I don't have a quick answer, but out of curiosity, how far does the FD need to 
go to get another water source?
 
BTW, the hose allowance in the sprinkler design must surely be part of the 
fireflow.

Dave 

David A. de Vries, P.E., CSP 
Firetech Engineering Incorporated 




--- On Thu, 9/3/09, Ron Greenman <[email protected]> wrote:


From: Ron Greenman <[email protected]>
Subject: Fire Flow
To: [email protected]
Date: Thursday, September 3, 2009, 2:39 PM


When determining tank size on a property supplied only from a tank is
the sprinkler demand added to fire flow as a cumulative fire flow or
is it considered part of the fire flow? And if the former does the
hose stream need to be added or is it negated by the fact that the
tank is already supplying the hydrants? Example: 30,000 sqft fully
sprinklered building requires a fire flow (reduced 75% then rounded up
to the minimum) of 1500 gpm for 2 hours requiring a 180,000 gallon
tank. The sprinkler demand is 650 gpm plus a 250 gpm hose stream for
one hour for a total of 54,000 gallons. Is the 54K gallons included in
whole or in part with the fire flow storage or is it added? Thanks.

-- 
Ron Greenman
Instructor
Fire Protection Engineering
Bates Technical College
Tacoma, WA

Member:
SFPE, ASCET, NFPA, AFSA, NFSA AFAA
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to