Thank you all. I was thinking most demand only (fire flow requirement)
and mop-up with the leftovers. Now I'm much more comfortable with
that.

On Thu, Sep 3, 2009 at 2:16 PM, <[email protected]> wrote:
> 11.1.5.1 An allowance for inside and outside hose shall not be required where 
> tanks supply
> sprinklers only.
>
> COMMENTARY:
> With regard to 11.1.5.1, where tanks supply sprinklers only, the hose stream 
> requirements
> need not be added when sizing the tank. For example, if the tank supplies a 
> system that is
> required to be equipped with small hose stations, the demand of the hose 
> stations needs to
> be included when sizing the tank. For related commentary when sizing pumps, 
> see 11.1.5.3.
>
>
> 11.1.5.4 Water allowance for outside hose shall be added to the sprinkler 
> requirement at the
> connection to the city main or a yard hydrant, whichever is closer to the 
> system riser.
>
> COMMENTARY:
> With regard to 11.1.5.4, if no inside hose connections are provided, the 
> outside hose requirement
> is the value in the third column from the left, Total Combined Inside and 
> Outside Hose,
> in Table 11.2.3.1.2. This relatively small quantity of water is apportioned 
> to the fire department
> to allow for final and complete extinguishment of the fire. The flow rate 
> established in Table
> 11.2.3.1.2 can be added to the hydraulic calculations at the connection to 
> the city water main
> or yard hydrant at the prevailing system pressure. The outside hose stream 
> water typically
> receives its pressure from the fire department apparatus.
>
> Craig L. Prahl, CET
> Fire Protection Specialist
> Mechanical Department
> CH2MHILL
> Lockwood Greene
> 1500 International Drive
> PO Box 491, Spartanburg, SC  29304-0491
> Direct - 864.599.4102
> Fax - 864.599.8439
> [email protected]
> http://www.ch2m.com
>
>
> -----Original Message-----
> From: [email protected] 
> [mailto:[email protected]] On Behalf Of Gregg Fontes
> Sent: Thursday, September 03, 2009 5:10 PM
> To: [email protected]
> Subject: RE: Fire Flow
>
> NFPA 13 2002 Edition 11.2.3.1.3; "An allowance for inside and outside hose 
> shall not be required where the tanks supply sprinklers only."  Since the 
> tank supplies both site fire hydrant and fire sprinklers, it needs to 
> accommodate both the site and sprinklers.  The questions I think needs to be 
> asked is for the site allowance, do you use the 1500 gpm (which is my guess) 
> or the 250 gpm hose allowance?
>
> Thanks,
> Gregg Fontes
> Cen-Cal Fire Systems, Inc.
> (209)334-9119
>
> -----Original Message-----
> From: [email protected]
> [mailto:[email protected]] On Behalf Of Ron Greenman
> Sent: Thursday, September 03, 2009 1:33 PM
> To: [email protected]
> Subject: Re: Fire Flow
>
> Far. And yes the fire flow accommodates the demand for both. I'm trying to 
> figure how much storage is needed.
>
> On Thu, Sep 3, 2009 at 1:30 PM, David de Vries<[email protected]>
> wrote:
>> I don't have a quick answer, but out of curiosity, how far does the FD
> need to go to get another water source?
>>
>> BTW, the hose allowance in the sprinkler design must surely be part of
>> the
> fireflow.
>>
>> Dave
>>
>> David A. de Vries, P.E., CSP
>> Firetech Engineering Incorporated
>>
>>
>>
>>
>> --- On Thu, 9/3/09, Ron Greenman <[email protected]> wrote:
>>
>>
>> From: Ron Greenman <[email protected]>
>> Subject: Fire Flow
>> To: [email protected]
>> Date: Thursday, September 3, 2009, 2:39 PM
>>
>>
>> When determining tank size on a property supplied only from a tank is
>> the sprinkler demand added to fire flow as a cumulative fire flow or
>> is it considered part of the fire flow? And if the former does the
>> hose stream need to be added or is it negated by the fact that the
>> tank is already supplying the hydrants? Example: 30,000 sqft fully
>> sprinklered building requires a fire flow (reduced 75% then rounded up
>> to the minimum) of 1500 gpm for 2 hours requiring a 180,000 gallon
>> tank. The sprinkler demand is 650 gpm plus a 250 gpm hose stream for
>> one hour for a total of 54,000 gallons. Is the 54K gallons included in
>> whole or in part with the fire flow storage or is it added? Thanks.
>>
>> --
>> Ron Greenman
>> Instructor
>> Fire Protection Engineering
>> Bates Technical College
>> Tacoma, WA
>>
>> Member:
>> SFPE, ASCET, NFPA, AFSA, NFSA AFAA
>> _______________________________________________
>> Sprinklerforum mailing list
>> [email protected]
>> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>>
>> For Technical Assistance, send an email to: [email protected]
>>
>> To Unsubscribe, send an email
>> to:[email protected]
>> (Put the word unsubscribe in the subject field)
>> _______________________________________________
>> Sprinklerforum mailing list
>> [email protected]
>> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>>
>> For Technical Assistance, send an email to: [email protected]
>>
>> To Unsubscribe, send an email
>> to:[email protected]
>> (Put the word unsubscribe in the subject field)
>>
>
>
>
> --
> Ron Greenman
> Instructor
> Fire Protection Engineering
> Bates Technical College
> Tacoma, WA
>
> Member:
> SFPE, ASCET, NFPA, AFSA, NFSA AFAA
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> For Technical Assistance, send an email to: [email protected]
>
> To Unsubscribe, send an email to:[email protected]
> (Put the word unsubscribe in the subject field)
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> For Technical Assistance, send an email to: [email protected]
>
> To Unsubscribe, send an email to:[email protected]
> (Put the word unsubscribe in the subject field)
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> For Technical Assistance, send an email to: [email protected]
>
> To Unsubscribe, send an email to:[email protected]
> (Put the word unsubscribe in the subject field)
>



-- 
Ron Greenman
Instructor
Fire Protection Engineering
Bates Technical College
Tacoma, WA

Member:
SFPE, ASCET, NFPA, AFSA, NFSA AFAA
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to