Chris,

Lacking because we can all see the questions coming and the answers
aren't there. We're saying the same thing, put it on the engineer, but
since Ray seems to have a good, at this point, relationship with the
owner it may be to his benefit to get the questions answered up front.
After all his will eventually be the face that the AHJ comes to know
and love.

On Thu, Oct 16, 2008 at 10:50 AM, Chris Cahill <[EMAIL PROTECTED]> wrote:
> Why is it lacking?  If they gave you the area/density sounds like you have
> all you need.  While the rest you indicate would be nice and the AHJ will
> probably require at some point isn't this the engineering firms problem?
> I'd send my plans in with the density and attach the engineers "design
> documents".  I'd refer any questions regarding the density or use to the
> engineer.  Even if the engineering firm came up with the wrong area/density
> that isn't your problem is it?  I agree you might want to cross reference to
> help the owner with a big problem later.  If you are just bidding qualify
> you don't know, don't have the information and are relying on the engineer.
>
>
> I'm assuming you are the sprinkler contractor only.  As a contractor give me
> the area/density and that's all I need?  0.576263/3289.8975 fine, I can
> design around that.  It doesn't make a difference to me where it came from.
> If they tell you the commodity is Class 0 stored 3' high you still design to
> the given density.  Don't be the defacto engineer if you don't have too.  We
> contractors hold the hand of engineers to often.  Seems to me the
> appropriate (or perhaps inappropriate but irrelevant) protection scheme has
> already been decided.
>
> Dude, I'd be in heaven if any specifying engineer around here could come up
> with an area/density. Of course the one exception is forumite Scott Futrell
> but he doesn't do much specifying that I am aware of.  I assume it costs too
> much to do it right.
>
> Chris Cahill, P.E.
> Fire Protection Engineer
> Sentry Fire Protection, Inc.
>
> 763-658-4483
> 763-658-4921 fax
>
> Email: [EMAIL PROTECTED]
>
> Mail: P.O. Box 69
>        Waverly, MN 55390
>
> Location: 4439 Hwy 12 SW
>              Waverly, MN 55390
> -----Original Message-----
> From: [EMAIL PROTECTED]
> [mailto:[EMAIL PROTECTED] On Behalf Of Ray Vance
> Sent: Thursday, October 16, 2008 11:58 AM
> To: [email protected]
> Subject: RE: Pesticides Storage
>
> Thanks Todd.
>
> I have already gone down that path and the client is in the process of
> getting the MSDS sheets for us.
> We have been given a set of "design documents" from an engineering firm
> indicating an area/density requirement, but no information was given as to
> the storage height, storage arrangement, commodity classification, building
> height, clearances, container types or sizes, etc. so an informed decision
> can be made relating to the appropriate protection scheme.
>
> Fortunately, the containment requirements of NFPA 434 have been addressed,
> but the fire protection portion is definitely lacking in sufficient detail
> to determine an adequate direction.
>
> Ray Vance - SET
> Chief Sales Designer
> Wayne Automatic Fire Sprinklers, Inc.
> www.waynefire.com
> (407) 877-5563  office
> (321) 436-2184  cell
>
> -----Original Message-----
> From: [EMAIL PROTECTED]
> [mailto:[EMAIL PROTECTED] On Behalf Of Todd Williams
> - FPDC
> Sent: 2008-10-16 11:39
> To: [email protected]
> Subject: Re: Pesticides Storage
>
> Ray, Get MSDS's on the stuff and see exactly what you are dealing with.
>
>
>
> At 11:29 AM 10/16/2008, you wrote:
>>Esteemed Collegues:
>>
>>Can anyone give guidance on a Pesticides Storage warehouse and the
>>approriate fire protection requirements?
>>NFPA-434 doesn't give prescriptove requiremetns or a definitive path to
>>follow. It only indicates a risk analysis be done by a "competent
>>individual" (I read PE or FPE) to determine the extent and type of fire
>>protection to be provide.
>>
>>Without regard to storage arrangement and heights, what TYPE of
>>commodity would be appropriate to consider, since the amount stored is
>>over 10,000 lbs and is extermely varied in the types and configurations
>>of products to be stored?
>>I am leaning towards NFPA-30 "Flammable and Combustible Liquids" to
>>begin my analysis, but would like the opinions of anyone who has had
>>experience with this process.
>>
>>Thanks in advance,
>>
>>Ray Vance -SET
>>Chief Sales Designer
>>Wayne Automatic Fire Sprinklers, Inc.
>>www.waynefire.com<blocked::blocked::http://www.waynefire.com/>
>>(407) 877-5563  office
>>(321) 436-2184  cell
>>
>>_______________________________________________
>>Sprinklerforum mailing list
>>http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
>>For Technical Assistance, send an email to:
>>[EMAIL PROTECTED]
>>
>>To Unsubscribe, send an email
>>to:[EMAIL PROTECTED]
>>(Put the word unsubscribe in the subject field)
>
> Todd G. Williams, PE
> Fire Protection Design/Consulting
> Stonington, Connecticut
> www.fpdc.com
> 860.535.2080
> _______________________________________________
> Sprinklerforum mailing list
> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
> For Technical Assistance, send an email to: [EMAIL PROTECTED]
>
> To Unsubscribe, send an email to:[EMAIL PROTECTED]
> (Put the word unsubscribe in the subject field)
> _______________________________________________
> Sprinklerforum mailing list
> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
> For Technical Assistance, send an email to: [EMAIL PROTECTED]
>
> To Unsubscribe, send an email to:[EMAIL PROTECTED]
> (Put the word unsubscribe in the subject field)
>
> _______________________________________________
> Sprinklerforum mailing list
> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
> For Technical Assistance, send an email to: [EMAIL PROTECTED]
>
> To Unsubscribe, send an email to:[EMAIL PROTECTED]
> (Put the word unsubscribe in the subject field)
>



-- 
Ron Greenman
at home....