UK DTI applying generic standard to test hair dryer for conformity

2003-01-29 Thread Paul Chan

Dear subscribers,

I have read a news regarding on 3 Sept 02, UK Department of Trade Industry
(DTI) applied EMC Generic standard EN50081-1 Radiated Emission to test for
compliance on a AC Hair dryer, which claimed to interfere TV reception.  The
hair dryer failed the test and the importer was prosecuted by violation of
EMC Directive.

Should the product be covered by EN55014-1 already?  Please comment.

Regards
Paul Chan



This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Ron Pickard:  emc-p...@hypercom.com
 Dave Heald:   davehe...@attbi.com

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

Archive is being moved, we will announce when it is back on-line.
All emc-pstc postings are archived and searchable on the web at:
http://www.ieeecommunities.org/emc-pstc



Re: single fault conditions

2003-01-29 Thread Rich Nute




Hi Brian:


   The environment being considered is a switching power supply. The technique
   that safety agencies use to simulate a SFC on a power FET does not seem,
   IMHO, to simulate the actual failure mode of the device. To wit: when the
   mosfet fails short, it blows itself open; so the amount of current sucked
   out of mains, e.g., the PFC FET, would probably open the component after a
   few input cycles. But if I apply a direct mechanical short (source to
   drain), current is being forced to flow until the fuse blows, or until some
   series trace or component opens.

The shorting of a component does not test that
component.  Instead it tests the remainder of
the circuit for (safety?) weaknesses in the 
event of a short (or near-short) of that 
component.

I suppose the opening of a circuit does test 
for the component failing in the open condition.
But, the effect of the open-circuit is to test
the remainder of the circuit for (safety?)
weaknesses.

So, shorting or opening of a component does not
test the component but other parts of the 
circuit.

In general, the termination of fault tests 
should be not only repeatable, but should be
understood so that the parameters that make
the termination repeatable are under control.

The operation of a fuse is a good termination
of a fault test.

A cascaded fault of another component may not 
be a good termination of a fault test because 
the safe termination may depend on unknown
or uncontrolled component characteristics.  

   The Bad: some FETs fail very violently, and can actually be a fire hazard
   and/or shock hazard in open-frame switchers; but if the FET itself does not
   provide the short circuit, we will never know

Switchers generally drive the switching FETs 
with a pulse-width-modulated waveform.  One
way to introduce a fault that tests the FET is
to simulate a 100% duty cycle pulse by applying
a dc voltage of the same voltage as the PWM
signal.  This will turn on the FET continuously,
and you should get your spectacular failure.

   The Good: providing a continuous (mechanical) short will reveal if there
   are other components in the current path that could be cause the unit to
   fail in an unsafe mode. Although, according to QA records, these components
   have never failed, so it can be both demonstrated by design equations and
   empirical evidence that the SFC test does necessarily demonstrate anything
   relevant...

Uh, no... I don't think you want to base your
fault-condition safety on empirical data that
the fault will not occur.  

I have never seen the fault of basic insulation
in the field, but we nevertheless account for
the failure of basic insulation with either 
grounding or supplemental insulation.

There is nothing like a test.

   The Ugly: Safety testing results in design corrections that do not increase
   product safety.

I would argue this point.  I have not seen undue
design corrections due to a fault test.

   So would it be legitimate to over-drive the gate, forcing short circuit
   current to flow through the FET, but not to apply a mechanical short across
   the component? 

Yes!

But, unfortunately, some components do not lend
themselves for such testing.  Capacitors are a
good example -- almost impossible to induce a
fault.


Best regards,
Rich





This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Ron Pickard:  emc-p...@hypercom.com
 Dave Heald:   davehe...@attbi.com

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

Archive is being moved, we will announce when it is back on-line.
All emc-pstc postings are archived and searchable on the web at:
http://www.ieeecommunities.org/emc-pstc



RE: EN55022:1998 + A1:2000

2003-01-29 Thread Cortland Richmond

   Dave Cuthbert write

 the point at which ferrites are placed will not always have a common
mode impedance of 50 ohms. Here's An example: a large DUT has a 1 meter
long cable that connects 

Not always; make that rarely. 

Comments about the 150 ohm impedance are on target. That might be difficult
to hold to. I can see the entry needing to be a bump of not more than 15
ohms at the high frequency end, and increasing per unit length attenuation
with distance from the entry.


Cortland


This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Ron Pickard:  emc-p...@hypercom.com
 Dave Heald:   davehe...@attbi.com

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

Archive is being moved, we will announce when it is back on-line.
All emc-pstc postings are archived and searchable on the web at:
http://www.ieeecommunities.org/emc-pstc



Re: Telephone Book for Iran, again

2003-01-29 Thread Ron Pickard

David et al,

I've checked further and found the teldir site has changed to the following:

http://www.infobel.com/teldir/default.asp

Maybe that's why their servers were always busy. Who knows.

Anyway, IHTH you more.

Best regards,

Ron Pickard
rpick...@hypercom.com




  
  
  Ron Pickard 
  
   To: 
pat...@patton-assoc.com   
  
  01/29/2003 01:14 cc: 
emc-p...@majordomo.ieee.org, t...@world.std.com   
  
  PM   Subject: Re: Telephone Book for
Iran(Document link: Ron Pickard)  
  
  
  
  



David,

As for getting an actual Iranian telephone book, I'm afraid I cannot help you.
However, you might
want to try the following link. If you're not familiar with it, it provides
telephone number/address
search capabilities for essentially any country on the planet by linking to
localized telephone
company sites. Unfortunately, this site is currently experiencing technical
difficulties, at
present. But, when its working, it does work well.

http://www.teldir.com/eng/

IHTH.

Best regards,

Ron Pickard
rpick...@hypercom.com




  
   
  patton@patton-ass   
   
  oc.com   To:  
emc-p...@majordomo.ieee.org, t...@world.std.com   
  
  Sent by: cc:
   
  treg-approval@worSubject:  Telephone Book for
Iran  
  ld.std.com  
   
  
   
  
   
  01/29/2003 11:50
   
  AM  
   
  Please respond to   
   
  patton  
   
  
   
  
   




Hello All:

Would any one have a contact(s) with some any one that has an up to date
Iranian Telephone book?

We are seeking information (translated into English) which is generally
contained in the first few pages of the telephone book, which identifies
specific numbers for calling different types of services, such as the
operator, international calling, Emergency Services, and others.

Any name or contact or E Mail address information would be most sincerely
appreciated.

Best Regards

David Patton

Patton  Associates
82 Wildwood Drive
Prescott, Arizona 86305-5093 USA

Tel: +1.928.771.2900
Fax: +1.928.771.2990
Toll Free: +1.877.311.8735
E Mail: pat...@patton-assoc.com
Web: http://www.patton-assoc.com








This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Ron Pickard:  

Re: Unity Power Factor

2003-01-29 Thread Rich Nute





Hi John:


   The only other problem that I know of is distribution
   transformer overheating.  But, I believe such 
   transformers are very much larger than 3 kVA, so 3 kVA
   of non-linear loads would have very little effect. 
   
   I mean *concentrations* of loads, individually below 3 kVA or so.
   Distribution transformer overheating is the sort of effect that I am
   interested in. Are these MV/LV transformers, 'pole-pig' types or larger.

Yes, delta-wye distribution transformer overheating 
does occur due to the circulation and dissipation of 
the triplen harmonics in the primary (delta) winding.

As for the type of transformer, it is the first three-
phase transformer upstream from a commercial or 
industrial load.  (In North America, these transformers
are relatively small compared to Euro practice.)  Such 
transformers are usually a part of the (larger) 
customer premises wiring and installation, and are not 
a part of the public utility distribution system.  So,
harmonics in commercial/industrial equipment do not
appear on the public network.

In North America, this overheating problem due to 
triplen harmonics has largely disappeared with the 
advent of the distribution transformer K-factor
rating that was developed especially for this problem.

By contrast, homes in North America a supplied with 
single-phase from a single-phase distribution 
transformer (which is connected across two legs of a
three-phase delta supply).  So, harmonics in home
equipment do not appear on the public network.  (Each
distribution transformer supplies a maximum of 8 homes,
each with 200-amp service.)

In addition to overheating neutrals, some manufacturers
of partitions (for office cubes -- cube sweet cube!) 
included three-phase wiring.  The neutral connection 
of partition-to-partition connectors tended to overheat
due to harmonics, and several fires were reported.  
These, too, were fixed (I believe by doubling the
neutral or the neutral connection).


Best regards,
Rich





This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Ron Pickard:  emc-p...@hypercom.com
 Dave Heald:   davehe...@attbi.com

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

Archive is being moved, we will announce when it is back on-line.
All emc-pstc postings are archived and searchable on the web at:
http://www.ieeecommunities.org/emc-pstc



power-line LAN

2003-01-29 Thread Hans Mellberg

What are the unique testing requirements for a power-line based LAN (i.e. the
information is transported on the powerlines within a home as an example) for
CE
mark? Would the power line harmonics be an issue? ANy unique set-up besides a
couple
of devices exchanging info?

Hans Mellberg

__
Do you Yahoo!?
Yahoo! Mail Plus - Powerful. Affordable. Sign up now.
http://mailplus.yahoo.com


This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Ron Pickard:  emc-p...@hypercom.com
 Dave Heald:   davehe...@attbi.com

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

Archive is being moved, we will announce when it is back on-line.
All emc-pstc postings are archived and searchable on the web at:
http://www.ieeecommunities.org/emc-pstc



RE: single fault conditions

2003-01-29 Thread drcuthbert
Brian,
 
I believe that forcing a FET failure would be a good test but should be in
addition to the mechanical short method. If your power supply is safe for both
failure modes that would be great. The fuse should open before the failed FET
can cause a heat or fire problem. And it was already a shock hazard so that
might not be an issue. 
 
The reason I would hesitate to use only the failed FET test is that changes in
the type or manufacture or the FET could be an issue. And someone at UL might
call you on not using the mechanical short test. If an actual failed component
reveals a problem that the mechanical short does not, then the whole idea of a
mechanical short test has a problem! 
 
   Dave Cuthbert   
 
 -Original Message-
From: boconn...@t-yuden.com [mailto:boconn...@t-yuden.com]
Sent: Wednesday, January 29, 2003 2:40 PM
To: emc-p...@majordomo.ieee.org
Subject: single fault conditions



Good People of PSTC 

The environment being considered is a switching power supply. The technique
that safety agencies use to simulate a SFC on a power FET does not seem, IMHO,
to simulate the actual failure mode of the device. To wit: when the mosfet
fails short, it blows itself open; so the amount of current sucked out of
mains, e.g., the PFC FET, would probably open the component after a few input
cycles. But if I apply a direct mechanical short (source to drain), current is
being forced to flow until the fuse blows, or until some series trace or
component opens.

The Bad: some FETs fail very violently, and can actually be a fire hazard
and/or shock hazard in open-frame switchers; but if the FET itself does not
provide the short circuit, we will never know

The Good: providing a continuous (mechanical) short will reveal if there are
other components in the current path that could be cause the unit to fail in
an unsafe mode. Although, according to QA records, these components have never
failed, so it can be both demonstrated by design equations and empirical
evidence that the SFC test does necessarily demonstrate anything relevant...

The Ugly: Safety testing results in design corrections that do not increase
product safety. 

So would it be legitimate to over-drive the gate, forcing short circuit
current to flow through the FET, but not to apply a mechanical short across
the component? Experiences  comments are appreciated.

R/S, 
Brian 




RE: EN55022:1998 + A1:2000

2003-01-29 Thread drcuthbert

Chris' Maxwell equations look correct. But the point at which ferrites are
placed will not always have a common mode impedance of 50 ohms. Here's An
example: a large DUT has a 1 meter long cable that connects to the ground
plane. At 75 MHz the common mode impedance of the cable, at the DUT, is
about 3k ohms. Adding a 1k +j1k ferrite at the DUT knocks down the radiation
by 10 dB. But the radiation is not reduced mainly by losses but by
detuning the antenna. The resonant frequency has shifted from 76 MHz to
60 MHz. Now 60 MHz could be a problem. I noticed this type of thing while
trying ferrites to reduce emissions from a digital device that had a DUT
cable (not grounded at the end). I could fix one frequency with ferrites but
it would just tune the cable/system to resonance at another frequency. The
person I was working with didn't believe this theory so I ADDED wire to the
end of the DUT cable to make it 1/2 wavelength, rather than 1/4 wavelength
at the offending frequency and dropped the signal by 20 dB. 

If anyone has any changes to the model or a what-if, I can simulate it and
send you the simulated data.

Dave Cuthbert
Micron Technology


From: Pettit, Ghery [mailto:ghery.pet...@intel.com]
Sent: Wednesday, January 29, 2003 12:09 PM
To: 'Chris Maxwell'; Pettit, Ghery; neve...@attbi.com;
emc-p...@majordomo.ieee.org
Subject: RE: EN55022:1998 + A1:2000



Chris,

You can indeed make your own, but my bet is that A2LA or NIST NVLAP
inspectors will want to see calibration data, not calculations.

Now, if we just had a published calibration technique...

Ghery


From: Chris Maxwell [mailto:chris.maxw...@nettest.com]
Sent: Wednesday, January 29, 2003 10:57 AM
To: Pettit, Ghery; neve...@attbi.com; emc-p...@majordomo.ieee.org
Subject: RE: EN55022:1998 + A1:2000


Ghery,

If the standard is assuming a 50 Ohm system, doesn't this breakdown to a
simple calculation?

Insertion Loss = IL = 20 x log((50 + Zf) / 50)where Zf is the ferrite
impedance

This could easily be solved for Zf if you assume IL to be 15dB  (in this
case the dB are truely dimensionless; as you are calculating a pure loss
from an arbitrary level).

I would think that you would just have to:

1.  Solve the above for Zf.  By the way, I get 231.2 Ohms.  Can someone
check this?

2.  Gather up a box of doughnuts such that the total Zf is above the
answer for step 1 at all frequencies from 30Mhz to 1Ghz

3.  Color code the doughnuts (or whatever) and write a procedure that says
something like clamp three blue doughnuts and two red doughnuts over each
cable ...

Have I over simplified this???  Wouldn't this be proof enough for any
accreditation body?  I know that $300 may not seem like alot to some; but it
adds up after a few cables.  Besides; we went to college to learn all of
that math; why not use some of it?  I don't mind paying for stuff that I
can't make; but this one seems possible to me.

Chris Maxwell | Design Engineer - Optical Division
email chris.maxw...@nettest.com | dir +1 315 266 5128 | fax +1 315 797 8024

NetTest | 6 Rhoads Drive, Utica, NY 13502 | USA
web www.nettest.com | tel +1 315 797 4449 | 









 -Original Message-
 From: Pettit, Ghery [SMTP:ghery.pet...@intel.com]
 Sent: Wednesday, January 29, 2003 11:59 AM
 To:   'neve...@attbi.com'; emc-p...@majordomo.ieee.org
 Subject:  RE: EN55022:1998 + A1:2000
 
 
 Amendment 1 to CISPR 22:1997 (Amendment A1:2000 to EN 55022:1998) requires
 that the clamps provide at least 15 dB of loss in a 50 ohm system over the
 frequency range of 30 MHz to 1000 MHz.  The use of extension cords is
 prohibited.  Can you guarantee that your bucket of doughnuts will meet
this
 requirement?  How will you demonstrate that to your lab's accrediting
body?
 
 
 Fischer's clamps are around $300 each.  Compared with what we had to
choose
 from prior to their product, these are not big bucks.
 
 Ghery Pettit
 Intel
 
 
 
 


This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Ron Pickard:  emc-p...@hypercom.com
 Dave Heald:   davehe...@attbi.com

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

Archive is being moved, we will announce when it is back on-line.
All emc-pstc postings are archived and searchable on the web at:
http://www.ieeecommunities.org/emc-pstc


This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Ron 

RE: single fault conditions

2003-01-29 Thread boconn...@t-yuden.com
Yes sir, this is another thing I've wondered about; i.e., simulating the big
bus cap (short) SFC by applying a mechanical short accross the terminals. Does
not really demonstrate what would occur if the cap itself fails. A blown
electrolytic can be very messy.
 
I am beginning to wonder about some of the testing that I perform that the
agencies think is really great stuff...
 
R/S,
Brian


From: Lou Aiken [mailto:ai...@gulftel.com]
Sent: Wednesday, January 29, 2003 2:19 PM
To: boconn...@t-yuden.com; emc-p...@majordomo.ieee.org
Subject: Re: single fault conditions


Wow, I would have to think a while about this.  The first thing that comes to
my mind, is the risk any greater than the bulk cap failure that spew debris
around, and sometimes catch fire?  There is no reasonable way to simulate that.
 
Lou Aiken, LaMer LLC 





RE: EN55022:1998 + A1:2000

2003-01-29 Thread drcuthbert

The EM radiation from wires with and without ferrite cores can be simulated
with NEC. The required parameters are: length of wire, physical orientation,
how the end is terminated (floating? To ground?, frequency, the RL model of
the ferrite). Then one can move the ferrite around to see what happens.
There are situations where a single ferrite does virtually nothing. This why
I am wary of just throwing on a ferrite and calling it good (although I have
been known to do this). The complex impedance of a ferrite can be measured
on a VNA. If a VNA isn't available an RF source, and a spectrum analyzer
will give the scalar impedance. Or lately I have used a pulse generator and
an oscilloscope to characterize ferrites for the design of wide-band time
domain transmission line transformers. And I have used an MFJ-259B (only
$260) to measure ferrites from 1.7 to 170 MHz.  

   Dave Cuthbert
   Micron Technology 


From: Chris Maxwell [mailto:chris.maxw...@nettest.com]
Sent: Wednesday, January 29, 2003 11:57 AM
To: Pettit, Ghery; neve...@attbi.com; emc-p...@majordomo.ieee.org
Subject: RE: EN55022:1998 + A1:2000



Ghery,

If the standard is assuming a 50 Ohm system, doesn't this breakdown to a
simple calculation?

Insertion Loss = IL = 20 x log((50 + Zf) / 50)where Zf is the ferrite
impedance

This could easily be solved for Zf if you assume IL to be 15dB  (in this
case the dB are truely dimensionless; as you are calculating a pure loss
from an arbitrary level).

I would think that you would just have to:

1.  Solve the above for Zf.  By the way, I get 231.2 Ohms.  Can someone
check this?

2.  Gather up a box of doughnuts such that the total Zf is above the
answer for step 1 at all frequencies from 30Mhz to 1Ghz

3.  Color code the doughnuts (or whatever) and write a procedure that says
something like clamp three blue doughnuts and two red doughnuts over each
cable ...

Have I over simplified this???  Wouldn't this be proof enough for any
accreditation body?  I know that $300 may not seem like alot to some; but it
adds up after a few cables.  Besides; we went to college to learn all of
that math; why not use some of it?  I don't mind paying for stuff that I
can't make; but this one seems possible to me.

Chris Maxwell | Design Engineer - Optical Division
email chris.maxw...@nettest.com | dir +1 315 266 5128 | fax +1 315 797 8024

NetTest | 6 Rhoads Drive, Utica, NY 13502 | USA
web www.nettest.com | tel +1 315 797 4449 | 









 -Original Message-
 From: Pettit, Ghery [SMTP:ghery.pet...@intel.com]
 Sent: Wednesday, January 29, 2003 11:59 AM
 To:   'neve...@attbi.com'; emc-p...@majordomo.ieee.org
 Subject:  RE: EN55022:1998 + A1:2000
 
 
 Amendment 1 to CISPR 22:1997 (Amendment A1:2000 to EN 55022:1998) requires
 that the clamps provide at least 15 dB of loss in a 50 ohm system over the
 frequency range of 30 MHz to 1000 MHz.  The use of extension cords is
 prohibited.  Can you guarantee that your bucket of doughnuts will meet
this
 requirement?  How will you demonstrate that to your lab's accrediting
body?
 
 
 Fischer's clamps are around $300 each.  Compared with what we had to
choose
 from prior to their product, these are not big bucks.
 
 Ghery Pettit
 Intel
 
 
 
 


This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Ron Pickard:  emc-p...@hypercom.com
 Dave Heald:   davehe...@attbi.com

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

Archive is being moved, we will announce when it is back on-line.
All emc-pstc postings are archived and searchable on the web at:
http://www.ieeecommunities.org/emc-pstc


This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Ron Pickard:  emc-p...@hypercom.com
 Dave Heald:   davehe...@attbi.com

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

Archive is being moved, we will announce when it is back on-line.
All emc-pstc postings are archived and searchable on the web at:
http://www.ieeecommunities.org/emc-pstc



Re: single fault conditions

2003-01-29 Thread Lou Aiken
Wow, I would have to think a while about this.  The first thing that comes to
my mind, is the risk any greater than the bulk cap failure that spew debris
around, and sometimes catch fire?  There is no reasonable way to simulate that.
 
Lou Aiken, LaMer LLC 
27109 Palmetto Drive
Orange Beach, AL
36561 USA
 
tel ++ 1 251 981 6786
fax ++ 1 251 981 3054
Cell ++ 1 251 979 4648

- Original Message - 
From: boconn...@t-yuden.com 
To: emc-p...@majordomo.ieee.org 
Sent: Wednesday, January 29, 2003 3:40 PM
Subject: single fault conditions


Good People of PSTC 

The environment being considered is a switching power supply. The technique
that safety agencies use to simulate a SFC on a power FET does not seem, IMHO,
to simulate the actual failure mode of the device. To wit: when the mosfet
fails short, it blows itself open; so the amount of current sucked out of
mains, e.g., the PFC FET, would probably open the component after a few input
cycles. But if I apply a direct mechanical short (source to drain), current is
being forced to flow until the fuse blows, or until some series trace or
component opens.

The Bad: some FETs fail very violently, and can actually be a fire hazard
and/or shock hazard in open-frame switchers; but if the FET itself does not
provide the short circuit, we will never know

The Good: providing a continuous (mechanical) short will reveal if there are
other components in the current path that could be cause the unit to fail in
an unsafe mode. Although, according to QA records, these components have never
failed, so it can be both demonstrated by design equations and empirical
evidence that the SFC test does necessarily demonstrate anything relevant...

The Ugly: Safety testing results in design corrections that do not increase
product safety. 

So would it be legitimate to over-drive the gate, forcing short circuit
current to flow through the FET, but not to apply a mechanical short across
the component? Experiences  comments are appreciated.

R/S, 
Brian 




RE: EN55022:1998 + A1:2000

2003-01-29 Thread neve...@attbi.com

I believe that selecting the right combination of ferrites once, by testing 
them to provide at least 15 dB S21 should do it. Then it should be a matter of 
keeping it documented and used in a test-procedure, to ensure that every time 
one uses the same arrangement.

Regrading the proposal that it must provide at least 15 dB attenuation AND 150 
Ohm input impedance at the same time, that sounds somewhat trickier.

Neven
 
 Chris,
 
 You can indeed make your own, but my bet is that A2LA or NIST NVLAP
 inspectors will want to see calibration data, not calculations.
 
 Now, if we just had a published calibration technique...
 
 Ghery
 
 -Original Message-
 From: Chris Maxwell [mailto:chris.maxw...@nettest.com]
 Sent: Wednesday, January 29, 2003 10:57 AM
 To: Pettit, Ghery; neve...@attbi.com; emc-p...@majordomo.ieee.org
 Subject: RE: EN55022:1998 + A1:2000
 
 
 Ghery,
 
 If the standard is assuming a 50 Ohm system, doesn't this breakdown to a
 simple calculation?
 
 Insertion Loss = IL = 20 x log((50 + Zf) / 50)where Zf is the ferrite
 impedance
 
 This could easily be solved for Zf if you assume IL to be 15dB  (in this
 case the dB are truely dimensionless; as you are calculating a pure loss
 from an arbitrary level).
 
 I would think that you would just have to:
 
 1.  Solve the above for Zf.  By the way, I get 231.2 Ohms.  Can someone
 check this?
 
 2.  Gather up a box of doughnuts such that the total Zf is above the
 answer for step 1 at all frequencies from 30Mhz to 1Ghz
 
 3.  Color code the doughnuts (or whatever) and write a procedure that says
 something like clamp three blue doughnuts and two red doughnuts over each
 cable ...
 
 Have I over simplified this???  Wouldn't this be proof enough for any
 accreditation body?  I know that $300 may not seem like alot to some; but it
 adds up after a few cables.  Besides; we went to college to learn all of
 that math; why not use some of it?  I don't mind paying for stuff that I
 can't make; but this one seems possible to me.
 
 Chris Maxwell | Design Engineer - Optical Division
 email chris.maxw...@nettest.com | dir +1 315 266 5128 | fax +1 315 797 8024
 
 NetTest | 6 Rhoads Drive, Utica, NY 13502 | USA
 web www.nettest.com | tel +1 315 797 4449 | 
 
 
 
 
 
 
 
 
 
  -Original Message-
  From:   Pettit, Ghery [SMTP:ghery.pet...@intel.com]
  Sent:   Wednesday, January 29, 2003 11:59 AM
  To: 'neve...@attbi.com'; emc-p...@majordomo.ieee.org
  Subject:RE: EN55022:1998 + A1:2000
  
  
  Amendment 1 to CISPR 22:1997 (Amendment A1:2000 to EN 55022:1998) requires
  that the clamps provide at least 15 dB of loss in a 50 ohm system over the
  frequency range of 30 MHz to 1000 MHz.  The use of extension cords is
  prohibited.  Can you guarantee that your bucket of doughnuts will meet
 this
  requirement?  How will you demonstrate that to your lab's accrediting
 body?
  
  
  Fischer's clamps are around $300 each.  Compared with what we had to
 choose
  from prior to their product, these are not big bucks.
  
  Ghery Pettit
  Intel
  
  
  
  
 
 ---
 This message is from the IEEE EMC Society Product Safety
 Technical Committee emc-pstc discussion list.
 
 Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/
 
 To cancel your subscription, send mail to:
  majord...@ieee.org
 with the single line:
  unsubscribe emc-pstc
 
 For help, send mail to the list administrators:
  Ron Pickard:  emc-p...@hypercom.com
  Dave Heald:   davehe...@attbi.com
 
 For policy questions, send mail to:
  Richard Nute:   ri...@ieee.org
  Jim Bacher: j.bac...@ieee.org
 
 Archive is being moved, we will announce when it is back on-line.
 All emc-pstc postings are archived and searchable on the web at:
 http://www.ieeecommunities.org/emc-pstc


This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Ron Pickard:  emc-p...@hypercom.com
 Dave Heald:   davehe...@attbi.com

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

Archive is being moved, we will announce when it is back on-line.
All emc-pstc postings are archived and searchable on the web at:
http://www.ieeecommunities.org/emc-pstc



Re: Unity Power Factor

2003-01-29 Thread Ken Javor

I haven't been following this thread closely, so if the following has 
already been addressed, I apologize.  I noticed this several years ago at
the office building I worked in at the time.  My cube moved from one end of
the building to another, and my computer wouldn't always start - it took
several tries.  I brought in a scope, and saw that the ac voltage waveform
was flattened.  It was more flattened at my new cube than at my old one.
Clearly this is related to power supplies recharging filter caps at the peak
of the ac waveform, and the relative distance from the building main breaker
at the two different cubes.  This is a power/crest factor issue, not
directly a harmonic issue, although drawing current only near the peak of
the waveform will definitely generate harmonics.


From: John Woodgate j...@jmwa.demon.co.uk
To: emc-p...@majordomo.ieee.org
Subject: Re: Unity Power Factor
Date: Wed, Jan 29, 2003, 2:23 PM



 I read in !emc-pstc that Rich Nute ri...@sdd.hp.com wrote (in
 200301291623.iaa07...@epgc264.sdd.hp.com) about 'Unity Power Factor'
 on Wed, 29 Jan 2003:



Hi John:


   In the USA, this has largely been fixed by a change in
   the USA National Electrical Code.

   There must be quite a number of installations that are not yet upgraded.

Where a problem existed, it was fixed by pulling
another neutral.

 Yes, we do that, too.

   Are there any other problems appearing in the field which can be
   reliably determined as due to concentrations of non-linear loads of less
   than 3 kVA or so?

Probably not.

The only other problem that I know of is distribution
transformer overheating.  But, I believe such
transformers are very much larger than 3 kVA, so 3 kVA
of non-linear loads would have very little effect.

 I mean *concentrations* of loads, individually below 3 kVA or so.
 Distribution transformer overheating is the sort of effect that I am
 interested in. Are these MV/LV transformers, 'pole-pig' types or larger.
 --
 Regards, John Woodgate, OOO - Own Opinions Only. http://www.jmwa.demon.co.uk
 Interested in professional sound reinforcement and distribution? Then go to
 http://www.isce.org.uk
 PLEASE do NOT copy news posts to me by E-MAIL!

 ---
 This message is from the IEEE EMC Society Product Safety
 Technical Committee emc-pstc discussion list.

 Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

 To cancel your subscription, send mail to:
  majord...@ieee.org
 with the single line:
  unsubscribe emc-pstc

 For help, send mail to the list administrators:
  Ron Pickard:  emc-p...@hypercom.com
  Dave Heald:   davehe...@attbi.com

 For policy questions, send mail to:
  Richard Nute:   ri...@ieee.org
  Jim Bacher: j.bac...@ieee.org

 Archive is being moved, we will announce when it is back on-line.
 All emc-pstc postings are archived and searchable on the web at:
 http://www.ieeecommunities.org/emc-pstc
 


This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Ron Pickard:  emc-p...@hypercom.com
 Dave Heald:   davehe...@attbi.com

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

Archive is being moved, we will announce when it is back on-line.
All emc-pstc postings are archived and searchable on the web at:
http://www.ieeecommunities.org/emc-pstc



Re: EN55022:1998 + A1:2000

2003-01-29 Thread John Woodgate

I read in !emc-pstc that Chris Maxwell chris.maxw...@nettest.com wrote
(in 83d652574e7af740873674f9fc12dbaaf7e...@utexh1w2.gnnettest.com)
about 'EN55022:1998 + A1:2000' on Wed, 29 Jan 2003:

If the standard is assuming a 50 Ohm system, doesn't this breakdown to a
simple 
calculation?

Quite possibly, but it *isn't* a 50 ohm system. The device should absorb
the energy passing down the cable, not reflect it, so it should match
the impedance of the cable/ground propagator well. This propagator has
traditionally been assumed to have a characteristic impedance of 150
ohms.

In an earlier post, I said that the transfer attenuation is
'irrelevant', and it escaped before I could correct it. It wouldn't be
irrelevant if it were 3 dB, say, because that would mean that only half
the energy was absorbed. So, it would be fairer to say that the
attenuation is 'of secondary importance' compared with the input
impedance, because if the impedance is far out, the energy never gets
into the device, so can't be absorbed.
-- 
Regards, John Woodgate, OOO - Own Opinions Only. http://www.jmwa.demon.co.uk 
Interested in professional sound reinforcement and distribution? Then go to 
http://www.isce.org.uk
PLEASE do NOT copy news posts to me by E-MAIL!


This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Ron Pickard:  emc-p...@hypercom.com
 Dave Heald:   davehe...@attbi.com

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

Archive is being moved, we will announce when it is back on-line.
All emc-pstc postings are archived and searchable on the web at:
http://www.ieeecommunities.org/emc-pstc



Re: Declaration of Conformity

2003-01-29 Thread John Woodgate

I read in !emc-pstc that Scott Douglas dougl...@naradnetworks.com
wrote (in 5.0.2.1.2.20030129141347.00a63...@pop.business.earthlink.net
) about 'Declaration of Conformity' on Wed, 29 Jan 2003:
Please forgive my mental lapse here. I know this subject has come 
up before. This is a question of what to do with the Declaration of 
Conformity for the EU.

So please tell me what you do.

Do you put a CE mark on the outside of the box?

It's a good idea to do so; it keeps the Customs fingers out of the box.

 Is this in lieu of 
the D of C?

Absolutely not.

Do you put the D of C on the outside of the box?

Not normally. I see no reason to do so.

Do you put the D of C inside the box on separate paper?

If you want to, or print it in the instruction book. Most safety
standards *require* an instruction book to be provided.

Do you put the D of C in (on) a CD ROM and no paper in the box?

It's a few lines of text. Why would you put it on a CD-ROM?

Do you include the D of C with Customs papers only?

It is highly advisable to include it with shipping documents, but 'only'
is too definite.
-- 
Regards, John Woodgate, OOO - Own Opinions Only. http://www.jmwa.demon.co.uk 
Interested in professional sound reinforcement and distribution? Then go to 
http://www.isce.org.uk
PLEASE do NOT copy news posts to me by E-MAIL!


This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Ron Pickard:  emc-p...@hypercom.com
 Dave Heald:   davehe...@attbi.com

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

Archive is being moved, we will announce when it is back on-line.
All emc-pstc postings are archived and searchable on the web at:
http://www.ieeecommunities.org/emc-pstc



Re: RTTE directive.

2003-01-29 Thread John Woodgate

I read in !emc-pstc that Gary McInturff Gary.McInturff@worldwidepackets
.com wrote (in 4e9a9436c008314eaa32033b23e96fd90b0...@thorondor.wwp.co
m) about 'RTTE directive.' on Wed, 29 Jan 2003:
Anybody have a link to peruse and purchase this, and a brief synopsis.

Replied to a previous e-mail question, by e-mail.
-- 
Regards, John Woodgate, OOO - Own Opinions Only. http://www.jmwa.demon.co.uk 
Interested in professional sound reinforcement and distribution? Then go to 
http://www.isce.org.uk
PLEASE do NOT copy news posts to me by E-MAIL!


This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Ron Pickard:  emc-p...@hypercom.com
 Dave Heald:   davehe...@attbi.com

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

Archive is being moved, we will announce when it is back on-line.
All emc-pstc postings are archived and searchable on the web at:
http://www.ieeecommunities.org/emc-pstc



single fault conditions

2003-01-29 Thread boconn...@t-yuden.com
Good People of PSTC 

The environment being considered is a switching power supply. The technique
that safety agencies use to simulate a SFC on a power FET does not seem, IMHO,
to simulate the actual failure mode of the device. To wit: when the mosfet
fails short, it blows itself open; so the amount of current sucked out of
mains, e.g., the PFC FET, would probably open the component after a few input
cycles. But if I apply a direct mechanical short (source to drain), current is
being forced to flow until the fuse blows, or until some series trace or
component opens.

The Bad: some FETs fail very violently, and can actually be a fire hazard
and/or shock hazard in open-frame switchers; but if the FET itself does not
provide the short circuit, we will never know

The Good: providing a continuous (mechanical) short will reveal if there are
other components in the current path that could be cause the unit to fail in
an unsafe mode. Although, according to QA records, these components have never
failed, so it can be both demonstrated by design equations and empirical
evidence that the SFC test does necessarily demonstrate anything relevant...

The Ugly: Safety testing results in design corrections that do not increase
product safety. 

So would it be legitimate to over-drive the gate, forcing short circuit
current to flow through the FET, but not to apply a mechanical short across
the component? Experiences  comments are appreciated.

R/S, 
Brian 




Re: EN55022:1998 + A1:2000

2003-01-29 Thread John Woodgate

I read in !emc-pstc that Gert Gremmen g.grem...@cetest.nl wrote (in
mpeeiccjhhndekobpnnbmeegckaa.g.grem...@cetest.nl) about 'EN55022:1998
+ A1:2000' on Wed, 29 Jan 2003:

Proposals are on their way to specify
both transfer attenuation (first) and
input CM impedance of those clamps  (later)
The radiation properties of the exposed wire will
vary widely depending on the CM load impedance.
The attenuation characteristic is to isolate
auxilary wire (and signal) from the test setup.

When we discussed this in the UK committee, it was pointed out that this
clamp is NOT a filter and its transfer attenuation is irrelevant. It is
*intended* to absorb energy propagating down the cable, so it is the
*input impedance* that matters.

AIUI, even though that is so, because CISPR/I (G?) specified a transfer
attenuation, CISPR 16-1 will continue to specify a value for this
irrelevant property!
-- 
Regards, John Woodgate, OOO - Own Opinions Only. http://www.jmwa.demon.co.uk 
Interested in professional sound reinforcement and distribution? Then go to 
http://www.isce.org.uk
PLEASE do NOT copy news posts to me by E-MAIL!


This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Ron Pickard:  emc-p...@hypercom.com
 Dave Heald:   davehe...@attbi.com

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

Archive is being moved, we will announce when it is back on-line.
All emc-pstc postings are archived and searchable on the web at:
http://www.ieeecommunities.org/emc-pstc



EN61000-3-2/3 applicability

2003-01-29 Thread Sam Wismer
The scope of these standards includes all equipment having an input current
upto and including 16A per phase and intended to be connected to a public
low-voltage distribution systems of between 220V and 250V at 50Hz line to
neutral.  Does public infer that only consumer goods that use residential
service are obligated to these standards or are industrial products used in
industrial locations that meet the electrical specifications as identified
above also obligated to these standards? 
 
Kind Regards,
 
 
Sam Wismer
Engineering Manager
ACS, Inc.
 
*Tel: (770) 831-8048
*Fax: (770) 831-8598
*Web:   http://www.acstestlab.com www.acstestlab.com
 mailto:*swis...@acstestlab.com *swis...@acstestlab.com
 
 



RE: EN55022:1998 + A1:2000

2003-01-29 Thread Cortland Richmond


Ghery Pettit wrote:

Chris,

You can indeed make your own, but my bet is that A2LA or NIST NVLAP
inspectors will want to see calibration data, not calculations.

Now, if we just had a published calibration technique...


This is still not rocket science. Using Z = 138*(log OD/ID) --- for an
air dielectric --  a 2.3:1 ratio of inner conductor diameter to outer
conductor's inner diameter gives a 50 ohm fixture. A fixture with this
impedance may be constructed which will allow slipping beads on the center
conductor and _measuring_ the resulting attenuation. The instruments we
measure with ARE traceably calibrated to a primary standard. And since the
attenuation requirement is a _minimum_, not a precise value, it is quite
easy to insure that it is met. 


Cortland


This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Ron Pickard:  emc-p...@hypercom.com
 Dave Heald:   davehe...@attbi.com

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

Archive is being moved, we will announce when it is back on-line.
All emc-pstc postings are archived and searchable on the web at:
http://www.ieeecommunities.org/emc-pstc



RE: EN55022:1998 + A1:2000

2003-01-29 Thread Chris Maxwell

Indeed,  a very good point!

I wonder what is meant by the 50 Ohm system does that mean a function
generator with 50 Ohm output impedance, 50 Ohm cable and a 50 Ohm load?  (This
could be simulated nicely by connecting a function generator to a 50 Ohm
spectrum analyzer input using 50 Ohm cable)  

If that were the case, then calibration would be relatively easy.  

If that were the case, then my initial calculation would also have to be
adjusted to take into account the total non-ferrite impedance which would be
closer to 150 Ohms...Yielding a  calculated Zf  of 693 Ohms.  I previously
assumed that a 50Ohm system had a total pre-ferrite impedance of 50 Ohms,
which gave me a Zf of 231 Ohms.  Of course, the standard says 15dB
minimum... so you could just use 1000 Ohms (at all frequencies, remember)
and be done with it!  It probably still wouldn't cost $300.  

Before anybody goes out and buys ferrites ala carte, remember; I'm not on
any CISPR commitees; I'm just throwing out a little bit of Math and some
assumptions and suggesting that this could be done.  

Chris Maxwell | Design Engineer - Optical Division
email chris.maxw...@nettest.com | dir +1 315 266 5128 | fax +1 315 797 8024

NetTest | 6 Rhoads Drive, Utica, NY 13502 | USA
web www.nettest.com | tel +1 315 797 4449 | 




 -Original Message-
 From: Pettit, Ghery [SMTP:ghery.pet...@intel.com]
 Sent: Wednesday, January 29, 2003 2:09 PM
 To:   Chris Maxwell; Pettit, Ghery; neve...@attbi.com;
emc-p...@majordomo.ieee.org
 Subject:  RE: EN55022:1998 + A1:2000
 
 Chris,
 
 You can indeed make your own, but my bet is that A2LA or NIST NVLAP
 inspectors will want to see calibration data, not calculations.
 
 Now, if we just had a published calibration technique...
 
 Ghery
 
 


This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Ron Pickard:  emc-p...@hypercom.com
 Dave Heald:   davehe...@attbi.com

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

Archive is being moved, we will announce when it is back on-line.
All emc-pstc postings are archived and searchable on the web at:
http://www.ieeecommunities.org/emc-pstc



Re: Unity Power Factor

2003-01-29 Thread John Woodgate

I read in !emc-pstc that Rich Nute ri...@sdd.hp.com wrote (in
200301291623.iaa07...@epgc264.sdd.hp.com) about 'Unity Power Factor'
on Wed, 29 Jan 2003:



Hi John:


   In the USA, this has largely been fixed by a change in
   the USA National Electrical Code.  
   
   There must be quite a number of installations that are not yet upgraded.

Where a problem existed, it was fixed by pulling
another neutral.

Yes, we do that, too.

   Are there any other problems appearing in the field which can be
   reliably determined as due to concentrations of non-linear loads of less
   than 3 kVA or so?

Probably not.

The only other problem that I know of is distribution
transformer overheating.  But, I believe such 
transformers are very much larger than 3 kVA, so 3 kVA
of non-linear loads would have very little effect. 

I mean *concentrations* of loads, individually below 3 kVA or so.
Distribution transformer overheating is the sort of effect that I am
interested in. Are these MV/LV transformers, 'pole-pig' types or larger.
-- 
Regards, John Woodgate, OOO - Own Opinions Only. http://www.jmwa.demon.co.uk 
Interested in professional sound reinforcement and distribution? Then go to 
http://www.isce.org.uk
PLEASE do NOT copy news posts to me by E-MAIL!


This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Ron Pickard:  emc-p...@hypercom.com
 Dave Heald:   davehe...@attbi.com

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

Archive is being moved, we will announce when it is back on-line.
All emc-pstc postings are archived and searchable on the web at:
http://www.ieeecommunities.org/emc-pstc



Re: Telephone Book for Iran

2003-01-29 Thread Ron Pickard


David,

As for getting an actual Iranian telephone book, I'm afraid I cannot help you.
However, you might
want to try the following link. If you're not familiar with it, it provides
telephone number/address
search capabilities for essentially any country on the planet by linking to
localized telephone
company sites. Unfortunately, this site is currently experiencing technical
difficulties, at
present. But, when its working, it does work well.

http://www.teldir.com/eng/

IHTH.

Best regards,

Ron Pickard
rpick...@hypercom.com




  
   
  patton@patton-ass   
   
  oc.com   To:  
emc-p...@majordomo.ieee.org, t...@world.std.com   
  
  Sent by: cc:
   
  treg-approval@worSubject:  Telephone Book for
Iran  
  ld.std.com  
   
  
   
  
   
  01/29/2003 11:50
   
  AM  
   
  Please respond to   
   
  patton  
   
  
   
  
   




Hello All:

Would any one have a contact(s) with some any one that has an up to date
Iranian Telephone book?

We are seeking information (translated into English) which is generally
contained in the first few pages of the telephone book, which identifies
specific numbers for calling different types of services, such as the
operator, international calling, Emergency Services, and others.

Any name or contact or E Mail address information would be most sincerely
appreciated.

Best Regards

David Patton

Patton  Associates
82 Wildwood Drive
Prescott, Arizona 86305-5093 USA

Tel: +1.928.771.2900
Fax: +1.928.771.2990
Toll Free: +1.877.311.8735
E Mail: pat...@patton-assoc.com
Web: http://www.patton-assoc.com







This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Ron Pickard:  emc-p...@hypercom.com
 Dave Heald:   davehe...@attbi.com

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

Archive is being moved, we will announce when it is back on-line.
All emc-pstc postings are archived and searchable on the web at:
http://www.ieeecommunities.org/emc-pstc



Associated Research Model 6554SA Compliance Analyzer for sale

2003-01-29 Thread Dave Lorusso
For anyone looking for a very useful piece of Product Safety test gear, you
can’t beat Associated Research’s line of automated Compliance Analyzers. 
I have an extra one and am offering it for sale on eBay:
 
http://cgi.ebay.com/ws/eBayISAPI.dll?ViewItem
http://cgi.ebay.com/ws/eBayISAPI.dll?ViewItemitem=3309216981
item=3309216981
 
Best regards,
 
Dave
512.695.5871
www.lorusso.com http://www.lorusso.com/  



RE: Automotive v. EMC Directives

2003-01-29 Thread Jim Eichner

You're right that the link I gave only gets you a copy of the Directive
without the figures.  The only downloadable versions I've found that do have
the figures are the .tif format ones available if you search on the document
from the following location:
http://europa.eu.int/eur-lex/en/search/search_lif.html

The search results will offer you the option of having a .tif file e-mailed
to you.  There are drawbacks to this - slow fuzzy viewing and large file
size which resulted in them breaking the directive into 2 parts when they
sent it to me.

Does anyone know another way to get directives on-line complete with the
figures, without resorting to .tif files?

Thanks,

Jim Eichner, P.Eng. 
Regulatory Compliance Manager
Xantrex Technology Inc. 
phone: (604) 422-2546 
fax: (604) 420-1591 
e-mail: jim.eich...@xantrex.com 
web: www.xantrex.com 
Confidentiality Notice: This email message, including any attachments, is
for the sole use of the intended recipient(s) and may contain confidential
and privileged information. Any unauthorized review, use, disclosure or
distribution is prohibited. If you are not the intended recipient, please
contact the sender by reply e-mail and destroy all copies of the original
message.




From: KC CHAN [PDD] [mailto:kcc...@hkpc.org]
Sent: Tuesday, January 28, 2003 7:40 PM
To: alan.hud...@amsjv.com; emc-p...@majordomo.ieee.org;
jim.eich...@xantrex.com
Subject: RE: Automotive v. EMC Directives



Where can I have the figures referenced in the link?

 Jim Eichner jim.eich...@xantrex.com 01/29/03 03:46am 

The requirements are very different, especially in the test setup, and I
don't think you can make assumptions in either direction.  For an electronic
sub-assembly, for example, you do radiated emissions at a measurement
distance of 1m, which is very much in the near field.  You won't likely be
able to make any assumptions from that as to how you will fare in a 3m or
10m emissions test for the EMC Directive, which is arguably in the far
field.  There are lots of other significant differences, so I'm afraid
you'll need to do the reading and do some testing.  

One bit of good news:  the Automotive EMC Directive contains its own
requirements, so you don't need to buy standards to go along with it.
Here's a link:

http://europa.eu.int/smartapi/cgi/sga_doc?smartapi!celexapi!prod!CELEXnumdoc

lg=ENnumdoc=31995L0054model=guichett

Good luck,

Jim Eichner, P.Eng. 
Regulatory Compliance Manager  
Xantrex Technology Inc. 
e-mail: jim.eich...@xantrex.com 
web: www.xantrex.com 

Any opinions expressed are those of my invisible friend, who really exists.
Honest.  No really.

Confidentiality Notice: This email message, including any attachments, is
for the sole use of the intended recipient(s) and may contain confidential
and privileged information. Any unauthorized review, use, disclosure or
distribution is prohibited. If you are not the intended recipient, please
contact the sender by reply e-mail and destroy all copies of the original
message.






From: Hudson, Alan [mailto:alan.hud...@amsjv.com] 
Sent: Tuesday, January 28, 2003 9:34 AM
To: EMC-pstc (E-mail)
Subject: Automotive v. EMC Directives






G'Day!

Is anyone familiar with the standards needed to comply with the Automotive
*and* the EMC Directives? How do they compare? Or to put it another way, if
an item of equipment was known to be compliant with the Automotive
Directive, is it likely that it would therefore meet the requirements of the
EMC Directive?

Alan
-- 
Alenia Marconi Systems
Scotland


This email and any attachments are confidential to the intended
recipient and may also be privileged. If you are not the intended
recipient please delete it from your system and notify the sender.
You should not copy it or use it for any purpose nor disclose or
distribute its contents to any other person.



This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/ 

To cancel your subscription, send mail to:
 majord...@ieee.org 
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Ron Pickard:  emc-p...@hypercom.com 
 Dave Heald:   davehe...@attbi.com 

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org 
 Jim Bacher: j.bac...@ieee.org 

All emc-pstc postings are archived and searchable on the web at:
http://ieeepstc.mindcruiser.com/ 
Click on browse and then emc-pstc mailing list


This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/ 

To cancel your subscription, send mail to:
 majord...@ieee.org 
with the single line:
 unsubscribe emc-pstc

For 

Telephone Book for Iran

2003-01-29 Thread David Patton

Hello All:

Would any one have a contact(s) with some any one that has an up to date
Iranian Telephone book?

We are seeking information (translated into English) which is generally
contained in the first few pages of the telephone book, which identifies
specific numbers for calling different types of services, such as the
operator, international calling, Emergency Services, and others.

Any name or contact or E Mail address information would be most sincerely
appreciated.

Best Regards

David Patton

Patton  Associates
82 Wildwood Drive
Prescott, Arizona 86305-5093 USA

Tel: +1.928.771.2900
Fax: +1.928.771.2990
Toll Free: +1.877.311.8735
E Mail: pat...@patton-assoc.com
Web: http://www.patton-assoc.com



This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Ron Pickard:  emc-p...@hypercom.com
 Dave Heald:   davehe...@attbi.com

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

Archive is being moved, we will announce when it is back on-line.
All emc-pstc postings are archived and searchable on the web at:
http://www.ieeecommunities.org/emc-pstc



Declaration of Conformity

2003-01-29 Thread Scott Douglas
Hi Ya'll,

Please forgive my mental lapse here. I know this subject has come up before.
This is a question of what to do with the Declaration of Conformity for the EU.

So please tell me what you do.

Do you put a CE mark on the outside of the box? Is this in lieu of the D of C?

Do you put the D of C on the outside of the box?

Do you put the D of C inside the box on separate paper?

Do you put the D of C in (on) a CD ROM and no paper in the box?

Do you include the D of C with Customs papers only?

So as to not clutter the list, off-list replies would be preferred.

Thanks in advance for you replies.

Scott Douglas


Senior Compliance Engineer
Narad Networks
515 Groton Road 
Westford, MA 01886
phone:  978 589-1869
dougl...@naradnetworks.com
www.naradnetworks.com http://www.naradnetworks.com/ 




--- This message is from the IEEE EMC
Society Product Safety Technical Committee emc-pstc discussion list. Visit our
web site at: http://www.ewh.ieee.org/soc/emcs/pstc/ To cancel your
subscription, send mail to: majord...@ieee.org with the single line:
unsubscribe emc-pstc For help, send mail to the list administrators: Ron
Pickard: emc-p...@hypercom.com Dave Heald: davehe...@attbi.com For policy
questions, send mail to: Richard Nute: ri...@ieee.org Jim Bacher:
j.bac...@ieee.org Archive is being moved, we will announce when it is back
on-line. All emc-pstc postings are archived and searchable on the web at:
http://www.ieeecommunities.org/emc-pstc



RE: EN55022:1998 + A1:2000

2003-01-29 Thread Pettit, Ghery

Chris,

You can indeed make your own, but my bet is that A2LA or NIST NVLAP
inspectors will want to see calibration data, not calculations.

Now, if we just had a published calibration technique...

Ghery


From: Chris Maxwell [mailto:chris.maxw...@nettest.com]
Sent: Wednesday, January 29, 2003 10:57 AM
To: Pettit, Ghery; neve...@attbi.com; emc-p...@majordomo.ieee.org
Subject: RE: EN55022:1998 + A1:2000


Ghery,

If the standard is assuming a 50 Ohm system, doesn't this breakdown to a
simple calculation?

Insertion Loss = IL = 20 x log((50 + Zf) / 50)where Zf is the ferrite
impedance

This could easily be solved for Zf if you assume IL to be 15dB  (in this
case the dB are truely dimensionless; as you are calculating a pure loss
from an arbitrary level).

I would think that you would just have to:

1.  Solve the above for Zf.  By the way, I get 231.2 Ohms.  Can someone
check this?

2.  Gather up a box of doughnuts such that the total Zf is above the
answer for step 1 at all frequencies from 30Mhz to 1Ghz

3.  Color code the doughnuts (or whatever) and write a procedure that says
something like clamp three blue doughnuts and two red doughnuts over each
cable ...

Have I over simplified this???  Wouldn't this be proof enough for any
accreditation body?  I know that $300 may not seem like alot to some; but it
adds up after a few cables.  Besides; we went to college to learn all of
that math; why not use some of it?  I don't mind paying for stuff that I
can't make; but this one seems possible to me.

Chris Maxwell | Design Engineer - Optical Division
email chris.maxw...@nettest.com | dir +1 315 266 5128 | fax +1 315 797 8024

NetTest | 6 Rhoads Drive, Utica, NY 13502 | USA
web www.nettest.com | tel +1 315 797 4449 | 









 -Original Message-
 From: Pettit, Ghery [SMTP:ghery.pet...@intel.com]
 Sent: Wednesday, January 29, 2003 11:59 AM
 To:   'neve...@attbi.com'; emc-p...@majordomo.ieee.org
 Subject:  RE: EN55022:1998 + A1:2000
 
 
 Amendment 1 to CISPR 22:1997 (Amendment A1:2000 to EN 55022:1998) requires
 that the clamps provide at least 15 dB of loss in a 50 ohm system over the
 frequency range of 30 MHz to 1000 MHz.  The use of extension cords is
 prohibited.  Can you guarantee that your bucket of doughnuts will meet
this
 requirement?  How will you demonstrate that to your lab's accrediting
body?
 
 
 Fischer's clamps are around $300 each.  Compared with what we had to
choose
 from prior to their product, these are not big bucks.
 
 Ghery Pettit
 Intel
 
 
 
 


This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Ron Pickard:  emc-p...@hypercom.com
 Dave Heald:   davehe...@attbi.com

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

Archive is being moved, we will announce when it is back on-line.
All emc-pstc postings are archived and searchable on the web at:
http://www.ieeecommunities.org/emc-pstc



RE: EN55022:1998 + A1:2000

2003-01-29 Thread Chris Maxwell

Ghery,

If the standard is assuming a 50 Ohm system, doesn't this breakdown to a
simple calculation?

Insertion Loss = IL = 20 x log((50 + Zf) / 50)where Zf is the ferrite
impedance

This could easily be solved for Zf if you assume IL to be 15dB  (in this case
the dB are truely dimensionless; as you are calculating a pure loss from an
arbitrary level).

I would think that you would just have to:

1.  Solve the above for Zf.  By the way, I get 231.2 Ohms.  Can someone check
this?

2.  Gather up a box of doughnuts such that the total Zf is above the answer
for step 1 at all frequencies from 30Mhz to 1Ghz

3.  Color code the doughnuts (or whatever) and write a procedure that says
something like clamp three blue doughnuts and two red doughnuts over each
cable ...

Have I over simplified this???  Wouldn't this be proof enough for any
accreditation body?  I know that $300 may not seem like alot to some; but it
adds up after a few cables.  Besides; we went to college to learn all of that
math; why not use some of it?  I don't mind paying for stuff that I can't
make; but this one seems possible to me.

Chris Maxwell | Design Engineer - Optical Division
email chris.maxw...@nettest.com | dir +1 315 266 5128 | fax +1 315 797 8024

NetTest | 6 Rhoads Drive, Utica, NY 13502 | USA
web www.nettest.com | tel +1 315 797 4449 | 









 -Original Message-
 From: Pettit, Ghery [SMTP:ghery.pet...@intel.com]
 Sent: Wednesday, January 29, 2003 11:59 AM
 To:   'neve...@attbi.com'; emc-p...@majordomo.ieee.org
 Subject:  RE: EN55022:1998 + A1:2000
 
 
 Amendment 1 to CISPR 22:1997 (Amendment A1:2000 to EN 55022:1998) requires
 that the clamps provide at least 15 dB of loss in a 50 ohm system over the
 frequency range of 30 MHz to 1000 MHz.  The use of extension cords is
 prohibited.  Can you guarantee that your bucket of doughnuts will meet this
 requirement?  How will you demonstrate that to your lab's accrediting body?
 
 
 Fischer's clamps are around $300 each.  Compared with what we had to choose
 from prior to their product, these are not big bucks.
 
 Ghery Pettit
 Intel
 
 
 
 


This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Ron Pickard:  emc-p...@hypercom.com
 Dave Heald:   davehe...@attbi.com

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

Archive is being moved, we will announce when it is back on-line.
All emc-pstc postings are archived and searchable on the web at:
http://www.ieeecommunities.org/emc-pstc



RE: RTTE directive.

2003-01-29 Thread Mark Render

Hope the following links help - I think it is what you are looking for :

Link to the text of the RTTE Directive : 

http://europa.eu.int/comm/enterprise/rtte/dir99-5.htm

List of harmonised standards published in the Official Journal of the EC for
the RTTE:

http://europa.eu.int/eur-lex/en/dat/2002/c_304/c_30420021207en00160042.pdf

General RTTE information :

http://europa.eu.int/comm/enterprise/rtte/infor.htm


Mark Render
EMC and Radio Group  Manager
KTL
Saxon Way
Priory Park West
Hessle
East Yorkshire
HU13 9PB


From: Gary McInturff [mailto:gary.mcintu...@worldwidepackets.com]
Sent: 29 January 2003 16:11
To: EMC-PSTC (E-mail)
Subject: RTTE directive.



Anybody have a link to peruse and purchase this, and a brief
synopsis.
I assume it calls out the standard EMC tests -  EN55022, EN55024,
and Safety standards, along with a standard or section which deals with the
intentional radiator portion of box, and harmonized frequencies etc. The
device itself is a Wi-fi type box. Ethernet in, and RF out. Is that correct?
Gary


This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Ron Pickard:  emc-p...@hypercom.com
 Dave Heald:   davehe...@attbi.com

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

Archive is being moved, we will announce when it is back on-line.
All emc-pstc postings are archived and searchable on the web at:
http://www.ieeecommunities.org/emc-pstc


This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Ron Pickard:  emc-p...@hypercom.com
 Dave Heald:   davehe...@attbi.com

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

Archive is being moved, we will announce when it is back on-line.
All emc-pstc postings are archived and searchable on the web at:
http://www.ieeecommunities.org/emc-pstc



RE: EN55022:1998 + A1:2000

2003-01-29 Thread John Cronin
Gert et al

Can anyone provide a spec for the ferrite.  For example, what is typically
used in a CISPR 16 radiated power clamp?  I am guessing when I say that I
believe these were originally a Philips type ferrite ring.  I have two of
these clamps (Luthi MDS21 and Anritsu) and have found them to be quite
different in terms of attenuation characteristics when used as loads in
61000-4-6 conducted immunity testing.

A short tutorial on the characteristics of ferrites as used in these clamps
would be nice.  Is anyone aware of a source, eg in a particular standard?

Best Regards

John Cronin



From: Gert Gremmen 
Reply-To: Gert Gremmen 
To: Gordon,Ian , 
Subject: RE: EN55022:1998 + A1:2000 
Date: Wed, 29 Jan 2003 16:54:00 +0100 
 
 
Hi Group, 
 
 
Proposals are on their way to specify 
both transfer attenuation (first) and 
input CM impedance of those clamps (later) 
The radiation properties of the exposed wire will 
vary widely depending on the CM load impedance. 
The attenuation characteristic is to isolate 
auxilary wire (and signal) from the test setup. 
 
Both will be published as an Amendment on CISPR 16 
document. 
A controllable impedance clamp system can be 
constructed using a current clamp system 
with variable load . (like current clamp/transformer) 
The first 1-5 rings can be loaded with a 
screened wire that terminates into a variable ( or fixed) 
impedance. Target CM impedance will probably be 150 Ohm 
to be transferred to the load. 
 
This has best impact in the lower frequency range. 
High loss ferrite will do better as low loss ferrite. 
Attenuation is just a matter of quantity of rings. 
Regards, 
 
Gert Gremmen 
Manager 
 
 
Ce-test, Qualified Testing 
ce marking and more .. 
EMCD LVD RTTED MDD MD 
www.cetest.nl 
Electrical / Electronic Equipment 
 
 
 
-Original Message- 
From: owner-emc-p...@majordomo.ieee.org 
[mailto:owner-emc-p...@majordomo.ieee.org]On Behalf Of Gordon,Ian 
Sent: Wednesday, January 29, 2003 11:51 AM 
To: emc-p...@majordomo.ieee.org 
Subject: RE: EN55022:1998 + A1:2000 
 
 
 
All 
I can see that my manager would prefer to use Neven's approach - it is 
probably much cheaper than buying clamps. However, does anybody have any 
practical experience of this? 
A reply from an accredited test house would be welcomed! 
 
Thanks 
Ian Gordon 
-Original Message- 
From: neve...@attbi.com [mailto:neve...@attbi.com] 
Sent: 29 January 2003 05:22 
To: emc-p...@majordomo.ieee.org 
Subject: Re: EN55022:1998 + A1:2000 
 
 
 
Instead of paying big bucks for the clamps (I am not sure what the price is, 
 
but I'm sure it is too much anyway :), why not buying a bucket of ferrite 
doughnuts that can be used over cables. Or, when possible, building in-line 
adapters out of sections of cables (maybe 1m long) and lining them up with 
ferrites. I'd select a combination of ferrites to cover 30 MHz to about 300 
MHz. The high frequencies will be radiated anyway by the segment of the 
cables 
close to the DUT. Taking a little more thorough approach, I'd check the 
impedance with the lineup fixed over a defined height above a GND plane. 
(Not 
sure if that would make a big practical difference.) 
 
 
Neven 
  
  A1 to EN55022:1998 requires the use of ferrite clamps on all cables 
leaving 
  the table-top EUT for a connection outside the test site. Are there any 
  other manufacturers of these clamps other than Fischer Custom 
  Communications? 
  
  Richard Woods 
  Sensormatic Electronics 
  Tyco International 
 
 
_ 
This e-mail has been scanned for viruses by the WorldCom Internet Managed 
Scanning Service - powered by MessageLabs. For further information visit 
http://www.worldcom.com 
 
--- 
This message is from the IEEE EMC Society Product Safety 
Technical Committee emc-pstc discussion list. 
 
Visit our web site at: http://www.ewh.ieee.org/soc/emcs/pstc/ 
 
To cancel your subscription, send mail to: 
 majord...@ieee.org 
with the single line: 
 unsubscribe emc-pstc 
 
For help, send mail to the list administrators: 
 Ron Pickard: emc-p...@hypercom.com 
 Dave Heald: davehe...@attbi.com 
 
For policy questions, send mail to: 
 Richard Nute: ri...@ieee.org 
 Jim Bacher: j.bac...@ieee.org 
 
Archive is being moved, we will announce when it is back on-line. 
All emc-pstc postings are archived and searchable on the web at: 
 http://www.ieeecommunities.org/emc-pstc 
 
 
 
 
--- 
This message is from the IEEE EMC Society Product Safety 
Technical Committee emc-pstc discussion list. 
 
Visit our web site at: http://www.ewh.ieee.org/soc/emcs/pstc/ 
 
To cancel your subscription, send mail to: 
 majord...@ieee.org 
with the single line: 
 unsubscribe emc-pstc 
 
For help, send mail to the list administrators: 
 Ron Pickard: emc-p...@hypercom.com 
 Dave Heald: davehe...@attbi.com 
 
For policy questions, send mail to: 
 Richard Nute: 

RE: EN55022:1998 + A1:2000

2003-01-29 Thread Gert Gremmen

Hi Group,


Proposals are on their way to specify
both transfer attenuation (first) and
input CM impedance of those clamps  (later)
The radiation properties of the exposed wire will
vary widely depending on the CM load impedance.
The attenuation characteristic is to isolate
auxilary wire (and signal) from the test setup.

Both will be published as an Amendment on CISPR 16
document.
A controllable impedance clamp system can be
constructed using a current clamp system
with variable load . (like current clamp/transformer)
The first 1-5 rings can be loaded with a
screened wire that terminates into a variable ( or fixed)
impedance. Target CM impedance will probably be 150 Ohm
to be transferred to the load.

This has best impact in the lower frequency range.
High loss ferrite will do better as low loss ferrite.
Attenuation is just a matter of quantity of rings.
Regards,

Gert Gremmen
Manager


Ce-test, Qualified Testing
ce marking and more ..
EMCD  LVD  RTTED  MDD  MD
www.cetest.nl
Electrical / Electronic Equipment




From: owner-emc-p...@majordomo.ieee.org
[mailto:owner-emc-p...@majordomo.ieee.org]On Behalf Of Gordon,Ian
Sent: Wednesday, January 29, 2003 11:51 AM
To: emc-p...@majordomo.ieee.org
Subject: RE: EN55022:1998 + A1:2000



All
I can see that my manager would prefer to use Neven's approach - it is
probably much cheaper than buying clamps. However, does anybody have any
practical experience of this?
A reply from an accredited test house would be welcomed!

Thanks
Ian Gordon

From: neve...@attbi.com [mailto:neve...@attbi.com]
Sent: 29 January 2003 05:22
To: emc-p...@majordomo.ieee.org
Subject: Re: EN55022:1998 + A1:2000



Instead of paying big bucks for the clamps (I am not sure what the price is,

but I'm sure it is too much anyway :), why not buying a bucket of ferrite
doughnuts that can be used over cables. Or, when possible, building in-line
adapters out of sections of cables (maybe 1m long) and lining them up with
ferrites. I'd select a combination of ferrites to cover 30 MHz to about 300
MHz. The high frequencies will be radiated anyway by the segment of the
cables
close to the DUT. Taking a little more thorough approach, I'd check the
impedance with the lineup fixed over a defined height above a GND plane.
(Not
sure if that would make a big practical difference.)


Neven

 A1 to EN55022:1998 requires the use of ferrite clamps on all cables
leaving
 the table-top EUT for a connection outside the test site. Are there any
 other manufacturers of these clamps other than Fischer Custom
 Communications?

 Richard Woods
 Sensormatic Electronics
 Tyco International


_
This e-mail has been scanned for viruses by the WorldCom Internet Managed
Scanning Service - powered by MessageLabs. For further information visit
http://www.worldcom.com


This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Ron Pickard:  emc-p...@hypercom.com
 Dave Heald:   davehe...@attbi.com

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

Archive is being moved, we will announce when it is back on-line.
All emc-pstc postings are archived and searchable on the web at:
http://www.ieeecommunities.org/emc-pstc





This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Ron Pickard:  emc-p...@hypercom.com
 Dave Heald:   davehe...@attbi.com

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

Archive is being moved, we will announce when it is back on-line.
All emc-pstc postings are archived and searchable on the web at:
http://www.ieeecommunities.org/emc-pstc



RE: EN55022:1998 + A1:2000

2003-01-29 Thread Pettit, Ghery

Amendment 1 to CISPR 22:1997 (Amendment A1:2000 to EN 55022:1998) requires
that the clamps provide at least 15 dB of loss in a 50 ohm system over the
frequency range of 30 MHz to 1000 MHz.  The use of extension cords is
prohibited.  Can you guarantee that your bucket of doughnuts will meet this
requirement?  How will you demonstrate that to your lab's accrediting body?


Fischer's clamps are around $300 each.  Compared with what we had to choose
from prior to their product, these are not big bucks.

Ghery Pettit
Intel


From: neve...@attbi.com [mailto:neve...@attbi.com]
Sent: Tuesday, January 28, 2003 9:22 PM
To: emc-p...@majordomo.ieee.org
Subject: Re: EN55022:1998 + A1:2000



Instead of paying big bucks for the clamps (I am not sure what the price is,

but I'm sure it is too much anyway :), why not buying a bucket of ferrite 
doughnuts that can be used over cables. Or, when possible, building in-line 
adapters out of sections of cables (maybe 1m long) and lining them up with 
ferrites. I'd select a combination of ferrites to cover 30 MHz to about 300 
MHz. The high frequencies will be radiated anyway by the segment of the
cables 
close to the DUT. Taking a little more thorough approach, I'd check the 
impedance with the lineup fixed over a defined height above a GND plane.
(Not 
sure if that would make a big practical difference.)


Neven
 
 A1 to EN55022:1998 requires the use of ferrite clamps on all cables
leaving
 the table-top EUT for a connection outside the test site. Are there any
 other manufacturers of these clamps other than Fischer Custom
 Communications?
 
 Richard Woods
 Sensormatic Electronics
 Tyco International
 
 
 ---
 This message is from the IEEE EMC Society Product Safety
 Technical Committee emc-pstc discussion list.
 
 Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/
 
 To cancel your subscription, send mail to:
  majord...@ieee.org
 with the single line:
  unsubscribe emc-pstc
 
 For help, send mail to the list administrators:
  Ron Pickard:  emc-p...@hypercom.com
  Dave Heald:   davehe...@attbi.com
 
 For policy questions, send mail to:
  Richard Nute:   ri...@ieee.org
  Jim Bacher: j.bac...@ieee.org
 
 All emc-pstc postings are archived and searchable on the web at:
 http://ieeepstc.mindcruiser.com/
 Click on browse and then emc-pstc mailing list


This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Ron Pickard:  emc-p...@hypercom.com
 Dave Heald:   davehe...@attbi.com

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

Archive is being moved, we will announce when it is back on-line.
All emc-pstc postings are archived and searchable on the web at:
http://www.ieeecommunities.org/emc-pstc


This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Ron Pickard:  emc-p...@hypercom.com
 Dave Heald:   davehe...@attbi.com

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

Archive is being moved, we will announce when it is back on-line.
All emc-pstc postings are archived and searchable on the web at:
http://www.ieeecommunities.org/emc-pstc



RE: Circuit Breaker Tripping Dring Fault Tests

2003-01-29 Thread Peter L. Tarver

From: Gregg Kervill
Sent: Tuesday, January 28, 2003 3:21 PM

 Like most regulatory issues the answer is YES and NO.

 Therefore it is dangerous and extremely misleading (to
many
 lurkers) to apply a general answer to all conditions:

 Generally the equipment is expected to protect itself with
 internal over current and short-circuit protection.

I disagree.  It may be possible for equipment to possess
inherent features that do not require supplementary
protection or that a piece of equipment is adequately
protected by the branch circuit protection.  Much depends on
the application and design.

 The equipment will be tested with the worst case fault
 condition – 60 kAmp or more is not uncommon

This value may be true for equipment installed in Category
IV and possibly Category III environments (per IEC60664-1),
but is neither the general case nor very common for
equipment installed in Category II environments.  Consider
that every finite (though minute) impedance at every
electrical connection will serve to limit the fault current
available at equipment.  Impedances will also exist at each
switchable contact (molded case switches and circuit
breakers) and each wiping contact (fuse holders for
replaceable cartridge fuses, outlets/plugs, knife switches).

For North America:

In a typical household operating at 120V, it's unlikely
that a fault current available to Pluggable Equipment Type A
will be much above 5kA, even if the outlet supplying the
equipment is within 5 ft. of the service entrance.  In a
typical household operating at 240V, the available fault
current will be somewhat higher (approximately doubled +).
This is also, in large measure, due to the relatively small
last distribution transformer before the household and other
loads on the transformer from other households supplied by
the same transformer.

In a typical business the fault current available will be
larger, due largely to a larger transformer connected to the
service entrance and that the service entrance voltages are
greater (480V three phase is not uncommon for larger
facilities; 120/208V is most common).  I'm not certain of
the typical fault currents available at an outlet in this
case, but I'd venture a guess that its not more than 25kA at
a ANSI/NEMA 5-15 outlet.

I'm interested in hearing typical values for other regions
of the world, so if anyone has any data or reasonable
guesses, please let us all know.

 Where we rely upon the ‘breaker’ for - non-domestic
 equipment - it is ALWAYS mandatory (and common sense)
 to specify the characteristics of that breaker in
 terms of  ‘tripping (operating) current’ – time
 characteristics (Type I, II or III) and Breaking
 Current 2,500 Amps is low for most domestic situations.

This must be for Europe.  In the US (and I believe Canada is
the same), 5kA is a gimme interrupting rating for molded
case switches and circuit breakers.  The minimum
interrupting rating for branch circuit fuses is 10kA.

 A failure to provide the necessary information
 WILL eventually result in a fire or nuisance tripping.

Or not, depending on the installation environment.

 Best regards

 Gregg


Regards,

Peter L. Tarver, PE
Product Safety Manager
Sanmina-SCI Homologation Services
San Jose, CA
peter.tar...@sanmina-sci.com



This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Ron Pickard:  emc-p...@hypercom.com
 Dave Heald:   davehe...@attbi.com

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

Archive is being moved, we will announce when it is back on-line.
All emc-pstc postings are archived and searchable on the web at:
http://www.ieeecommunities.org/emc-pstc



Re: Unity Power Factor

2003-01-29 Thread Rich Nute




Hi John:


   In the USA, this has largely been fixed by a change in
   the USA National Electrical Code.  
   
   There must be quite a number of installations that are not yet upgraded.

Where a problem existed, it was fixed by pulling
another neutral.

   Are there any other problems appearing in the field which can be
   reliably determined as due to concentrations of non-linear loads of less
   than 3 kVA or so?

Probably not.

The only other problem that I know of is distribution
transformer overheating.  But, I believe such 
transformers are very much larger than 3 kVA, so 3 kVA
of non-linear loads would have very little effect. 


Best regards,
Rich





This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Ron Pickard:  emc-p...@hypercom.com
 Dave Heald:   davehe...@attbi.com

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

Archive is being moved, we will announce when it is back on-line.
All emc-pstc postings are archived and searchable on the web at:
http://www.ieeecommunities.org/emc-pstc



RTTE directive.

2003-01-29 Thread Gary McInturff

Anybody have a link to peruse and purchase this, and a brief synopsis.
I assume it calls out the standard EMC tests -  EN55022, EN55024, and 
Safety
standards, along with a standard or section which deals with the intentional
radiator portion of box, and harmonized frequencies etc. The device itself is
a Wi-fi type box. Ethernet in, and RF out. Is that correct?
Gary


This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Ron Pickard:  emc-p...@hypercom.com
 Dave Heald:   davehe...@attbi.com

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

Archive is being moved, we will announce when it is back on-line.
All emc-pstc postings are archived and searchable on the web at:
http://www.ieeecommunities.org/emc-pstc



RE: MRA US-EU: Sectoral Annex Safety suspended

2003-01-29 Thread gr...@test4safety.com

Subject: RE: MRA US-EU: Sectoral Annex Safety suspended


Dear Group,

Having read the document given, can anybody explain what it means?


You simple take the original terms and conditions and press the Delete key

For the benefit of those that did not archive the original documents I will
post a few Abstracts.


Fortunately the CE Marking Directives were written BEFORE the MRA and
therefore one simply reverts to what we were required to do before that
date.

The only comment that I would make is that some (if not all) Eu countries
may increase their surveillance activities.


This sounds like a queue for a presentation I shall be giving at the Austin
(Tx) Product Safety Group entitled

Preparing for the Economic Recovery  -  the SMART Use of Safety Files

It will cover
CONTENT
How to write UL/CSA/CE Marking files, What MUST be in the LVD Technical
File, Using report templates, working with subcontractors - working with
prime contractors and OEM's
Many CE Marking Technical Files are incomplete - so I will bring a sample of
a completed CE Marking (LVD) Technical File and show how the UL Product
Description can be used to avoid unnecessary duplication of effort.
Prime contractors can spend an excessive amount of time monitoring
sub-contractors - just as some sub-contractors could gain a competitive
advantage by giving what their customer Needs.
Many small companies will not embrace safety compliance processes as being
too difficult -  and loose opportunities.


The presentation will be aimed at two interest groups:
Large and Medium Sized companies with regulatory processes in place - this
will help them harmonize documentation and to assess their sub-contract
design and manufacture.
Small companies that do not have formal compliance processes - this will
help them demonstrate compliance to their (OEM) customers.


I anyone wishes for further information of the presentation or the MRA we
have set up a m...@test4safety.com account and forward information as it
comes available.



Best regards

Gregg

Gregg Kervill DipIM, MIMgt, MIEEE
VP Engineering
Test4Safety.com Inc
PO Box 310,
Reedville, VA
22539. USA
Phone  ( 804) 453-3141
Fax(804) 453-9039
http://www.test4safety.com/

Extracting from the MRA we have
Article 2

PURPOSE OF THE AGREEMENT

This Agreement specifies the conditions by which each Party will accept or
recognize results of conformity assessment procedures, produced by the other
Party's conformity assessment bodies or authorities, in assessing conformity
to the importing Party's requirements, as specified on a sector-specific
basis in the Sectoral Annexes, and to provide for other related cooperative
activities.   The objective of such mutual recognition is to provide
effective market access throughout the territories of the Parties with
regard to conformity assessment for all products covered under this
Agreement.  If any obstacles to such access arise, consultations will
promptly be held.  In the absence of a satisfactory outcome of such
consultations, the Party alleging its market access has been denied, may,
within 90 days of such consultation, invoke its right to terminate the
Agreement in accordance with Article 21.


Article 3

GENERAL OBLIGATIONS

1.  The United States shall, as specified in the Sectoral Annexes, accept or
recognize results of specified procedures, used in assessing conformity to
specified legislative, regulatory, and administrative provisions of the
United States, produced by the other Party's conformity assessment bodies
and/or authorities.

2.  The European Community and its Member States shall, as specified in the
Sectoral Annexes, accept or recognize results of specified procedures, used
in assessing conformity to specified legislative, regulatory and
administrative provisions of the European Community and its Member States,
produced by the other Party's conformity assessment bodies and/or
authorities.
3.  Where sectoral transition arrangements have been specified in Sectoral
Annexes, the above obligations will apply following the successful
completion of those sectoral transition arrangements, with the understanding
that the conformity assessment procedures utilized assure conformity to the
satisfaction of the receiving Party, with applicable legislative, regulatory
and administrative provisions of that Party, equivalent to the assurance
offered by the receiving  Party's own procedures.



There are then a series of EMC and Safety Annexes that specify the National
Instruments (e.g. the LVD for EU )


The more useful article is (perhaps) this:

Press Guidance -- Mutual Recognition Agreements
Draft 6/13


* We are pleased today to announce the completion of a balanced package of
Mutual Recognition Agreements (MRAs) between the United States and the
European Union  recognizing product test, inspection or certification
results required by both governments in six economic sectors and eliminating
the need for duplicative testing or approval on both 

RE: question on test labs for multiple burst multiple stroke lightning

2003-01-29 Thread Garry Hojan


Hi Susan,

I would check with Met Labs who bought the old TUV Santa Clara facility.
Sorry, I don't have contact information for them.

Best regards,
Garry Hojan
Strategic Compliance Services (SCS)
www.regulatory-compliance.com

Now that DO-160D, change 3 is published, does anyone have suggestions for
test labs that can perform mulitple burst  multiple stroke lightning?



This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Ron Pickard:  emc-p...@hypercom.com
 Dave Heald:   davehe...@attbi.com

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
http://ieeepstc.mindcruiser.com/
Click on browse and then emc-pstc mailing list


This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Ron Pickard:  emc-p...@hypercom.com
 Dave Heald:   davehe...@attbi.com

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

Archive is being moved, we will announce when it is back on-line.
All emc-pstc postings are archived and searchable on the web at:
http://www.ieeecommunities.org/emc-pstc



RE: Circuit Breaker Tripping Dring Fault Tests

2003-01-29 Thread gkt4s
Thank you Richard – this situation vividly illustrates the danger of
nuisances tripping – what message does that give to the Home Owner –
“FIT A BIGGER FUSE!”
 
That is why (some) CSA standards require a Turn-On Test – ON-OFF 10 times
within a minute – protection devices MUST NOT OPERATE.
 
I have been recommending this test to clients as GOOD ENGINEERING PRACTICE for
the last 10 years.
 
Best regards
 
Gregg
 
 

From: owner-emc-p...@majordomo.ieee.org
[mailto:owner-emc-p...@majordomo.ieee.org]On Behalf Of
richard.pitten...@hobartcorp.com
Sent: Wednesday, January 29, 2003 7:58 AM
To: Rich Nute
Cc: emc-p...@majordomo.ieee.org
Subject: Re: Circuit Breaker Tripping Dring Fault Tests
 

Rich and group, 

Just one interesting point continuing the thought of fuse sizes for
branch circuit protection. Awhile back, I was conducting a series of UL tests
on a household food mixer. For one of the abnormal tests, UL required me to
use a 30 A time-delay branch circuit fuse (lamp base) in the power supply to
the unit under test. I thought this was extreme, believing that a 20  A fuse
would be the maximum anyone would ever use. When questioned, I was told that
such fuses are available and still in use, primarily in old residential areas. 
I visited my local hardware store and, sure enough, they were readily
available, right along with the other more common sizes. You may want to
consider this when considering such tests in the future. 

Good day, 

Richard Pittenger
Agency Approval Engineer
Hobart Corporation




 
Rich Nute ri...@sdd.hp.com 
Sent by: owner-emc-p...@majordomo.ieee.org 
01/28/2003 07:23 PM 
Please respond to Rich Nute 

To:pmerguerian2...@yahoo.com 
cc:emc-p...@majordomo.ieee.org 
Subject:Re: Circuit Breaker Tripping Dring Fault Tests







Hi Peter:


   For safety, it is not clear from the standards whether 
   the main branch circuit breaker tripping during fault 
   conditions is an acceptable result.
   
   I see no reason why this should not be acceptable. What 
   is your view? Some third party labs find it acceptable 
   and others do not.

Some products are provided with internal overcurrent
protection and some are not.  

Clearly, those that do not have internal overcurrent
protection rely on the branch circuit protection.

If a product has an internal overcurrent protective
device, and the fault is on the load side of that 
device, then the internal device should provide the
protection and not the branch circuit device.  
(Otherwise, the internal device provides no 
protection, and might as well be removed.)

If the fault is on the supply side of the internal
device, then clearly the internal device cannot 
provide protection, and the branch circuit must 
provide the protection.  

The real question is whether or not the product is
safe when the fault current is just below the
operating point of the branch circuit device.  
Examining this question requires an understanding
of the fault and whether its resistance can be high
enough to not trip the branch circuit yet not create
a hazardous condition (such as a fire).  If the 
fault resistance always is no more than 120/20 = 6 
ohms, then I would say that the branch circuit 
could be relied upon to provide protection against
the fault.

Note that in the USA, a 120-volt branch circuit can
be provided with either a 15-amp or a 20-amp
overcurrent device.  Therefore, the product must be
safe when the fault current is 20 amps, just below
the overcurrent device operating point.  That means
that the product must be capable of dissipating 
2400 watts without catching fire or destroying 
internal insulation that serves a safety purpose.


Best regards,
Rich






This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
majord...@ieee.org
with the single line:
unsubscribe emc-pstc

For help, send mail to the list administrators:
Ron Pickard:  emc-p...@hypercom.com
Dave Heald:   davehe...@attbi.com

For policy questions, send mail to:
Richard Nute:   ri...@ieee.org
Jim Bacher: j.bac...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
   http://ieeepstc.mindcruiser.com/
   Click on browse and then emc-pstc mailing list





RE: Circuit Breaker Tripping Dring Fault Tests

2003-01-29 Thread Peter L. Tarver

Peter -

I agree that this is an acceptable result in the US and
Canada.  There are, however, additional considerations:

For Pluggable Equipment Type A (to borrow a term from the
60950 standards), the largest branch circuit protection is
assumed during testing (20A) and there is no further
requirement.

For Pluggable Equipment Type B and permanently connected
equipment, it would then be necessary to specify the largest
branch circuit protection device the equipment may be safely
supplied from in the installation instructions.  This would
necessarily be the size of the protection involved during
your testing.

I am very interested in the nonNorth American view on this
issue.


Regards,

Peter L. Tarver, PE
Product Safety Manager
Sanmina-SCI Homologation Services
San Jose, CA
peter.tar...@sanmina-sci.com



From: peter merguerian
Sent: Tuesday, January 28, 2003 11:54 AM

Dear All,
For safety, it is not clear from the standards whether the
main branch circuit breaker tripping during fault conditions
is an acceptable result.

I see no reason why this should not be acceptable. What is
your view? Some third party labs find it acceptable and
others do not.

Anyone can lead me to some inernational decisions regarding
this issue?

Thanks,
Peter




This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Ron Pickard:  emc-p...@hypercom.com
 Dave Heald:   davehe...@attbi.com

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

Archive is being moved, we will announce when it is back on-line.
All emc-pstc postings are archived and searchable on the web at:
http://www.ieeecommunities.org/emc-pstc



RE: Circuit Breaker Tripping Dring Fault Tests

2003-01-29 Thread Garnier, David S (MED)
I am going to jump into this frey, here is my 2 cents...
 
In the case of Medical Electronics, if the fault condition would cause 
more exposure of radiation to the patient than what was dialed in
(X-Ray, MRI, Ultrasound) that would be a BAD thing. End of subject.
 
dave garnier


From: Lou Aiken [mailto:ai...@gulftel.com]
Sent: Tuesday, January 28, 2003 11:00 PM
To: peter merguerian; emc-p...@majordomo.ieee.org
Subject: Re: Circuit Breaker Tripping Dring Fault Tests


Here is what I think the requirements are:
 
If the product remains safe, within the meaning of the standard, and the
branch circuit overcurrent protection device does, or does not, operate as a
result of fault testing, internal overcurrent is unnecessary.
 
If the product does NOT remain safe, within the meaning of the standard, as a
result of fault testing, internal overcurrent protection IS necessary, branch
circuit overcurrent protection is   inadequate, and internal overcurrent
protection is necessary.
 
Safe within the meaning of the standard:  Does not exceed allowable fault
temperature limits, does not catch fire, enclosure does not deform to the
extent that parts involving the risk of electric shock or personal injury
become exposed to the test finger or probe, will pass the required electric
strength test after the fault, etc.
 
IN order to be confident that the design is safe one must continue the fault
testing until steady state conditions exist, OR for the maximum clearing time
(for the resulting fault current) as stated in the standard for the particular
overcurrent device.  It is incorrect consider the result acceptable when the
overcurrent device opens the circuit.  The overcurrent device should be
removed from the circuit and the current monitored during the fault test. 
Only approved fuses and circuit breakers should be specified if they are
necessary make the product remain safe - within the meaning of the standard.
 
There is a significant difference in the endurance and clearing limits between
the UL and IEC standards for fuses and circuit breakers with the same current
rating. 
 
 
 
Lou Aiken, LaMer LLC 
27109 Palmetto Drive
Orange Beach, AL
36561 USA
 
tel ++ 1 251 981 6786
fax ++ 1 251 981 3054
Cell ++ 1 251 979 4648

- Original Message - 
From: peter merguerian mailto:pmerguerian2...@yahoo.com  
To: emc-p...@majordomo.ieee.org 
Sent: Tuesday, January 28, 2003 1:54 PM
Subject: Circuit Breaker Tripping Dring Fault Tests


Dear All,

For safety, it is not clear from the standards whether the main branch circuit
breaker tripping during fault conditions is an acceptable result.

I see no reason why this should not be acceptable. What is your view? Some
third party labs find it acceptable and others do not.

Anyone can lead me to some inernational decisions regarding this issue?

Thanks,

Peter

 

 




  _  

Do you Yahoo!?
Yahoo!  http://rd.yahoo.com/mail/mailsig/*http://mailplus.yahoo.com Mail
Plus - Powerful. Affordable. Sign up  
ttp://rd.yahoo.com/mail/mailsig/*http://mailplus.yahoo.com now




Is pulse dialing still needed in Australia?

2003-01-29 Thread j...@aol.com

Hello All:

I am trying to cost reduce an older, worldwide PSTN line interface design.  
This circuit contains a pulse dialing transient limiter that was needed to 
meet the pulse dialing requirements in the Netherlands and Australia.  I 
would like to take this circuit out and restrict dialing to DTMF only in the 
Netherlands and Australia.

I know that in the Netherlands, 100% of the PSTN lines now accept DTMF 
dialing, but I don't know if the same is true for Australia.  A few years ago 
I was told that Australia would be 100% DTMF compatible soon, but I do not 
have reliable confirmation that this transition has been completed. 

Can any of you confirm that Australia's PSTN is now 100% DTMF compatible?  Is 
there an official source that I can reference for this information?

Also, can you confirm that there is no additional charge to use DTMF in 
Australia?  I know this may sound ridiculous to those of you outside the USA, 
but when DTMF dialing was first introduced in the USA, the operating 
companies typically charged extra for the service.  In some states, those 
charges are still being applied.


Thanks,

Joe Randolph
Telecom Design Consultant
Randolph Telecom, Inc.
781-721-2848
j...@randolph-telecom.com
http://www.randolph-telecom.com



This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Ron Pickard:  emc-p...@hypercom.com
 Dave Heald:   davehe...@attbi.com

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

Archive is being moved, we will announce when it is back on-line.
All emc-pstc postings are archived and searchable on the web at:
http://www.ieeecommunities.org/emc-pstc



RE: Circuit Breaker Tripping Dring Fault Tests

2003-01-29 Thread Robert Johnson

 
Two points:

To assure the safety of your product consider not whether it is safe if the
breaker trips, but what is the failure mode of your product if the breaker
(which you do not provide) does not trip. If you rely on the breaker, you
need to properly specify it.

In the US, there have been code changes to introduce a new device called an
arc fault interrupting breaker which uses RF noise from an arc to trip a
breaker at currents below normal overcurrent trip levels. This was
introduced because there were many instances where an arc in power cords or
similar places would generate enough energy to melt copper and blast it
away. The molten copper is capable of starting fires. Often the breaker
failed to trip during this momentary fault, and permitted arc tracking to
cause repeated cycles of arcs. The message is, some types of failures are
not well protected by ordinary overcurrent devices. This may or may not be
relevant in your case.


Bob Johnson
ITE Safety



This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Ron Pickard:  emc-p...@hypercom.com
 Dave Heald:   davehe...@attbi.com

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

Archive is being moved, we will announce when it is back on-line.
All emc-pstc postings are archived and searchable on the web at:
http://www.ieeecommunities.org/emc-pstc



RE: 'DOW' of standards

2003-01-29 Thread charles.mar...@ps.ge.com

Hi Group,

Does anyone have a clear idea or knows a link that shows the differences
between the old and new 61010 standard.

Thank You

Charlie Martin
GE Panametrics


From: iun...@servomex.com [mailto:iun...@servomex.com]
Sent: Tuesday, January 28, 2003 9:33 AM
To: emc-p...@majordomo.ieee.org
Subject: 'DOW' of standards



Dear Group,

 The  OJ for the LVD (page C317/73) gives 1.1.2004 as being the date beyond
 which   IEC   61010-1:1990/A2:1995  can  no  longer  be  used  to  presume
 conformance  with the requirements of this Directive. After this date, can
 equipment  previously  assessed to this standard still be marketed without
 reassessment to the new standard (IEC 61010-1:2001)? If so, until when?

 Between  1.4.2001  (the  'dow' of IEC 61010-1:1990+A1:1992 (Modified)) and
 1.1.2004   (the   dow   of   IEC  61010-1:1990/A2:1995),  can  either  IEC
 61010-1:1990/A2:1995  or  IEC  61010-1:2001 be used to presume conformance
 with the requirements of LVD?

 Apologies if the answers to the above have been covered before and are
   thus locked up in the group's archives.

 Ian Unwin

 Servomex Group Limited




This email has been scanned for all viruses by the MessageLabs SkyScan
service. 
This electronic message contains information from Servomex which may be
privileged or confidential. 
The information is intended to be for the use of the individual(s) or entity
named above. 
If you are not the intended recipient be aware that any disclosure, copying,
distribution or use of the contents of this information is prohibited. 
If you have received this electronic message in error, please notify us
immediately.
Activity and use of the Servomex E-mail system is monitored to secure its
effective operation and for other lawful business purposes. Communications
using this system may also be monitored and may be
recorded to secure effective operation and for other lawful business
purposes.


This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Ron Pickard:  emc-p...@hypercom.com
 Dave Heald:   davehe...@attbi.com

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
http://ieeepstc.mindcruiser.com/
Click on browse and then emc-pstc mailing list


This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Ron Pickard:  emc-p...@hypercom.com
 Dave Heald:   davehe...@attbi.com

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

Archive is being moved, we will announce when it is back on-line.
All emc-pstc postings are archived and searchable on the web at:
http://www.ieeecommunities.org/emc-pstc



RE: Circuit Breaker Tripping Dring Fault Tests

2003-01-29 Thread Kurt Mikolajewski
Jim
 
I your case the required BASIC INSULATION is not present or adequate. BASIC
INSULATION provides a level of protection. The branch circuit provides an
additional level of protection if there is a failure of the BASIC INSULATION.
The standard in this instance allows the designer to provide an alternate
protection method to replace the BASIC INSULATION, with the requirement that
it fails safe and it does not impact any other insulation system. 
 
Regards,
Kurt Mikolajewski


From: Jim Eichner [mailto:jim.eich...@xantrex.com]
Sent: Tuesday, January 28, 2003 5:13 PM
To: emc-p...@majordomo.ieee.org
Subject: RE: Circuit Breaker Tripping Dring Fault Tests


I've been trying to solve this one myself.  I work with one pair of standards
(UL458 / CSA107.1) where they specifically say that opening the branch circuit
protection is acceptable during component fault testing, but NOT during short
circuit tests done for the purposes of validating inadequate trace spacings
(an easement offered in the standards in some situations).  I've always been
puzzled why we can't rely on branch circuit protection for both situations,
but neither agency has been able to explain the difference to me.
 
Jim Eichner, P.Eng.
Regulatory Compliance Manager
Xantrex Technology Inc.
phone: (604) 422-2546
fax: (604) 420-1591
e-mail: jim.eich...@xantrex.com
web: www.xantrex.com 
Confidentiality Notice: This email message, including any attachments, is for
the sole use of the intended recipient(s) and may contain confidential and
privileged information. Any unauthorized review, use, disclosure or
distribution is prohibited. If you are not the intended recipient, please
contact the sender by reply e-mail and destroy all copies of the original
message.

 




  _  

Do you Yahoo!?
Yahoo!  http://rd.yahoo.com/mail/mailsig/*http://mailplus.yahoo.com Mail
Plus - Powerful. Affordable. Sign up  
ttp://rd.yahoo.com/mail/mailsig/*http://mailplus.yahoo.com now




RE: Circuit Breaker Tripping Dring Fault Tests

2003-01-29 Thread bryan.c...@control-concepts.com
Peter,
 
I do not have specifics, so I can only offer general information.
 
The use of external breakers is acceptable for testing and certifying products
that are hardwired to the electrical distribution of a facility for when fault
current or withstand testing is required.  In the US, the UL standards
typically denote the overall requirements of the test and pass/fail criteria. 
The NEC may also detail specific information about over-current protection for
specific devices.
 
When an external breaker is utilized, it is required to be denoted in the
installation instructions (UL requirement).  However, this does present some
issues when installed as the product may be preceded with a breaker that is
different than what was tested.  Remember, not all breakers are created equal.
 Therefore, testing of fault currents with one breaker may yield one result
and testing of another manufacturer's breaker may have a second result.
 
When products are cord connected, one is usually required to have internal
over-current protection.  However, I believe that this is a general guideline
not a stead fast rule.
 
Thanks,

Bryan Cole 
Director of Engineering 
Product Safety Officer 
Emerson Network Power - Control Concepts 
Binghamton, New York 13902 
Phone: 607.724.1352 extension 238 
Fax: 607.724.0153 
E-mail: bryan.c...@control-concepts.com 
www.Liebert.com 
www.Control-Concepts.com 
www.Edcosurge.com 


From: peter merguerian [mailto:pmerguerian2...@yahoo.com]
Sent: Tuesday, January 28, 2003 2:54 PM
To: emc-p...@majordomo.ieee.org
Subject: Circuit Breaker Tripping Dring Fault Tests



Dear All,

For safety, it is not clear from the standards whether the main branch circuit
breaker tripping during fault conditions is an acceptable result.

I see no reason why this should not be acceptable. What is your view? Some
third party labs find it acceptable and others do not.

Anyone can lead me to some inernational decisions regarding this issue?

Thanks,

Peter

 

 




  _  

Do you Yahoo!?
Yahoo! Mail  http://rd.yahoo.com/mail/mailsig/*http://mailplus.yahoo.com
Plus - Powerful. Affordable. Sign up  
ttp://rd.yahoo.com/mail/mailsig/*http://mailplus.yahoo.com now

The information in this electronic message may be privileged and confidential
and is intended for the use of the individual(s) named above. If you are not
the intended recipient, you are on notice that any unauthorized disclosure,
copying, distribution, or taking of any action in reliance on the contents of
these electronically transmitted materials is prohibited. 




RE: MRA US-EU: Sectoral Annex Safety suspended

2003-01-29 Thread Carpentier Kristiaan

Ian,

In short.
There is an MRA between US and Europe that covers the Sectoral Annex EMC and
Telecom.
E.g for EMC, Conformity Assessment Bodies (CAB's) were assigned in the
Europe for FCC regulation as wel as CAB's were assigned in US for EMC
directive in Europe. An easy way for European Companies to get products
approved locally in Europe for US and vice versa. And it works.
The Sectoral Annex Safety could have given the same benefits to mftr's, but
will be suspended now from EU side for the reasons as explained in the OJEC.

So no need to panic, life could have been easier, but you can sleep
peacefully.

Regards,
Kris


From: iun...@servomex.com [mailto:iun...@servomex.com]
Sent: woensdag 29 januari 2003 9:37
To: emc-p...@majordomo.ieee.org
Subject: RE: MRA US-EU: Sectoral Annex Safety suspended



Dear Group,

Having read the document given, can anybody explain what it means?

As an instrument  manufacturer selling products into both the US and EU do
I need to panic over this, or can I ignore it and sleep peacefully in my
bed at nights?

Regards

Ian D Unwin
Servomex Group Limited





This email has been scanned for all viruses by the MessageLabs SkyScan
service. 
This electronic message contains information from Servomex which may be
privileged or confidential. 
The information is intended to be for the use of the individual(s) or entity
named above. 
If you are not the intended recipient be aware that any disclosure, copying,
distribution or use of the contents of this information is prohibited. 
If you have received this electronic message in error, please notify us
immediately.
Activity and use of the Servomex E-mail system is monitored to secure its
effective operation and for other lawful business purposes. Communications
using this system may also be monitored and may be
recorded to secure effective operation and for other lawful business
purposes.


This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Ron Pickard:  emc-p...@hypercom.com
 Dave Heald:   davehe...@attbi.com

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

Archive is being moved, we will announce when it is back on-line.
All emc-pstc postings are archived and searchable on the web at:
http://www.ieeecommunities.org/emc-pstc


This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Ron Pickard:  emc-p...@hypercom.com
 Dave Heald:   davehe...@attbi.com

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

Archive is being moved, we will announce when it is back on-line.
All emc-pstc postings are archived and searchable on the web at:
http://www.ieeecommunities.org/emc-pstc



Re: Circuit Breaker Tripping Dring Fault Tests

2003-01-29 Thread richard.pitten...@hobartcorp.com

Rich and group, 

Just one interesting point continuing the thought of fuse sizes for
branch circuit protection. Awhile back, I was conducting a series of UL tests
on a household food mixer. For one of the abnormal tests, UL required me to
use a 30 A time-delay branch circuit fuse (lamp base) in the power supply to
the unit under test. I thought this was extreme, believing that a 20  A fuse
would be the maximum anyone would ever use. When questioned, I was told that
such fuses are available and still in use, primarily in old residential areas. 
I visited my local hardware store and, sure enough, they were readily
available, right along with the other more common sizes. You may want to
consider this when considering such tests in the future. 

Good day, 

Richard Pittenger
Agency Approval Engineer
Hobart Corporation




Rich Nute ri...@sdd.hp.com 
Sent by: owner-emc-p...@majordomo.ieee.org 


01/28/2003 07:23 PM 
Please respond to Rich Nute 

To:pmerguerian2...@yahoo.com 
cc:emc-p...@majordomo.ieee.org 
Subject:Re: Circuit Breaker Tripping Dring Fault Tests








Hi Peter:


   For safety, it is not clear from the standards whether 
   the main branch circuit breaker tripping during fault 
   conditions is an acceptable result.
   
   I see no reason why this should not be acceptable. What 
   is your view? Some third party labs find it acceptable 
   and others do not.

Some products are provided with internal overcurrent
protection and some are not.  

Clearly, those that do not have internal overcurrent
protection rely on the branch circuit protection.

If a product has an internal overcurrent protective
device, and the fault is on the load side of that 
device, then the internal device should provide the
protection and not the branch circuit device.  
(Otherwise, the internal device provides no 
protection, and might as well be removed.)

If the fault is on the supply side of the internal
device, then clearly the internal device cannot 
provide protection, and the branch circuit must 
provide the protection.  

The real question is whether or not the product is
safe when the fault current is just below the
operating point of the branch circuit device.  
Examining this question requires an understanding
of the fault and whether its resistance can be high
enough to not trip the branch circuit yet not create
a hazardous condition (such as a fire).  If the 
fault resistance always is no more than 120/20 = 6 
ohms, then I would say that the branch circuit 
could be relied upon to provide protection against
the fault.

Note that in the USA, a 120-volt branch circuit can
be provided with either a 15-amp or a 20-amp
overcurrent device.  Therefore, the product must be
safe when the fault current is 20 amps, just below
the overcurrent device operating point.  That means
that the product must be capable of dissipating 
2400 watts without catching fire or destroying 
internal insulation that serves a safety purpose.


Best regards,
Rich






This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
majord...@ieee.org
with the single line:
unsubscribe emc-pstc

For help, send mail to the list administrators:
Ron Pickard:  emc-p...@hypercom.com
Dave Heald:   davehe...@attbi.com

For policy questions, send mail to:
Richard Nute:   ri...@ieee.org
Jim Bacher: j.bac...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
   http://ieeepstc.mindcruiser.com/
   Click on browse and then emc-pstc mailing list






Re: Unity Power Factor

2003-01-29 Thread John Woodgate

I read in !emc-pstc that Rich Nute ri...@sdd.hp.com wrote (in
200301281747.jaa29...@epgc264.sdd.hp.com) about 'Unity Power Factor'
on Tue, 28 Jan 2003:




Hi John:


   No, this is not much of an issue for the U.S. (unless your facility
is 
   actually affecting the utility);
   
   ... or frying the neutral conductors with third-harmonic current.

In the USA, this has largely been fixed by a change in
the USA National Electrical Code.  

There must be quite a number of installations that are not yet upgraded.

When the load is largely electronic (off-line rectifiers)
the Code now requires a larger neutral conductor in three-
phase distributions.

Yes, we do that in UK as well, for new installations. In some cases, the
neutral, which is the same size as the phase conductors, is supplemented
by another conductor, because the neutral current can, in an extreme
case, exceed the phase current.

Many constructions, while supplied from a three-phase source,
are wired as single-phase.  So, in this case, the neutral
only carries the current of one phase, and we don't fry
the neutral.

That is a good solution. 

Are there any other problems appearing in the field which can be
reliably determined as due to concentrations of non-linear loads of less
than 3 kVA or so?
-- 
Regards, John Woodgate, OOO - Own Opinions Only. http://www.jmwa.demon.co.uk 
Interested in professional sound reinforcement and distribution? Then go to 
http://www.isce.org.uk
PLEASE do NOT copy news posts to me by E-MAIL!


This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Ron Pickard:  emc-p...@hypercom.com
 Dave Heald:   davehe...@attbi.com

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

Archive is being moved, we will announce when it is back on-line.
All emc-pstc postings are archived and searchable on the web at:
http://www.ieeecommunities.org/emc-pstc



RE: EN55022:1998 + A1:2000

2003-01-29 Thread Gordon,Ian

All
I can see that my manager would prefer to use Neven's approach - it is
probably much cheaper than buying clamps. However, does anybody have any
practical experience of this?
A reply from an accredited test house would be welcomed! 

Thanks
Ian Gordon

From: neve...@attbi.com [mailto:neve...@attbi.com]
Sent: 29 January 2003 05:22
To: emc-p...@majordomo.ieee.org
Subject: Re: EN55022:1998 + A1:2000



Instead of paying big bucks for the clamps (I am not sure what the price is,

but I'm sure it is too much anyway :), why not buying a bucket of ferrite 
doughnuts that can be used over cables. Or, when possible, building in-line 
adapters out of sections of cables (maybe 1m long) and lining them up with 
ferrites. I'd select a combination of ferrites to cover 30 MHz to about 300 
MHz. The high frequencies will be radiated anyway by the segment of the
cables 
close to the DUT. Taking a little more thorough approach, I'd check the 
impedance with the lineup fixed over a defined height above a GND plane.
(Not 
sure if that would make a big practical difference.)


Neven
 
 A1 to EN55022:1998 requires the use of ferrite clamps on all cables
leaving
 the table-top EUT for a connection outside the test site. Are there any
 other manufacturers of these clamps other than Fischer Custom
 Communications?
 
 Richard Woods
 Sensormatic Electronics
 Tyco International


_
This e-mail has been scanned for viruses by the WorldCom Internet Managed
Scanning Service - powered by MessageLabs. For further information visit
http://www.worldcom.com


This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Ron Pickard:  emc-p...@hypercom.com
 Dave Heald:   davehe...@attbi.com

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

Archive is being moved, we will announce when it is back on-line.
All emc-pstc postings are archived and searchable on the web at:
http://www.ieeecommunities.org/emc-pstc



RE: MRA US-EU: Sectoral Annex Safety suspended

2003-01-29 Thread iun...@servomex.com

Dear Group,

Having read the document given, can anybody explain what it means?

As an instrument  manufacturer selling products into both the US and EU do
I need to panic over this, or can I ignore it and sleep peacefully in my
bed at nights?

Regards

Ian D Unwin
Servomex Group Limited





This email has been scanned for all viruses by the MessageLabs SkyScan
service. 
This electronic message contains information from Servomex which may be
privileged or confidential. 
The information is intended to be for the use of the individual(s) or entity
named above. 
If you are not the intended recipient be aware that any disclosure, copying,
distribution or use of the contents of this information is prohibited. 
If you have received this electronic message in error, please notify us
immediately.
Activity and use of the Servomex E-mail system is monitored to secure its
effective operation and for other lawful business purposes. Communications
using this system may also be monitored and may be
recorded to secure effective operation and for other lawful business
purposes.


This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Ron Pickard:  emc-p...@hypercom.com
 Dave Heald:   davehe...@attbi.com

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

Archive is being moved, we will announce when it is back on-line.
All emc-pstc postings are archived and searchable on the web at:
http://www.ieeecommunities.org/emc-pstc



Re: EN55022:1998 + A1:2000

2003-01-29 Thread neve...@attbi.com

Instead of paying big bucks for the clamps (I am not sure what the price is, 
but I'm sure it is too much anyway :), why not buying a bucket of ferrite 
doughnuts that can be used over cables. Or, when possible, building in-line 
adapters out of sections of cables (maybe 1m long) and lining them up with 
ferrites. I'd select a combination of ferrites to cover 30 MHz to about 300 
MHz. The high frequencies will be radiated anyway by the segment of the cables 
close to the DUT. Taking a little more thorough approach, I'd check the 
impedance with the lineup fixed over a defined height above a GND plane. (Not 
sure if that would make a big practical difference.)


Neven
 
 A1 to EN55022:1998 requires the use of ferrite clamps on all cables leaving
 the table-top EUT for a connection outside the test site. Are there any
 other manufacturers of these clamps other than Fischer Custom
 Communications?
 
 Richard Woods
 Sensormatic Electronics
 Tyco International
 
 
 ---
 This message is from the IEEE EMC Society Product Safety
 Technical Committee emc-pstc discussion list.
 
 Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/
 
 To cancel your subscription, send mail to:
  majord...@ieee.org
 with the single line:
  unsubscribe emc-pstc
 
 For help, send mail to the list administrators:
  Ron Pickard:  emc-p...@hypercom.com
  Dave Heald:   davehe...@attbi.com
 
 For policy questions, send mail to:
  Richard Nute:   ri...@ieee.org
  Jim Bacher: j.bac...@ieee.org
 
 All emc-pstc postings are archived and searchable on the web at:
 http://ieeepstc.mindcruiser.com/
 Click on browse and then emc-pstc mailing list


This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Ron Pickard:  emc-p...@hypercom.com
 Dave Heald:   davehe...@attbi.com

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

Archive is being moved, we will announce when it is back on-line.
All emc-pstc postings are archived and searchable on the web at:
http://www.ieeecommunities.org/emc-pstc



Re: Circuit Breaker Tripping Dring Fault Tests

2003-01-29 Thread Lou Aiken
Here is what I think the requirements are:
 
If the product remains safe, within the meaning of the standard, and the
branch circuit overcurrent protection device does, or does not, operate as a
result of fault testing, internal overcurrent is unnecessary.
 
If the product does NOT remain safe, within the meaning of the standard, as a
result of fault testing, internal overcurrent protection IS necessary, branch
circuit overcurrent protection is   inadequate, and internal overcurrent
protection is necessary.
 
Safe within the meaning of the standard:  Does not exceed allowable fault
temperature limits, does not catch fire, enclosure does not deform to the
extent that parts involving the risk of electric shock or personal injury
become exposed to the test finger or probe, will pass the required electric
strength test after the fault, etc.
 
IN order to be confident that the design is safe one must continue the fault
testing until steady state conditions exist, OR for the maximum clearing time
(for the resulting fault current) as stated in the standard for the particular
overcurrent device.  It is incorrect consider the result acceptable when the
overcurrent device opens the circuit.  The overcurrent device should be
removed from the circuit and the current monitored during the fault test. 
Only approved fuses and circuit breakers should be specified if they are
necessary make the product remain safe - within the meaning of the standard.
 
There is a significant difference in the endurance and clearing limits between
the UL and IEC standards for fuses and circuit breakers with the same current
rating. 
 
 
 
Lou Aiken, LaMer LLC 
27109 Palmetto Drive
Orange Beach, AL
36561 USA
 
tel ++ 1 251 981 6786
fax ++ 1 251 981 3054
Cell ++ 1 251 979 4648

- Original Message - 
From: peter merguerian mailto:pmerguerian2...@yahoo.com  
To: emc-p...@majordomo.ieee.org 
Sent: Tuesday, January 28, 2003 1:54 PM
Subject: Circuit Breaker Tripping Dring Fault Tests


Dear All,

For safety, it is not clear from the standards whether the main branch circuit
breaker tripping during fault conditions is an acceptable result.

I see no reason why this should not be acceptable. What is your view? Some
third party labs find it acceptable and others do not.

Anyone can lead me to some inernational decisions regarding this issue?

Thanks,

Peter

 

 




  _  

Do you Yahoo!?
Yahoo! Mail  http://rd.yahoo.com/mail/mailsig/*http://mailplus.yahoo.com
Plus - Powerful. Affordable. Sign up  
ttp://rd.yahoo.com/mail/mailsig/*http://mailplus.yahoo.com now




RE: Automotive v. EMC Directives

2003-01-29 Thread gkt4s

Automotive products must comply with the Automotive Directive - this
actually requires additional elements beyond the
EMC Directive.



Safety issues are as one would expect - Fire and Energy Hazard - and are
potentially more serious than mains operated equipment because you do not
usually have 12 gallons of gas sitting on you stereo.



About 30 years ago I watched as a guy fitted a temporary Parking Light to
the cigarette outlet of his car - opened the window - fitted the light
(bracket) over the windowpane - closed the window then  locked and closed
the car door.

We all watched is astonishment as the wiring began to smolder and the car
filled with smoke. I did not wait to find out what happened next



Now that's what you call a non-compliance!!

Best regards

gregg


From: owner-emc-p...@majordomo.ieee.org
[mailto:owner-emc-p...@majordomo.ieee.org]On Behalf Of Hudson, Alan
Sent: Tuesday, January 28, 2003 12:34 PM
To: EMC-pstc (E-mail)
Subject: Automotive v. EMC Directives




G'Day!

Is anyone familiar with the standards needed to comply with the Automotive
*and* the EMC Directives? How do they compare? Or to put it another way, if
an item of equipment was known to be compliant with the Automotive
Directive, is it likely that it would therefore meet the requirements of the
EMC Directive?

Alan
--
Alenia Marconi Systems
Scotland


This email and any attachments are confidential to the intended
recipient and may also be privileged. If you are not the intended
recipient please delete it from your system and notify the sender.
You should not copy it or use it for any purpose nor disclose or
distribute its contents to any other person.



This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Ron Pickard:  emc-p...@hypercom.com
 Dave Heald:   davehe...@attbi.com

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
http://ieeepstc.mindcruiser.com/
Click on browse and then emc-pstc mailing list



This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
 majord...@ieee.org
with the single line:
 unsubscribe emc-pstc

For help, send mail to the list administrators:
 Ron Pickard:  emc-p...@hypercom.com
 Dave Heald:   davehe...@attbi.com

For policy questions, send mail to:
 Richard Nute:   ri...@ieee.org
 Jim Bacher: j.bac...@ieee.org

Archive is being moved, we will announce when it is back on-line.
All emc-pstc postings are archived and searchable on the web at:
http://www.ieeecommunities.org/emc-pstc