I think your 40% overage is way too high based on the flow test. A good design oops, layout will limit the overage to less than 20%. Your not going to use 20 x 20 EC's because of the flow test and the smaller the K factor the lower the accumlation in the system so I would recommend 1/2" 5.6K heads at 130 max.
Ron Fletcher Aero Automatic Phoenix, AZ -----Original Message----- From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of Brian Harris Sent: Tuesday, March 27, 2007 5:35 AM To: [email protected] Subject: Selecting Heads For a New System Let me start by saying I've only been in the sprinkler world for just over a year so if any thing I ask is "rookie-ish" please keep that in mind. I'm looking for ideas that some of you may use when starting a new project when it comes to selecting what heads (head spacing) to use. For example: I am starting a retail store (mercantile) that has a Static of 47 psi Residual of 42 psi, & flow of 1090 gpm. What I do now to get me "in the ballpark" is take the density x area of operation x 1.4 (for overage) + hose allowance. That gets me roughly the system gpm demand. So .20 x 1500 = 300 x 1.4 = 420 + 250 (hose) = 670 gpm. I then plot that gpm on my water supply curve (N1.85) to get the psi for that gpm; in this case that's around 45psi. >From that psi I take out for the BFP, elevation, 40% (friction loss & etc) and whatever is left I find a head with an end head pressure that's slightly under that and away I go.... Any thoughts? Suggestions? Better Ideas? Regards, Brian Harris First Defense Fire Protection <mailto:[EMAIL PROTECTED]> [EMAIL PROTECTED] 704.948.3506 phone 704.948.3507 fax _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum