Thank you. If you can't get under the curve because of hose allowance, then I'd have you provide OH II for the room and reduce the hose allowance to obtain a safety factor.
I don't see many projects where 29 gallons make an impact. On the few that I do see we have allowed a reduction in hose demand in favor of sprinkler protection. Most fires at sprinkler protected buildings are out by the time the first responders arrive and no hose demand is needed for suppression activities. David Autry Plans Examiner Nebraska State Fire Marshal's Office 246 S. 14th Street Lincoln, NE 68508 402-471-9659 402-471-3118 fax www.sfm.ne.gov ** Note new email address: [email protected] -----Original Message----- From: [email protected] [mailto:[email protected]] On Behalf Of Greg McGahan Sent: Tuesday, October 27, 2009 8:11 AM To: [email protected] Subject: RE: mercantile area in a bar Let me elaborate. 1) we can make it work either way but there is an impact. 2) it is already installed improperly and we are correcting the head installation (incorrect sidewall orientation and spacing) 3) I would usually assume OH2 in a new install and never ask a question. BUT, since this one is tricky I thought it a good time to ask the question. Greg McGahan Operations Manager Living Water Fire Protection 1160 McKenzie Road P.O. Box 877 Cantonment, Florida 32533 (850) 937.1850 | Fax (850) 937.1852 | CellĀ (850) 554.3231 [email protected] _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field)