I realize that I’m a week late to the party (Merry Christmas, everyone), but I 
want to reply to first say that this is a pretty interesting topic and I 
appreciate reading the different opinions.

Secondly, I think I agree with everything Steve has said here. And I appreciate 
that your answers aren’t always just “what’s the safest way to cover my a##” 
like it can be with some people (although I do understand the professional and 
financial risk that can be present, especially for P.E.s and other licensed 
individuals).

Lastly, I want to throw out this hypothetical: Let’s say I’m a building owner 
and I get tired of dealing with sprinkler system “issues” in an area of my 
building. Maybe I’m doing some operation that creates excess heat and I’ve 
activated a sprinkler once or twice. Or maybe I have an area where my operation 
(loading with a forklift, etc.) has damaged the sprinklers or pipe multiple 
times and resulted in water damage. Or maybe I’ve got a corrosive operation 
(maybe acid-dipping as part of a galvanizing operation) and I’m constantly 
dealing with corroded sprinkler heads/pipe/hangers. So, I decide that I know 
enough about how the sprinkler system works and it’s doing me more harm than 
good. So, on my own (or maybe with some of my building maintenance guys) I 
decide to shut the valve, drain the system, cut and cap the main before it gets 
to this troublesome area, proceed to remove all evidence of a sprinkler system 
from said area, then turn the system back on. If you were inspecting my 
building after that, would you go to that area and say to yourself “well, there 
is no sprinkler system present, so there are no deficiencies to report”? To 
take it a step further, what if you were the inspector previously and you 
remembered all the deficiencies you had written up about that room on previous 
visits, so you know that there used to be sprinklers present? “No deficiencies 
noted”? Or do you say something like “Attempted to inspect sprinkler system in 
‘Room X’. Could not locate sprinkler system. WTF?”

-Kyle Montgomery
Aero Automatic Sprinkler Co.

From: Steve Leyton <[email protected]>
Sent: Monday, December 23, 2024 9:31 AM
To: Discussion list on issues relating to automatic fire sprinklers 
<[email protected]>
Subject: [External][Sprinklerforum] Re: Unprotected areas

I’ve stayed out of this conversation because I’m no longer in contracting and 
not in close enough touch with best practices on this subject.   But I’ve done 
a lot of expert witness work and when you edge into the concept of “standard of 
care”, it’s no longer a contractor’s license law issue exclusively.   With so 
many municipalities adopting electronic reporting and archival services, it’s 
easier than ever to inform both owner and AHJ of conditions and concerns, and 
also to step in poo if you go beyond the line of whatever constitutes “best 
practices” or “standard of care”.

Others have already clearly informed that NFPA 25 does not intend for the 
inspector to investigate so-called design deficiencies, but the consequences of 
not documenting such observations may well vary from state to state.   Even if 
we agree that you don’t “fail” a property because of design or installation 
deficiencies, that doesn’t mean that it’s not a good practice to inform the 
owner that they have such issues and as Matthew implies, it’s pretty 
complicated either way, so for me I would err on the side of caution and 
protect myself from allegations of negligence.

Noting that an area doesn’t have fire sprinkler protection when it should isn’t 
an engineering analysis.   Running calc’s on a system that you think is 
undersized is.   Observing that sprinklers are spaced at 225 sq. ft. in a lab 
space that has fume hoods isn’t a design consultation, it’s simply an informed 
opinion.   These can be conveyed to the owner in a separate letter or 
memorialized as field notes.   The significant aspect that’s not been discussed 
here is that the owner may be responsible for these deficiencies because they 
made building improvements without a permit, or the use of spaces has evolved 
as was described in the appellate court opinion that Dominick shared where 
spaces under stairs were enclosed and then used for storage.

The inspecting contractor isn’t responsible for the actions of the owner but 
that definitely doesn’t mean that they have to subject themselves to potential 
ownership of the conditions by being quiet (IMHO).   The reason that 
jurisdictional agencies adopt NFPA 25 mandates to raise the level of fire 
safety throughout the built environment.  Ignoring conditions that could lead 
to loss of life is antithetical and subverts the intent of such statutory 
requirements.   I cannot tell you how many times we’ve been asked by a property 
owner to work with them to intentionally dodge plan review, permit and 
inspection requirements.

We were asked as a 3rd party consultant to look at a large tortilla plant last 
year and the owner had built four platforms on the production floor so 
supervisors could look down on workers (yeah, like towers at a prison).    Then 
they stored stuff under the towers.   Then they had a fire in one of those 
storage piles and it off-gassed something toxic and ended up shutting down the 
facility – thank God nobody was seriously injured.   The bottom line is that if 
the FD in that jurisdiction had known, they’d have compelled the owner to 
update the AFS system.  I’m not sure I have any specific advice, but this 
discussion illustrates that there is an insanely fine line between “best 
practices” and “intent of the standard” and “putting our heads in the sand”.

Steve L.



From: [email protected]<mailto:[email protected]> 
<[email protected]<mailto:[email protected]>>
Sent: Monday, December 23, 2024 7:57 AM
To: 
[email protected]<mailto:[email protected]>
Subject: [Sprinklerforum] Re: Unprotected areas

It extends to 25 IF we step outside of it. Write up not protected, fire starts, 
someone dies because original calculations were way off.
Since you  started evaluating it at an engineering level, then it will be 
extended that you neglected to report the inadequate design.

IF we stay within 25, we are NOT there to inspect Engineering determinations. 
We are only there to evaluate the two things previously mentioned.

How can you be held liable for sticking to doing the job you were hired to do? 
What would be the basis of it?

R/
Matt





Matthew J. Willis, C.E.T.

Ferguson Fire Design, LLC

D: (602) 337-0721<(602)%20337-0721> C: (307) 236-8249<(307)%20236-8249>

[email protected]<mailto:[email protected]>



________________________________
From: Fpdcdesign <[email protected]<mailto:[email protected]>>
Sent: Monday, December 23, 2024 10:30 AM
To: Discussion list on issues relating to automatic fire sprinklers 
<[email protected]<mailto:[email protected]>>
Subject: [Sprinklerforum] Re: Unprotected areas

Caution:  This email originated from outside of the organization.  DO NOT click 
links or open attachments unless you recognize and trust the sender.
________________________________
David, all very true. But we can also be sued in civil court for not reporting 
an unsafe condition which results in a loss (liability). My question is does 
this also extend to someone doing a 25 inspection? If they notice an unsafe 
condition and do not report it, even though it is not part of their inspection, 
could they still be held liable in the event of a loss? The answer is not going 
to come from 25 or State Code, but actual experience.

Todd G Williams, PE
Fire Protection Design/Consulting
Stonington, CT
860-535-2080<tel:860-535-2080> (ofc)
860-554-7054<tel:860-554-7054>  (fax)
860-608-4559<tel:860-608-4559> (cell)


On Dec 23, 2024 at 10:11 AM, <David 
Williams<mailto:[email protected]>> wrote:

If you hold a PE/FPE license, you are likely to be required to report unsafe 
conditions as part of your license as protecting the public is part and parcel 
of such a license to prevent getting pulled up in front of the licensing board 
for an ethics violation.



[Icon    Description automatically generated]



DAVID WILLIAMS, PE, FPE

Senior Mechanical / Fire Protection Engineer



LHBcorp.com<https://www.lhbcorp.com/> |  PERFORMANCE DRIVEN DESIGN

See LHBcorp.com for states of licensure.







From: John Denhardt 
<[email protected]<mailto:[email protected]>>
Date: Sunday, December 22, 2024 at 8:51 PM
To: Discussion list on issues relating to automatic fire sprinklers 
<[email protected]<mailto:[email protected]>>
Subject: [Sprinklerforum] Re: Unprotected areas

If you are performing a NFPA 25 inspection, stay in you lane. Only do what the 
standard states and your contract requires.



Thanks,

John



John August Denhardt, P.E

Vice President Engineering and Technical Services

American Fire Sprinkler Association

301-343-1457



Are you a member with a technical question?

Don't forget one of the most valuable resources that AFSA provides is Technical 
Reviews by our Technical Services Department. It’s like having an FPE on your 
staff. Visit 
www.firesprinkler.org/technicalreview<https://www.firesprinkler.org/technicalreview>
 to submit a question today! (Member login required.)

On Dec 22, 2024, at 20:40, Dominick Kasmauskas 
<[email protected]<mailto:[email protected]>> wrote:



You don't often get email from 
[email protected]<mailto:[email protected]>. Learn why 
this is important<https://aka.ms/LearnAboutSenderIdentification>

https://caselaw.findlaw.com/court/nj-supreme-court/1677993.html



“Stay in your lane.” IMHO.


Dominick Kasmauskas
Legislative Consultant
American Fire Sprinkler Association (AFSA)
518.937.4790
Kingsport, TN
www.FireSprinkler.org<http://www.firesprinkler.org/>





On Sun, Dec 22, 2024 at 20:34 Fpdcdesign 
<[email protected]<mailto:[email protected]>> wrote:

So what is worse, liability for operating outside a standard or the liability 
for not reporting a dangerous even if it is outside of that standard?



Todd Williams

Fire Protection Design/Consulting

Stonington, CT

860-608-4559



On Dec 22, 2024 at 8:19 PM, <Matthew 
Willis1<mailto:[email protected]>> wrote:

That is why we operate as Technicians, with predescribed action all written out 
for us.



Diligence dictates we cry foul for sure. Just note as an observation. The NFPA 
25 report is not the plcae for it.



Now, this is a bit different in LA. One of the states I worked in as an NFPA 25 
inspector. LA is a life safety state. So, we are Life Safety Inspectors. There 
are clear Negligence, and Gross Negligence requirements in obtaining the State 
License.



But in the end, operating outside of the adopted, predescribed standard, is a 
dangerous liability walk I do not care to take.



R/

Matt





Matthew J. Willis, C.E.T.

Ferguson Fire Design, LLC

D: [http://(602)%20337-0721](602) 337-0721 C: [http://(307)%20236-8249](307) 
236-8249

[email protected]<mailto:[email protected]>





________________________________

From: Fpdcdesign <[email protected]<mailto:[email protected]>>
Sent: Sunday, December 22, 2024 8:14 PM
To: Discussion list on issues relating to automatic fire sprinklers 
<[email protected]<mailto:[email protected]>>
Subject: [Sprinklerforum] Re: Unprotected areas



Caution:  This email originated from outside of the organization.  DO NOT click 
links or open attachments unless you recognize and trust the sender.



________________________________

I understand the requirements and limitations of 25. But let me ask this. If 
the inspector notices and obvious problem that is outside of 25 and does not 
report it. If a fire occurs that is caused or exacerbated by the problem that 
he noticed but did not report, what liability does he have.



As a PE, if I notice a dangerous condition and do not reported, I can be held 
liable.



Todd Williams

Fire Protection Design/Consulting

Stonington, CT

860-608-4559



On Dec 22, 2024 at 7:57 PM, <Matthew 
Willis1<mailto:[email protected]>> wrote:

Guys, this is a losing battle with Mike. He vents about how crappy our jobs are 
on other social media.



It's a shame, I used to like corresponding with him.



Mike, since our industry is so bad, and you are clearly making bank with your 
current position, might I suggest:









https://www.petforums.co.uk/forums/dog-walking.85/

[https://images.platforum.cloud/logos/petforums_co_uk_profile.png]<https://www.petforums.co.uk/forums/dog-walking.85/>

Dog Walking - UK Pet Forums 
Forum<https://www.petforums.co.uk/forums/dog-walking.85/>

Discuss everything regarding dog walking, from places to walk your dog, to help 
and advice in starting your own dog walking business.

www.petforums.co.uk<http://www.petforums.co.uk/>





R/

Matt





Matthew J. Willis, C.E.T.

Ferguson Fire Design, LLC

D: [(602)%20337-0721](602) 337-0721 C: [(307)%20236-8249](307) 236-8249

[email protected]<mailto:[email protected]>





________________________________

From: Bob Caputo <[email protected]<mailto:[email protected]>>
Sent: Friday, December 20, 2024 2:41 PM
To: Discussion list on issues relating to automatic fire sprinklers 
<[email protected]<mailto:[email protected]>>
Subject: [Sprinklerforum] Re: Unprotected areas



Caution:  This email originated from outside of the organization.  DO NOT click 
links or open attachments unless you recognize and trust the sender.



________________________________

Read section 1.1.3 of NFPA 25.  You’re inspecting what is there for wear and 
tear purposes. You are not verifying the design or installation of any system



[https://www.dropbox.com/s/g4h8r7hdtsr6154/AFSA_L.png?raw=1]

Bob Caputo, CFPS

President

American Fire Sprinkler Association

p:

214-349-5965 ext124

w:

firesprinkler.org<http://firesprinkler.org/>

[http://cdn2.hubspot.net/hubfs/184235/dev_images/signature_app/facebook_sig.png]<https://www.facebook.com/firesprinkler.org>
  
[http://cdn2.hubspot.net/hubfs/184235/dev_images/signature_app/twitter_sig.png] 
<https://twitter.com/afsa/status/1039528345367732224>   
[http://cdn2.hubspot.net/hubfs/184235/dev_images/signature_app/linkedin_sig.png]
 <https://www.linkedin.com/company/american-fire-sprinkler-association-afsa->   
[http://cdn2.hubspot.net/hubfs/184235/dev_images/signature_app/instagram_sig.png]
 <https://www.instagram.com/firesprinklerorg>

Train a safer, more efficient workforce.

By enrolling your employees in the AFSA Apprenticeship Training Series for 
Sprinkler 
Fitters<https://www.firesprinkler.org/WWW/Education/Apprentice_Training/WWW/Education/Apprenticeship_Training.aspx?hkey=e88ef09e-d74c-407f-abcd-995aff866149>,
 you will reap the benefits of a qualified, professional installation crew. 
Well-trained employees will work smarter, increasing your company's 
productivity and, in turn, its profits. Learn 
more<https://www.firesprinkler.org/WWW/Education/Apprentice_Training/WWW/Education/Apprenticeship_Training.aspx?hkey=e88ef09e-d74c-407f-abcd-995aff866149>.





On Fri, Dec 20, 2024 at 10:35 AM Brandon Bridgford 
<[email protected]<mailto:[email protected]>> wrote:

How do you approach unprotected areas in regards to ITM and NFPA 25. I know 
there was a discussion in the past regarding inspecting a system as is, rather 
than writing up deficiencies that have to do with system design. I have been 
told that this can open up more liability if you are not inspecting all design 
elements (i.e. density, hazard levels, etc.)



Thank you!

Brandon







_________________________________________________________
SprinklerForum mailing list:
https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org
To unsubscribe send an email to 
[email protected]<mailto:[email protected]>

_________________________________________________________ SprinklerForum 
mailing list: 
https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org To 
unsubscribe send an email to 
[email protected]<mailto:[email protected]>

_________________________________________________________ SprinklerForum 
mailing list: 
https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org To 
unsubscribe send an email to 
[email protected]<mailto:[email protected]>

_________________________________________________________
SprinklerForum mailing list:
https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org
To unsubscribe send an email to 
[email protected]<mailto:[email protected]>

_________________________________________________________
SprinklerForum mailing list:
https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org
To unsubscribe send an email to 
[email protected]<mailto:[email protected]>
_________________________________________________________ SprinklerForum 
mailing list: 
https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org To 