11.1.5.1 An allowance for inside and outside hose shall not be required where 
tanks supply
sprinklers only.

COMMENTARY:
With regard to 11.1.5.1, where tanks supply sprinklers only, the hose stream 
requirements
need not be added when sizing the tank. For example, if the tank supplies a 
system that is
required to be equipped with small hose stations, the demand of the hose 
stations needs to
be included when sizing the tank. For related commentary when sizing pumps, see 
11.1.5.3. 


11.1.5.4 Water allowance for outside hose shall be added to the sprinkler 
requirement at the
connection to the city main or a yard hydrant, whichever is closer to the 
system riser.

COMMENTARY:
With regard to 11.1.5.4, if no inside hose connections are provided, the 
outside hose requirement
is the value in the third column from the left, Total Combined Inside and 
Outside Hose,
in Table 11.2.3.1.2. This relatively small quantity of water is apportioned to 
the fire department
to allow for final and complete extinguishment of the fire. The flow rate 
established in Table
11.2.3.1.2 can be added to the hydraulic calculations at the connection to the 
city water main
or yard hydrant at the prevailing system pressure. The outside hose stream 
water typically
receives its pressure from the fire department apparatus.

Craig L. Prahl, CET   
Fire Protection Specialist
Mechanical Department
CH2MHILL
Lockwood Greene
1500 International Drive
PO Box 491, Spartanburg, SC  29304-0491
Direct - 864.599.4102
Fax - 864.599.8439
[email protected]
http://www.ch2m.com 


-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of Gregg Fontes
Sent: Thursday, September 03, 2009 5:10 PM
To: [email protected]
Subject: RE: Fire Flow

NFPA 13 2002 Edition 11.2.3.1.3; "An allowance for inside and outside hose 
shall not be required where the tanks supply sprinklers only."  Since the tank 
supplies both site fire hydrant and fire sprinklers, it needs to accommodate 
both the site and sprinklers.  The questions I think needs to be asked is for 
the site allowance, do you use the 1500 gpm (which is my guess) or the 250 gpm 
hose allowance?  

Thanks,
Gregg Fontes
Cen-Cal Fire Systems, Inc.
(209)334-9119

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Ron Greenman
Sent: Thursday, September 03, 2009 1:33 PM
To: [email protected]
Subject: Re: Fire Flow

Far. And yes the fire flow accommodates the demand for both. I'm trying to 
figure how much storage is needed.

On Thu, Sep 3, 2009 at 1:30 PM, David de Vries<[email protected]>
wrote:
> I don't have a quick answer, but out of curiosity, how far does the FD
need to go to get another water source?
>
> BTW, the hose allowance in the sprinkler design must surely be part of 
> the
fireflow.
>
> Dave
>
> David A. de Vries, P.E., CSP
> Firetech Engineering Incorporated
>
>
>
>
> --- On Thu, 9/3/09, Ron Greenman <[email protected]> wrote:
>
>
> From: Ron Greenman <[email protected]>
> Subject: Fire Flow
> To: [email protected]
> Date: Thursday, September 3, 2009, 2:39 PM
>
>
> When determining tank size on a property supplied only from a tank is 
> the sprinkler demand added to fire flow as a cumulative fire flow or 
> is it considered part of the fire flow? And if the former does the 
> hose stream need to be added or is it negated by the fact that the 
> tank is already supplying the hydrants? Example: 30,000 sqft fully 
> sprinklered building requires a fire flow (reduced 75% then rounded up 
> to the minimum) of 1500 gpm for 2 hours requiring a 180,000 gallon 
> tank. The sprinkler demand is 650 gpm plus a 250 gpm hose stream for 
> one hour for a total of 54,000 gallons. Is the 54K gallons included in 
> whole or in part with the fire flow storage or is it added? Thanks.
>
> --
> Ron Greenman
> Instructor
> Fire Protection Engineering
> Bates Technical College
> Tacoma, WA
>
> Member:
> SFPE, ASCET, NFPA, AFSA, NFSA AFAA
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> For Technical Assistance, send an email to: [email protected]
>
> To Unsubscribe, send an email 
> to:[email protected]
> (Put the word unsubscribe in the subject field) 
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> For Technical Assistance, send an email to: [email protected]
>
> To Unsubscribe, send an email 
> to:[email protected]
> (Put the word unsubscribe in the subject field)
>



--
Ron Greenman
Instructor
Fire Protection Engineering
Bates Technical College
Tacoma, WA

Member:
SFPE, ASCET, NFPA, AFSA, NFSA AFAA
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to