Frans:

I know this is not germane to your problem, but it is a reason I do not spec
or use low pressure air DPV's.

While visiting Rowe sprinkler I had the opportunity to have their lead
designer show me how Counter Intuitive the air supply is using the water
delivery time software from TYCO. We were able to run delivery time on
several different systems at various air pressures in a few short minutes.
We could watch the graphic water display on the monitor which even showed
the water compression bounce on dead end branch line. It was an amazing
experience to actually see what was happening as the air exhausted from just
one or two heads.

Long story getting longer, basically the delivery time was a lot shorter in
the higher air pressure system than in a low air pressure system, because
you had to "FILL" less of the HP system with water before it came out the
open orifice.

Basically our dry systems here operate on a much higher air pressure,
because of our high incoming water pressures. That combined with the high
Altitude, make our air compressors work harder. (Burn Out sooner.) but our
delivery times work.