Ron,

Is this in a rural setting?  As Craig suggested lots of times you only need
to size for the sprinkler demand and associated hose allowance with this
scenario.  It sounds like your project is in a rural setting, IFC Appendix B
B103.3 allows the use of NFPA 1142 in areas without water supplies provided
that the AHJ accepts it.  I have utilized this numerous times in Eastern
Washington and Oregon, you still need to provide enough hydrants though but
you don't have to provide the IFC required fire flow for the particular
building. 

Jim Johnston, P.E.
Fire Protection Engineer
Inland Fire Protection, Inc
1100 Ahtanum Road
Yakima, WA 98903
Phone 509-248-4471
Fax 509-248-1180
[email protected]


-----Original Message-----
From: Ron Greenman [mailto:[email protected]] 
Sent: Thursday, September 03, 2009 12:57 PM
To: [email protected]
Subject: Re: Fire Flow

The reduction has already been approved. The fire flow demand is to
supply a hydrant on the property. My question is (and no fire marshal
to ask today),is the sprinkler demand included or need to be added?
This tank supplies all fire water needs (no jokes-I know what you're
all thinking) for this property.

On Thu, Sep 3, 2009 at 12:50 PM, <[email protected]> wrote:
> If you're talking about the fire flows referenced in the IFC, Appendix B,
this seems to be an AHJ or IU call.  For the most part when the building is
fully sprinklered only the sprinkler system demand and hose stream demands
are used for water tank sizing.  I've not had one AHJ or IU apply the fire
flow section of the IFC to the water supply when those conditions exist.
 Now when a building is not protected I have had this section of the IFC
applied.  However note that this section is not mandatory and is not a part
of the actual Code.  See wording at the top of the first page.   So it
requires clarification from the AHJ and/or IU as to what is applicable.  But
if there is no direction we use it as the basis.
>
> Also note that the 75% reduction is "up to 75%" and "as approved", so it's
not an automatic reduction.
>
>
> Craig L. Prahl, CET
> Fire Protection Specialist
> Mechanical Department
> CH2MHILL
> Lockwood Greene
> 1500 International Drive
> PO Box 491, Spartanburg, SC  29304-0491
> Direct - 864.599.4102
> Fax - 864.599.8439
> [email protected]
> http://www.ch2m.com
>
>
> -----Original Message-----
> From: [email protected]
[mailto:[email protected]] On Behalf Of Ron Greenman
> Sent: Thursday, September 03, 2009 3:40 PM
> To: [email protected]
> Subject: Fire Flow
>
> When determining tank size on a property supplied only from a tank is the
sprinkler demand added to fire flow as a cumulative fire flow or is it
considered part of the fire flow? And if the former does the hose stream
need to be added or is it negated by the fact that the tank is already
supplying the hydrants? Example: 30,000 sqft fully sprinklered building
requires a fire flow (reduced 75% then rounded up to the minimum) of 1500
gpm for 2 hours requiring a 180,000 gallon tank. The sprinkler demand is 650
gpm plus a 250 gpm hose stream for one hour for a total of 54,000 gallons.
Is the 54K gallons included in whole or in part with the fire flow storage
or is it added? Thanks.
>
> --
> Ron Greenman
> Instructor
> Fire Protection Engineering
> Bates Technical College
> Tacoma, WA
>
> Member:
> SFPE, ASCET, NFPA, AFSA, NFSA AFAA
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> For Technical Assistance, send an email to: [email protected]
>
> To Unsubscribe, send an email to:[email protected]
> (Put the word unsubscribe in the subject field)
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> For Technical Assistance, send an email to: [email protected]
>
> To Unsubscribe, send an email to:[email protected]
> (Put the word unsubscribe in the subject field)
>



-- 
Ron Greenman
Instructor
Fire Protection Engineering
Bates Technical College
Tacoma, WA

Member:
SFPE, ASCET, NFPA, AFSA, NFSA AFAA
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to