I am currently looking at the same situation, only rather than a restaurant
I'm at an OLD grain mill.  It's now being renovated but trying to keep as
much as they can from the Mill.  
My "lego" ceiling will be located in a flower shop and the pockets are 5'3 x
4' and are 56" deep!  My heart stopped when I looked at it.  Here's the
kicker, it's all heavy timber.  So, are sprinklers required?

Carole Holmes
Kalamazoo, MI

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Ed Kramer
Sent: Wednesday, February 07, 2007 10:44 PM
To: [email protected]
Subject: RE: pockets vs obstructed

Greg - What's the spacing of the sides of the 'lego's'?  If they're 3' to
7.5' on-center, it likely does qualify as obstructed construction.  And if
they're not more than 22" deep (or close to that), sprinkler spacing should
be fairly simple.

Ed Kramer
Littleton, CO


>The ceiling looks like the bottom of my sons lego's!
>How many soffits / pockets does it take to consider a ceiling obstructed
>construction rather than trying to protect every small pocket?