With the limited fire loading, you could ask if AHJ would agree to OH1 instead of II ?
And- what Dave said. glc -----Original Message----- From: [email protected] [mailto:[email protected]] On Behalf Of Autry, David Sent: Tuesday, October 27, 2009 9:32 AM To: [email protected] Subject: RE: mercantile area in a bar Thank you. If you can't get under the curve because of hose allowance, then I'd have you provide OH II for the room and reduce the hose allowance to obtain a safety factor. I don't see many projects where 29 gallons make an impact. On the few that I do see we have allowed a reduction in hose demand in favor of sprinkler protection. Most fires at sprinkler protected buildings are out by the time the first responders arrive and no hose demand is needed for suppression activities. David Autry Plans Examiner Nebraska State Fire Marshal's Office 246 S. 14th Street Lincoln, NE 68508 402-471-9659 402-471-3118 fax www.sfm.ne.gov ** Note new email address: [email protected] _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field)