I would refer to NFPA 13 (2007) section 8.15.13.  This refers to the
obstruction of the vertical member to the developing spray pattern.  I
would reduce the square footage per head to protect this area.

Ryan Hinson
Burns & McDonnell
Direct: 952-656-6003 Ext 3662

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of
Richardson, R
Sent: Thursday, October 29, 2009 2:55 PM
To: [email protected]
Subject: Sound Baffles

We are reviewing a proposal to install sound baffles suspended from the
roof, and evaluating obstructions to sprinkler discharge.   The baffles
are 2 ft. deep panels hung vertically every ft.  The top of the baffle
is just over 18 ins. From the sprinkler heads so NFPA 13 would indicate
that there is no obstruction problem because they do not exceed the 4
ft. obstruction trigger for obstruction more than 18 in. below the
heads. 

However, the panels are every foot and it sure seems like a significant
obstruction, but the installation does not violate NFPA 13 for
obstructions.

Has anyone ever dealt with this issue and offer any insight.

Thanks,

Rich Richardson
Seattle Fire Department



_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email
to:[email protected]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to