Re: [PSES] IEC 60950-1 Ed. 2 Class A Pluggable equipment and VDR bridging basic insulation.

2010-12-21 Thread emc-p...@ieee.org
In message 
63056535adcf774b87d41a999d9a7f2b23732...@bct1e2k301.americas.tsp.ad, 
dated Tue, 21 Dec 2010, Goedderz, Jim jgoedd...@tycoint.com writes:

Is there any additional response to Pat's inquiry? I would also like to 
know the justification of a VDR/gas discharge tube connection in the 
primary circuit.

It would be useful to have that available.

Some information became available very recently. This is not a standard 
or even an official interpretation of a standard. I suppose it is advice 
having a strong provenance:

TC108 position on varistors having connection to the mains, also 
identified as voltage dependent resistors (VDR) and metal oxide 
varistors (MOV).

During the recent TC108 meetings in Seattle, October 2010, the use of 
varistors having connection to mains circuits was discussed. There 
seemed to be different opinions and interpretations regarding the 
requirements contained in several of the TC108 standards. This INF 
document is intended to clarify the current interpretation of TC108 on 
those aspects where agreement has been reached. Some issues are still 
under discussion and these will be explained as soon as possible. 
Existing requirements not addressed below remain applicable.

The following statements are supported by the experts and the management 
of TC108 on the application of varistors in the IEC 60065, IEC 60950-1 
and IEC 62368-1 standards.
--
Compliance with IEC 61051-2

Where a varistor is used in connection with the mains, it shall comply 
with IEC 61051-2. The combination pulse test of IEC 61051-2:1991, Am 
1:2009 (2.3.6, Table I group 1 and Annex A), including consideration of
the nominal mains voltage and overvoltage category, should be allowed as 
an alternative to the requirements in the current standards.

Protection of varistors

Where a varistor is used in parallel with the mains connection, it 
should be protected against temporary overvoltages, overloads or short 
circuits. Details can be found in IEC 60950-1, clause 1.5.9.2.

Varistors in series with a GDT (for all types of equipment, including 
'normal' Pluggable Type A equipment)

Where a varistor in series with a GDT is used to bridge BASIC 
INSULATION, the following applies:

– the varistor has to comply with IEC 61051-2 as indicated in the 
standards; and
– the GDT has to comply with:
• the electric strength test for BASIC INSULATION; and
• the external CLEARANCE and CREEPAGE DISTANCE requirements for BASIC 
INSULATION.

It should be noted that the use of a VDR in series with a GDT to bridge 
reinforced insulation was also discussed. So far, no agreement was 
reached within IEC TC108.
--
It should be noted that each of the mentioned standards is currently 
being revised under the TC 108 maintenance procedures and these 
clarifications will be introduced in the relevant standards as deemed
necessary.
-- 
OOO - Own Opinions Only. Try www.jmwa.demon.co.uk and www.isce.org.uk
John Woodgate, J M Woodgate and Associates, Rayleigh, Essex UK
Plural: data, criteria. Singular: datum (different meaning: use 'data element'
for a single item), criterion. 'Effect' is a noun, 'affect' is a verb (except
in psychiatry).

-

This message is from the IEEE Product Safety Engineering Society emc-pstc 
discussion list. To post a message to the list, send your e-mail to 
emc-p...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
http://product-compliance.oc.ieee.org/
Graphics (in well-used formats), large files, etc. can be posted to that URL.

Website:  http://www.ieee-pses.org/
Instructions:  http://listserv.ieee.org/request/user-guide.html
List rules: http://www.ieee-pses.org/listrules.html

For help, send mail to the list administrators:
Scott Douglas emcp...@radiusnorth.net
Mike Cantwell mcantw...@ieee.org

For policy questions, send mail to:
Jim Bacher:  j.bac...@ieee.org
David Heald: dhe...@gmail.com


RE: [PSES] IEC 60950-1 Ed. 2 Class A Pluggable equipment and VDR bridging basic insulation.

2010-12-21 Thread emc-p...@ieee.org
Is there any additional response to Pat's inquiry? I would also like to
know the justification of a VDR/gas discharge tube connection in the
primary circuit.

It would be useful to have that available. 

James Goedderz
Sr. Principal Engineer-Product Safety
Sensormatic Electronics, LLC
561.912.6378


-Original Message-
From: emc-p...@ieee.org [mailto:emc-p...@ieee.org] On Behalf Of
pat.law...@slpower.com
Sent: Wednesday, December 15, 2010 9:05 PM
To: emc-p...@ieee.org
Subject: Re: [PSES] IEC 60950-1 Ed. 2 Class A Pluggable equipment and
VDR bridging basic insulation.

I found this in UL 60950, clause 1.5.9.1:

-- quote ---
If a surge suppressor is used in a PRIMARY CIRCUIT, it shall be a VDR
and 
it shall comply with Annex Q.
NOTE 1 A VDR is sometimes referred to as a varistor or a metal oxide 
varistor (MOV). Devices such as gas discharge tubes, carbon
blocks and semiconductor devices with non-linear voltage/current 
characteristics are not considered as VDRs in this standard.
--- end quote ---

This sounds like it prevents the use of VDR/gas discharge tube 
combinations to limit primary-to-earth line surges, or gas discharge
tubes 
in the primary completely.  Is this correct?
I'll bet the gas tube companies are having heartburn over this.

Pat Lawler
EMC Engineer
SL Power Electronics Corp.


ri...@ieee.org wrote on 12/15/2010 12:05:18 PM:
 On 12/15/2010 11:41, Kunde, Brian wrote:
  Does it make VDRs safer to use them in series with a gas-tube like 
some
  do with Varistors?

 Hi Brian:

 
 Yes.

 Today, this is the trend among manufacturers that
 want to use a VDR between mains and earth.

 And, TC108 is still trying to sort out the requirements
 for both devices in such a circuit.

 
 Best wishes for a Merry Christmas,
 Rich

 -
 
 This message is from the IEEE Product Safety Engineering Society 
 emc-pstc discussion list. To post a message to the list, send your 
 e-mail to emc-p...@ieee.org

 All emc-pstc postings are archived and searchable on the web at:
 http://product-compliance.oc.ieee.org/
 Graphics (in well-used formats), large files, etc. can be posted to
that 
URL.

 Website:  http://www.ieee-pses.org/
 Instructions:  http://listserv.ieee.org/request/user-guide.html
 List rules: http://www.ieee-pses.org/listrules.html

 For help, send mail to the list administrators:
 Scott Douglas emcp...@radiusnorth.net
 Mike Cantwell mcantw...@ieee.org

 For policy questions, send mail to:
 Jim Bacher:  j.bac...@ieee.org
 David Heald: dhe...@gmail.com

-

This message is from the IEEE Product Safety Engineering Society
emc-pstc discussion list. To post a message to the list, send your
e-mail to emc-p...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
http://product-compliance.oc.ieee.org/
Graphics (in well-used formats), large files, etc. can be posted to that
URL.

Website:  http://www.ieee-pses.org/
Instructions:  http://listserv.ieee.org/request/user-guide.html
List rules: http://www.ieee-pses.org/listrules.html

For help, send mail to the list administrators:
Scott Douglas emcp...@radiusnorth.net
Mike Cantwell mcantw...@ieee.org

For policy questions, send mail to:
Jim Bacher:  j.bac...@ieee.org
David Heald: dhe...@gmail.com

-

This message is from the IEEE Product Safety Engineering Society emc-pstc
discussion list. To post a message to the list, send your e-mail to
emc-p...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
http://product-compliance.oc.ieee.org/
Graphics (in well-used formats), large files, etc. can be posted to that URL.

Website:  http://www.ieee-pses.org/
Instructions:  http://listserv.ieee.org/request/user-guide.html
List rules: http://www.ieee-pses.org/listrules.html

For help, send mail to the list administrators:
Scott Douglas emcp...@radiusnorth.net
Mike Cantwell mcantw...@ieee.org

For policy questions, send mail to:
Jim Bacher:  j.bac...@ieee.org
David Heald: dhe...@gmail.com


Re: [PSES] IEC 60950-1 Ed. 2 Class A Pluggable equipment and VDR bridging basic insulation.

2010-12-16 Thread emc-p...@ieee.org
As I previously mentioned, the hi-pot test is for
SOLID insulation.

Presumably, the insulation between the side panels
and the mains circuits is air, or air in series
with solid insulation.  So, it should be valid to
test without the side panels.


Merry Christmas!
Rich




On 12/16/2010 06:16, Kunde, Brian wrote:
 Here is another clunky suggestion. What if you put your Surge Suppressor
 circuit after a dual pole circuit breaker that is only energized when
 the device is powered up. That way, the VDR is out of the circuit during
 the Hipot test, but in-circuit during the Surge Immunity test.

 This brings up a good point in regards to production hipot testing. Some
 of our instruments have double pole relays, so during hipot those
 downstream circuits do not get tested. So those circuits have to be
 individually hipot tested before the side panels are installed. As you
 said, this goes against the intent of the production hipot test, but
 what else can you do? You do the best you can. If an inspector
 disagrees, have him give you the solution.

 The Other Brian


-

This message is from the IEEE Product Safety Engineering Society emc-pstc
discussion list. To post a message to the list, send your e-mail to
emc-p...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
http://product-compliance.oc.ieee.org/
Graphics (in well-used formats), large files, etc. can be posted to that URL.

Website:  http://www.ieee-pses.org/
Instructions:  http://listserv.ieee.org/request/user-guide.html
List rules: http://www.ieee-pses.org/listrules.html

For help, send mail to the list administrators:
Scott Douglas emcp...@radiusnorth.net
Mike Cantwell mcantw...@ieee.org

For policy questions, send mail to:
Jim Bacher:  j.bac...@ieee.org
David Heald: dhe...@gmail.com


RE: OT A BIT........ [PSES] IEC 60950-1 Ed. 2 Class A Pluggable equipment and VDR bridging basic insulation.

2010-12-16 Thread emc-p...@ieee.org
David,

You have to ask yourself, what would secondary protection be protecting?

As part of your Risk Assessment or circuit Fault Analysis, you must consider
what would happen if the VDR/MOV faulted in a high current or short circuit
condition. If the high current can cause overheating in wiring, traces,
connectors, components, etc. which could cause a fire, then yes, some kind of
additional protection device must be added. If not, the answer is no. 

I hate it when I'm told by safety people that you must do this or do that
without consideration of the specific design.

For example, most power supplies (PSU) have a Line to Line VDR/MOV, but it is
after the onboard fuse provided to protect the entire PSU. If the VDR/MOV
faulted, the fuse would open. So an additional protection device for the
VDR/MOV would not be needed. 

If you do need to add protection for your VDRs, make it robust enough so it
does not open after your first thunderstorm. 

The Other Brian


-Original Message-
From: emc-p...@ieee.org [mailto:emc-p...@ieee.org] On Behalf Of Spencer, David
H
Sent: Wednesday, December 15, 2010 7:12 PM
To: Bill Owsley; EMC-PSTC@LISTSERV.IEEE.ORG; oconne...@tamuracorp.com
Subject: RE: OT A BIT [PSES] IEC 60950-1 Ed. 2 Class A Pluggable
equipment and VDR bridging basic insulation.

My safety people are telling me that part of Ed. 2 also requires that VDR's
line to line ( or line to neutral) have secondary protection.  
Either a fuse, gas tube, or double insulated cap.They have been with great
gusto been pulling out the VDR's or replacing them with fused versions.

From an EMC aspect,  we never know when a VDR (from now on MOV) goes bad.   

SO

with respect to line to line (neutral) MOV's only and Ed.2

Do MOV's need a secondary protection? 

thanks for any comments

Regards

David Spencer
EHS EMC Engineer
Xerox Corp   


-Original Message-
From: emc-p...@ieee.org on behalf of Bill Owsley
Sent: Wed 12/15/2010 3:57 PM
To: EMC-PSTC@LISTSERV.IEEE.ORG; oconne...@tamuracorp.com
Subject: RE: [PSES] IEC 60950-1 Ed. 2 Class A Pluggable equipment and VDR
bridging basic insulation.
 
In EMC are testing to 2 kV surge.  But Brazil deemed our product telecom
and applied 4 kV.  A couple of our products spark and arc impressively and
continue running.  A couple of others quit, died, castors up, and the smoke
got out... (It fun when they do that!)  
EMC says it has to continue to work.  
Safety says it only has to fail safely.  
Engineering says fix it but don't change anything.
VDR between line and earth, 
and between line to line fixes it to 4 kV.
But I run right into the safety guy and all these notes, about pluggable,
single/double fused, screwed down earths, permanent connect, etc.


 Bill
In the event of a national emergency, 
click on the following links to provide directions to your duly elected
mis-representatives.http://www.usa.gov/Contact/Elected.shtml
or...
https://writerep.house.gov/writerep/welcome.shtml
http://www.senate.gov/general/contact_information/senators_cfm.cfmif really
desperate...
http://www.usa.gov/Contact/Elected.shtml






--- On Wed, 12/15/10, Brian O'Connell oconne...@tamuracorp.com wrote:

From: Brian O'Connell oconne...@tamuracorp.com
Subject: RE: [PSES] IEC 60950-1 Ed. 2 Class A Pluggable equipment and VDR
bridging basic insulation.
To: EMC-PSTC@LISTSERV.IEEE.ORG
List-Post: emc-pstc@listserv.ieee.org
Date: Wednesday, December 15, 2010, 3:33 PM

The problem with the VDR being rated for a level 3 surge, which is
significantly greater than the typical test V for BI, is that the VDR will
typically start conducting long before required test voltage is reached.

Di-electric withstand and surge immunity are very different animals.

I saw a VDR from line to chassis in a competitor's component P/S - never
understood the reason for this construction.

Is the VDR rating for 62368 conformity a working voltage or surge rating ?

Brian 

  -Original Message-
  From: emc-p...@ieee.org [mailto:emc-p...@ieee.org]On Behalf 
  Of Richard
  Nute
  Sent: Wednesday, December 15, 2010 12:01 PM
  To: JIM WIESE
  Cc: EMC-PSTC@LISTSERV.IEEE.ORG
  Subject: Re: [PSES] IEC 60950-1 Ed. 2 Class A Pluggable equipment and
  VDR bridging basic insulation.
  
  
  Hi Jim:
  
  Thanks for your remarks.
  
  You CAN remove the VDR during hi-pot testing.
  This is specified in 5.2.2:
  
       To avoid damage to components or insulation
       that are not involved in the test,
       disconnection of integrated circuits or the
       like and the use of equipotential bonding are
       permitted.
  
  This is for the type test, not the routine
  test.  Nevertheless, your point is well taken.
  
  Also note that 5.2.1 specifies:
  
       The electric strength of the SOLID INSULATION
       used in the equipment shall be adequate.
  
  So, the hi-pot test only applies to solid
  insulation.
  
  The other option is to specify the VDR at a higher
  voltage than the hi-pot test voltage

Re: [PSES] IEC 60950-1 Ed. 2 Class A Pluggable equipment and VDR bridging basic insulation.

2010-12-16 Thread emc-p...@ieee.org
A solution we used years ago involved three elements in series, the VDR, 
a gas tube and a fuse.
The gas tube prevented the development of leakage currents as transients 
age the VDR.
If the VDR failed, the fuse prevented full line to neutral fault 
currents through the gas tube in the event of transients. Removing the 
fuse also allowed disconnection of the circuit for hipot testing.
This was used as a fix for an existing design, but for cost reasons was 
avoided in new products by better product design.

Bob Johnson



On 12/15/2010 05:18 PM, JIM WIESE wrote:
 Thanks Rich,

 Your first paragraph is what I tried with the safety lab to no avail as
 they still required a factory hipot, which requires disassembly or some
 other form of clunky workaround as Brian mentioned.  Brian's method
 could be feasible in some cases from the safety perspective to remove
 the MOV for the hipot, but lousy if you need a low impedance reliable
 path for thousands of amps of lightning current.  It also is not
 feasible in most cases for potted or OSP sealed telecom equipment.

 Merry Christmas,

 Jim

 Jim Wiese
 Senior Compliance Engineer
 ADTRAN, Inc.
 901 Explorer Blvd.
 Huntsville, AL 35806
 256-963-8431
 256-714-5882 (cell)
 256-963-6218 (fax)
 jim.wi...@adtran.com


 -Original Message-
 From: Richard Nute [mailto:rn...@san.rr.com]
 Sent: Wednesday, December 15, 2010 4:06 PM
 To: JIM WIESE
 Cc: EMC-PSTC@LISTSERV.IEEE.ORG
 Subject: Re: [PSES] IEC 60950-1 Ed. 2 Class A Pluggable equipment and
 VDR bridging basic insulation.



 Hi Jim:


 If the equipment is permanently grounded, then
 you can put in a VDR/MOV between mains and ground.
 Think of a permanent ground as a reinforced
 safeguard, with no need for basic insulation (in
 my opinion).

 For cord-connected equipment, IEC 62368-1 will
 likely require a series circuit of VDR and gas
 discharge tube.

 The big problem with VDR/MOVs is that we don't
 know the energy that must be dissipated by the
 VDR/MOV.  If the energy is high enough, the
 VDR/MOV will be destroyed and you will have arcs
 to ground.


 Have a Merry Christmas!
 Rich




 On 12/15/2010 13:06, JIM WIESE wrote:

 Hey Rich,

 The reason for VDR's (MOV's) to ground is to prevent arcing to the
 chassis for customers that demand either 6KV or 10KV lightning tests.
 The products are permanently grounded so the arcing to ground is not a
 safety hazard at those levels.  The products easily pass the hipot
 without the MOV's to several KV (well above the hipot level).

 The arcing at 6 or 10KV often functionally kills the supply or other
 circuitry, which of course 60950 could not care less about
 functionality.  But other standards do.

 It sounds like IEC 62368 will mess up using MOV's to ground though as
  
 I

 am not aware of MOV's rated several KV.

 Best regards,

 Jim

 Jim Wiese
 Senior Compliance Engineer
 ADTRAN, Inc.
 901 Explorer Blvd.
 Huntsville, AL 35806
 256-963-8431
 256-714-5882 (cell)
 256-963-6218 (fax)
 jim.wi...@adtran.com


 -Original Message-
 From: Richard Nute [mailto:rn...@san.rr.com]
 Sent: Wednesday, December 15, 2010 2:01 PM
 To: JIM WIESE
 Cc: EMC-PSTC@LISTSERV.IEEE.ORG
 Subject: Re: [PSES] IEC 60950-1 Ed. 2 Class A Pluggable equipment and
 VDR bridging basic insulation.



 Hi Jim:


 Thanks for your remarks.

 You CAN remove the VDR during hi-pot testing.
 This is specified in 5.2.2:

To avoid damage to components or insulation
that are not involved in the test,
disconnection of integrated circuits or the
like and the use of equipotential bonding are
permitted.

 This is for the type test, not the routine
 test.  Nevertheless, your point is well taken.

 Also note that 5.2.1 specifies:

The electric strength of the SOLID INSULATION
used in the equipment shall be adequate.

 So, the hi-pot test only applies to solid
 insulation.

 The other option is to specify the VDR at a higher
 voltage than the hi-pot test voltage.

 Regarding VDRs, I don't know why any equipment
 would need a VDR between mains and earth.  The
 requirements for clearance, creepage, and solid
 insulations require an electric strength at least
 as great as the expected transient overvoltage,
 regardless whether a VDR is between mains and
 earth or not.  So, the VDR does not protect
 anything against any voltage up to the required
 electric strength of the equipment.

 The VDR *may* be useful to protect against
 transient voltages exceeding the required electric
 strength.n which case it will pass the hi-pot
 test.

 In the new IEC 62368, the requirement is that any
 VDR between mains and earth shall be rated greater
 than the required electric strength.


 Best wishes for the Christmas season,
 Rich






  
 -
 
 This message is from the IEEE Product Safety Engineering Society emc-pstc
discussion list. To post a message to the list, send your e-mail
toemc-p

RE: [PSES] IEC 60950-1 Ed. 2 Class A Pluggable equipment and VDR bridging basic insulation.

2010-12-16 Thread emc-p...@ieee.org
I am not positive, but I think this is just a North American glitch
(UL/CSA).I think internationally you could make the justification
that Rich pointed out that it is inherently safe and on these products
skip a final AC hipot.  So what if line and neutral are shorted to
ground (other than for functionality reasons).  The MOV's will short the
line and neutral to ground at a couple hundred volts anyway and could
fail short permanently.

If it is the case that internationally it isn't a problem, yet somehow
domestically it becomes a safety hazard only due to the follow-up
services required ac hi-pot aspect, something seems wrong.

It just doesn't seem to hold water from a technical basis.

Jim
 
Jim Wiese
Senior Compliance Engineer
ADTRAN, Inc.
901 Explorer Blvd.
Huntsville, AL 35806
256-963-8431
256-714-5882 (cell)
256-963-6218 (fax)
jim.wi...@adtran.com
 

-Original Message-
From: Kunde, Brian [mailto:brian_ku...@lecotc.com] 
Sent: Thursday, December 16, 2010 8:17 AM
To: EMC-PSTC@LISTSERV.IEEE.ORG
Subject: Re: [PSES] IEC 60950-1 Ed. 2 Class A Pluggable equipment and
VDR bridging basic insulation.

Here is another clunky suggestion. What if you put your Surge Suppressor
circuit after a dual pole circuit breaker that is only energized when
the device is powered up. That way, the VDR is out of the circuit during
the Hipot test, but in-circuit during the Surge Immunity test. 

This brings up a good point in regards to production hipot testing. Some
of our instruments have double pole relays, so during hipot those
downstream circuits do not get tested. So those circuits have to be
individually hipot tested before the side panels are installed. As you
said, this goes against the intent of the production hipot test, but
what else can you do? You do the best you can. If an inspector
disagrees, have him give you the solution. 

The Other Brian

-Original Message-
From: emc-p...@ieee.org [mailto:emc-p...@ieee.org] On Behalf Of JIM
WIESE
Sent: Wednesday, December 15, 2010 5:18 PM
To: ri...@ieee.org
Cc: EMC-PSTC@LISTSERV.IEEE.ORG
Subject: RE: [PSES] IEC 60950-1 Ed. 2 Class A Pluggable equipment and
VDR bridging basic insulation.

Thanks Rich,

Your first paragraph is what I tried with the safety lab to no avail as
they still required a factory hipot, which requires disassembly or some
other form of clunky workaround as Brian mentioned.  Brian's method
could be feasible in some cases from the safety perspective to remove
the MOV for the hipot, but lousy if you need a low impedance reliable
path for thousands of amps of lightning current.  It also is not
feasible in most cases for potted or OSP sealed telecom equipment. 

Merry Christmas,

Jim
 
Jim Wiese
Senior Compliance Engineer
ADTRAN, Inc.
901 Explorer Blvd.
Huntsville, AL 35806
256-963-8431
256-714-5882 (cell)
256-963-6218 (fax)
jim.wi...@adtran.com
 

-Original Message-
From: Richard Nute [mailto:rn...@san.rr.com] 
Sent: Wednesday, December 15, 2010 4:06 PM
To: JIM WIESE
Cc: EMC-PSTC@LISTSERV.IEEE.ORG
Subject: Re: [PSES] IEC 60950-1 Ed. 2 Class A Pluggable equipment and
VDR bridging basic insulation.



Hi Jim:


If the equipment is permanently grounded, then
you can put in a VDR/MOV between mains and ground.
Think of a permanent ground as a reinforced
safeguard, with no need for basic insulation (in
my opinion).

For cord-connected equipment, IEC 62368-1 will
likely require a series circuit of VDR and gas
discharge tube.

The big problem with VDR/MOVs is that we don't
know the energy that must be dissipated by the
VDR/MOV.  If the energy is high enough, the
VDR/MOV will be destroyed and you will have arcs
to ground.


Have a Merry Christmas!
Rich




On 12/15/2010 13:06, JIM WIESE wrote:
 Hey Rich,

 The reason for VDR's (MOV's) to ground is to prevent arcing to the
 chassis for customers that demand either 6KV or 10KV lightning tests.
 The products are permanently grounded so the arcing to ground is not a
 safety hazard at those levels.  The products easily pass the hipot
 without the MOV's to several KV (well above the hipot level).

 The arcing at 6 or 10KV often functionally kills the supply or other
 circuitry, which of course 60950 could not care less about
 functionality.  But other standards do.

 It sounds like IEC 62368 will mess up using MOV's to ground though as
I
 am not aware of MOV's rated several KV.

 Best regards,

 Jim

 Jim Wiese
 Senior Compliance Engineer
 ADTRAN, Inc.
 901 Explorer Blvd.
 Huntsville, AL 35806
 256-963-8431
 256-714-5882 (cell)
 256-963-6218 (fax)
 jim.wi...@adtran.com


 -Original Message-
 From: Richard Nute [mailto:rn...@san.rr.com]
 Sent: Wednesday, December 15, 2010 2:01 PM
 To: JIM WIESE
 Cc: EMC-PSTC@LISTSERV.IEEE.ORG
 Subject: Re: [PSES] IEC 60950-1 Ed. 2 Class A Pluggable equipment and
 VDR bridging basic insulation.



 Hi Jim:


 Thanks for your remarks.

 You CAN remove the VDR during hi-pot testing.
 This is specified in 5.2.2:

   To avoid damage to components

RE: [PSES] IEC 60950-1 Ed. 2 Class A Pluggable equipment and VDR bridging basic insulation.

2010-12-16 Thread emc-p...@ieee.org
Here is another clunky suggestion. What if you put your Surge Suppressor
circuit after a dual pole circuit breaker that is only energized when
the device is powered up. That way, the VDR is out of the circuit during
the Hipot test, but in-circuit during the Surge Immunity test. 

This brings up a good point in regards to production hipot testing. Some
of our instruments have double pole relays, so during hipot those
downstream circuits do not get tested. So those circuits have to be
individually hipot tested before the side panels are installed. As you
said, this goes against the intent of the production hipot test, but
what else can you do? You do the best you can. If an inspector
disagrees, have him give you the solution. 

The Other Brian

-Original Message-
From: emc-p...@ieee.org [mailto:emc-p...@ieee.org] On Behalf Of JIM
WIESE
Sent: Wednesday, December 15, 2010 5:18 PM
To: ri...@ieee.org
Cc: EMC-PSTC@LISTSERV.IEEE.ORG
Subject: RE: [PSES] IEC 60950-1 Ed. 2 Class A Pluggable equipment and
VDR bridging basic insulation.

Thanks Rich,

Your first paragraph is what I tried with the safety lab to no avail as
they still required a factory hipot, which requires disassembly or some
other form of clunky workaround as Brian mentioned.  Brian's method
could be feasible in some cases from the safety perspective to remove
the MOV for the hipot, but lousy if you need a low impedance reliable
path for thousands of amps of lightning current.  It also is not
feasible in most cases for potted or OSP sealed telecom equipment. 

Merry Christmas,

Jim
 
Jim Wiese
Senior Compliance Engineer
ADTRAN, Inc.
901 Explorer Blvd.
Huntsville, AL 35806
256-963-8431
256-714-5882 (cell)
256-963-6218 (fax)
jim.wi...@adtran.com
 

-Original Message-
From: Richard Nute [mailto:rn...@san.rr.com] 
Sent: Wednesday, December 15, 2010 4:06 PM
To: JIM WIESE
Cc: EMC-PSTC@LISTSERV.IEEE.ORG
Subject: Re: [PSES] IEC 60950-1 Ed. 2 Class A Pluggable equipment and
VDR bridging basic insulation.



Hi Jim:


If the equipment is permanently grounded, then
you can put in a VDR/MOV between mains and ground.
Think of a permanent ground as a reinforced
safeguard, with no need for basic insulation (in
my opinion).

For cord-connected equipment, IEC 62368-1 will
likely require a series circuit of VDR and gas
discharge tube.

The big problem with VDR/MOVs is that we don't
know the energy that must be dissipated by the
VDR/MOV.  If the energy is high enough, the
VDR/MOV will be destroyed and you will have arcs
to ground.


Have a Merry Christmas!
Rich




On 12/15/2010 13:06, JIM WIESE wrote:
 Hey Rich,

 The reason for VDR's (MOV's) to ground is to prevent arcing to the
 chassis for customers that demand either 6KV or 10KV lightning tests.
 The products are permanently grounded so the arcing to ground is not a
 safety hazard at those levels.  The products easily pass the hipot
 without the MOV's to several KV (well above the hipot level).

 The arcing at 6 or 10KV often functionally kills the supply or other
 circuitry, which of course 60950 could not care less about
 functionality.  But other standards do.

 It sounds like IEC 62368 will mess up using MOV's to ground though as
I
 am not aware of MOV's rated several KV.

 Best regards,

 Jim

 Jim Wiese
 Senior Compliance Engineer
 ADTRAN, Inc.
 901 Explorer Blvd.
 Huntsville, AL 35806
 256-963-8431
 256-714-5882 (cell)
 256-963-6218 (fax)
 jim.wi...@adtran.com


 -Original Message-
 From: Richard Nute [mailto:rn...@san.rr.com]
 Sent: Wednesday, December 15, 2010 2:01 PM
 To: JIM WIESE
 Cc: EMC-PSTC@LISTSERV.IEEE.ORG
 Subject: Re: [PSES] IEC 60950-1 Ed. 2 Class A Pluggable equipment and
 VDR bridging basic insulation.



 Hi Jim:


 Thanks for your remarks.

 You CAN remove the VDR during hi-pot testing.
 This is specified in 5.2.2:

   To avoid damage to components or insulation
   that are not involved in the test,
   disconnection of integrated circuits or the
   like and the use of equipotential bonding are
   permitted.

 This is for the type test, not the routine
 test.  Nevertheless, your point is well taken.

 Also note that 5.2.1 specifies:

   The electric strength of the SOLID INSULATION
   used in the equipment shall be adequate.

 So, the hi-pot test only applies to solid
 insulation.

 The other option is to specify the VDR at a higher
 voltage than the hi-pot test voltage.

 Regarding VDRs, I don't know why any equipment
 would need a VDR between mains and earth.  The
 requirements for clearance, creepage, and solid
 insulations require an electric strength at least
 as great as the expected transient overvoltage,
 regardless whether a VDR is between mains and
 earth or not.  So, the VDR does not protect
 anything against any voltage up to the required
 electric strength of the equipment.

 The VDR *may* be useful to protect against
 transient voltages exceeding the required electric
 strength.n which case it will pass the hi-pot
 test

RE: OT A BIT........ [PSES] IEC 60950-1 Ed. 2 Class A Pluggable equipment and VDR bridging basic insulation.

2010-12-16 Thread emc-p...@ieee.org
And then there's the EMC surge test, where the equipment must operate
(main fuse not open) after the surge.

James Goedderz
Sr. Principal Engineer-Product Safety
Sensormatic Electronics, LLC
561.912.6378

-Original Message-
From: emc-p...@ieee.org [mailto:emc-p...@ieee.org] On Behalf Of Brian
O'Connell
Sent: Wednesday, December 15, 2010 8:01 PM
To: EMC-PSTC@LISTSERV.IEEE.ORG
Subject: RE: OT A BIT [PSES] IEC 60950-1 Ed. 2 Class A Pluggable
equipment and VDR bridging basic insulation.

The requirement for secondary protection is based on the results of
Type
Tests for components that are across the line, and the requirements
found
in 1.5.9.2. The assumption is that the component is rated to be used
across mains, and the box is Class I construction.

The best result for a surge is that when the varistor (MOV) conducts,
the
fault current has a low-Z path to the current interrupt device (input
fuse) which quickly opens. In this case, the 'additional' protection is
provided by a typical input fuse.

Brian 

  -Original Message-
  From: emc-p...@ieee.org [mailto:emc-p...@ieee.org]On Behalf 
  Of Spencer,
  David H
  Sent: Wednesday, December 15, 2010 4:12 PM
  To: Bill Owsley; EMC-PSTC@LISTSERV.IEEE.ORG; oconne...@tamuracorp.com
  Subject: RE: OT A BIT [PSES] IEC 60950-1 Ed. 2 Class 
  A Pluggable
  equipment and VDR bridging basic insulation.
  
  My safety people are telling me that part of Ed. 2 also 
  requires that VDR's line to line ( or line to neutral) have 
  secondary protection.  
  Either a fuse, gas tube, or double insulated cap.They 
  have been with great gusto been pulling out the VDR's or 
  replacing them with fused versions.
  
  From an EMC aspect,  we never know when a VDR (from now on 
  MOV) goes bad.   
  
  SO
  
  with respect to line to line (neutral) MOV's only and Ed.2
  
  Do MOV's need a secondary protection? 
  
  thanks for any comments
  
  Regards
  
  David Spencer
  EHS EMC Engineer
  Xerox Corp   
  Is the VDR rating for 62368 conformity a working voltage or 
  surge rating ?

-

This message is from the IEEE Product Safety Engineering Society
emc-pstc discussion list. To post a message to the list, send your
e-mail to emc-p...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
http://product-compliance.oc.ieee.org/
Graphics (in well-used formats), large files, etc. can be posted to that
URL.

Website:  http://www.ieee-pses.org/
Instructions:  http://listserv.ieee.org/request/user-guide.html
List rules: http://www.ieee-pses.org/listrules.html

For help, send mail to the list administrators:
Scott Douglas emcp...@radiusnorth.net
Mike Cantwell mcantw...@ieee.org

For policy questions, send mail to:
Jim Bacher:  j.bac...@ieee.org
David Heald: dhe...@gmail.com

-

This message is from the IEEE Product Safety Engineering Society emc-pstc
discussion list. To post a message to the list, send your e-mail to
emc-p...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
http://product-compliance.oc.ieee.org/
Graphics (in well-used formats), large files, etc. can be posted to that URL.

Website:  http://www.ieee-pses.org/
Instructions:  http://listserv.ieee.org/request/user-guide.html
List rules: http://www.ieee-pses.org/listrules.html

For help, send mail to the list administrators:
Scott Douglas emcp...@radiusnorth.net
Mike Cantwell mcantw...@ieee.org

For policy questions, send mail to:
Jim Bacher:  j.bac...@ieee.org
David Heald: dhe...@gmail.com


Re: [PSES] IEC 60950-1 Ed. 2 Class A Pluggable equipment and VDR bridging basic insulation.

2010-12-15 Thread emc-p...@ieee.org
I found this in UL 60950, clause 1.5.9.1:

-- quote ---
If a surge suppressor is used in a PRIMARY CIRCUIT, it shall be a VDR and 
it shall comply with Annex Q.
NOTE 1 A VDR is sometimes referred to as a varistor or a metal oxide 
varistor (MOV). Devices such as gas discharge tubes, carbon
blocks and semiconductor devices with non-linear voltage/current 
characteristics are not considered as VDRs in this standard.
--- end quote ---

This sounds like it prevents the use of VDR/gas discharge tube 
combinations to limit primary-to-earth line surges, or gas discharge tubes 
in the primary completely.  Is this correct?
I'll bet the gas tube companies are having heartburn over this.

Pat Lawler
EMC Engineer
SL Power Electronics Corp.


ri...@ieee.org wrote on 12/15/2010 12:05:18 PM:
 On 12/15/2010 11:41, Kunde, Brian wrote:
  Does it make VDRs safer to use them in series with a gas-tube like 
some
  do with Varistors?

 Hi Brian:

 
 Yes.

 Today, this is the trend among manufacturers that
 want to use a VDR between mains and earth.

 And, TC108 is still trying to sort out the requirements
 for both devices in such a circuit.

 
 Best wishes for a Merry Christmas,
 Rich

 -
 
 This message is from the IEEE Product Safety Engineering Society 
 emc-pstc discussion list. To post a message to the list, send your 
 e-mail to emc-p...@ieee.org

 All emc-pstc postings are archived and searchable on the web at:
 http://product-compliance.oc.ieee.org/
 Graphics (in well-used formats), large files, etc. can be posted to that 
URL.

 Website:  http://www.ieee-pses.org/
 Instructions:  http://listserv.ieee.org/request/user-guide.html
 List rules: http://www.ieee-pses.org/listrules.html

 For help, send mail to the list administrators:
 Scott Douglas emcp...@radiusnorth.net
 Mike Cantwell mcantw...@ieee.org

 For policy questions, send mail to:
 Jim Bacher:  j.bac...@ieee.org
 David Heald: dhe...@gmail.com

-

This message is from the IEEE Product Safety Engineering Society emc-pstc
discussion list. To post a message to the list, send your e-mail to
emc-p...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
http://product-compliance.oc.ieee.org/
Graphics (in well-used formats), large files, etc. can be posted to that URL.

Website:  http://www.ieee-pses.org/
Instructions:  http://listserv.ieee.org/request/user-guide.html
List rules: http://www.ieee-pses.org/listrules.html

For help, send mail to the list administrators:
Scott Douglas emcp...@radiusnorth.net
Mike Cantwell mcantw...@ieee.org

For policy questions, send mail to:
Jim Bacher:  j.bac...@ieee.org
David Heald: dhe...@gmail.com


RE: OT A BIT........ [PSES] IEC 60950-1 Ed. 2 Class A Pluggable equipment and VDR bridging basic insulation.

2010-12-15 Thread emc-p...@ieee.org
The requirement for secondary protection is based on the results of Type
Tests for components that are across the line, and the requirements found
in 1.5.9.2. The assumption is that the component is rated to be used
across mains, and the box is Class I construction.

The best result for a surge is that when the varistor (MOV) conducts, the
fault current has a low-Z path to the current interrupt device (input
fuse) which quickly opens. In this case, the 'additional' protection is
provided by a typical input fuse.

Brian 

  -Original Message-
  From: emc-p...@ieee.org [mailto:emc-p...@ieee.org]On Behalf 
  Of Spencer,
  David H
  Sent: Wednesday, December 15, 2010 4:12 PM
  To: Bill Owsley; EMC-PSTC@LISTSERV.IEEE.ORG; oconne...@tamuracorp.com
  Subject: RE: OT A BIT [PSES] IEC 60950-1 Ed. 2 Class 
  A Pluggable
  equipment and VDR bridging basic insulation.
  
  My safety people are telling me that part of Ed. 2 also 
  requires that VDR's line to line ( or line to neutral) have 
  secondary protection.  
  Either a fuse, gas tube, or double insulated cap.They 
  have been with great gusto been pulling out the VDR's or 
  replacing them with fused versions.
  
  From an EMC aspect,  we never know when a VDR (from now on 
  MOV) goes bad.   
  
  SO
  
  with respect to line to line (neutral) MOV's only and Ed.2
  
  Do MOV's need a secondary protection? 
  
  thanks for any comments
  
  Regards
  
  David Spencer
  EHS EMC Engineer
  Xerox Corp   
  Is the VDR rating for 62368 conformity a working voltage or 
  surge rating ?

-

This message is from the IEEE Product Safety Engineering Society emc-pstc
discussion list. To post a message to the list, send your e-mail to
emc-p...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
http://product-compliance.oc.ieee.org/
Graphics (in well-used formats), large files, etc. can be posted to that URL.

Website:  http://www.ieee-pses.org/
Instructions:  http://listserv.ieee.org/request/user-guide.html
List rules: http://www.ieee-pses.org/listrules.html

For help, send mail to the list administrators:
Scott Douglas emcp...@radiusnorth.net
Mike Cantwell mcantw...@ieee.org

For policy questions, send mail to:
Jim Bacher:  j.bac...@ieee.org
David Heald: dhe...@gmail.com


RE: OT A BIT........ [PSES] IEC 60950-1 Ed. 2 Class A Pluggable equipment and VDR bridging basic insulation.

2010-12-15 Thread emc-p...@ieee.org
My safety people are telling me that part of Ed. 2 also requires that VDR's
line to line ( or line to neutral) have secondary protection.  
Either a fuse, gas tube, or double insulated cap.They have been with great
gusto been pulling out the VDR's or replacing them with fused versions.

From an EMC aspect,  we never know when a VDR (from now on MOV) goes bad.   

SO

with respect to line to line (neutral) MOV's only and Ed.2

Do MOV's need a secondary protection? 

thanks for any comments

Regards

David Spencer
EHS EMC Engineer
Xerox Corp   


-Original Message-
From: emc-p...@ieee.org on behalf of Bill Owsley
Sent: Wed 12/15/2010 3:57 PM
To: EMC-PSTC@LISTSERV.IEEE.ORG; oconne...@tamuracorp.com
Subject: RE: [PSES] IEC 60950-1 Ed. 2 Class A Pluggable equipment and VDR
bridging basic insulation.
 
In EMC are testing to 2 kV surge.  But Brazil deemed our product telecom
and applied 4 kV.  A couple of our products spark and arc impressively and
continue running.  A couple of others quit, died, castors up, and the smoke
got out... (It fun when they do that!)  
EMC says it has to continue to work.  
Safety says it only has to fail safely.  
Engineering says fix it but don't change anything.
VDR between line and earth, 
and between line to line fixes it to 4 kV.
But I run right into the safety guy and all these notes, about pluggable,
single/double fused, screwed down earths, permanent connect, etc.


 Bill
In the event of a national emergency, 
click on the following links to provide directions to your duly elected
mis-representatives.http://www.usa.gov/Contact/Elected.shtml
or...
https://writerep.house.gov/writerep/welcome.shtml
http://www.senate.gov/general/contact_information/senators_cfm.cfmif really
desperate...
http://www.usa.gov/Contact/Elected.shtml






--- On Wed, 12/15/10, Brian O'Connell oconne...@tamuracorp.com wrote:

From: Brian O'Connell oconne...@tamuracorp.com
Subject: RE: [PSES] IEC 60950-1 Ed. 2 Class A Pluggable equipment and VDR
bridging basic insulation.
To: EMC-PSTC@LISTSERV.IEEE.ORG
List-Post: emc-pstc@listserv.ieee.org
Date: Wednesday, December 15, 2010, 3:33 PM

The problem with the VDR being rated for a level 3 surge, which is
significantly greater than the typical test V for BI, is that the VDR will
typically start conducting long before required test voltage is reached.

Di-electric withstand and surge immunity are very different animals.

I saw a VDR from line to chassis in a competitor's component P/S - never
understood the reason for this construction.

Is the VDR rating for 62368 conformity a working voltage or surge rating ?

Brian 

  -Original Message-
  From: emc-p...@ieee.org [mailto:emc-p...@ieee.org]On Behalf 
  Of Richard
  Nute
  Sent: Wednesday, December 15, 2010 12:01 PM
  To: JIM WIESE
  Cc: EMC-PSTC@LISTSERV.IEEE.ORG
  Subject: Re: [PSES] IEC 60950-1 Ed. 2 Class A Pluggable equipment and
  VDR bridging basic insulation.
  
  
  Hi Jim:
  
  Thanks for your remarks.
  
  You CAN remove the VDR during hi-pot testing.
  This is specified in 5.2.2:
  
       To avoid damage to components or insulation
       that are not involved in the test,
       disconnection of integrated circuits or the
       like and the use of equipotential bonding are
       permitted.
  
  This is for the type test, not the routine
  test.  Nevertheless, your point is well taken.
  
  Also note that 5.2.1 specifies:
  
       The electric strength of the SOLID INSULATION
       used in the equipment shall be adequate.
  
  So, the hi-pot test only applies to solid
  insulation.
  
  The other option is to specify the VDR at a higher
  voltage than the hi-pot test voltage.
  
  Regarding VDRs, I don't know why any equipment
  would need a VDR between mains and earth.  The
  requirements for clearance, creepage, and solid
  insulations require an electric strength at least
  as great as the expected transient overvoltage,
  regardless whether a VDR is between mains and
  earth or not.  So, the VDR does not protect
  anything against any voltage up to the required
  electric strength of the equipment.
  
  The VDR *may* be useful to protect against
  transient voltages exceeding the required electric
  strength.n which case it will pass the hi-pot
  test.
  
  In the new IEC 62368, the requirement is that any
  VDR between mains and earth shall be rated greater
  than the required electric strength.
  
  
  Best wishes for the Christmas season,
  Rich

-

This message is from the IEEE Product Safety Engineering Society emc-pstc
discussion list. To post a message to the list, send your e-mail to
emc-p...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
http://product-compliance.oc.ieee.org/
Graphics (in well-used formats), large files, etc. can be posted to that URL.

Website:  http://www.ieee-pses.org/
Instructions:  http://listserv.ieee.org/request/user-guide.html
List rules

RE: [PSES] IEC 60950-1 Ed. 2 Class A Pluggable equipment and VDR bridging basic insulation.

2010-12-15 Thread emc-p...@ieee.org
Thanks Rich,

Your first paragraph is what I tried with the safety lab to no avail as
they still required a factory hipot, which requires disassembly or some
other form of clunky workaround as Brian mentioned.  Brian's method
could be feasible in some cases from the safety perspective to remove
the MOV for the hipot, but lousy if you need a low impedance reliable
path for thousands of amps of lightning current.  It also is not
feasible in most cases for potted or OSP sealed telecom equipment. 

Merry Christmas,

Jim
 
Jim Wiese
Senior Compliance Engineer
ADTRAN, Inc.
901 Explorer Blvd.
Huntsville, AL 35806
256-963-8431
256-714-5882 (cell)
256-963-6218 (fax)
jim.wi...@adtran.com
 

-Original Message-
From: Richard Nute [mailto:rn...@san.rr.com] 
Sent: Wednesday, December 15, 2010 4:06 PM
To: JIM WIESE
Cc: EMC-PSTC@LISTSERV.IEEE.ORG
Subject: Re: [PSES] IEC 60950-1 Ed. 2 Class A Pluggable equipment and
VDR bridging basic insulation.



Hi Jim:


If the equipment is permanently grounded, then
you can put in a VDR/MOV between mains and ground.
Think of a permanent ground as a reinforced
safeguard, with no need for basic insulation (in
my opinion).

For cord-connected equipment, IEC 62368-1 will
likely require a series circuit of VDR and gas
discharge tube.

The big problem with VDR/MOVs is that we don't
know the energy that must be dissipated by the
VDR/MOV.  If the energy is high enough, the
VDR/MOV will be destroyed and you will have arcs
to ground.


Have a Merry Christmas!
Rich




On 12/15/2010 13:06, JIM WIESE wrote:
 Hey Rich,

 The reason for VDR's (MOV's) to ground is to prevent arcing to the
 chassis for customers that demand either 6KV or 10KV lightning tests.
 The products are permanently grounded so the arcing to ground is not a
 safety hazard at those levels.  The products easily pass the hipot
 without the MOV's to several KV (well above the hipot level).

 The arcing at 6 or 10KV often functionally kills the supply or other
 circuitry, which of course 60950 could not care less about
 functionality.  But other standards do.

 It sounds like IEC 62368 will mess up using MOV's to ground though as
I
 am not aware of MOV's rated several KV.

 Best regards,

 Jim

 Jim Wiese
 Senior Compliance Engineer
 ADTRAN, Inc.
 901 Explorer Blvd.
 Huntsville, AL 35806
 256-963-8431
 256-714-5882 (cell)
 256-963-6218 (fax)
 jim.wi...@adtran.com


 -Original Message-
 From: Richard Nute [mailto:rn...@san.rr.com]
 Sent: Wednesday, December 15, 2010 2:01 PM
 To: JIM WIESE
 Cc: EMC-PSTC@LISTSERV.IEEE.ORG
 Subject: Re: [PSES] IEC 60950-1 Ed. 2 Class A Pluggable equipment and
 VDR bridging basic insulation.



 Hi Jim:


 Thanks for your remarks.

 You CAN remove the VDR during hi-pot testing.
 This is specified in 5.2.2:

   To avoid damage to components or insulation
   that are not involved in the test,
   disconnection of integrated circuits or the
   like and the use of equipotential bonding are
   permitted.

 This is for the type test, not the routine
 test.  Nevertheless, your point is well taken.

 Also note that 5.2.1 specifies:

   The electric strength of the SOLID INSULATION
   used in the equipment shall be adequate.

 So, the hi-pot test only applies to solid
 insulation.

 The other option is to specify the VDR at a higher
 voltage than the hi-pot test voltage.

 Regarding VDRs, I don't know why any equipment
 would need a VDR between mains and earth.  The
 requirements for clearance, creepage, and solid
 insulations require an electric strength at least
 as great as the expected transient overvoltage,
 regardless whether a VDR is between mains and
 earth or not.  So, the VDR does not protect
 anything against any voltage up to the required
 electric strength of the equipment.

 The VDR *may* be useful to protect against
 transient voltages exceeding the required electric
 strength.n which case it will pass the hi-pot
 test.

 In the new IEC 62368, the requirement is that any
 VDR between mains and earth shall be rated greater
 than the required electric strength.


 Best wishes for the Christmas season,
 Rich







-

This message is from the IEEE Product Safety Engineering Society emc-pstc
discussion list. To post a message to the list, send your e-mail to
emc-p...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
http://product-compliance.oc.ieee.org/
Graphics (in well-used formats), large files, etc. can be posted to that URL.

Website:  http://www.ieee-pses.org/
Instructions:  http://listserv.ieee.org/request/user-guide.html
List rules: http://www.ieee-pses.org/listrules.html

For help, send mail to the list administrators:
Scott Douglas emcp...@radiusnorth.net
Mike Cantwell mcantw...@ieee.org

For policy questions, send mail to:
Jim Bacher:  j.bac...@ieee.org
David Heald: dhe...@gmail.com


Re: [PSES] IEC 60950-1 Ed. 2 Class A Pluggable equipment and VDR bridging basic insulation.

2010-12-15 Thread emc-p...@ieee.org
Hi Jim:


If the equipment is permanently grounded, then
you can put in a VDR/MOV between mains and ground.
Think of a permanent ground as a reinforced
safeguard, with no need for basic insulation (in
my opinion).

For cord-connected equipment, IEC 62368-1 will
likely require a series circuit of VDR and gas
discharge tube.

The big problem with VDR/MOVs is that we don't
know the energy that must be dissipated by the
VDR/MOV.  If the energy is high enough, the
VDR/MOV will be destroyed and you will have arcs
to ground.


Have a Merry Christmas!
Rich




On 12/15/2010 13:06, JIM WIESE wrote:
 Hey Rich,

 The reason for VDR's (MOV's) to ground is to prevent arcing to the
 chassis for customers that demand either 6KV or 10KV lightning tests.
 The products are permanently grounded so the arcing to ground is not a
 safety hazard at those levels.  The products easily pass the hipot
 without the MOV's to several KV (well above the hipot level).

 The arcing at 6 or 10KV often functionally kills the supply or other
 circuitry, which of course 60950 could not care less about
 functionality.  But other standards do.

 It sounds like IEC 62368 will mess up using MOV's to ground though as I
 am not aware of MOV's rated several KV.

 Best regards,

 Jim

 Jim Wiese
 Senior Compliance Engineer
 ADTRAN, Inc.
 901 Explorer Blvd.
 Huntsville, AL 35806
 256-963-8431
 256-714-5882 (cell)
 256-963-6218 (fax)
 jim.wi...@adtran.com


 -Original Message-
 From: Richard Nute [mailto:rn...@san.rr.com]
 Sent: Wednesday, December 15, 2010 2:01 PM
 To: JIM WIESE
 Cc: EMC-PSTC@LISTSERV.IEEE.ORG
 Subject: Re: [PSES] IEC 60950-1 Ed. 2 Class A Pluggable equipment and
 VDR bridging basic insulation.



 Hi Jim:


 Thanks for your remarks.

 You CAN remove the VDR during hi-pot testing.
 This is specified in 5.2.2:

   To avoid damage to components or insulation
   that are not involved in the test,
   disconnection of integrated circuits or the
   like and the use of equipotential bonding are
   permitted.

 This is for the type test, not the routine
 test.  Nevertheless, your point is well taken.

 Also note that 5.2.1 specifies:

   The electric strength of the SOLID INSULATION
   used in the equipment shall be adequate.

 So, the hi-pot test only applies to solid
 insulation.

 The other option is to specify the VDR at a higher
 voltage than the hi-pot test voltage.

 Regarding VDRs, I don't know why any equipment
 would need a VDR between mains and earth.  The
 requirements for clearance, creepage, and solid
 insulations require an electric strength at least
 as great as the expected transient overvoltage,
 regardless whether a VDR is between mains and
 earth or not.  So, the VDR does not protect
 anything against any voltage up to the required
 electric strength of the equipment.

 The VDR *may* be useful to protect against
 transient voltages exceeding the required electric
 strength.n which case it will pass the hi-pot
 test.

 In the new IEC 62368, the requirement is that any
 VDR between mains and earth shall be rated greater
 than the required electric strength.


 Best wishes for the Christmas season,
 Rich







-

This message is from the IEEE Product Safety Engineering Society emc-pstc
discussion list. To post a message to the list, send your e-mail to
emc-p...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
http://product-compliance.oc.ieee.org/
Graphics (in well-used formats), large files, etc. can be posted to that URL.

Website:  http://www.ieee-pses.org/
Instructions:  http://listserv.ieee.org/request/user-guide.html
List rules: http://www.ieee-pses.org/listrules.html

For help, send mail to the list administrators:
Scott Douglas emcp...@radiusnorth.net
Mike Cantwell mcantw...@ieee.org

For policy questions, send mail to:
Jim Bacher:  j.bac...@ieee.org
David Heald: dhe...@gmail.com


Re: [PSES] IEC 60950-1 Ed. 2 Class A Pluggable equipment and VDR bridging basic insulation.

2010-12-15 Thread emc-p...@ieee.org
Hi Brian:


You describe the problem accurately.  The
VDR will start conducting before the required
test voltage is reached.

 From a safety point of view, this is not
acceptable unless the equipment is reliably
grounded.

 From a functional point of view, this is the
intended performance.

Let's put it this way.

Normal mains voltage is comprised of two
elements:

 mains operating voltage;
 mains transient voltage.

The safety of the equipment is dependent
upon the mains insulation (between mains
and accessible parts, including ground)
being able to withstand both voltages.

As near as I can discern, surge immunity
is the same as mains transient withstand.

Surge immunity implies withstanding a
1.2x50 impulse waveform, while mains
transient withstand implies a sinewave.
(The mains transient withstand test can
be done with a sinewave, DC, or a 1.2x50
impulse.)

The IEC 62368-1 requirement is that
EVERYTHING connected between mains and
earth must pass a dielectric withstand
test.


Have a Merry Christmas,
Rich






On 12/15/2010 12:33, Brian O'Connell wrote:
 The problem with the VDR being rated for a level 3 surge, which is
significantly greater than the typical test V for BI, is that the VDR will
typically start conducting long before required test voltage is reached.

 Di-electric withstand and surge immunity are very different animals.

 I saw a VDR from line to chassis in a competitor's component P/S - never
understood the reason for this construction.

 Is the VDR rating for 62368 conformity a working voltage or surge rating ?

 Brian


-

This message is from the IEEE Product Safety Engineering Society emc-pstc
discussion list. To post a message to the list, send your e-mail to
emc-p...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
http://product-compliance.oc.ieee.org/
Graphics (in well-used formats), large files, etc. can be posted to that URL.

Website:  http://www.ieee-pses.org/
Instructions:  http://listserv.ieee.org/request/user-guide.html
List rules: http://www.ieee-pses.org/listrules.html

For help, send mail to the list administrators:
Scott Douglas emcp...@radiusnorth.net
Mike Cantwell mcantw...@ieee.org

For policy questions, send mail to:
Jim Bacher:  j.bac...@ieee.org
David Heald: dhe...@gmail.com


RE: [PSES] IEC 60950-1 Ed. 2 Class A Pluggable equipment and VDR bridging basic insulation.

2010-12-15 Thread emc-p...@ieee.org
Hey Rich,

The reason for VDR's (MOV's) to ground is to prevent arcing to the
chassis for customers that demand either 6KV or 10KV lightning tests.
The products are permanently grounded so the arcing to ground is not a
safety hazard at those levels.  The products easily pass the hipot
without the MOV's to several KV (well above the hipot level).

The arcing at 6 or 10KV often functionally kills the supply or other
circuitry, which of course 60950 could not care less about
functionality.  But other standards do.

It sounds like IEC 62368 will mess up using MOV's to ground though as I
am not aware of MOV's rated several KV.

Best regards,

Jim
 
Jim Wiese
Senior Compliance Engineer
ADTRAN, Inc.
901 Explorer Blvd.
Huntsville, AL 35806
256-963-8431
256-714-5882 (cell)
256-963-6218 (fax)
jim.wi...@adtran.com
 

-Original Message-
From: Richard Nute [mailto:rn...@san.rr.com] 
Sent: Wednesday, December 15, 2010 2:01 PM
To: JIM WIESE
Cc: EMC-PSTC@LISTSERV.IEEE.ORG
Subject: Re: [PSES] IEC 60950-1 Ed. 2 Class A Pluggable equipment and
VDR bridging basic insulation.



Hi Jim:


Thanks for your remarks.

You CAN remove the VDR during hi-pot testing.
This is specified in 5.2.2:

 To avoid damage to components or insulation
 that are not involved in the test,
 disconnection of integrated circuits or the
 like and the use of equipotential bonding are
 permitted.

This is for the type test, not the routine
test.  Nevertheless, your point is well taken.

Also note that 5.2.1 specifies:

 The electric strength of the SOLID INSULATION
 used in the equipment shall be adequate.

So, the hi-pot test only applies to solid
insulation.

The other option is to specify the VDR at a higher
voltage than the hi-pot test voltage.

Regarding VDRs, I don't know why any equipment
would need a VDR between mains and earth.  The
requirements for clearance, creepage, and solid
insulations require an electric strength at least
as great as the expected transient overvoltage,
regardless whether a VDR is between mains and
earth or not.  So, the VDR does not protect
anything against any voltage up to the required
electric strength of the equipment.

The VDR *may* be useful to protect against
transient voltages exceeding the required electric
strength.n which case it will pass the hi-pot
test.

In the new IEC 62368, the requirement is that any
VDR between mains and earth shall be rated greater
than the required electric strength.


Best wishes for the Christmas season,
Rich






On 12/15/2010 11:27, JIM WIESE wrote:
 Rich,

 The issue we ran into with this is that UL and other NRTL's require
 factory hi-pot testing on AC interfaces as part of follow-up services.
 The product will obviously fail at that point.   The  original 60950-1
 safety testing is done with the VDR's removed.  But for the factory
 hi-pot the VDR's often cannot be removed without disassembly of the
 product, and even if they could be removed it violates the intent of
the
 test, which is to perform the factory hi-pot right before it is boxed
up
 for shipping, not rip it apart, do a hipot, and then re-assemble the
 product.

 As you point out the conditions necessary to allow the VDR's to ground
 in the first place already require the assumption that the VDR can go
 short and not create a hazard.

 So 60950-1 now allows the VDR's to ground, but the follow-up services
 and listing requirements for the factory hi-pot here in the US and
 Canada more or less prevent doing it.

 So, there should be some kind of waiver from the factory hi-pot if the
 product has VDR's to ground as permitted in 60950-1, but unless that
 happens it is silly to allow it in the UL/CSA version, unless people
 feel tearing a product apart to disable VDR's, then doing a hi-pot,
then
 reassembling the equipment makes sense.

 Best regards,

 Jim

 Jim Wiese
 Senior Compliance Engineer
 ADTRAN, Inc.
 901 Explorer Blvd.
 Huntsville, AL 35806
 256-963-8431
 256-714-5882 (cell)
 256-963-6218 (fax)
 jim.wi...@adtran.com



-

This message is from the IEEE Product Safety Engineering Society emc-pstc
discussion list. To post a message to the list, send your e-mail to
emc-p...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
http://product-compliance.oc.ieee.org/
Graphics (in well-used formats), large files, etc. can be posted to that URL.

Website:  http://www.ieee-pses.org/
Instructions:  http://listserv.ieee.org/request/user-guide.html
List rules: http://www.ieee-pses.org/listrules.html

For help, send mail to the list administrators:
Scott Douglas emcp...@radiusnorth.net
Mike Cantwell mcantw...@ieee.org

For policy questions, send mail to:
Jim Bacher:  j.bac...@ieee.org
David Heald: dhe...@gmail.com


RE: [PSES] IEC 60950-1 Ed. 2 Class A Pluggable equipment and VDR bridging basic insulation.

2010-12-15 Thread emc-p...@ieee.org
In EMC are testing to 2 kV surge.  But Brazil deemed our product telecom and
applied 4 kV.  A couple of our products spark and arc impressively and
continue running.  A couple of others quit, died, castors up, and the smoke
got out... (It fun when they do that!)  
EMC says it has to continue to work.  
Safety says it only has to fail safely.  
Engineering says fix it but don't change anything.
VDR between line and earth, 
and between line to line fixes it to 4 kV.
But I run right into the safety guy and all these notes, about pluggable,
single/double fused, screwed down earths, permanent connect, etc.


 Bill


In the event of a national emergency, 


click on the following links to provide directions to your duly elected
mis-representatives.

http://www.usa.gov/Contact/Elected.shtml
or...
https://writerep.house.gov/writerep/welcome.shtml
http://www.senate.gov/general/contact_information/senators_cfm.cfm

if really desperate...
http://www.usa.gov/Contact/Elected.shtml







--- On Wed, 12/15/10, Brian O'Connell oconne...@tamuracorp.com wrote:



From: Brian O'Connell oconne...@tamuracorp.com
Subject: RE: [PSES] IEC 60950-1 Ed. 2 Class A Pluggable equipment and 
VDR
bridging basic insulation.
To: EMC-PSTC@LISTSERV.IEEE.ORG
Date: Wednesday, December 15, 2010, 3:33 PM


The problem with the VDR being rated for a level 3 surge, which is
significantly greater than the typical test V for BI, is that the VDR will
typically start conducting long before required test voltage is reached.

Di-electric withstand and surge immunity are very different animals.

I saw a VDR from line to chassis in a competitor's component P/S - never
understood the reason for this construction.

Is the VDR rating for 62368 conformity a working voltage or surge 
rating ?

Brian 

 -Original Message-
 From: emc-p...@ieee.org [mailto:emc-p...@ieee.org]On Behalf 
 Of Richard
 Nute
 Sent: Wednesday, December 15, 2010 12:01 PM
 To: JIM WIESE
 Cc: EMC-PSTC@LISTSERV.IEEE.ORG
 Subject: Re: [PSES] IEC 60950-1 Ed. 2 Class A Pluggable equipment and
 VDR bridging basic insulation.
 
 
 Hi Jim:
 
 Thanks for your remarks.
 
 You CAN remove the VDR during hi-pot testing.
 This is specified in 5.2.2:
 
  To avoid damage to components or insulation
  that are not involved in the test,
  disconnection of integrated circuits or the
  like and the use of equipotential bonding are
  permitted.
 
 This is for the type test, not the routine
 test.  Nevertheless, your point is well taken.
 
 Also note that 5.2.1 specifies:
 
  The electric strength of the SOLID INSULATION
  used in the equipment shall be adequate.
 
 So, the hi-pot test only applies to solid
 insulation.
 
 The other option is to specify the VDR at a higher
 voltage than the hi-pot test voltage.
 
 Regarding VDRs, I don't know why any equipment
 would need a VDR between mains and earth.  The
 requirements for clearance, creepage, and solid
 insulations require an electric strength at least
 as great as the expected transient overvoltage,
 regardless whether a VDR is between mains and
 earth or not.  So, the VDR does not protect
 anything against any voltage up to the required
 electric strength of the equipment.
 
 The VDR *may* be useful to protect against
 transient voltages exceeding the required electric
 strength.n which case it will pass the hi-pot
 test.
 
 In the new IEC 62368, the requirement is that any
 VDR between mains and earth shall be rated greater
 than the required electric strength.
 
 
 Best wishes for the Christmas season,
 Rich

-

This message is from the IEEE Product Safety Engineering Society 
emc-pstc
discussion list. To post a message to the list, send your e-mail to
emc-p...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
http://product-compliance.oc.ieee.org/
Graphics (in well-used formats), large files, etc. can be posted to 
that URL.

Website:  http://www.ieee-pses.org/
Instructions:  http://listserv.ieee.org/request/user-guide.html
List rules: http://www.ieee-pses.org/listrules.html

For help, send mail to the list administrators:
Scott Douglas emcp...@radiusnorth.net
Mike Cantwell mcantw...@ieee.org

RE: [PSES] IEC 60950-1 Ed. 2 Class A Pluggable equipment and VDR bridging basic insulation.

2010-12-15 Thread emc-p...@ieee.org
The problem with the VDR being rated for a level 3 surge, which is
significantly greater than the typical test V for BI, is that the VDR will
typically start conducting long before required test voltage is reached.

Di-electric withstand and surge immunity are very different animals.

I saw a VDR from line to chassis in a competitor's component P/S - never
understood the reason for this construction.

Is the VDR rating for 62368 conformity a working voltage or surge rating ?

Brian 

  -Original Message-
  From: emc-p...@ieee.org [mailto:emc-p...@ieee.org]On Behalf 
  Of Richard
  Nute
  Sent: Wednesday, December 15, 2010 12:01 PM
  To: JIM WIESE
  Cc: EMC-PSTC@LISTSERV.IEEE.ORG
  Subject: Re: [PSES] IEC 60950-1 Ed. 2 Class A Pluggable equipment and
  VDR bridging basic insulation.
  
  
  Hi Jim:
  
  Thanks for your remarks.
  
  You CAN remove the VDR during hi-pot testing.
  This is specified in 5.2.2:
  
   To avoid damage to components or insulation
   that are not involved in the test,
   disconnection of integrated circuits or the
   like and the use of equipotential bonding are
   permitted.
  
  This is for the type test, not the routine
  test.  Nevertheless, your point is well taken.
  
  Also note that 5.2.1 specifies:
  
   The electric strength of the SOLID INSULATION
   used in the equipment shall be adequate.
  
  So, the hi-pot test only applies to solid
  insulation.
  
  The other option is to specify the VDR at a higher
  voltage than the hi-pot test voltage.
  
  Regarding VDRs, I don't know why any equipment
  would need a VDR between mains and earth.  The
  requirements for clearance, creepage, and solid
  insulations require an electric strength at least
  as great as the expected transient overvoltage,
  regardless whether a VDR is between mains and
  earth or not.  So, the VDR does not protect
  anything against any voltage up to the required
  electric strength of the equipment.
  
  The VDR *may* be useful to protect against
  transient voltages exceeding the required electric
  strength.n which case it will pass the hi-pot
  test.
  
  In the new IEC 62368, the requirement is that any
  VDR between mains and earth shall be rated greater
  than the required electric strength.
  
  
  Best wishes for the Christmas season,
  Rich

-

This message is from the IEEE Product Safety Engineering Society emc-pstc
discussion list. To post a message to the list, send your e-mail to
emc-p...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
http://product-compliance.oc.ieee.org/
Graphics (in well-used formats), large files, etc. can be posted to that URL.

Website:  http://www.ieee-pses.org/
Instructions:  http://listserv.ieee.org/request/user-guide.html
List rules: http://www.ieee-pses.org/listrules.html

For help, send mail to the list administrators:
Scott Douglas emcp...@radiusnorth.net
Mike Cantwell mcantw...@ieee.org

For policy questions, send mail to:
Jim Bacher:  j.bac...@ieee.org
David Heald: dhe...@gmail.com


Re: [PSES] IEC 60950-1 Ed. 2 Class A Pluggable equipment and VDR bridging basic insulation.

2010-12-15 Thread emc-p...@ieee.org
On 12/15/2010 11:41, Kunde, Brian wrote:
 Does it make VDRs safer to use them in series with a gas-tube like some
 do with Varistors?

Hi Brian:


Yes.

Today, this is the trend among manufacturers that
want to use a VDR between mains and earth.

And, TC108 is still trying to sort out the requirements
for both devices in such a circuit.


Best wishes for a Merry Christmas,
Rich

-

This message is from the IEEE Product Safety Engineering Society emc-pstc
discussion list. To post a message to the list, send your e-mail to
emc-p...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
http://product-compliance.oc.ieee.org/
Graphics (in well-used formats), large files, etc. can be posted to that URL.

Website:  http://www.ieee-pses.org/
Instructions:  http://listserv.ieee.org/request/user-guide.html
List rules: http://www.ieee-pses.org/listrules.html

For help, send mail to the list administrators:
Scott Douglas emcp...@radiusnorth.net
Mike Cantwell mcantw...@ieee.org

For policy questions, send mail to:
Jim Bacher:  j.bac...@ieee.org
David Heald: dhe...@gmail.com


Re: [PSES] IEC 60950-1 Ed. 2 Class A Pluggable equipment and VDR bridging basic insulation.

2010-12-15 Thread emc-p...@ieee.org
Hi Jim:


Thanks for your remarks.

You CAN remove the VDR during hi-pot testing.
This is specified in 5.2.2:

 To avoid damage to components or insulation
 that are not involved in the test,
 disconnection of integrated circuits or the
 like and the use of equipotential bonding are
 permitted.

This is for the type test, not the routine
test.  Nevertheless, your point is well taken.

Also note that 5.2.1 specifies:

 The electric strength of the SOLID INSULATION
 used in the equipment shall be adequate.

So, the hi-pot test only applies to solid
insulation.

The other option is to specify the VDR at a higher
voltage than the hi-pot test voltage.

Regarding VDRs, I don't know why any equipment
would need a VDR between mains and earth.  The
requirements for clearance, creepage, and solid
insulations require an electric strength at least
as great as the expected transient overvoltage,
regardless whether a VDR is between mains and
earth or not.  So, the VDR does not protect
anything against any voltage up to the required
electric strength of the equipment.

The VDR *may* be useful to protect against
transient voltages exceeding the required electric
strength.n which case it will pass the hi-pot
test.

In the new IEC 62368, the requirement is that any
VDR between mains and earth shall be rated greater
than the required electric strength.


Best wishes for the Christmas season,
Rich






On 12/15/2010 11:27, JIM WIESE wrote:
 Rich,

 The issue we ran into with this is that UL and other NRTL's require
 factory hi-pot testing on AC interfaces as part of follow-up services.
 The product will obviously fail at that point.   The  original 60950-1
 safety testing is done with the VDR's removed.  But for the factory
 hi-pot the VDR's often cannot be removed without disassembly of the
 product, and even if they could be removed it violates the intent of the
 test, which is to perform the factory hi-pot right before it is boxed up
 for shipping, not rip it apart, do a hipot, and then re-assemble the
 product.

 As you point out the conditions necessary to allow the VDR's to ground
 in the first place already require the assumption that the VDR can go
 short and not create a hazard.

 So 60950-1 now allows the VDR's to ground, but the follow-up services
 and listing requirements for the factory hi-pot here in the US and
 Canada more or less prevent doing it.

 So, there should be some kind of waiver from the factory hi-pot if the
 product has VDR's to ground as permitted in 60950-1, but unless that
 happens it is silly to allow it in the UL/CSA version, unless people
 feel tearing a product apart to disable VDR's, then doing a hi-pot, then
 reassembling the equipment makes sense.

 Best regards,

 Jim

 Jim Wiese
 Senior Compliance Engineer
 ADTRAN, Inc.
 901 Explorer Blvd.
 Huntsville, AL 35806
 256-963-8431
 256-714-5882 (cell)
 256-963-6218 (fax)
 jim.wi...@adtran.com



-

This message is from the IEEE Product Safety Engineering Society emc-pstc
discussion list. To post a message to the list, send your e-mail to
emc-p...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
http://product-compliance.oc.ieee.org/
Graphics (in well-used formats), large files, etc. can be posted to that URL.

Website:  http://www.ieee-pses.org/
Instructions:  http://listserv.ieee.org/request/user-guide.html
List rules: http://www.ieee-pses.org/listrules.html

For help, send mail to the list administrators:
Scott Douglas emcp...@radiusnorth.net
Mike Cantwell mcantw...@ieee.org

For policy questions, send mail to:
Jim Bacher:  j.bac...@ieee.org
David Heald: dhe...@gmail.com


RE: [PSES] IEC 60950-1 Ed. 2 Class A Pluggable equipment and VDR bridging basic insulation.

2010-12-15 Thread emc-p...@ieee.org
Does it make VDRs safer to use them in series with a gas-tube like some
do with Varistors?

I've never seen it done but I was told years ago that some companies
have a screw in the back of their products that connects the
chassis/earth ground connection to their surge suppression circuit. The
screw is removed to break the ground point during the hipot test, then
reinstalled after the test.

The Other Brian

-Original Message-
From: emc-p...@ieee.org [mailto:emc-p...@ieee.org] On Behalf Of JIM
WIESE
Sent: Wednesday, December 15, 2010 2:28 PM
To: ri...@ieee.org; EMC-PSTC@LISTSERV.IEEE.ORG
Subject: RE: [PSES] IEC 60950-1 Ed. 2 Class A Pluggable equipment and
VDR bridging basic insulation.

Rich,

The issue we ran into with this is that UL and other NRTL's require
factory hi-pot testing on AC interfaces as part of follow-up services.
The product will obviously fail at that point.   The  original 60950-1
safety testing is done with the VDR's removed.  But for the factory
hi-pot the VDR's often cannot be removed without disassembly of the
product, and even if they could be removed it violates the intent of the
test, which is to perform the factory hi-pot right before it is boxed up
for shipping, not rip it apart, do a hipot, and then re-assemble the
product.

As you point out the conditions necessary to allow the VDR's to ground
in the first place already require the assumption that the VDR can go
short and not create a hazard.

So 60950-1 now allows the VDR's to ground, but the follow-up services
and listing requirements for the factory hi-pot here in the US and
Canada more or less prevent doing it. 

So, there should be some kind of waiver from the factory hi-pot if the
product has VDR's to ground as permitted in 60950-1, but unless that
happens it is silly to allow it in the UL/CSA version, unless people
feel tearing a product apart to disable VDR's, then doing a hi-pot, then
reassembling the equipment makes sense.

Best regards,

Jim
 
Jim Wiese
Senior Compliance Engineer
ADTRAN, Inc.
901 Explorer Blvd.
Huntsville, AL 35806
256-963-8431
256-714-5882 (cell)
256-963-6218 (fax)
jim.wi...@adtran.com
 

-Original Message-
From: Richard Nute [mailto:rn...@san.rr.com] 
Sent: Wednesday, December 15, 2010 1:02 PM
To: EMC-PSTC@LISTSERV.IEEE.ORG
Subject: Re: [PSES] IEC 60950-1 Ed. 2 Class A Pluggable equipment and
VDR bridging basic insulation.

Hi Donald:


A VDR is taken as a device that is likely to
fail.

If the VDR is connected between mains and the
protective earthing system, then the PE system
must be considered reliable, that is, equivalent
to a reinforced safeguard.

Ever since the days of 2-wire plugs and sockets,
grounding by means of a domestic plug and socket
has not been considered reliable (because you
could not predict whether the installation was
2-wire or 2-wire plus ground).

In order to have a reliable ground, the ground
construction must be permanent or equivalent.
(Equivalent is taken as by means of industrial-
grade plug and socket schemes.)  1.5.9.4 specifies
the equivalent grounding schemes.

Yes, you are correct in that a VDR is not permitted
to be connected to earth (ground) in pluggable
equipment type A.


Best wishes for a Merry Christmas,
Richard Nute
Product Safety Consultant
San Diego








On 12/14/2010 14:20, Donald McElheran wrote:
 All:

 Under clause 1.5.9.4 Bridging of basic insulation by a VDR in the
 latest version of 60950-1

 Paragraph two:

 Equipment with such a VDR bridging insulation shall be one of the
 following:

   -   equipment that has the provision for a permanently
 connected PROTECTIVE EARTHING CONNECTOR and is provided with
 instructions for the installation of that conductor.


 This requirement appears to rule out the use of power supplies making
 use of earthed VDRs in their primary circuits, if used in Pluggable
 Equipment Type A if a separate earthing terminal is not provided.

 Could anyone confirm that this interpretion is correct and wether this
 was the intent of the committee.

 Donald McElheran
 Product Compliance Specialist
 Ross Video | Live Production Technology
 www.rossvideo.com
 +1 (613) 652-4886


-

This message is from the IEEE Product Safety Engineering Society
emc-pstc discussion list. To post a message to the list, send your
e-mail to emc-p...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
http://product-compliance.oc.ieee.org/
Graphics (in well-used formats), large files, etc. can be posted to that
URL.

Website:  http://www.ieee-pses.org/
Instructions:  http://listserv.ieee.org/request/user-guide.html
List rules: http://www.ieee-pses.org/listrules.html

For help, send mail to the list administrators:
Scott Douglas emcp...@radiusnorth.net
Mike Cantwell mcantw...@ieee.org

For policy questions, send mail to:
Jim Bacher:  j.bac...@ieee.org
David Heald: dhe...@gmail.com

RE: [PSES] IEC 60950-1 Ed. 2 Class A Pluggable equipment and VDR bridging basic insulation.

2010-12-15 Thread emc-p...@ieee.org
Rich,

The issue we ran into with this is that UL and other NRTL's require
factory hi-pot testing on AC interfaces as part of follow-up services.
The product will obviously fail at that point.   The  original 60950-1
safety testing is done with the VDR's removed.  But for the factory
hi-pot the VDR's often cannot be removed without disassembly of the
product, and even if they could be removed it violates the intent of the
test, which is to perform the factory hi-pot right before it is boxed up
for shipping, not rip it apart, do a hipot, and then re-assemble the
product.

As you point out the conditions necessary to allow the VDR's to ground
in the first place already require the assumption that the VDR can go
short and not create a hazard.

So 60950-1 now allows the VDR's to ground, but the follow-up services
and listing requirements for the factory hi-pot here in the US and
Canada more or less prevent doing it. 

So, there should be some kind of waiver from the factory hi-pot if the
product has VDR's to ground as permitted in 60950-1, but unless that
happens it is silly to allow it in the UL/CSA version, unless people
feel tearing a product apart to disable VDR's, then doing a hi-pot, then
reassembling the equipment makes sense.

Best regards,

Jim
 
Jim Wiese
Senior Compliance Engineer
ADTRAN, Inc.
901 Explorer Blvd.
Huntsville, AL 35806
256-963-8431
256-714-5882 (cell)
256-963-6218 (fax)
jim.wi...@adtran.com
 

-Original Message-
From: Richard Nute [mailto:rn...@san.rr.com] 
Sent: Wednesday, December 15, 2010 1:02 PM
To: EMC-PSTC@LISTSERV.IEEE.ORG
Subject: Re: [PSES] IEC 60950-1 Ed. 2 Class A Pluggable equipment and
VDR bridging basic insulation.

Hi Donald:


A VDR is taken as a device that is likely to
fail.

If the VDR is connected between mains and the
protective earthing system, then the PE system
must be considered reliable, that is, equivalent
to a reinforced safeguard.

Ever since the days of 2-wire plugs and sockets,
grounding by means of a domestic plug and socket
has not been considered reliable (because you
could not predict whether the installation was
2-wire or 2-wire plus ground).

In order to have a reliable ground, the ground
construction must be permanent or equivalent.
(Equivalent is taken as by means of industrial-
grade plug and socket schemes.)  1.5.9.4 specifies
the equivalent grounding schemes.

Yes, you are correct in that a VDR is not permitted
to be connected to earth (ground) in pluggable
equipment type A.


Best wishes for a Merry Christmas,
Richard Nute
Product Safety Consultant
San Diego








On 12/14/2010 14:20, Donald McElheran wrote:
 All:

 Under clause 1.5.9.4 Bridging of basic insulation by a VDR in the
 latest version of 60950-1

 Paragraph two:

 Equipment with such a VDR bridging insulation shall be one of the
 following:

   -   equipment that has the provision for a permanently
 connected PROTECTIVE EARTHING CONNECTOR and is provided with
 instructions for the installation of that conductor.


 This requirement appears to rule out the use of power supplies making
 use of earthed VDRs in their primary circuits, if used in Pluggable
 Equipment Type A if a separate earthing terminal is not provided.

 Could anyone confirm that this interpretion is correct and wether this
 was the intent of the committee.

 Donald McElheran
 Product Compliance Specialist
 Ross Video | Live Production Technology
 www.rossvideo.com
 +1 (613) 652-4886


-

This message is from the IEEE Product Safety Engineering Society
emc-pstc discussion list. To post a message to the list, send your
e-mail to emc-p...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
http://product-compliance.oc.ieee.org/
Graphics (in well-used formats), large files, etc. can be posted to that
URL.

Website:  http://www.ieee-pses.org/
Instructions:  http://listserv.ieee.org/request/user-guide.html
List rules: http://www.ieee-pses.org/listrules.html

For help, send mail to the list administrators:
Scott Douglas emcp...@radiusnorth.net
Mike Cantwell mcantw...@ieee.org

For policy questions, send mail to:
Jim Bacher:  j.bac...@ieee.org
David Heald: dhe...@gmail.com

-

This message is from the IEEE Product Safety Engineering Society emc-pstc
discussion list. To post a message to the list, send your e-mail to
emc-p...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
http://product-compliance.oc.ieee.org/
Graphics (in well-used formats), large files, etc. can be posted to that URL.

Website:  http://www.ieee-pses.org/
Instructions:  http://listserv.ieee.org/request/user-guide.html
List rules: http://www.ieee-pses.org/listrules.html

For help, send mail to the list administrators:
Scott Douglas emcp...@radiusnorth.net
Mike Cantwell mcantw...@ieee.org

For policy questions, send mail to:
Jim Bacher:  j.bac...@ieee.org
David

Re: IEC 60950-1 Ed. 2 Class A Pluggable equipment and VDR bridging basic insulation.

2010-12-15 Thread emc-p...@ieee.org
Hi Donald:


A VDR is taken as a device that is likely to
fail.

If the VDR is connected between mains and the
protective earthing system, then the PE system
must be considered reliable, that is, equivalent
to a reinforced safeguard.

Ever since the days of 2-wire plugs and sockets,
grounding by means of a domestic plug and socket
has not been considered reliable (because you
could not predict whether the installation was
2-wire or 2-wire plus ground).

In order to have a reliable ground, the ground
construction must be permanent or equivalent.
(Equivalent is taken as by means of industrial-
grade plug and socket schemes.)  1.5.9.4 specifies
the equivalent grounding schemes.

Yes, you are correct in that a VDR is not permitted
to be connected to earth (ground) in pluggable
equipment type A.


Best wishes for a Merry Christmas,
Richard Nute
Product Safety Consultant
San Diego








On 12/14/2010 14:20, Donald McElheran wrote:
 All:

 Under clause 1.5.9.4 Bridging of basic insulation by a VDR in the
 latest version of 60950-1

 Paragraph two:

 Equipment with such a VDR bridging insulation shall be one of the
 following:

   -   equipment that has the provision for a permanently
 connected PROTECTIVE EARTHING CONNECTOR and is provided with
 instructions for the installation of that conductor.


 This requirement appears to rule out the use of power supplies making
 use of earthed VDRs in their primary circuits, if used in Pluggable
 Equipment Type A if a separate earthing terminal is not provided.

 Could anyone confirm that this interpretion is correct and wether this
 was the intent of the committee.

 Donald McElheran
 Product Compliance Specialist
 Ross Video | Live Production Technology
 www.rossvideo.com
 +1 (613) 652-4886


-

This message is from the IEEE Product Safety Engineering Society emc-pstc
discussion list. To post a message to the list, send your e-mail to
emc-p...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
http://product-compliance.oc.ieee.org/
Graphics (in well-used formats), large files, etc. can be posted to that URL.

Website:  http://www.ieee-pses.org/
Instructions:  http://listserv.ieee.org/request/user-guide.html
List rules: http://www.ieee-pses.org/listrules.html

For help, send mail to the list administrators:
Scott Douglas emcp...@radiusnorth.net
Mike Cantwell mcantw...@ieee.org

For policy questions, send mail to:
Jim Bacher:  j.bac...@ieee.org
David Heald: dhe...@gmail.com


IEC 60950-1 Ed. 2 Class A Pluggable equipment and VDR bridging basic insulation.

2010-12-14 Thread emc-p...@ieee.org
All:

Under clause 1.5.9.4 Bridging of basic insulation by a VDR in the
latest version of 60950-1

Paragraph two:  

Equipment with such a VDR bridging insulation shall be one of the
following:

-   equipment that has the provision for a permanently
connected PROTECTIVE EARTHING CONNECTOR and is provided with
instructions for the installation of that conductor.


This requirement appears to rule out the use of power supplies making
use of earthed VDRs in their primary circuits, if used in Pluggable
Equipment Type A if a separate earthing terminal is not provided.

Could anyone confirm that this interpretion is correct and wether this
was the intent of the committee. 

Donald McElheran 
Product Compliance Specialist
Ross Video | Live Production Technology
www.rossvideo.com
+1 (613) 652-4886

-

This message is from the IEEE Product Safety Engineering Society emc-pstc
discussion list. To post a message to the list, send your e-mail to
emc-p...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
http://product-compliance.oc.ieee.org/
Graphics (in well-used formats), large files, etc. can be posted to that URL.

Website:  http://www.ieee-pses.org/
Instructions:  http://listserv.ieee.org/request/user-guide.html
List rules: http://www.ieee-pses.org/listrules.html

For help, send mail to the list administrators:
Scott Douglas emcp...@radiusnorth.net
Mike Cantwell mcantw...@ieee.org

For policy questions, send mail to:
Jim Bacher:  j.bac...@ieee.org
David Heald: dhe...@gmail.com