Fire Protection, Inc.

-----Original Message-----
From: Sprinklerforum <[email protected]> On Behalf 
Of J H via Sprinklerforum
Sent: Wednesday, October 27, 2021 1:03 PM
Cc: J H <[email protected]>; [email protected]
Subject: Re: Gridded dry system

So, on any looped system, if you add sprinklers to the looped main (adding flow 
from more than two directions) does that now constitute a grid? I see both 
viewpoints but am posing as devil's advocate. As I said I would steer clear 
from the original scenario unless necessity dictated otherwise.

JH

On Wed, Oct 27, 2021 at 9:58 AM J H <[email protected]> wrote:

> I would call it a Tree/Loop hybrid. :-P
>
> The branchlines are not connecting two parallel cross mains per the
> definition of a grid.
> JH
>
>
> On Wed, Oct 27, 2021 at 9:50 AM Kevin Hall <[email protected]>
> wrote:
>
>> If the pipe marked in red is removed and capped off, it eliminates
>> any split flows/transfer lines on the branch lines. So with the red
>> pipe removed I would define it as a tree. With the red pipe
>> installed, I would define it as a grid.
>>
>> The above is my opinion and has not been processed as a formal
>> interpretation in accordance with the NFPA Regulations Governing
>> Committee Projects. This is provided with the understanding that the
>> AFSA assumes no liability for this opinion or actions taken on it and
>> they are not to be considered the official position of the NFPA or its 
>> technical committees.
>> AFSA cannot provide design or consulting engineering services, and
>> this opinion should therefore not be considered, nor relied upon, as such.
>>
>>
>> Kevin Hall, M.Eng., P.E., ET, CWBSP, PMSFPE
>>
>> Coordinator, Engineering and Technical Services
>>
>> American Fire Sprinkler Association
>>
>> [email protected]
>>
>> 214-349-5971
>>
>>
>> On Wed, Oct 27, 2021 at 12:47 PM J H via Sprinklerforum <
>> [email protected]> wrote:
>>
>>> So, for discussions sake take a look at the image link - what would
>>> you all call this system? I have my opinion but I don't see how it's
>>> much different than Ed's original drawing:
>>> https://ibb.co/xSW04dj
>>>
>>> On Wed, Oct 27, 2021 at 9:46 AM J H <[email protected]> wrote:
>>>
>>> > So, for discussions sake take a look at the image link - what
>>> > would you all call this system? I have my opinion but I don't see
>>> > how it's much different than Ed's original drawing:
>>> > https://ibb.co/xSW04dj
>>> >
>>> > On Wed, Oct 27, 2021 at 9:40 AM Kevin Hall
>>> > <[email protected]>
>>> > wrote:
>>> >
>>> >> Yes, I see that now... looks like I have another PI to add to the
>>> NFPA 13
>>> >> list. Look for that line of sprinklers to be removed in the 2025
>>> edition
>>> >> haha.
>>> >>
>>> >> The above is my opinion and has not been processed as a formal
>>> >> interpretation in accordance with the NFPA Regulations Governing
>>> Committee
>>> >> Projects. This is provided with the understanding that the AFSA
>>> assumes no
>>> >> liability for this opinion or actions taken on it and they are
>>> >> not to
>>> be
>>> >> considered the official position of the NFPA or its technical
>>> committees.
>>> >> AFSA cannot provide design or consulting engineering services,
>>> >> and
>>> this
>>> >> opinion should therefore not be considered, nor relied upon, as such.
>>> >>
>>> >>
>>> >> Kevin Hall, M.Eng., P.E., ET, CWBSP, PMSFPE
>>> >>
>>> >> Coordinator, Engineering and Technical Services
>>> >>
>>> >> American Fire Sprinkler Association
>>> >>
>>> >> [email protected]
>>> >>
>>> >> 214-349-5971
>>> >>
>>> >>
>>> >> On Wed, Oct 27, 2021 at 12:19 PM J H via Sprinklerforum <
>>> >> [email protected]> wrote:
>>> >>
>>> >>> Kevin,
>>> >>> That's true for most of the sprinklers in the diagram but look
>>> >>> at
>>> figure
>>> >>> A.3.3.206.6 (2019) - the farthest loop from the supply has
>>> sprinklers on
>>> >>> it
>>> >>> and it's connecting both loops - those sprinklers are receiving
>>> >>> water from two mains. Likewise, per the definition of a main the
>>> >>> only main in
>>> Ed's
>>> >>> example is the center line. Everything else are looped
>>> >>> branchlines
>>> per
>>> >>> the
>>> >>> definitions.
>>> >>>
>>> >>> JH
>>> >>>
>>> >>>
>>> >>> On Wed, Oct 27, 2021 at 9:09 AM Kevin Hall via Sprinklerforum <
>>> >>> [email protected]> wrote:
>>> >>>
>>> >>> > The annex shows the branch lines fed by the cross main from
>>> >>> > two
>>> >>> directions,
>>> >>> > the sprinkler can still only receive water from one direction
>>> >>> > from
>>> the
>>> >>> > branch line... that is the distinction in the definition.
>>> >>> >
>>> >>> > The above is my opinion and has not been processed as a formal
>>> >>> > interpretation in accordance with the NFPA Regulations
>>> >>> > Governing
>>> >>> Committee
>>> >>> > Projects. This is provided with the understanding that the
>>> >>> > AFSA
>>> >>> assumes no
>>> >>> > liability for this opinion or actions taken on it and they are
>>> >>> > not
>>> to
>>> >>> be
>>> >>> > considered the official position of the NFPA or its technical
>>> >>> committees.
>>> >>> > AFSA cannot provide design or consulting engineering services,
>>> >>> > and
>>> this
>>> >>> > opinion should therefore not be considered, nor relied upon,
>>> >>> > as
>>> such.
>>> >>> >
>>> >>> >
>>> >>> > Kevin Hall, M.Eng., P.E., ET, CWBSP, PMSFPE
>>> >>> >
>>> >>> > Coordinator, Engineering and Technical Services
>>> >>> >
>>> >>> > American Fire Sprinkler Association
>>> >>> >
>>> >>> > [email protected]
>>> >>> >
>>> >>> > 214-349-5971
>>> >>> >
>>> >>> >
>>> >>> > On Wed, Oct 27, 2021 at 12:05 PM J H via Sprinklerforum <
>>> >>> > [email protected]> wrote:
>>> >>> >
>>> >>> > > I have a problem with the simplified definition floated out
>>> >>> > > here
>>> >>> that a
>>> >>> > > grid system is one that feeds a sprinkler from two
>>> >>> > > directions
>>> >>> because of
>>> >>> > > the illustration of a looped system in the annex of '13
>>> >>> > > which
>>> shows
>>> >>> > > sprinklers attached to the end portion of the loop resulting
>>> >>> > > in
>>> those
>>> >>> > > sprinklers receiving water from two directions. Technically
>>> >>> > > the
>>> only
>>> >>> > cross
>>> >>> > > main is the center piping - everything else are looped
>>> branchlines. I
>>> >>> > would
>>> >>> > > be prepared for kickback from a knowledgeable AHJ. I would
>>> personally
>>> >>> > avoid
>>> >>> > > a design like this if at all possible to avoid the headache
>>> >>> > > of
>>> >>> hashing it
>>> >>> > > out w/ an AHJ. But if it's the difference between a system
>>> >>> > > like
>>> this
>>> >>> and
>>> >>> > a
>>> >>> > > fire pump it might be worth the fight.
>>> >>> > >
>>> >>> > > JH
>>> >>> > >
>>> >>> > > On Wed, Oct 27, 2021 at 6:04 AM Sean Conlin via
>>> >>> > > Sprinklerforum < [email protected]> wrote:
>>> >>> > >
>>> >>> > > > If you were to put caps on the left and right lines going
>>> north and
>>> >>> > > south,
>>> >>> > > > it resembles a compound gridded system and a sprinkler can
>>> receive
>>> >>> > water
>>> >>> > > > from both sides.
>>> >>> > > >
>>> >>> > > > The east and west lines are essentially the mains and so
>>> >>> > > > is
>>> the 4"
>>> >>> in
>>> >>> > the
>>> >>> > > > middle.
>>> >>> > > >
>>> >>> > > > Yes is has a looped piping  arrangement and is symmetrical
>>> >>> > > > but
>>> it
>>> >>> is a
>>> >>> > > > gridded system by NFPA-13 definition.  If you were to not
>>> >>> > > > tie
>>> the
>>> >>> lines
>>> >>> > > > together, it would be a loop.
>>> >>> > > >
>>> >>> > > > Regards,
>>> >>> > > >
>>> >>> > > > Sean W. Conlin
>>> >>> > > > E:[email protected]
>>> >>> > > >
>>> >>> > > > This message, including any attachments is considered
>>> confidential
>>> >>> and
>>> >>> > > for
>>> >>> > > > use only by the intended recipient(s).
>>> >>> > > > Any other distribution, copying or disclosure is strictly
>>> >>> prohibited.
>>> >>> > > > Please delete this communication and notify Demand
>>> >>> > > > Sprinkler Design Inc. if you are not the intended
>>> recipient
>>> >>> or
>>> >>> > > have
>>> >>> > > > received this message in error. Demand Sprinkler Design
>>> >>> > > > Inc. accepts no responsibility or liability
>>> for
>>> >>> any
>>> >>> > loss
>>> >>> > > > or damage from use, including damage from viruses.
>>> >>> > > >
>>> >>> > > > -----Original Message-----
>>> >>> > > > From: Ed Kramer <[email protected]>
>>> >>> > > > Sent: October 26, 2021 1:31 PM
>>> >>> > > > To: [email protected]
>>> >>> > > > Subject: Gridded dry system
>>> >>> > > >
>>> >>> > > > Is this sprinkler system a gridded system?   I've avoided this
>>> >>> type of
>>> >>> > > > design in the past for dry systems because it 'kinda' a
>>> >>> > > > grid,
>>> but
>>> >>> not
>>> >>> > > > really.  Now I'm questioning my questioning.  What are
>>> >>> > > > your
>>> >>> thoughts?
>>> >>> > > >
>>> >>> > > >
>>> >>> > > >
>>> >>> > > > Reference NFPA 13 (2019) sections 8.2.3.10 and 3.3.206.5.
>>> >>> > > >
>>> >>> > > >
>>> >>> > > >
>>> >>> > > >
>>> >>> >
>>> >>>
>>> https://www.dropbox.com/s/u2hw3cbvlga4fcq/Dry%20Attic%20System.pdf?d
>>> l=0
>>> >>> > > >
>>> >>> > > >
>>> >>> > > >
>>> >>> > > >
>>> >>> > > >
>>> >>> > > > Ed Kramer
>>> >>> > > >
>>> >>> > > >
>>> >>> > > >
>>> >>> > > >
>>> >>> > > > _______________________________________________
>>> >>> > > > Sprinklerforum mailing list
>>> >>> > > > [email protected]
>>> >>> > > >
>>> >>> > > >
>>> >>> > >
>>> >>> >
>>> >>>
>>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprin
>>> kler.org
>>> >>> > > >
>>> >>> > > _______________________________________________
>>> >>> > > Sprinklerforum mailing list
>>> >>> > > [email protected]
>>> >>> > >
>>> >>> > >
>>> >>> >
>>> >>>
>>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprin
>>> kler.org
>>> >>> > >
>>> >>> > _______________________________________________
>>> >>> > Sprinklerforum mailing list
>>> >>> > [email protected]
>>> >>> >
>>> >>> >
>>> >>>
>>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprin
>>> kler.org
>>> >>> >
>>> >>> _______________________________________________
>>> >>> Sprinklerforum mailing list
>>> >>> [email protected]
>>> >>>
>>> >>>
>>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprin
>>> kler.org
>>> >>>
>>> >>
>>> _______________________________________________
>>> Sprinklerforum mailing list
>>> [email protected]
>>>
>>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprin
>>> kler.org
>>>
>>
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
This email and any files transmitted with it are confidential and intended 
solely for the use of the individual or entity to whom they are addressed. If 
you have received this email in error please notify the system manager. This 
message contains confidential information and is intended only for the 
individual named. If you are not the named addressee you should not 
disseminate, distribute or copy this e-mail. Please notify the sender 
immediately by e-mail if you have received this e-mail by mistake and delete 
this e-mail from your system. If you are not the intended recipient you are 
notified that disclosing, copying, distributing or taking any action in 
reliance on the contents of this information is strictly prohibited.
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to