Re: [RE-wrenches] Sol-Ark 15K AC Coupling

2024-08-24 Thread david quattro via RE-wrenches
Sorry I just noticed that you’re dealing with 15Ks. My scenario was with a 12K ___ List sponsored by Redwood Alliance Pay optional member dues here: http://re-wrenches.org List Address: RE-wrenches@lists.re-wrenches.org Change listserver email address

Re: [RE-wrenches] Sol-Ark 15K AC Coupling

2024-08-24 Thread Jason Szumlanski via RE-wrenches
That's interesting on two fronts. I believe the documentation says you can AC couple when off-grid with load side interconnected inverters. It would have to have some mechanism to turn off AC coupled sources for that to work. And it also says there is no modulation and it's on or off only. Strange

Re: [RE-wrenches] Sol-Ark 15K AC Coupling

2024-08-24 Thread david quattro via RE-wrenches
last year SolArk tech support told me only the Gen ports have the freq/volt modulation, and only when you program the master “AC Couple on GEN” ___ List sponsored by Redwood Alliance Pay optional member dues here: http://re-wrenches.org List Address: RE

Re: [RE-wrenches] Sol-Ark 15K AC Coupling

2024-08-24 Thread Jason Szumlanski via RE-wrenches
Hi Kirpal, This is hugely helpful. More than you can imagine. I actually brought this up with tech support because two of the inverters have Savant insignia on them. The first slave inverter does not have this insignia. I did not supply these inverters, as the customer already had them from anothe

Re: [RE-wrenches] Sol-Ark 15K AC Coupling

2024-08-24 Thread Kirpal Khalsa via RE-wrenches
Jason... We had a similar situation with a dual SolArk 15K system. After approximately an hour of turning system on we would get the F41 error on the master ‐ the slave inverter would show an error and then the master would shut down with the paralleling error F41 because the slave inverter had sho

Re: [RE-wrenches] Sol-Ark 15K AC Coupling

2024-08-24 Thread Peter Giroux via RE-wrenches
. Peter Giroux American Solar From: RE-wrenches On Behalf Of Jason Szumlanski via RE-wrenches Sent: Saturday, August 24, 2024 5:07 PM To: RE-wrenches Cc: Jason Szumlanski Subject: Re: [RE-wrenches] Sol-Ark 15K AC Coupling Good information. Thank you. I don't believe the Sol-A

Re: [RE-wrenches] Sol-Ark 15K AC Coupling

2024-08-24 Thread Jason Szumlanski via RE-wrenches
*Sent:* Saturday, August 24, 2024 1:32 PM > *To:* RE-wrenches > *Cc:* Jason Szumlanski > *Subject:* [RE-wrenches] Sol-Ark 15K AC Coupling > > > > Hi all, > > > > Over the last three days I have had one of this infuriating and > frustrating experiences with Sol-Ark

Re: [RE-wrenches] Sol-Ark 15K AC Coupling

2024-08-24 Thread pieter offgridenterprises.org via RE-wrenches
Subject: [RE-wrenches] Sol-Ark 15K AC Coupling Hi all, Over the last three days I have had one of this infuriating and frustrating experiences with Sol-Ark where you talk to 3 people and get 10 different answers. At least I think I finally got the right one today. Here is the scenario and

[RE-wrenches] Sol-Ark 15K AC Coupling

2024-08-24 Thread Jason Szumlanski via RE-wrenches
Hi all, Over the last three days I have had one of this infuriating and frustrating experiences with Sol-Ark where you talk to 3 people and get 10 different answers. At least I think I finally got the right one today. Here is the scenario and problem I was experiencing: At a (very) remote locatio

Re: [RE-wrenches] Sol-Ark 15k solar panel frame grounding

2024-06-06 Thread Christopher Warfel via RE-wrenches
essage. *From:* RE-wrenches on behalf of William Miller via RE-wrenches *Sent:* Wednesday, June 5, 2024 12:53:52 PM *To:* RE-wrenches *Cc:* William Miller *Subject:* Re: [RE-wrenches] Sol-Ark 15k solar panel frame grounding Friends: On a r

Re: [RE-wrenches] Sol-Ark 15k solar panel frame grounding

2024-06-05 Thread david quattro via RE-wrenches
in their installation manuals, SolArk indicates black and red colors for PV conductors. ___ List sponsored by Redwood Alliance Pay optional member dues here: http://re-wrenches.org List Address: RE-wrenches@lists.re-wrenches.org Change listserver email

Re: [RE-wrenches] Sol-Ark 15k solar panel frame grounding

2024-06-05 Thread Eric Smiley via RE-wrenches
complicated!” > > > > William Miller > > > > Miller Solar > > 17395 Oak Road, Atascadero, CA 93422 > > 805-438-5600 > > www.millersolar.com > > CA Lic. 773985 > > > > > > *From:* RE-wrenches [mailto:re-wrenches-boun...@lists.re-wrenches.org]

Re: [RE-wrenches] Sol-Ark 15k solar panel frame grounding

2024-06-05 Thread Brian Mehalic via RE-wrenches
; > > > Confusing? Yeah, a bit. But as my local roofing companies say: “Solar? > It can’t be that complicated!” > > > > William Miller > > > > Miller Solar > > 17395 Oak Road, Atascadero, CA 93422 > > 805-438-5600 > > www.millersolar.com &

Re: [RE-wrenches] Sol-Ark 15k solar panel frame grounding

2024-06-05 Thread Bryan Norkunas via RE-wrenches
alf of William Miller via RE-wrenches Sent: Wednesday, June 5, 2024 12:53:52 PM To: RE-wrenches Cc: William Miller Subject: Re: [RE-wrenches] Sol-Ark 15k solar panel frame grounding Friends: On a related subject, I was researching the question: What color should my grounded PV conduc

Re: [RE-wrenches] Sol-Ark 15k solar panel frame grounding

2024-06-05 Thread Glenn Burt via RE-wrenches
iam Miller;Subject:Re: [RE-wrenches] Sol-Ark 15k solar panel frame groundingFriends: On a related subject, I was researching the question: What color should my grounded PV conductor be?   History: In the beginning, negative leads were always black.    When it became apparent that negative PV leads w

Re: [RE-wrenches] Sol-Ark 15k solar panel frame grounding

2024-06-05 Thread William Miller via RE-wrenches
*Sent:* Wednesday, June 5, 2024 6:02 AM *To:* RE-wrenches *Cc:* Jason Szumlanski *Subject:* [RE-wrenches] Sol-Ark 15k solar panel frame grounding Can anybody clarify the following instruction from the manual? "GND the panel MOUNTS/FRAMES to any GND outside the circuit via 12AWG wire"

Re: [RE-wrenches] Sol-Ark 15k solar panel frame grounding

2024-06-05 Thread Jason Szumlanski via RE-wrenches
This is a partial backup scenario and the main service panel has a solid neutral to ground bond. I have not been able to find anywhere else where there is a bond, but there is always the chance that there is a neutral wire in a switch box or outlet box somewhere in the house that is touching an equ

Re: [RE-wrenches] Sol-Ark 15k solar panel frame grounding

2024-06-05 Thread Mac Lewis via RE-wrenches
Hi Jason, You should be able to land your PV EGC in the inverter ground bar. You could do a quick resistance check to verify the +, - PV Is there a bond somewhere (upstream service panel or in the Sol-Ark itself) between ground and neutral? If not, this can cause this fault. On Wed, Jun 5, 202

Re: [RE-wrenches] Sol-Ark 15k solar panel frame grounding

2024-06-05 Thread Maverick Brown via RE-wrenches
I usually get the 08 GFDI error when I haven’t bonded neutral to ground downstream. (Typically because I booted up the inverter after DC connection but before any AC wires are landed.) That goes away once it is fully commissioned. I get the F23 - Tz_GFCI_OC_Fault If is related to the PV array,

[RE-wrenches] Sol-Ark 15k solar panel frame grounding

2024-06-05 Thread Jason Szumlanski via RE-wrenches
Can anybody clarify the following instruction from the manual? "GND the panel MOUNTS/FRAMES to any GND outside the circuit via 12AWG wire" Does this mean do not connect the array equipment grounding conductor to the grounding terminal in the inverter? Where would be the suggested place to connect

Re: [RE-wrenches] Sol-Ark 15K AC Output

2024-03-27 Thread Jason Szumlanski via RE-wrenches
m > > CA Lic. 773985 > > > > > > *From:* Jason Szumlanski [mailto:ja...@floridasolardesigngroup.com] > *Sent:* Wednesday, March 27, 2024 3:52 PM > *To:* Kirk Herander > *Cc:* William Miller; RE-wrenches > *Subject:* Re: [RE-wrenches] Sol-Ark 15K AC Output > >

Re: [RE-wrenches] Sol-Ark 15K AC Output

2024-03-27 Thread William Miller via RE-wrenches
Solar 17395 Oak Road, Atascadero, CA 93422 805-438-5600 www.millersolar.com CA Lic. 773985 *From:* Jason Szumlanski [mailto:ja...@floridasolardesigngroup.com] *Sent:* Wednesday, March 27, 2024 3:52 PM *To:* Kirk Herander *Cc:* William Miller; RE-wrenches *Subject:* Re: [RE-wrenches] Sol-Ark 15K

Re: [RE-wrenches] Sol-Ark 15K AC Output

2024-03-27 Thread Jason Szumlanski via RE-wrenches
ining, the interlocked >> bypass and output breakers all fit into one load center. >> >> >> >> I hope the time we spent on this discussion helps someone out there. >> That’s why we do it. >> >> >> >> Wm >> >> >> >> M

Re: [RE-wrenches] Sol-Ark 15K AC Output

2024-03-27 Thread Kirk Herander via RE-wrenches
eone out there. > That’s why we do it. > > > > Wm > > > > Miller Solar > > 17395 Oak Road, Atascadero, CA 93422 > > 805-438-5600 > > www.millersolar.com > > CA Lic. 773985 > > > > > > *From:* Kirk Herander [mai

Re: [RE-wrenches] Sol-Ark 15K AC Output

2024-03-27 Thread William Miller via RE-wrenches
*Subject:* Re: [RE-wrenches] Sol-Ark 15K AC Output www.interlockkit.com - they stock and custom make interlock bypasses including multiple breakers. Square D also makes a 400 A panel which excepts either bolt on or snap on QO breakers. *Kirk Herander / **kirkh@vermont.solar * *Owner

Re: [RE-wrenches] Sol-Ark 15K AC Output

2024-03-27 Thread Kirk Herander via RE-wrenches
, Atascadero, CA 93422 > > 805-438-5600 > > www.millersolar.com > > CA Lic. 773985 > > > > > > *From:* Jason Szumlanski [mailto:ja...@floridasolardesigngroup.com] > *Sent:* Wednesday, March 27, 2024 3:12 AM > *To:* will...@millersolar.com > *Cc:* RE-wrenches > *Su

Re: [RE-wrenches] Sol-Ark 15K AC Output

2024-03-27 Thread William Miller via RE-wrenches
*Subject:* Re: [RE-wrenches] Sol-Ark 15K AC Output William, Thanks for the information on grid peak shaving. That is what I thought could be done. The description is a misnomer of sorts (like a lot of things in Sol-Ark lingo). It's a bit hard to follow and not nearly well enough docum

Re: [RE-wrenches] Sol-Ark 15K AC Output

2024-03-27 Thread Jason Szumlanski via RE-wrenches
> > > > > > PS:  Below is a diagram on how to provide bypass.  I tried to depict the > > > bypass interlock graphically.  The point is you cannot turn on the bypass > > > breaker without turning off the inverter output breakers.  See photos of > > > the actual hardware on the web page linked b

Re: [RE-wrenches] Sol-Ark 15K AC Output

2024-03-27 Thread Chris Sparadeo via RE-wrenches
ware on the web page linked below. I find bypass >> very handy because if there is an inverter or battery failure the client >> can restore power immediately and I can respond at a more convenient time. >> >> >> >> >> >> >> >> >> >> Wm >> &g

Re: [RE-wrenches] Sol-Ark 15K AC Output

2024-03-27 Thread Michael Morningstar via RE-wrenches
ass >> very handy because if there is an inverter or battery failure the client >> can restore power immediately and I can respond at a more convenient time. >> >> >> >> >> >> >> >> >> >> Wm >> >> >> >> Mil

Re: [RE-wrenches] Sol-Ark 15K AC Output

2024-03-26 Thread Jerry Shafer via RE-wrenches
Wrenches, Jason I have always either with outback and with solark have always connected each unit with a distribution panel with breakers regardless of what's in the inverter package. This same goes for the gen set connections with proper breakers so not to have to over size the wires. I have conne

Re: [RE-wrenches] Sol-Ark 15K AC Output

2024-03-26 Thread Jason Szumlanski via RE-wrenches
> > Miller Solar > > 17395 Oak Road, Atascadero, CA 93422 > > 805-438-5600 > > www.millersolar.com > > CA Lic. 773985 > > > > > > *From:* RE-wrenches [mailto:re-wrenches-boun...@lists.re-wrenches.org] *On > Behalf Of *Jason Szumlanski via RE-wr

Re: [RE-wrenches] Sol-Ark 15K AC Output

2024-03-26 Thread Jason Szumlanski via RE-wrenches
Hi Dave, XW inverters do a decent job of explaining generator support mode where small generators can be supplemented by inverter power to start up large loads. I believe several other brands can do this, and I believe Sol-Ark is one of them. But front line customer service wasn't really up to spe

Re: [RE-wrenches] Sol-Ark 15K AC Output

2024-03-26 Thread William Miller via RE-wrenches
*Jason Szumlanski via RE-wrenches *Sent:* Tuesday, March 26, 2024 2:26 PM *To:* RE-wrenches *Cc:* Jason Szumlanski *Subject:* [RE-wrenches] Sol-Ark 15K AC Output I am going to have a quad-stack of Sol-Ark 15K for an off-grid 120/240V system with a 150A generator. I know the max real power is 62.5

Re: [RE-wrenches] Sol-Ark 15K AC Output

2024-03-26 Thread Dave Tedeyan via RE-wrenches
I may be wrong, but I was under the impression that most inverter/chargers are either being an inverter or a charger at any given time, but not both. So, once the inverter sees the AC voltage from the generator, then it will switch to being a charger and use the generator AC power to charge the bat

[RE-wrenches] Sol-Ark 15K AC Output

2024-03-26 Thread Jason Szumlanski via RE-wrenches
I am going to have a quad-stack of Sol-Ark 15K for an off-grid 120/240V system with a 150A generator. I know the max real power is 62.5A each inverter including battery and PV. That would be 62.5A x 4 = 250A total. I intend to connect the output of the 4 inverters together with a 5-port Polaris tap

Re: [RE-wrenches] Sol-Ark 15k Conduit Entries

2023-08-05 Thread Max Balchowsky via RE-wrenches
i like using gutters, it keeps it clean you can just as easily put the gutter vertical on the side and use close nipples….. Max Balchowsky SEE Systems On Wed, Aug 2, 2023 at 8:04 AM Jason Szumlanski via RE-wrenches < re-wrenches@lists.re-wrenches.org> wrote: > I see a lot of pictures with condui

Re: [RE-wrenches] Sol-Ark 15k Conduit Entries

2023-08-04 Thread Michael Morningstar via RE-wrenches
I just checked out the Homegrid batteries. Just throwing this out there. If there is enough ceiling height you could hang them. That's typically how we deal with transformers in commercial and industrial settings. We usually build a permanent gantry out of square tubing, 1/2" rod and strut. Then ra

Re: [RE-wrenches] Sol-Ark 15k Conduit Entries

2023-08-04 Thread Dave Angelini Offgrid Solar via RE-wrenches
Very nice Install Michael! Was that the project on the xxCloud River we talked about? It looks like you have kept the gutter heat gain down to protect electronics. "the rule of thumb is that every 10°C increase in temperature reduces component life by half" https://www.electronics-cooling

Re: [RE-wrenches] Sol-Ark 15k Conduit Entries

2023-08-04 Thread Jason Szumlanski via RE-wrenches
Michael, I think your work looks stellar, and I seriously doubt there would be any airflow issues. I plan to use strut to put the inverters out from the wall to deal with the working depth issue, which should also help with airflow. That was part of my thought process - even if the inverters don'

Re: [RE-wrenches] Sol-Ark 15k Conduit Entries

2023-08-04 Thread Michael Morningstar via RE-wrenches
We handle the 15Ks much like most vfds since both have cooling vents in the rear and knockouts or wiring compartments in the rear. What we do is set the units back so that the rear portion is hanging off of the rear of the gutter. The gutter in this case is held off of the wall for air flow. It doe

Re: [RE-wrenches] Sol-Ark 15k Conduit Entries

2023-08-04 Thread Jason Szumlanski via RE-wrenches
Thanks, Lou. I missed that 6" bottom spacing requirement in the manual. That could explain a lot of the installation pictures I have seen. On the flip side, we have seen some examples of installations in this thread without this 6-inch spacing, presumably without any adverse effects. Obviously, NE

Re: [RE-wrenches] Sol-Ark 15k Conduit Entries

2023-08-03 Thread Lou Russo via RE-wrenches
Hello All, Super impressive install, Michael. Almost worth a flight, and a site visit! Back to Jason's initial question If you are using the 15kW Outdoor Sol-Ark they vent from the top and bottom with a required 6" minimum spacing on both the top and bottom. A 12kW Outdoor with 8x8 gutter an

Re: [RE-wrenches] Sol-Ark 15k Conduit Entries

2023-08-02 Thread Jerry Shafer via RE-wrenches
Jason In plenty of applications l will use couplers with chase nipples, height is one issue but installed working height is very important. I use a 8"x8"x X gutter and sometimes even off set that from the wall, l have had AHJ not want to see mixed cables LVDC and AC in the same conduit so pass thro

Re: [RE-wrenches] Sol-Ark 15k Conduit Entries

2023-08-02 Thread Maverick Brown via RE-wrenches
Jason The old Sol-Ark had the PV disconnect and the Wi-Fi adapter connection on the bottom and that needed about six or 8 inches of clearance. The current Sol-Ark has those items on the side of the unit so you don’t need such clearance on the bottom. I installed several Sol-Ark and I use the re

[RE-wrenches] Sol-Ark 15k Conduit Entries

2023-08-02 Thread Jason Szumlanski via RE-wrenches
I see a lot of pictures with conduit nipples coming out of a gutter that are fairly long. I have a height limit issue and I'm wondering if there are any negative implications of using very short nipples between a wireway below and the inverter. I'm thinking about using close nipples or perhaps 2-in

Re: [RE-wrenches] Sol-Ark 15k

2022-05-10 Thread Jerry Shafer via RE-wrenches
Just so it is abundantly clear to all that wish to modify or cut open an inverter, SMA will not do any advanced replacements of any inverters that have been modified, Outback is not a problem as they are field serviceable, SolArk is a all in one unit and any modification to the cabinet will prevent

Re: [RE-wrenches] Sol-Ark 15k

2022-05-09 Thread Jason Szumlanski via RE-wrenches
I think the idea here is that 690.9 allows the inverter output conductors to be sized based on the maximum ampacity and an OCPD is actually not required is the conductor ampacity is sufficient. So in an off-grid scenario, the wires could be as small as #4. In a grid interconnected situation where t

Re: [RE-wrenches] Sol-Ark 15k

2022-05-09 Thread Jerry Shafer via RE-wrenches
Wrenches The new solark 15 has a 200 amp rated contactor this is so if you want to have whole home pass through you can but if you only have an inverter then use that as your starting point and if the genny is contributing then add that is, you do not need 2/0 for a single 15 k off grid but you may

Re: [RE-wrenches] Sol-Ark 15k

2022-05-08 Thread Jeff Clearwater via RE-wrenches
I've been using two gutters with multiple 12KW Sol-Arks Installs - one 4x4" that I mount immediately under the AC KOs using forward biased offset nipples (it's front face is just abouut 1/2" in front of front plane of Sol-Arks)  and then a 6x6" set back and down and reached with 4" nipples exte

Re: [RE-wrenches] Sol-Ark 15k

2022-05-08 Thread Jerry Shafer via RE-wrenches
Be carefull about modifying inverters or any cabinets with long term warranties because modifying may result in sending your unit for repair and not getting exchange units in the event of a warranty issue. Outback is served in parts so that may not be an issue, solark is too soon to tell. Fronius r

Re: [RE-wrenches] Sol-Ark 15k

2022-05-08 Thread Michael Morningstar via RE-wrenches
We cut out the bottom plate entirely with a die grinder/cut off wheel and then wrap the raw edge with vinyl "edge wrap" and set the inverters on top of 10 x 10 x whatever gutters. The layout and sizes of Sol-Arks knock-outs is screwy. Just need a bonding jumper between both enclosures. This is comm

Re: [RE-wrenches] Sol-Ark 15k

2022-05-08 Thread Jay via RE-wrenches
Hi Chris, Can’t you increase the size of the KO’s? Jay > On May 7, 2022, at 7:17 PM, Chris Sparadeo via RE-wrenches > wrote: > >  > Jason, > > I think I agree with your interpretation of the wiring diagram. My hesitation > is, with a 1-1/4” KO for AC inputs, only choice seems to be a >24”

Re: [RE-wrenches] Sol-Ark 15k

2022-05-07 Thread Chris Sparadeo via RE-wrenches
Jason, I think I agree with your interpretation of the wiring diagram. My hesitation is, with a 1-1/4” KO for AC inputs, only choice seems to be a >24” stub conduit for 2/0 conductores to a fused disconnect. Not a fun pipe to bend…and extra BOS seems like a less than ideal solution. Is this your

Re: [RE-wrenches] Sol-Ark 15k

2022-04-17 Thread Darryl Thayer via RE-wrenches
Yes and no, I think this is a tap, "a tap shall be permitted anywhere along a feeder" ' as long as it is less than a 10-foot rule or 25-foot rule ending in a listed OCPD with a rating sufficient to handle the maximum overcurrent'. Service equipment residential is rated for fault currents of up to

Re: [RE-wrenches] Sol-Ark 15k

2022-04-17 Thread Jason Szumlanski via RE-wrenches
But this isn't a tap. It's a feeder conductor connected to an OCPD. I guess if you don't have a grid in or generator in or AC Coupled PV, you could just call it an inverter output circuit and it could be sized accordingly. But it would still need to be protected at it's source by an appropriately

Re: [RE-wrenches] Sol-Ark 15k

2022-04-17 Thread Darryl Thayer via RE-wrenches
The tap rule says you can reduce to 10% of the nominal size for 10 feet and protect at the downstream OCPD or 25% for 25 feet for solar with multiple sources see 705 On Sat, Apr 16, 2022 at 9:16 PM Jason Szumlanski via RE-wrenches < re-wrenches@lists.re-wrenches.org> wrote: > That's what I'm thin

Re: [RE-wrenches] Sol-Ark 15k

2022-04-16 Thread Jason Szumlanski via RE-wrenches
That's what I'm thinking. You would need to use a 200A conductor to a separate load out OCPD before downsizing the wire. I guess there are pros and cons, but it seems this is geared toward whole house backup for 200A services. I'm eager to get an opportunity to use it in that scenario. Jason O

Re: [RE-wrenches] Sol-Ark 15k

2022-04-16 Thread Chris Sparadeo via RE-wrenches
Jason, Any additional OCPD downstream of the 200A load output breaker could allow for a smaller wire size to be used at these terminals. For example, load output conductors run to a 100A main breaker panel board. Obviously depending on circumstances, a #4 copper could fit the bill. What I’m not

Re: [RE-wrenches] Sol-Ark 15k

2022-04-16 Thread Darryl Thayer via RE-wrenches
Hello, The overcurrent device is to protect the conductors. you can put any size wire, but you must protect with the overcurrent device. REmember in solar equipment; you may have more than one supply source. The DC best example is solar modules connected in parallel, on On Fri, Apr 15, 202

Re: [RE-wrenches] Sol-Ark 15k

2022-04-15 Thread Jason Szumlanski via RE-wrenches
That's a different scenario, as a 100A genny would have a 100A OCPD. I understand that the inverter output rating is limited, but what section of code allows a 200A breaker to protect a #4 wire? On Fri, Apr 15, 2022 at 9:26 PM Jerry Shafer via RE-wrenches < re-wrenches@lists.re-wrenches.org>

Re: [RE-wrenches] Sol-Ark 15k

2022-04-15 Thread Jerry Shafer via RE-wrenches
You must meet all expected source output potentials within the design and operating limits, as long as the distribution panel and connected wiring is rated for the max output of the protected source then you are good. A 200 ATS connected to a 10 kW genny does not require 2/0 as it will never meet t

Re: [RE-wrenches] Sol-Ark 15k

2022-04-15 Thread Chris Sparadeo via RE-wrenches
Hi Jason, You bring up a valid point….in an off-grid scenario with the 15k do you size the conductors to the continuous capacity, surge capacity or the OCPD of the unit? -Chris On Fri, Apr 15, 2022 at 4:01 PM Jason Szumlanski via RE-wrenches < re-wrenches@lists.re-wrenches.org> wrote: > P.S. IC

Re: [RE-wrenches] Sol-Ark 15k

2022-04-15 Thread Jason Szumlanski via RE-wrenches
P.S. ICYMI, this inverter has a massive combined AC coupled and DC coupled capacity. They allow 15kWdc plus 19.2kWac!!! Impressive. On Fri, Apr 15, 2022 at 10:59 AM Jason Szumlanski < ja...@floridasolardesigngroup.com> wrote: > I'm not following the wiring diagrams for this new inverter. It

[RE-wrenches] Sol-Ark 15k

2022-04-15 Thread Jason Szumlanski via RE-wrenches
I'm not following the wiring diagrams for this new inverter. It has 200A pass-through capability with an integrated 200A load disconnect. But then it says the wire gauge for the load out wiring can be #4 to 2/0. In an off-grid scenario where there is no generator, the max continuous output is 62.5