Well then, the option is to dive into something beyond one’s level of 
experience and expertise and hope your liability insurance is all paid up.

NFPA 13 is not the end all when it come to design.  If you haven’t looked at 
the building code and then the fire code (local and/or state) and then the 
applicable NFPA Standard which sometimes isn’t NFPA 13, you’ve not done anyone 
a real service.

And sometimes it might be better to let the guy down the road have it.

In our business lives are at stake. Be sure you can whole heartedly defend 
every note, every decision and every word without hesitation because one day 
you might have to do so.

Oh and be sure to find out the temp of the extruder head, sometimes they can be 
real hot and those 155°F sprinklers just aren’t going to cut it.

And y’all be careful now, ya hear.

Craig Prahl | Jacobs | Fire Protection SME – EV, AM, DC, Special Hazards
[email protected]<mailto:[email protected]> | 
www.jacobs.com<https://urldefense.com/v3/__http:/www.jacobs.com/__;!!KZTdOCjhgt4hgw!-_khxU8gU0_6jc895I7kRbnU8JghRDsWgqOblZ4jr7Qp2IVbR30VYw_hWvNFtphnl0uWpB9KIvbYi1pvZz4$>
1041 East Butler Road   Greenville, South Carolina  29606
CONTACT BY: Phone 1-864-676-5252, Email or MS TEAMS


From: [email protected] <[email protected]>
Sent: Thursday, October 24, 2024 4:50 PM
To: [email protected]
Subject: [EXTERNAL] [Sprinklerforum] Re: Metal manufacturing

I love all you guys. I really do. (Even you Todd)

But, Hire an Engineer, or Should be provided by an Engineer, just does not work 
out here in the trenches.

The answer is there in 13. Even "extruding" by a 3-D printer is extruding. I 
had to do Metal Working for folks cutting 4x8 sheets of aluminum.
There is not a distinction. Some AHJ's see that and live by it.

 IS it the intent? Probably not.

But it IS what the book says.

Which is the only thing we have in most cases.

I really wish we could kick it back. But more times than not, they just go to 
the next person in line.

Just saying. Those are not really answers to the questions.

Rant over..

R/
Matt



Matthew J. Willis, CWBSP, C.E.T.

Ferguson Fire Design, LLC

D: (602) 337-0721<(602)%20337-0721> C: (307) 236-8249<(307)%20236-8249>

[email protected]<mailto:[email protected]>



________________________________
From: Craig Hanson <[email protected]<mailto:[email protected]>>
Sent: Thursday, October 24, 2024 12:48 PM
To: Discussion list on issues relating to automatic fire sprinklers 
<[email protected]<mailto:[email protected]>>
Subject: [Sprinklerforum] Re: Metal manufacturing

Caution:  This email originated from outside of the organization.  DO NOT click 
links or open attachments unless you recognize and trust the sender.
________________________________
They need to provide for you the hazard analysis that should have been done by 
an FPE and in accordance with IFC 104.7.2 and NFPA 13: 4.2(2022). The AHJ 
should have requested that information also. These are tricky operations as 
dissimilar metals create a deflagration issue. the design may also be outside 
the scope of the NFPA 13 due to the process involved. Their insurance company 
should also be requiring a hazard analysis.



Craig D. Hanson, CFPS
Fire Division Manager
West Coast Code Consultants, Inc. (WC³)
Meridian Satellite Office
C: 253.225.9977 | E: [email protected]<mailto:[email protected]> | 
www.WC-3.com<https://urldefense.com/v3/__https:/www.wc-3.com/__;!!B5cixuoO7ltTeg!ApwbOjp7WhvKzN4KGihpDFSrZ8N-0yVMVP_N6ebL1tF6TsjkgSJUWayM24OErgv9oETCXeDM1jNFi4C5aqwf_S35sekTmA$>
Teaming With Your Community to Make a Difference


On Thu, Oct 24, 2024 at 12:21 PM Fpdcdesign 
<[email protected]<mailto:[email protected]>> wrote:
+1 for Tim Stone. Too often the contractor or their estimator are asked to 
figure out design criteria. That should fall upon the FPE.

Todd Williams
Fire Protection Design/Consulting
Stonington, CT
860-608-4559



On Oct 24, 2024 at 1:04 PM, <Tstone52<mailto:[email protected]>> wrote:

It should be recommended that an “Architect” or “Engineer of Record” should 
provide you with a Code Review.

Or hire a “Fire Protection Engineer” to assist you.



Regards,

G. Tim Stone



G. Tim Stone Consulting, LLC

NICET Level III Engineering Technician

Fire Protection Sprinkler Design

and Consulting Services



   117 Old Stage Rd. - Essex Jct., VT. 05452

                 CELL: (802) 373-0638

             [email protected]<mailto:[email protected]>



From: Bobby Welch <[email protected]<mailto:[email protected]>>
Sent: Thursday, October 24, 2024 12:57 PM
To: Discussion list on issues relating to automatic fire sprinklers 
<[email protected]<mailto:[email protected]>>
Subject: [Sprinklerforum] Metal manufacturing



I have a building were they are making metal products by multiple processes 
including Metal Casting of steel, Metal Forging, Additive Manufacturing and hot 
rolling. Most of the building is open warehouse where they are producing metal 
products with 3D printers.  NFPA has metal workings listed as ordinary hazard 
but also has Die Casting and Metal extruding under Extra hazard group 1. Does 
anyone know where I would start to figure out what hazard is required for this 
building?

Bobby Welch | Sprinkler Systems Designer
KOORSEN FIRE & SECURITY
8090 N Dixie Dr, Dayton, OH 45414
P 937.641.8403 | Ext. 0318 | M 937.594.8457
[email protected]<mailto:[email protected]> | 
www.koorsen.com<https://urldefense.com/v3/__http:/www.koorsen.com__;!!B5cixuoO7ltTeg!ApwbOjp7WhvKzN4KGihpDFSrZ8N-0yVMVP_N6ebL1tF6TsjkgSJUWayM24OErgv9oETCXeDM1jNFi4C5aqwf_S1HA_wFmw$>

24x7x365 Service: 937.660.7050 | 
[email protected]<mailto:[email protected]>
_________________________________________________________ SprinklerForum 
mailing list: 
https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org<https://urldefense.com/v3/__https:/lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org__;!!B5cixuoO7ltTeg!ApwbOjp7WhvKzN4KGihpDFSrZ8N-0yVMVP_N6ebL1tF6TsjkgSJUWayM24OErgv9oETCXeDM1jNFi4C5aqwf_S32DM4r9A$>
 To unsubscribe send an email to 
[email protected]<mailto:[email protected]>

_________________________________________________________
SprinklerForum mailing list:
https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org<https://urldefense.com/v3/__https:/lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org__;!!B5cixuoO7ltTeg!ApwbOjp7WhvKzN4KGihpDFSrZ8N-0yVMVP_N6ebL1tF6TsjkgSJUWayM24OErgv9oETCXeDM1jNFi4C5aqwf_S32DM4r9A$>
To unsubscribe send an email to 
[email protected]<mailto:[email protected]>

________________________________

NOTICE - This communication may contain confidential and privileged information 
that is for the sole use of the intended recipient. Any viewing, copying or 
distribution of, or reliance on this message by unintended recipients is 
strictly prohibited. If you have received this message in error, please notify 
us immediately by replying to the message and deleting it from your computer.
_________________________________________________________
SprinklerForum mailing list:
https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org
To unsubscribe send an email to [email protected]