Same. We've started calling our initial $100k+ proposals the 'kiss of Death' since we tend to never hear from them again. It's a good way to weed out those who aren't willing to spend the time/capital on a system that will actually perform what they're asking (reliably!). On Fri, Sep 6, 2019 at 12:07 PM Ray wrote: > Here in Colorado, I've been called upon to do a few design bids for > these. I always charge a healthy design fee to eliminate the tire > kickers. You can spend quite a bit of time just characterizing the loads, > only to lose the client when they find out its going to be several hundred > thousand dollars. > > Ray Walters > Remote Solar > 303 505-8760 > > On 9/6/19 10:32 AM, Andrew wrote: > > Yeah these are for industrial cannabis operations that are starting to > spring up due to legalization..36” industrial greenhouse fans, pre > vegetation lighting, supplemental light and dehumidifiers… why they still > want to do it in the middle of the boonies with now power is beyond me.. > > > > Andrew Perkins > > Greenwired > > P: 707-923-2001 ext. 100 > > 1150 #1 Evergreen Rd > > Redway, CA 95560 > > www.greenwired.com > > [image: Description: signature] > > > > > > > > *From:* RE-wrenches [mailto:re-wrenches-boun...@lists.re-wrenches.org > ] *On Behalf Of * > palumbo1...@gmail.com > *Sent:* Thursday, September 05, 2019 7:48 PM > *To:* RE-wrenches > *Subject:* Re: [RE-wrenches] Large off-grid inverter/storage > > > > Is “25 Kw per hour” a real value? For us old school people there is kW and > they is kWh (kilowatt hours). I’m guessing that it is 25 kWh per average > day, or, about 750 KWh / month. > > Dave Palumbo > > Hyde Park, VT > > Sent from my iPhone > > > On Sep 5, 2019, at 5:15 PM, Andrew wrote: > > Hey Everyone, > > I have been recently been getting more and more inquiries > for some quite large off-grid sytems(25kw per hour) and seeing what you > guys have for suggestions on bigger inverters and storage systems? I could > do 2 triple stack Schneider’s and a bunch of HUPS industrial batteries but > it all just takes up so much space and I know there are some other > companies out there with package units. Thoughts? > > > > Andrew Perkins > > Greenwired > > P: 707-923-2001 ext. 100 > > 1150 #1 Evergreen Rd > > Redway, CA 95560 > > www.greenwired.com > > > > > > ___ > List sponsored by Redwood Alliance > > List Address: RE-wrenches@lists.re-wrenches.org > > Change listserver email address & settings: > http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org > > List-Archive: > http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html > > List rules & etiquette: > www.re-wrenches.org/etiquette.htm > > Check out or update participant bios: > www.members.re-wrenches.org > > > ___ > List sponsored by Redwood Alliance > > List Address: RE-wrenches@lists.re-wrenches.org > > Change listserver email address & > settings:http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org > > List-Archive: > http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html > > List rules & etiquette:www.re-wrenches.org/etiquette.htm > > Check out or update participant bios:www.members.re-wrenches.org > > ___ > List sponsored by Redwood Alliance > > List Address: RE-wrenches@lists.re-wrenches.org > > Change listserver email address & settings: > http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org > > List-Archive: > http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html > > List rules & etiquette: > www.re-wrenches.org/etiquette.htm > > Check out or update participant bios: > www.members.re-wrenches.org > > -- Loren Ortiz Technical PV Design Specialist - Commercial/Residential/Off-Grid lo...@cal-solar.com californiasolarco.com *Main: 530-274-3671 ext: 311 * *Fax: 530-274-7518* -- <https://californiasolarco.com/referral_form/> *Showroom located at: 149 E Main St. Grass Valley, CA 95945* ___ List sponsored by Redwood Alliance List Address: RE-wrenches@lists.re-wrenches.org Change listserver email address & settings: http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org List-Archive: http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html List rules & etiquette: www.re-wrenches.org/etiquette.htm Check out or update participant bios: www.members.re-wrenches.org
Re: [RE-wrenches] Large off-grid inverter/storage
Here in Colorado, I've been called upon to do a few design bids for these. I always charge a healthy design fee to eliminate the tire kickers. You can spend quite a bit of time just characterizing the loads, only to lose the client when they find out its going to be several hundred thousand dollars. Ray Walters Remote Solar 303 505-8760 On 9/6/19 10:32 AM, Andrew wrote: Yeah these are for industrial cannabis operations that are starting to spring up due to legalization..36” industrial greenhouse fans, pre vegetation lighting, supplemental light and dehumidifiers… why they still want to do it in the middle of the boonies with now power is beyond me.. Andrew Perkins Greenwired P: 707-923-2001 ext. 100 1150 #1 Evergreen Rd Redway, CA 95560 www.greenwired.com Description: signature *From:*RE-wrenches [mailto:re-wrenches-boun...@lists.re-wrenches.org] *On Behalf Of *palumbo1...@gmail.com *Sent:* Thursday, September 05, 2019 7:48 PM *To:* RE-wrenches *Subject:* Re: [RE-wrenches] Large off-grid inverter/storage Is “25 Kw per hour” a real value? For us old school people there is kW and they is kWh (kilowatt hours). I’m guessing that it is 25 kWh per average day, or, about 750 KWh / month. Dave Palumbo Hyde Park, VT Sent from my iPhone On Sep 5, 2019, at 5:15 PM, Andrew <mailto:and...@greenwired.com>> wrote: Hey Everyone, I have been recently been getting more and more inquiries for some quite large off-grid sytems(25kw per hour) and seeing what you guys have for suggestions on bigger inverters and storage systems? I could do 2 triple stack Schneider’s and a bunch of HUPS industrial batteries but it all just takes up so much space and I know there are some other companies out there with package units. Thoughts? Andrew Perkins Greenwired P: 707-923-2001 ext. 100 1150 #1 Evergreen Rd Redway, CA 95560 www.greenwired.com <http://www.greenwired.com> ___ List sponsored by Redwood Alliance List Address: RE-wrenches@lists.re-wrenches.org <mailto:RE-wrenches@lists.re-wrenches.org> Change listserver email address & settings: http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org List-Archive: http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html List rules & etiquette: www.re-wrenches.org/etiquette.htm <http://www.re-wrenches.org/etiquette.htm> Check out or update participant bios: www.members.re-wrenches.org <http://www.members.re-wrenches.org> ___ List sponsored by Redwood Alliance List Address: RE-wrenches@lists.re-wrenches.org Change listserver email address & settings: http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org List-Archive: http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html List rules & etiquette: www.re-wrenches.org/etiquette.htm Check out or update participant bios: www.members.re-wrenches.org ___ List sponsored by Redwood Alliance List Address: RE-wrenches@lists.re-wrenches.org Change listserver email address & settings: http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org List-Archive: http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html List rules & etiquette: www.re-wrenches.org/etiquette.htm Check out or update participant bios: www.members.re-wrenches.org
Re: [RE-wrenches] Large off-grid inverter/storage
Hi Andrew, Any phrase that includes “per hour” while describing power use, generation or storage in a RE system is probably a misnomer. Think about it: you could just as well say 25kW per second or per month. That’s because kW is a term that describes a rate or power, not a quantity of energy used or stored; kWh defines that. In our retail store I have heard this term hundreds of times. While I am describing the difference between Watts and Watt-Hours, which is typically the source of confusion, I ask, “Would you say that your car has a 200HP “per hour” engine?” No, you would just say 200HP because you are describing power. So, if you meant the combined loads require 25kW to operate, use that number to determine inverter or generator sizes. If you are describing 25kWh of energy use or storage, use that to determine power production and battery bank size. To your question: I am a fan of using Li-ion batteries for the long life, weight and space savings, no maintenance, much higher charge rates, fastest recharging, and the 40% reduction in the PV system size compared to LA storage. Plus you get battery protection and monitoring included. Since you never have to fully charge them, for offgrid use, the advantages are huge. For people making growing weeds, buy the best. Contact me off the list if you would like more understanding about Li battery storage. Larry Crutcher Starlight Solar Power Systems la...@starlightsolar.com On Sep 6, 2019, at 9:32 AM, Andrew wrote: Yeah these are for industrial cannabis operations that are starting to spring up due to legalization..36” industrial greenhouse fans, pre vegetation lighting, supplemental light and dehumidifiers… why they still want to do it in the middle of the boonies with now power is beyond me.. Andrew Perkins Greenwired P: 707-923-2001 ext. 100 1150 #1 Evergreen Rd Redway, CA 95560 On Sep 5, 2019, at 2:15 PM, Andrew wrote: Hey Everyone, I have been recently been getting more and more inquiries for some quite large off-grid sytems(25kw per hour) and seeing what you guys have for suggestions on bigger inverters and storage systems? I could do 2 triple stack Schneider’s and a bunch of HUPS industrial batteries but it all just takes up so much space and I know there are some other companies out there with package units. Thoughts? Andrew Perkins Greenwired P: 707-923-2001 ext. 100 1150 #1 Evergreen Rd Redway, CA 95560 ___ List sponsored by Redwood Alliance List Address: RE-wrenches@lists.re-wrenches.org Change listserver email address & settings: http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org List-Archive: http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html List rules & etiquette: www.re-wrenches.org/etiquette.htm Check out or update participant bios: www.members.re-wrenches.org
Re: [RE-wrenches] Large off-grid inverter/storage
Yeah these are for industrial cannabis operations that are starting to spring up due to legalization..36” industrial greenhouse fans, pre vegetation lighting, supplemental light and dehumidifiers… why they still want to do it in the middle of the boonies with now power is beyond me.. Andrew Perkins Greenwired P: 707-923-2001 ext. 100 1150 #1 Evergreen Rd Redway, CA 95560 www.greenwired.com Description: signature From: RE-wrenches [mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of palumbo1...@gmail.com Sent: Thursday, September 05, 2019 7:48 PM To: RE-wrenches Subject: Re: [RE-wrenches] Large off-grid inverter/storage Is “25 Kw per hour” a real value? For us old school people there is kW and they is kWh (kilowatt hours). I’m guessing that it is 25 kWh per average day, or, about 750 KWh / month. Dave Palumbo Hyde Park, VT Sent from my iPhone On Sep 5, 2019, at 5:15 PM, Andrew wrote: Hey Everyone, I have been recently been getting more and more inquiries for some quite large off-grid sytems(25kw per hour) and seeing what you guys have for suggestions on bigger inverters and storage systems? I could do 2 triple stack Schneider’s and a bunch of HUPS industrial batteries but it all just takes up so much space and I know there are some other companies out there with package units. Thoughts? Andrew Perkins Greenwired P: 707-923-2001 ext. 100 1150 #1 Evergreen Rd Redway, CA 95560 www.greenwired.com ___ List sponsored by Redwood Alliance List Address: RE-wrenches@lists.re-wrenches.org Change listserver email address & settings: http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org List-Archive: http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html List rules & etiquette: www.re-wrenches.org/etiquette.htm Check out or update participant bios: www.members.re-wrenches.org ___ List sponsored by Redwood Alliance List Address: RE-wrenches@lists.re-wrenches.org Change listserver email address & settings: http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org List-Archive: http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html List rules & etiquette: www.re-wrenches.org/etiquette.htm Check out or update participant bios: www.members.re-wrenches.org
Re: [RE-wrenches] Large off-grid inverter/storage
Last time I looked, victron was not UL and you needed 2 of them for split phase. Am I wrong? Dave Angelini Offgrid Solar "we go where powerlines don't" http://members.sti.net/offgridsolar/ [1] e-mail offgridso...@sti.net [2] text 209 813 0060 On Fri, 6 Sep 2019 07:17:32 -0400, Tump wrote: Victron has 10kW/120/100A pass thru, inverters and do your self a favor, buy individual 2 volt batteries. Cells DO GO BAD and replacing a cell in a HUPs battery is a CF. AND they really are a pain to install. On Sep 5, 2019, at 10:50 PM, David Katz wrote: The sentence "25KW per hour" does not make sense. Do they mean 25KWh per hour? That would be 600 KWh per day! That would require over 200KW of PV. David Katz On Thu, Sep 5, 2019 at 3:33 PM Dave Angelini Offgrid Solar wrote: I often find that numbers like 25KW per hour are just overblown and the rest of the Offgrid load power data is too high. Offgrid is all about the state of the art in not needing high power levels by using the best equipment available for the loads. One can't simply take a power bill from a utility and try to duplicate it offgrid. The loads have to be reduced drastically. Maybe this is not the case here and if so I digress. Good Luck Dave Angelini Offgrid Solar "we go where powerlines don't" http://members.sti.net/offgridsolar/ [5] e-mail offgridso...@sti.net [6] text 209 813 0060 On Thu, 5 Sep 2019 16:16:27 -0600, "Dana" wrote: You will have to park the 'Package' somewhere... Yeah off grid takes space & WLA batteries like to be warm in the winter ">Basements? Dedicated building? Storage container [insulated]? Radiant floors make for happy batteries. Cool in summer "> Dana Orzel Great Solar Works, Inc. C - 208.721.7003 Idaho Contractor - # 028765 Idaho PV # 028374 NABCEP # 051112-136 www.solarwork.com [8] "Responsible Technologies for Responsible People since 1988" P Please consider the environment before printing this email. FROM: RE-wrenches ON BEHALF OF Andrew SENT: Thursday, September 05, 2019 3:15 PM TO: RE-wrenches SUBJECT: [RE-wrenches] Large off-grid inverter/storage Hey Everyone, I have been recently been getting more and more inquiries for some quite large off-grid sytems(25kw per hour) and seeing what you guys have for suggestions on bigger inverters and storage systems? I could do 2 triple stack Schneider's and a bunch of HUPS industrial batteries but it all just takes up so much space and I know there are some other companies out there with package units. Thoughts? Andrew Perkins Greenwired P: 707-923-2001 ext. 100 1150 #1 Evergreen Rd Redway, CA 95560 www.greenwired.com [11] -- ___ List sponsored by Redwood Alliance List Address: RE-wrenches@lists.re-wrenches.org [12] Change listserver email address & settings: http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org [13] List-Archive: http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html [14] List rules & etiquette: www.re-wrenches.org/etiquette.htm [15] Check out or update participant bios: www.members.re-wrenches.org [16] -- David Katz Sent from Gmail Mobile ___ List sponsored by Redwood Alliance List Address: RE-wrenches@lists.re-wrenches.org [17] Change listserver email address & settings: http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org [18] List-Archive: http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html List rules border-left:#1010ff 2px solid; margin-left:5px; width:100%"> WWW.SWNL.NET [19] Solarwinds Northernlights _ _ _ SERVING MID COAST MAINE "> _ 207-832-7574 CL. 610-517-8401 _ _ __BLAIR "TUMP" MAY_ MAINE'S CHARTER _ __ NABCEP "CERTIFIED PV INSTALLER"_ MAINE'S CHARTER _ TRACE XANTREX "CERTIFIED" DEALER / INSTALLER"_ -- Links: -- [1] http://members.sti.net/offgridsolar/ [2] mailto:offgridso...@sti.net [3] mailto:dk...@backwoodssolar.com [4] mailto:offgridso...@sti.net [5] http://members.sti.net/offgridsolar/ [6] mailto:offgridso...@sti.net [7] mailto:d...@solarwork.com [8] http://www.solarwork.com/ [9] mailto:re-wrenches-boun...@lists.re-wrenches.org [10] mailto:re-wrenches@lists.re-wrenches.org [11] http://www.greenwired.com/ [12] mailto:RE-wrenches@lists.re-wrenches.org [13] http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org [14] http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html [15] http://www.re-wrenches.org/etiquette.htm [16] http://www.members.re-wrenches.org/ [17] mailto:RE-wrenches@lists.re-wrenches.org [18] http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org [19] http://webmail.sti.net/blocked::http://www.swnl
Re: [RE-wrenches] Large off-grid inverter/storage
Victron has 10kW/120/100A pass thru, inverters and do your self a favor, buy individual 2 volt batteries. Cells DO GO BAD and replacing a cell in a HUPs battery is a CF. AND they really are a pain to install. > On Sep 5, 2019, at 10:50 PM, David Katz wrote: > > The sentence “25KW per hour“ does not make sense. Do they mean 25KWh per > hour? That would be 600 KWh per day! That would require over 200KW of PV. > David Katz > > On Thu, Sep 5, 2019 at 3:33 PM Dave Angelini Offgrid Solar > mailto:offgridso...@sti.net>> wrote: > I often find that numbers like 25KW per hour are just overblown and the rest > of the Offgrid load power data is too high. > > Offgrid is all about the state of the art in not needing high power levels by > using the best equipment available for the loads. > > One can't simply take a power bill from a utility and try to duplicate it > offgrid. The loads have to be reduced drastically. > > Maybe this is not the case here and if so I digress. Good Luck > > Dave Angelini Offgrid Solar > "we go where powerlines don't" > http://members.sti.net/offgridsolar/ <http://members.sti.net/offgridsolar/> > e-mail offgridso...@sti.net <mailto:offgridso...@sti.net> > text 209 813 0060 > On Thu, 5 Sep 2019 16:16:27 -0600, "Dana" <mailto:d...@solarwork.com>> wrote: > >> You will have to park the ‘Package’ somewhere… Yeah off grid takes space & >> WLA batteries like to be warm in the winter & not too hot in the summer. >> >> Basements? Dedicated building? Storage container [insulated]? >> >> Radiant floors make for happy batteries. Cool in summer & warm in winter. >> >> >> >> >> Dana Orzel Great Solar Works, Inc. >> >> C - 208.721.7003 d...@solarwork.com >> <mailto:d...@solarwork.com> >> Idaho Contractor - # 028765 Idaho PV # 028374 >> >> NABCEP # 051112-136 www.solarwork.com >> <http://www.solarwork.com/> >> "Responsible Technologies for Responsible People since 1988" >> >> P Please consider the environment before printing this email. >> >> >> >> From: RE-wrenches > <mailto:re-wrenches-boun...@lists.re-wrenches.org>> On Behalf Of Andrew >> Sent: Thursday, September 05, 2019 3:15 PM >> To: RE-wrenches > <mailto:re-wrenches@lists.re-wrenches.org>> >> Subject: [RE-wrenches] Large off-grid inverter/storage >> >> >> Hey Everyone, >> >> I have been recently been getting more and more inquiries >> for some quite large off-grid sytems(25kw per hour) and seeing what you guys >> have for suggestions on bigger inverters and storage systems? I could do 2 >> triple stack Schneider’s and a bunch of HUPS industrial batteries but it all >> just takes up so much space and I know there are some other companies out >> there with package units. Thoughts? >> >> >> Andrew Perkins >> >> Greenwired >> >> P: 707-923-2001 ext. 100 >> >> 1150 #1 Evergreen Rd >> >> Redway, CA 95560 >> >> www.greenwired.com <http://www.greenwired.com/> >> >> >> > -- > > > ___ > List sponsored by Redwood Alliance > > List Address: RE-wrenches@lists.re-wrenches.org > <mailto:RE-wrenches@lists.re-wrenches.org> > > Change listserver email address & settings: > http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org > <http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org> > > List-Archive: > http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html > <http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html> > > List rules & etiquette: > www.re-wrenches.org/etiquette.htm <http://www.re-wrenches.org/etiquette.htm> > > Check out or update participant bios: > www.members.re-wrenches.org <http://www.members.re-wrenches.org/> > > -- > David Katz Sent from Gmail Mobile > ___ > List sponsored by Redwood Alliance > > List Address: RE-wrenches@lists.re-wrenches.org > > Change listserver email address & settings: > http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org > > List-Archive: > http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html > > List rules & etiquette: > www.re-wrenches.org/etiquette.htm > > Check out or update
Re: [RE-wrenches] Large off-grid inverter/storage
Is “25 Kw per hour” a real value? For us old school people there is kW and they is kWh (kilowatt hours). I’m guessing that it is 25 kWh per average day, or, about 750 KWh / month. Dave Palumbo Hyde Park, VT Sent from my iPhone > On Sep 5, 2019, at 5:15 PM, Andrew wrote: > > Hey Everyone, > I have been recently been getting more and more inquiries for > some quite large off-grid sytems(25kw per hour) and seeing what you guys have > for suggestions on bigger inverters and storage systems? I could do 2 triple > stack Schneider’s and a bunch of HUPS industrial batteries but it all just > takes up so much space and I know there are some other companies out there > with package units. Thoughts? > > Andrew Perkins > Greenwired > P: 707-923-2001 ext. 100 > 1150 #1 Evergreen Rd > Redway, CA 95560 > www.greenwired.com > > > ___ > List sponsored by Redwood Alliance > > List Address: RE-wrenches@lists.re-wrenches.org > > Change listserver email address & settings: > http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org > > List-Archive: > http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html > > List rules & etiquette: > www.re-wrenches.org/etiquette.htm > > Check out or update participant bios: > www.members.re-wrenches.org > ___ List sponsored by Redwood Alliance List Address: RE-wrenches@lists.re-wrenches.org Change listserver email address & settings: http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org List-Archive: http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html List rules & etiquette: www.re-wrenches.org/etiquette.htm Check out or update participant bios: www.members.re-wrenches.org
Re: [RE-wrenches] Large off-grid inverter/storage
I often find that numbers like 25KW per hour are just overblown and the rest of the Offgrid load power data is too high. Offgrid is all about the state of the art in not needing high power levels by using the best equipment available for the loads. One can't simply take a power bill from a utility and try to duplicate it offgrid. The loads have to be reduced drastically. Maybe this is not the case here and if so I digress. Good Luck Dave Angelini Offgrid Solar "we go where powerlines don't" http://members.sti.net/offgridsolar/ [1] e-mail offgridso...@sti.net [2] text 209 813 0060 On Thu, 5 Sep 2019 16:16:27 -0600, "Dana" wrote: You will have to park the 'Package' somewhere… Yeah off grid takes space & WLA batteries like to be warm in the winter ">Basements? Dedicated building? Storage container [insulated]? Radiant floors make for happy batteries. Cool in summer "> Dana Orzel Great Solar Works, Inc. C - 208.721.7003 d...@solarwork.com Idaho Contractor - # 028765 Idaho PV # 028374 NABCEP # 051112-136 www.solarwork.com [3] "Responsible Technologies for Responsible People since 1988" P Please consider the environment before printing this email. FROM: RE-wrenches ON BEHALF OF Andrew SENT: Thursday, September 05, 2019 3:15 PM TO: RE-wrenches SUBJECT: [RE-wrenches] Large off-grid inverter/storage Hey Everyone, I have been recently been getting more and more inquiries for some quite large off-grid sytems(25kw per hour) and seeing what you guys have for suggestions on bigger inverters and storage systems? I could do 2 triple stack Schneider's and a bunch of HUPS industrial batteries but it all just takes up so much space and I know there are some other companies out there with package units. Thoughts? Andrew Perkins Greenwired P: 707-923-2001 ext. 100 1150 #1 Evergreen Rd Redway, CA 95560 www.greenwired.com [4] -- Links: -- [1] http://members.sti.net/offgridsolar/ [2] mailto:offgridso...@sti.net [3] http://www.solarwork.com [4] http://www.greenwired.com ___ List sponsored by Redwood Alliance List Address: RE-wrenches@lists.re-wrenches.org Change listserver email address & settings: http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org List-Archive: http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html List rules & etiquette: www.re-wrenches.org/etiquette.htm Check out or update participant bios: www.members.re-wrenches.org
[RE-wrenches] Large off-grid inverter/storage
You will have to park the 'Package' somewhere. Yeah off grid takes space & WLA batteries like to be warm in the winter & not too hot in the summer. Basements? Dedicated building? Storage container [insulated]? Radiant floors make for happy batteries. Cool in summer & warm in winter. Dana Orzel Great Solar Works, Inc. C - 208.721.7003 d...@solarwork.com Idaho Contractor - # 028765 Idaho PV # 028374 NABCEP # 051112-136<http://www.solarwork.com> www.solarwork.com "Responsible Technologies for Responsible People since 1988" P Please consider the environment before printing this email. From: RE-wrenches On Behalf Of Andrew Sent: Thursday, September 05, 2019 3:15 PM To: RE-wrenches Subject: [RE-wrenches] Large off-grid inverter/storage Hey Everyone, I have been recently been getting more and more inquiries for some quite large off-grid sytems(25kw per hour) and seeing what you guys have for suggestions on bigger inverters and storage systems? I could do 2 triple stack Schneider's and a bunch of HUPS industrial batteries but it all just takes up so much space and I know there are some other companies out there with package units. Thoughts? Andrew Perkins Greenwired P: 707-923-2001 ext. 100 1150 #1 Evergreen Rd Redway, CA 95560 www.greenwired.com <http://www.greenwired.com> ___ List sponsored by Redwood Alliance List Address: RE-wrenches@lists.re-wrenches.org Change listserver email address & settings: http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org List-Archive: http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html List rules & etiquette: www.re-wrenches.org/etiquette.htm Check out or update participant bios: www.members.re-wrenches.org
[RE-wrenches] Large off-grid inverter/storage
Hey Everyone, I have been recently been getting more and more inquiries for some quite large off-grid sytems(25kw per hour) and seeing what you guys have for suggestions on bigger inverters and storage systems? I could do 2 triple stack Schneider's and a bunch of HUPS industrial batteries but it all just takes up so much space and I know there are some other companies out there with package units. Thoughts? Andrew Perkins Greenwired P: 707-923-2001 ext. 100 1150 #1 Evergreen Rd Redway, CA 95560 www.greenwired.com Description: signature ___ List sponsored by Redwood Alliance List Address: RE-wrenches@lists.re-wrenches.org Change listserver email address & settings: http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org List-Archive: http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html List rules & etiquette: www.re-wrenches.org/etiquette.htm Check out or update participant bios: www.members.re-wrenches.org
Re: [RE-wrenches] Large Off Grid Inverter?
I must have missed this in your post! https://solar.schneider-electric.com/solution/centralised-solar-power-plants-1500v/ You can navigate to their engineering team. I have found that once you have a case number you communicate easily with e-mail. --Dave > I appreciate everyone's replies so far. First, we already have an > electronic soft start control, it just needs to be reprogrammed to > reduce the starting surge more. Second, we are way beyond 48v land. We > are in the realm of commercial scale inverters of at least 500 kW to 1.5 > MW. They will be running at 600 vdc min and probably 1500 v range. > Output is 480v 3 phase. > > When I mentioned SMA, it was not their Sunny Island, its their larger > scale Grid tie equipment syncing to a generator. > > https://www.sma-america.com/industrial-systems/pv-diesel-hybrid-applications.html > > Most of the inverters we are looking at are primarily being used with > batteries for peak shaving to reduce demand charges on grid. Some, such > as Dynapower can work off grid, but I am not finding evidence that > anyone has much real life field experience off grid. Princeton Power > has their 100 kW inverter in Haiti forming a micro-grid, but I have very > few details at the moment. > > Even if your experience with these large battery inverters is just on > grid, I'd love to hear about it. Offline is fine, if its not all good > news. > > Thanks, > > Ray Walters > > Remote Solar > > > On 4/26/18 5:23 PM, Kevin Pegg wrote: >> Hello Ray, >> >> I have a couple 60/100 kW SMA Sunny Island systems out there, systems >> with 100 kW generators, 400 kWh battery banks and generally token >> renewable inputs. I feel with this configuration we close maxing out >> what can be done with 48VDC. >> >> Getting into the MW scale scares me to be honest. I think that will be >> well beyond what can be handled at 48VDC and is well beyond capacity of >> the SMA systems. Really need to look into higher DC voltages to handle >> this kind of current. >> >> If this was my client I would first look to the loads and see if there >> are any alternatives to the 250 HP motor. I have learned there are often >> massive levels of engineering overkill in the industrial world. What is >> the duty cycle of that motor, what does it do, etc? Would they be better >> to go directly diesel for that? >> >> In terms of system designs I'd investigate a direct diesel/PV interface >> skipping battery storage. Perhaps a group of 250 kW synchronized >> generators that can ramp up/down based on demand. Perhaps similar tech >> to what Tesla is doing in Australia. >> >> Kevin >> >> >> -Original Message- >> From: RE-wrenches [mailto:re-wrenches-boun...@lists.re-wrenches.org] On >> Behalf Of Ray >> Sent: April-25-18 12:37 PM >> To: RE-wrenches <re-wrenches@lists.re-wrenches.org> >> Subject: [RE-wrenches] Large Off Grid Inverter? >> >> Greetings Fellow Wrenches; >> >> We are consulting on a power system for a large off grid facility that >> is currently operating on a 1500 kW gen set. The loads are enormous >> for normal off grid: in the neighborhood of 600 amps continuous at 480 v >> 3 phase. Surges are close to 2000 amps, but we are working on control >> programming to bring that number down substantially. That is due >> primarily to a 250 Hp motor start. (that's not a typo!). EPA and local >> regulations are dictating that the current generator be retired in the >> near future. Grid power is a possibility, but we need to offer a >> viable off grid option as well. >> >> My question to the group: does anyone have real off grid experience with >> large format battery based inverters?  I've heard of some micro-grid >> systems running in Haiti on Princeton Power inverters, and Dynapower has >> a 250 kW inverter that has a "grid forming" mode. As we all know, it >> is easier to make claims in spec sheets than to deliver hard motor >> starting power in a remote location. We need proven products, with a >> track record of reliability. >> >> We are considering SMA type systems that use AC coupled PV to offset >> fuel consumption of a generator, but those seem dependent on the >> generator to maintain the stability of the micro grid during hard >> starting loads. Ideally we would want to reduce the generator run time >> to under 200 hrs/ yr and reduce its size to 500 kW. We have excellent >> solar resources year round, and the possibility of limiting operations >> during cloudy weather to meet these goals. >> >&g
[RE-wrenches] Large Off Grid Inverter?
There are many large 250kw to multi mw battery based inverters that should cover this project. Most are coming out of china, so I don’t know if UL is something they have. Princeton is one here in the USA, looks like 250kw and 500kwh is their largest on the web site. Sun Grow is one of many out of china. Most of these are using 600-1500vdc lithium battery banks, 50kw 1000v-1500v CC etc. A whole new ball game. There are also 50-75 kw units as well, I think the days of larger cluster inverter systems is coming to an end. The advantages of higher voltage battery banks is just too good not to use. jay peltz power ___ List sponsored by Redwood Alliance List Address: RE-wrenches@lists.re-wrenches.org Change listserver email address & settings: http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org List-Archive: http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html List rules & etiquette: www.re-wrenches.org/etiquette.htm Check out or update participant bios: www.members.re-wrenches.org
Re: [RE-wrenches] Large Off Grid Inverter?
I appreciate everyone's replies so far. First, we already have an electronic soft start control, it just needs to be reprogrammed to reduce the starting surge more. Second, we are way beyond 48v land. We are in the realm of commercial scale inverters of at least 500 kW to 1.5 MW. They will be running at 600 vdc min and probably 1500 v range. Output is 480v 3 phase. When I mentioned SMA, it was not their Sunny Island, its their larger scale Grid tie equipment syncing to a generator. https://www.sma-america.com/industrial-systems/pv-diesel-hybrid-applications.html Most of the inverters we are looking at are primarily being used with batteries for peak shaving to reduce demand charges on grid. Some, such as Dynapower can work off grid, but I am not finding evidence that anyone has much real life field experience off grid. Princeton Power has their 100 kW inverter in Haiti forming a micro-grid, but I have very few details at the moment. Even if your experience with these large battery inverters is just on grid, I'd love to hear about it. Offline is fine, if its not all good news. Thanks, Ray Walters Remote Solar On 4/26/18 5:23 PM, Kevin Pegg wrote: Hello Ray, I have a couple 60/100 kW SMA Sunny Island systems out there, systems with 100 kW generators, 400 kWh battery banks and generally token renewable inputs. I feel with this configuration we close maxing out what can be done with 48VDC. Getting into the MW scale scares me to be honest. I think that will be well beyond what can be handled at 48VDC and is well beyond capacity of the SMA systems. Really need to look into higher DC voltages to handle this kind of current. If this was my client I would first look to the loads and see if there are any alternatives to the 250 HP motor. I have learned there are often massive levels of engineering overkill in the industrial world. What is the duty cycle of that motor, what does it do, etc? Would they be better to go directly diesel for that? In terms of system designs I'd investigate a direct diesel/PV interface skipping battery storage. Perhaps a group of 250 kW synchronized generators that can ramp up/down based on demand. Perhaps similar tech to what Tesla is doing in Australia. Kevin -Original Message- From: RE-wrenches [mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Ray Sent: April-25-18 12:37 PM To: RE-wrenches <re-wrenches@lists.re-wrenches.org> Subject: [RE-wrenches] Large Off Grid Inverter? Greetings Fellow Wrenches; We are consulting on a power system for a large off grid facility that is currently operating on a 1500 kW gen set. The loads are enormous for normal off grid: in the neighborhood of 600 amps continuous at 480 v 3 phase. Surges are close to 2000 amps, but we are working on control programming to bring that number down substantially. That is due primarily to a 250 Hp motor start. (that's not a typo!). EPA and local regulations are dictating that the current generator be retired in the near future. Grid power is a possibility, but we need to offer a viable off grid option as well. My question to the group: does anyone have real off grid experience with large format battery based inverters? I've heard of some micro-grid systems running in Haiti on Princeton Power inverters, and Dynapower has a 250 kW inverter that has a "grid forming" mode. As we all know, it is easier to make claims in spec sheets than to deliver hard motor starting power in a remote location. We need proven products, with a track record of reliability. We are considering SMA type systems that use AC coupled PV to offset fuel consumption of a generator, but those seem dependent on the generator to maintain the stability of the micro grid during hard starting loads. Ideally we would want to reduce the generator run time to under 200 hrs/ yr and reduce its size to 500 kW. We have excellent solar resources year round, and the possibility of limiting operations during cloudy weather to meet these goals. Thanks, Ray Walters Remote Solar ___ List sponsored by Redwood Alliance List Address: RE-wrenches@lists.re-wrenches.org Change listserver email address & settings: http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org List-Archive: http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html List rules & etiquette: www.re-wrenches.org/etiquette.htm Check out or update participant bios: www.members.re-wrenches.org ___ List sponsored by Redwood Alliance List Address: RE-wrenches@lists.re-wrenches.org Change listserver email address & settings: http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org List-Archive: http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html List rules & etiquette: www.re-wrenches.org/etiquette.htm Chec
Re: [RE-wrenches] Large Off Grid Inverter?
I know Schneider would love to sell you their cluster of 15 XW6848+ for a max of 102KW and probably well over 300KW of surge. Here is a link to their commercial offgrid. I do own their stock and other companies also :) Their commercial engineers are pretty smart about this. https://solar.schneider-electric.com/solution/commercial-off-grid-solar-2/ This does sound like a challenge and keep us informed on what you do please! Good Luck! --Dave > Hello Ray, > > I have a couple 60/100 kW SMA Sunny Island systems out there, systems with > 100 kW generators, 400 kWh battery banks and generally token renewable > inputs. I feel with this configuration we close maxing out what can be > done with 48VDC. > > Getting into the MW scale scares me to be honest. I think that will be > well beyond what can be handled at 48VDC and is well beyond capacity of > the SMA systems. Really need to look into higher DC voltages to handle > this kind of current. > > If this was my client I would first look to the loads and see if there are > any alternatives to the 250 HP motor. I have learned there are often > massive levels of engineering overkill in the industrial world. What is > the duty cycle of that motor, what does it do, etc? Would they be better > to go directly diesel for that? > > In terms of system designs I'd investigate a direct diesel/PV interface > skipping battery storage. Perhaps a group of 250 kW synchronized > generators that can ramp up/down based on demand. Perhaps similar tech to > what Tesla is doing in Australia. > > Kevin > > > -Original Message- > From: RE-wrenches [mailto:re-wrenches-boun...@lists.re-wrenches.org] On > Behalf Of Ray > Sent: April-25-18 12:37 PM > To: RE-wrenches <re-wrenches@lists.re-wrenches.org> > Subject: [RE-wrenches] Large Off Grid Inverter? > > Greetings Fellow Wrenches; > > We are consulting on a power system for a large off grid facility that is > currently operating on a 1500 kW gen set. The loads are enormous for > normal off grid: in the neighborhood of 600 amps continuous at 480 v 3 > phase. Surges are close to 2000 amps, but we are working on control > programming to bring that number down substantially. That is due > primarily to a 250 Hp motor start. (that's not a typo!). EPA and local > regulations are dictating that the current generator be retired in the > near future. Grid power is a possibility, but we need to offer a viable > off grid option as well. > > My question to the group: does anyone have real off grid experience with > large format battery based inverters?  I've heard of some micro-grid > systems running in Haiti on Princeton Power inverters, and Dynapower has a > 250 kW inverter that has a "grid forming" mode. As we all know, it is > easier to make claims in spec sheets than to deliver hard motor starting > power in a remote location. We need proven products, with a track record > of reliability. > > We are considering SMA type systems that use AC coupled PV to offset fuel > consumption of a generator, but those seem dependent on the generator to > maintain the stability of the micro grid during hard starting loads. > Ideally we would want to reduce the generator run time to under 200 hrs/ > yr and reduce its size to 500 kW. We have excellent solar resources year > round, and the possibility of limiting operations during cloudy weather > to meet these goals. > > Thanks, > > Ray Walters > > Remote Solar > > ___ > List sponsored by Redwood Alliance > > List Address: RE-wrenches@lists.re-wrenches.org > > Change listserver email address & settings: > http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org > > List-Archive: > http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html > > List rules & etiquette: > www.re-wrenches.org/etiquette.htm > > Check out or update participant bios: > www.members.re-wrenches.org > > ___ > List sponsored by Redwood Alliance > > List Address: RE-wrenches@lists.re-wrenches.org > > Change listserver email address & settings: > http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org > > List-Archive: > http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html > > List rules & etiquette: > www.re-wrenches.org/etiquette.htm > > Check out or update participant bios: > www.members.re-wrenches.org > > Dave Angelini Offgrid Solar "we go where powerlines don't" http://members.sti.net/offgridsolar/ e-mail offgridso...@sti.net text 209 813 0060 ___ List sponsored by Red
Re: [RE-wrenches] Large Off Grid Inverter?
Try a three phase soft starter. Programmable start ramp time with relay bypass. Not as expensive as a full blown VFD. Frank BZP. On 4/26/2018 9:17 AM, Dave Angelini Offgrid Solar wrote: Agree with Daryl here at the end. You have to solve the motor surge with variable frequency drive and go 3 phase. If there is a reasonable cost to use the grid I would not even bother with quoting an off the grid solution. It is what the grid is best at and batteries are the wrong way for this. Dave Angelini Offgrid Solar "we go where powerlines don't" http://members.sti.net/offgridsolar/ e-mail offgridso...@sti.net text 209 813 0060 you have a problem that is much bigger than I work on. But on a large motor heavy starting loads problem, we used an extra capacitor on the DC bus of the frequency drive. the drive on its own greatly reduced the start surge, if the load can be started slowly. If the motor must ramp up quickly the voltage would drop and the capacitor reduced the bump on the line. This was a few years ago but we put a 200 HP drive on a 100 HP motor and added the extra capacitor. Another trick on a different job was to run a 3 phase motor with a flywheel and start this motor slowly when the motor that had to start rapidly the running motor acts as a frequency stabilizer and dumps it energy into the rapidly starting motor. again this was maybe 15 years ago. these kluge solutions were applied when the inverter could in no way handle the surge and would kick the inverter off the line. Another solution used by Catipiller they had a unit that could give 3000 amps 480 v0lts for I think 30 seconds running a motor as a flywheel for UPS giving the generator set time to start. Check with Catapiller. again another project we clutched the running motor to the load to start the load fast and not have to face starting current. One last comment we had a 5000 HP motor to start a very heavy load, this motor had a hydraulic coupling that filled with oil to control the motor load. But I think a speed drive is more practical. And there are regen drives also. There are some other kluges that can be applied, good luck, sorry if this is of no value. On Wed, Apr 25, 2018 at 2:36 PM, Raywrote: Greetings Fellow Wrenches; We are consulting on a power system for a large off grid facility that is currently operating on a 1500 kW gen set. The loads are enormous for normal off grid: in the neighborhood of 600 amps continuous at 480 v 3 phase. Surges are close to 2000 amps, but we are working on control programming to bring that number down substantially. That is due primarily to a 250 Hp motor start. (that's not a typo!). EPA and local regulations are dictating that the current generator be retired in the near future. Grid power is a possibility, but we need to offer a viable off grid option as well. My question to the group: does anyone have real off grid experience with large format battery based inverters? I've heard of some micro-grid systems running in Haiti on Princeton Power inverters, and Dynapower has a 250 kW inverter that has a "grid forming" mode. As we all know, it is easier to make claims in spec sheets than to deliver hard motor starting power in a remote location. We need proven products, with a track record of reliability. We are considering SMA type systems that use AC coupled PV to offset fuel consumption of a generator, but those seem dependent on the generator to maintain the stability of the micro grid during hard starting loads. Ideally we would want to reduce the generator run time to under 200 hrs/ yr and reduce its size to 500 kW. We have excellent solar resources year round, and the possibility of limiting operations during cloudy weather to meet these goals. Thanks, Ray Walters Remote Solar ___ List sponsored by Redwood Alliance List Address: RE-wrenches@lists.re-wrenches.org Change listserver email address & settings: http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org List-Archive: http://www.mail-archive.com/re-wrenches@lists.re-wrenches.or g/maillist.html List rules & etiquette: www.re-wrenches.org/etiquette.htm Check out or update participant bios: www.members.re-wrenches.org ___ List sponsored by Redwood Alliance List Address: RE-wrenches@lists.re-wrenches.org Change listserver email address & settings: http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org List-Archive: http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html List rules & etiquette: www.re-wrenches.org/etiquette.htm Check out or update participant bios: www.members.re-wrenches.org ___ List sponsored by Redwood Alliance List Address: RE-wrenches@lists.re-wrenches.org Change listserver email address & settings:
Re: [RE-wrenches] Large Off Grid Inverter?
Hello Ray, I have a couple 60/100 kW SMA Sunny Island systems out there, systems with 100 kW generators, 400 kWh battery banks and generally token renewable inputs. I feel with this configuration we close maxing out what can be done with 48VDC. Getting into the MW scale scares me to be honest. I think that will be well beyond what can be handled at 48VDC and is well beyond capacity of the SMA systems. Really need to look into higher DC voltages to handle this kind of current. If this was my client I would first look to the loads and see if there are any alternatives to the 250 HP motor. I have learned there are often massive levels of engineering overkill in the industrial world. What is the duty cycle of that motor, what does it do, etc? Would they be better to go directly diesel for that? In terms of system designs I'd investigate a direct diesel/PV interface skipping battery storage. Perhaps a group of 250 kW synchronized generators that can ramp up/down based on demand. Perhaps similar tech to what Tesla is doing in Australia. Kevin -Original Message- From: RE-wrenches [mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Ray Sent: April-25-18 12:37 PM To: RE-wrenches <re-wrenches@lists.re-wrenches.org> Subject: [RE-wrenches] Large Off Grid Inverter? Greetings Fellow Wrenches; We are consulting on a power system for a large off grid facility that is currently operating on a 1500 kW gen set. The loads are enormous for normal off grid: in the neighborhood of 600 amps continuous at 480 v 3 phase. Surges are close to 2000 amps, but we are working on control programming to bring that number down substantially. That is due primarily to a 250 Hp motor start. (that's not a typo!). EPA and local regulations are dictating that the current generator be retired in the near future. Grid power is a possibility, but we need to offer a viable off grid option as well. My question to the group: does anyone have real off grid experience with large format battery based inverters? I've heard of some micro-grid systems running in Haiti on Princeton Power inverters, and Dynapower has a 250 kW inverter that has a "grid forming" mode. As we all know, it is easier to make claims in spec sheets than to deliver hard motor starting power in a remote location. We need proven products, with a track record of reliability. We are considering SMA type systems that use AC coupled PV to offset fuel consumption of a generator, but those seem dependent on the generator to maintain the stability of the micro grid during hard starting loads. Ideally we would want to reduce the generator run time to under 200 hrs/ yr and reduce its size to 500 kW. We have excellent solar resources year round, and the possibility of limiting operations during cloudy weather to meet these goals. Thanks, Ray Walters Remote Solar ___ List sponsored by Redwood Alliance List Address: RE-wrenches@lists.re-wrenches.org Change listserver email address & settings: http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org List-Archive: http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html List rules & etiquette: www.re-wrenches.org/etiquette.htm Check out or update participant bios: www.members.re-wrenches.org ___ List sponsored by Redwood Alliance List Address: RE-wrenches@lists.re-wrenches.org Change listserver email address & settings: http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org List-Archive: http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html List rules & etiquette: www.re-wrenches.org/etiquette.htm Check out or update participant bios: www.members.re-wrenches.org
[RE-wrenches] Large off grid inverter
A tough assignment, but Daryl has the right idea. A company I used to work for did large off grid systems and would use something they called a rotary capacitor (or something like that). It was a large induction motor paralleled into the grid. It had a DC pony motor and some synchro hardware/software. The DC motor would run it up to synchronous speed and the contactors would bring it online. It would just sit there idling, drawing just enough to overcome friction and windage. When some big reactive load hit the grid it would smooth out the wobble in the waveform. If the functional motor in question doesn’t start under load, you might consider a DC pony motor to bring it up to synchro RPM before closing the main contactors. Good luck! Hilton Dier III Renewable Energy Design Missisquoi River Hydro LLC ___ List sponsored by Redwood Alliance List Address: RE-wrenches@lists.re-wrenches.org Change listserver email address & settings: http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org List-Archive: http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html List rules & etiquette: www.re-wrenches.org/etiquette.htm Check out or update participant bios: www.members.re-wrenches.org
Re: [RE-wrenches] Large Off Grid Inverter?
We're not too worried about reducing the surge at this point; the existing soft start controller is currently programmed for a fast start, because their electrician was worried about motor damage if the controller was set to limit current. It is currently surging to 700% of run current, so we should be able to easily bring that down to 200% with some programming. We just need to convince them that the motor will not be damaged. It will only see one start/ day. Grid is 3 miles away, but they may be required to suspend their operations for months or years, while all the necessary studies, easements, and approvals are obtained. Also, in this case, there is a strong incentive from their management to try off grid, as they have other operations that they want to wean off of gen-sets that will never have grid. I agree with both of you, and suggested the grid option first. With the right technology, we could use PV and battery storage off grid, then once grid power is available, go to a GT system with the battery storage used to reduce demand charges. I still haven't heard from anyone here that has actually done large scale (over 100kW) inverters off grid. I don't want to spec the next Studebaker of solar. Thanks everyone for your help, Ray On 4/26/18 8:17 AM, Dave Angelini Offgrid Solar wrote: Agree with Daryl here at the end. You have to solve the motor surge with variable frequency drive and go 3 phase. If there is a reasonable cost to use the grid I would not even bother with quoting an off the grid solution. It is what the grid is best at and batteries are the wrong way for this. Dave Angelini Offgrid Solar "we go where powerlines don't" http://members.sti.net/offgridsolar/ e-mail offgridso...@sti.net text 209 813 0060 you have a problem that is much bigger than I work on. But on a large motor heavy starting loads problem, we used an extra capacitor on the DC bus of the frequency drive. the drive on its own greatly reduced the start surge, if the load can be started slowly. If the motor must ramp up quickly the voltage would drop and the capacitor reduced the bump on the line. This was a few years ago but we put a 200 HP drive on a 100 HP motor and added the extra capacitor. Another trick on a different job was to run a 3 phase motor with a flywheel and start this motor slowly when the motor that had to start rapidly the running motor acts as a frequency stabilizer and dumps it energy into the rapidly starting motor. again this was maybe 15 years ago. these kluge solutions were applied when the inverter could in no way handle the surge and would kick the inverter off the line. Another solution used by Catipiller they had a unit that could give 3000 amps 480 v0lts for I think 30 seconds running a motor as a flywheel for UPS giving the generator set time to start. Check with Catapiller. again another project we clutched the running motor to the load to start the load fast and not have to face starting current. One last comment we had a 5000 HP motor to start a very heavy load, this motor had a hydraulic coupling that filled with oil to control the motor load. But I think a speed drive is more practical. And there are regen drives also. There are some other kluges that can be applied, good luck, sorry if this is of no value. On Wed, Apr 25, 2018 at 2:36 PM, Raywrote: Greetings Fellow Wrenches; We are consulting on a power system for a large off grid facility that is currently operating on a 1500 kW gen set. The loads are enormous for normal off grid: in the neighborhood of 600 amps continuous at 480 v 3 phase. Surges are close to 2000 amps, but we are working on control programming to bring that number down substantially. That is due primarily to a 250 Hp motor start. (that's not a typo!). EPA and local regulations are dictating that the current generator be retired in the near future. Grid power is a possibility, but we need to offer a viable off grid option as well. My question to the group: does anyone have real off grid experience with large format battery based inverters? I've heard of some micro-grid systems running in Haiti on Princeton Power inverters, and Dynapower has a 250 kW inverter that has a "grid forming" mode. As we all know, it is easier to make claims in spec sheets than to deliver hard motor starting power in a remote location. We need proven products, with a track record of reliability. We are considering SMA type systems that use AC coupled PV to offset fuel consumption of a generator, but those seem dependent on the generator to maintain the stability of the micro grid during hard starting loads. Ideally we would want to reduce the generator run time to under 200 hrs/ yr and reduce its size to 500 kW. We have excellent solar resources year round, and the possibility of limiting operations during cloudy weather to meet these goals. Thanks, Ray Walters Remote Solar
Re: [RE-wrenches] Large Off Grid Inverter?
Agree with Daryl here at the end. You have to solve the motor surge with variable frequency drive and go 3 phase. If there is a reasonable cost to use the grid I would not even bother with quoting an off the grid solution. It is what the grid is best at and batteries are the wrong way for this. Dave Angelini Offgrid Solar "we go where powerlines don't" http://members.sti.net/offgridsolar/ e-mail offgridso...@sti.net text 209 813 0060 > you have a problem that is much bigger than I work on. But on a large > motor heavy starting loads problem, we used an extra capacitor on the DC > bus of the frequency drive. the drive on its own greatly reduced the > start > surge, if the load can be started slowly. If the motor must ramp up > quickly the voltage would drop and the capacitor reduced the bump on the > line. This was a few years ago but we put a 200 HP drive on a 100 HP > motor > and added the extra capacitor. Another trick on a different job was to > run > a 3 phase motor with a flywheel and start this motor slowly when the motor > that had to start rapidly the running motor acts as a frequency > stabilizer and dumps it energy into the rapidly starting motor. again > this > was maybe 15 years ago. these kluge solutions were applied when the > inverter could in no way handle the surge and would kick the inverter off > the line. Another solution used by Catipiller they had a unit that could > give 3000 amps 480 v0lts for I think 30 seconds running a motor as a > flywheel for UPS giving the generator set time to start. Check with > Catapiller. again another project we clutched the running motor to the > load to start the load fast and not have to face starting current. One > last comment we had a 5000 HP motor to start a very heavy load, this motor > had a hydraulic coupling that filled with oil to control the motor load. > But I think a speed drive is more practical. And there are regen drives > also. > > There are some other kluges that can be applied, good luck, sorry if this > is of no value. > > On Wed, Apr 25, 2018 at 2:36 PM, Raywrote: > >> Greetings Fellow Wrenches; >> >> We are consulting on a power system for a large off grid facility that >> is >> currently operating on a 1500 kW gen set. The loads are enormous for >> normal off grid: in the neighborhood of 600 amps continuous at 480 v 3 >> phase. Surges are close to 2000 amps, but we are working on control >> programming to bring that number down substantially. That is due >> primarily >> to a 250 Hp motor start. (that's not a typo!). EPA and local regulations >> are dictating that the current generator be retired in the near future. >> Grid power is a possibility, but we need to offer a viable off grid >> option >> as well. >> >> My question to the group: does anyone have real off grid experience with >> large format battery based inverters? I've heard of some micro-grid >> systems running in Haiti on Princeton Power inverters, and Dynapower has >> a >> 250 kW inverter that has a "grid forming" mode. As we all know, it is >> easier to make claims in spec sheets than to deliver hard motor starting >> power in a remote location. We need proven products, with a track >> record >> of reliability. >> >> We are considering SMA type systems that use AC coupled PV to offset >> fuel >> consumption of a generator, but those seem dependent on the generator to >> maintain the stability of the micro grid during hard starting loads. >> Ideally we would want to reduce the generator run time to under 200 hrs/ >> yr >> and reduce its size to 500 kW. We have excellent solar resources year >> round, and the possibility of limiting operations during cloudy weather >> to >> meet these goals. >> >> Thanks, >> >> Ray Walters >> >> Remote Solar >> >> ___ >> List sponsored by Redwood Alliance >> >> List Address: RE-wrenches@lists.re-wrenches.org >> >> Change listserver email address & settings: >> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org >> >> List-Archive: >> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.or >> g/maillist.html >> >> List rules & etiquette: >> www.re-wrenches.org/etiquette.htm >> >> Check out or update participant bios: >> www.members.re-wrenches.org >> >> > ___ > List sponsored by Redwood Alliance > > List Address: RE-wrenches@lists.re-wrenches.org > > Change listserver email address & settings: > http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org > > List-Archive: > http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html > > List rules & etiquette: > www.re-wrenches.org/etiquette.htm > > Check out or update participant bios: > www.members.re-wrenches.org > > ___ List sponsored by Redwood Alliance List Address: RE-wrenches@lists.re-wrenches.org Change listserver email address & settings:
Re: [RE-wrenches] Large Off Grid Inverter?
you have a problem that is much bigger than I work on. But on a large motor heavy starting loads problem, we used an extra capacitor on the DC bus of the frequency drive. the drive on its own greatly reduced the start surge, if the load can be started slowly. If the motor must ramp up quickly the voltage would drop and the capacitor reduced the bump on the line. This was a few years ago but we put a 200 HP drive on a 100 HP motor and added the extra capacitor. Another trick on a different job was to run a 3 phase motor with a flywheel and start this motor slowly when the motor that had to start rapidly the running motor acts as a frequency stabilizer and dumps it energy into the rapidly starting motor. again this was maybe 15 years ago. these kluge solutions were applied when the inverter could in no way handle the surge and would kick the inverter off the line. Another solution used by Catipiller they had a unit that could give 3000 amps 480 v0lts for I think 30 seconds running a motor as a flywheel for UPS giving the generator set time to start. Check with Catapiller. again another project we clutched the running motor to the load to start the load fast and not have to face starting current. One last comment we had a 5000 HP motor to start a very heavy load, this motor had a hydraulic coupling that filled with oil to control the motor load. But I think a speed drive is more practical. And there are regen drives also. There are some other kluges that can be applied, good luck, sorry if this is of no value. On Wed, Apr 25, 2018 at 2:36 PM, Raywrote: > Greetings Fellow Wrenches; > > We are consulting on a power system for a large off grid facility that is > currently operating on a 1500 kW gen set. The loads are enormous for > normal off grid: in the neighborhood of 600 amps continuous at 480 v 3 > phase. Surges are close to 2000 amps, but we are working on control > programming to bring that number down substantially. That is due primarily > to a 250 Hp motor start. (that's not a typo!). EPA and local regulations > are dictating that the current generator be retired in the near future. > Grid power is a possibility, but we need to offer a viable off grid option > as well. > > My question to the group: does anyone have real off grid experience with > large format battery based inverters? I've heard of some micro-grid > systems running in Haiti on Princeton Power inverters, and Dynapower has a > 250 kW inverter that has a "grid forming" mode. As we all know, it is > easier to make claims in spec sheets than to deliver hard motor starting > power in a remote location. We need proven products, with a track record > of reliability. > > We are considering SMA type systems that use AC coupled PV to offset fuel > consumption of a generator, but those seem dependent on the generator to > maintain the stability of the micro grid during hard starting loads. > Ideally we would want to reduce the generator run time to under 200 hrs/ yr > and reduce its size to 500 kW. We have excellent solar resources year > round, and the possibility of limiting operations during cloudy weather to > meet these goals. > > Thanks, > > Ray Walters > > Remote Solar > > ___ > List sponsored by Redwood Alliance > > List Address: RE-wrenches@lists.re-wrenches.org > > Change listserver email address & settings: > http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org > > List-Archive: http://www.mail-archive.com/re-wrenches@lists.re-wrenches.or > g/maillist.html > > List rules & etiquette: > www.re-wrenches.org/etiquette.htm > > Check out or update participant bios: > www.members.re-wrenches.org > > ___ List sponsored by Redwood Alliance List Address: RE-wrenches@lists.re-wrenches.org Change listserver email address & settings: http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org List-Archive: http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html List rules & etiquette: www.re-wrenches.org/etiquette.htm Check out or update participant bios: www.members.re-wrenches.org
[RE-wrenches] Large Off Grid Inverter?
Greetings Fellow Wrenches; We are consulting on a power system for a large off grid facility that is currently operating on a 1500 kW gen set. The loads are enormous for normal off grid: in the neighborhood of 600 amps continuous at 480 v 3 phase. Surges are close to 2000 amps, but we are working on control programming to bring that number down substantially. That is due primarily to a 250 Hp motor start. (that's not a typo!). EPA and local regulations are dictating that the current generator be retired in the near future. Grid power is a possibility, but we need to offer a viable off grid option as well. My question to the group: does anyone have real off grid experience with large format battery based inverters? I've heard of some micro-grid systems running in Haiti on Princeton Power inverters, and Dynapower has a 250 kW inverter that has a "grid forming" mode. As we all know, it is easier to make claims in spec sheets than to deliver hard motor starting power in a remote location. We need proven products, with a track record of reliability. We are considering SMA type systems that use AC coupled PV to offset fuel consumption of a generator, but those seem dependent on the generator to maintain the stability of the micro grid during hard starting loads. Ideally we would want to reduce the generator run time to under 200 hrs/ yr and reduce its size to 500 kW. We have excellent solar resources year round, and the possibility of limiting operations during cloudy weather to meet these goals. Thanks, Ray Walters Remote Solar ___ List sponsored by Redwood Alliance List Address: RE-wrenches@lists.re-wrenches.org Change listserver email address & settings: http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org List-Archive: http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html List rules & etiquette: www.re-wrenches.org/etiquette.htm Check out or update participant bios: www.members.re-wrenches.org