I agree with Ron Fletcher.  They are 2 individual cases.  Your water
storage tank size is based on the greater demand.  I have not found
anywhere that states the two are additive.

Travis Mack
> Jim,
>
> Let's say semi-rural. The fire department is coming but all the water,
> for them and the sprinklers is from the tank. The actual flow has been
> determined by the fire marshal and he has reduced the IFC requirements
> in consideration of the sprinklers and has also actually reduced the
> duration to one hour. No problem there. My question, which I'm
> probably just not stating clearly, has to do with the amount of stored
> water. I need 1500 gallons a minute at 20 psi, supplied by a fire
> pump, for 60 minutes so that my storage has to be 90,000 gallons. I
> also need 650 gpm for the sprinklers plus 250 gpm for the hose stream,
> again for an hour or an additional 54,000 gallons when calculated
> separately. Do I need to add this 54,000 gallons to the 90,000 gallons
> in whole or part for total storage? Is the 54,000 gallons part of the
> 90,000 gallons? I'm used to urban areas where duration is considered
> unlimited as it applies to fire flow and so not part of the
> supply/demand equation.
>
> On Thu, Sep 3, 2009 at 1:10 PM, Jim
> Johnston<[email protected]> wrote:
>> Ron,
>>
>> Is this in a rural setting?  As Craig suggested lots of times you only
>> need
>> to size for the sprinkler demand and associated hose allowance with this
>> scenario.  It sounds like your project is in a rural setting, IFC
>> Appendix B
>> B103.3 allows the use of NFPA 1142 in areas without water supplies
>> provided
>> that the AHJ accepts it.  I have utilized this numerous times in Eastern
>> Washington and Oregon, you still need to provide enough hydrants though
>> but
>> you don't have to provide the IFC required fire flow for the particular
>> building.
>>
>> Jim Johnston, P.E.
>> Fire Protection Engineer
>> Inland Fire Protection, Inc
>> 1100 Ahtanum Road
>> Yakima, WA 98903
>> Phone 509-248-4471
>> Fax 509-248-1180
>> [email protected]
>>
>>
>> -----Original Message-----
>> From: Ron Greenman [mailto:[email protected]]
>> Sent: Thursday, September 03, 2009 12:57 PM
>> To: [email protected]
>> Subject: Re: Fire Flow
>>
>> The reduction has already been approved. The fire flow demand is to
>> supply a hydrant on the property. My question is (and no fire marshal
>> to ask today),is the sprinkler demand included or need to be added?
>> This tank supplies all fire water needs (no jokes-I know what you're
>> all thinking) for this property.
>>
>> On Thu, Sep 3, 2009 at 12:50 PM, <[email protected]> wrote:
>>> If you're talking about the fire flows referenced in the IFC, Appendix
>>> B,
>> this seems to be an AHJ or IU call.  For the most part when the building
>> is
>> fully sprinklered only the sprinkler system demand and hose stream
>> demands
>> are used for water tank sizing.  I've not had one AHJ or IU apply the
>> fire
>> flow section of the IFC to the water supply when those conditions exist.
>>  Now when a building is not protected I have had this section of the IFC
>> applied.  However note that this section is not mandatory and is not a
>> part
>> of the actual Code.  See wording at the top of the first page.   So it
>> requires clarification from the AHJ and/or IU as to what is applicable.
>>  But
>> if there is no direction we use it as the basis.
>>>
>>> Also note that the 75% reduction is "up to 75%" and "as approved", so
>>> it's
>> not an automatic reduction.
>>>
>>>
>>> Craig L. Prahl, CET
>>> Fire Protection Specialist
>>> Mechanical Department
>>> CH2MHILL
>>> Lockwood Greene
>>> 1500 International Drive
>>> PO Box 491, Spartanburg, SC  29304-0491
>>> Direct - 864.599.4102
>>> Fax - 864.599.8439
>>> [email protected]
>>> http://www.ch2m.com
>>>
>>>
>>> -----Original Message-----
>>> From: [email protected]
>> [mailto:[email protected]] On Behalf Of Ron
>> Greenman
>>> Sent: Thursday, September 03, 2009 3:40 PM
>>> To: [email protected]
>>> Subject: Fire Flow
>>>
>>> When determining tank size on a property supplied only from a tank is
>>> the
>> sprinkler demand added to fire flow as a cumulative fire flow or is it
>> considered part of the fire flow? And if the former does the hose stream
>> need to be added or is it negated by the fact that the tank is already
>> supplying the hydrants? Example: 30,000 sqft fully sprinklered building
>> requires a fire flow (reduced 75% then rounded up to the minimum) of
>> 1500
>> gpm for 2 hours requiring a 180,000 gallon tank. The sprinkler demand is
>> 650
>> gpm plus a 250 gpm hose stream for one hour for a total of 54,000
>> gallons.
>> Is the 54K gallons included in whole or in part with the fire flow
>> storage
>> or is it added? Thanks.
>>>
>>> --
>>> Ron Greenman
>>> Instructor
>>> Fire Protection Engineering
>>> Bates Technical College
>>> Tacoma, WA
>>>
>>> Member:
>>> SFPE, ASCET, NFPA, AFSA, NFSA AFAA
>>> _______________________________________________
>>> Sprinklerforum mailing list
>>> [email protected]
>>> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>>>
>>> For Technical Assistance, send an email to: [email protected]
>>>
>>> To Unsubscribe, send an email
>>> to:[email protected]
>>> (Put the word unsubscribe in the subject field)
>>> _______________________________________________
>>> Sprinklerforum mailing list
>>> [email protected]
>>> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>>>
>>> For Technical Assistance, send an email to: [email protected]
>>>
>>> To Unsubscribe, send an email
>>> to:[email protected]
>>> (Put the word unsubscribe in the subject field)
>>>
>>
>>
>>
>> --
>> Ron Greenman
>> Instructor
>> Fire Protection Engineering
>> Bates Technical College
>> Tacoma, WA
>>
>> Member:
>> SFPE, ASCET, NFPA, AFSA, NFSA AFAA
>> _______________________________________________
>> Sprinklerforum mailing list
>> [email protected]
>> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>>
>> For Technical Assistance, send an email to: [email protected]
>>
>> To Unsubscribe, send an email
>> to:[email protected]
>> (Put the word unsubscribe in the subject field)
>>
>> _______________________________________________
>> Sprinklerforum mailing list
>> [email protected]
>> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>>
>> For Technical Assistance, send an email to: [email protected]
>>
>> To Unsubscribe, send an email
>> to:[email protected]
>> (Put the word unsubscribe in the subject field)
>>
>
>
>
> --
> Ron Greenman
> Instructor
> Fire Protection Engineering
> Bates Technical College
> Tacoma, WA
>
> Member:
> SFPE, ASCET, NFPA, AFSA, NFSA AFAA
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> For Technical Assistance, send an email to: [email protected]
>
> To Unsubscribe, send an email to:[email protected]
> (Put the word unsubscribe in the subject field)
>


-- 


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to